based on the example bellow
http://www.lothar-miller.de/s9y/categories/46-Encoder
i need to use the INDEX input of the encoder, sometimes.
From what i understand, when needed, the INDEX pulse should clear the
position counter. Is it as simple as this?
double register INDEX input
dr_INDEX <= dr_INDEX(0) & INDEX    when rising_edge(CLK);
Have an Enable input, and
        -- index allow to clear count
        if ENA then
            if dr_INDEX = "01" then
                p <= 0;
            end if;
        end if;
T
Moderator (Company: Titel) #6363331
You're on the right way...
I would also check wether the counter value is (nearby) 0 at that point.
Because when not, then you have lost counts in the previous round. That
may be a reason to raise an ERROR flag.
Guest #6366653
Thanks for reply.
A bit more education required. :)
Nearby zero(0) means what exactly? I am getting confused with the signed
integer.
-- 32-bit signed integer range: -2147483647 to +2147483647
ENC_POS <= std_logic_vector(to_signed(p,32));
check when p is nearby 0? (p > X or p < -X, where X is 10? 100? 1000?)
check at the edges? (-2147483647 to +2147483647)
i was thinking like
        if ENA then
                if p > 1000 or p < -1000 then
                    EQEP_ERR <= '1';
                    p <= 0;
                else
                    EQEP_ERR <= '0';
                    p <= 0;
                end if;
            end if;
        end if;
T
Moderator (Company: Titel) #6371271
That depends on what you would allow for an deviation. Usually it must
be 0.
You will not be able to buy an encoder with somewhat 500000000 lines per
revolution. So you will never ever reach the limit of an integer number.
Because my code does a quadruple evaluation all of the 4 edges in one
"step" are counted. Usually the index pulse is 1 step wide, so at either
"end" of the index pulse the counters value is up to 3 or down to -3.
So I would raise the error flag when the counter >3 or <-3 at the
"begin" (=rising edge) of the index pulse.
        if ENA then
                p <= 0;
                EQEP_ERR <= '0';
                if p>3 or p<-3 then
                    EQEP_ERR <= '1';
                end if;
            end if;
        end if;
Guest #6632248
i come close to to use the encoder description, along with the error
detection.
Am running some simulations for building confidence and noticed that,
I get eqer_err active when evaluating everything on the risedge of
Index. see eqep_err image attached.
But if i clear the position count on the risedge of Index, and do the
checks on the falledge of Index, then it looks ok. see attached image
epeq_no_err
if ENA_I then
   if dr_I = "01" then
      pos_cnt <= 0;
   end if;
   if dr_I = "10" then
      if pos_cnt>3 or pos_cnt<-3 then
         err <= '1';
      else
         err <= '0';
      end if;
   end if;
end if;
What do you think?
Moderator (Company: Titel) #6632425
Sounds very like the traditional latency error. Just dig inside your
module and have a look for the pos_cnt that causes the error. Look at
the dr_I at the same time...
> What do you think?
The problem is located outside the posted piece of code.
Guest #6634633
Thanks for the reply.
Am attaching the file in use. It should look very, very familiar..
except the async reset.
Am also attaching a more detailed simulation (pre-synth). I guess the
err is triggered because value 37(in this specific sim) is used for the
check(?)
On another note, i fail to understand how clearing the pos_cnt and
checking it on the same edge of the index will produce an error (even
though the attached sim actually does..). the value of the pos_cnt while
checking it, should be zero, right?
Moderator (Company: Titel) #6634949
SparkyT wrote:
> I guess the err is triggered because value 37(in this specific sim) is
> used for the check(?)
No, its triggered because 25 in pos_cnt is more than 3 in this line:
    err <= '1';
> i fail to understand how clearing the pos_cnt and checking it on the
As I said: latency.
You must dig in much deeper in the behaviour of signals in processes!
To say it simple: they do not change their value throughout the process.
They keep their "start values" from the beginning of the process to the
end of the process.
When you assign a new value to a signal them the signal does not change
its value! The new value is just "memorized" until the end of the
process. Then it is assigned to the signal.
So in your specific "problem" it looks like that:
if ENA_I then          -- Sim: ENA_I is 1
  if dr_I = "01" then  -- Sim: dr_I is 01
    pos_cnt <= 0;      -- kind of magic here: pos_cnt does not change its value as it is a signal!
                       -- the assinged value is not updated till the end of the process!
      err <= '0';
      if pos_cnt>3 or pos_cnt<-3 then -- Sim: pos_cnt is still 25 here and throughout the whole process!
         err <= '1';  -- obviously we will end up here... :-(
This kind of behaviour is really nice, when you are used to it. But
first you must "get the trick" somehow...  ;-)
Start a new thread