Forum: µC & Digital Electronics OpenHR20: Firmware for Honeywell Rondostat HR20E
Author: Jiri Dobry (jdobry)
1. It is true on version 1.0, not in current code
2. you can increase P_factor, but major problem is that you not have
final "sumError" and wrong valve_center. If you increase P factor, it
will increase response of valve to error, but it will probably oscilate
If you really  need to know what happen, please use converter from 3v3
to RS232 or usb and create log. Without log you know nothing and usualy
have obly bad feeling.
3. it is 50%
4. It is normal after restart or battery change. Where is problem on
normal continous functionality.
5. You made deductions, but you don't know facts. Make logs and you will
see.
Author: Richard G. (gggggg)
Jiri: RS232 has been/ is on plan for this weekend ;-)
1 Rev.309 I-Part:
Allow integration = integration time set to 4 minmutes, if
error==0 OR sign of error changes OR direction of valve movement
changes...
a) ==> so this means, that if there is a constant error, the error is
added max 4 times (once a minute) to sumerror ?
b) The max impact on PI then is 4*error*I
2 Under which conditions would you change P3 and und when P factor
Richard G: last SVN version 311 have completely another model of windup
protection. Try it. You can enlarge P_factor to 6-12 ( default is 8 now
Jiri: I'm just trying 317. I have a problem with hyperterminal. It does
not catch the CR (just LineFeed)...looks like this
V:OpenHR20 17.1 Mar  5 2011 20:02:26 $Rev$
                                          D: d5 01.01.10 12:34:23 - V: 58 I: 236
4 S: 2300 B: 2644 Is: fe00 X
                            D: d5 01.01.10 12:37:11 - V: 58 I: 2364 S: 2300 B: 2
644 Is: fe00
any idea ?
Richard G:
Correct, code using UNIX end of lines to save flash and communication
size. Please use terminal which is able accept it. I recommend putty and
set it.
PS: MS hyperterminal is piece of ..... except other problems it was many
years unfixed bug, when you use bar to shift window contend, it change
contend
NOTE: SVN rev 318 contain biggest change after more than year, it is not
fully tested now. If you want to have rock stable code, please use
release 1.0 (SVN rev 285)
Jiri; Here is the protokoll from last night. Params of my valve:
  /* 0a */  {52,         30,        0,      100},   //!< valve_min
  /* 0b */  {60,         45,        0,      100},   //!< valve_center
  /* 0c */  {90,         80,        0,      100},   //!< valve_max
- It took from 22:42 until 1:50 until I part starts.
- I part does not increase until 2:29, no impact on V so far
- next I increase 3:37, no impact on V
- next I increase 4:09, no impact on V
- next I increase 4:13, no impact on V
- next I increase 4:17, no impact on V
- 5:01 my encoder simulation is runnning and needs about 15s to reach
the previous S=23,0"C again.
1.??? I thought that it takes 10s after wheel stops before PID is
updated ???
- next I increase 5:05, no impact on V
- next I increase 6:49, 1% impact on V
Resumee:
2. It starts increasing V, neverthelsess room is 1,75°C higer then S
3. Impact of I param is week. It seems that sumerror is increasing to
slow and I param is to low.
4. V on LCD is 1% less than on COM
Richard G:
What is your P, P3, I factors ?
Why you change setting in code, you can use service menu or terminal
(commands G,S)
1) it take 10sec, because wait to final setting. It is mornal if human
use wheel, that it not have machine precision. You ca see it in
CTL_temp_change_inc
2) again, what is P, P3, I ?
3) normaly it my valve it take 12-24 hours to find sumerror (I impact).
It must be slow, you can try in rfmsrc/doc/PI_tuning what happen on big
gain. I hope that 318 is faster without impact to windup (do yyou know
what is it?)
4) com show wanted valve, LCD show truncated real position. In real
world, I want 29, com show 29, but real position after valve stop is
28.99 -> LCD show 28. Reason is allow see motor movements on LCD in real
time.
Jiri: PI params are standard, yes I understand windup, but 24 hours to
find error is to long, because setpoint is changed more often
- ad 1) This would help to prevent update during wheel action:
controller.c 150:
if (((PID_update_timeout == 0)
&& (PID_force_update==-1)
) ||(PID_force_update==0)) {
- How can we prevent 2 ?
no 24 hours is not too long, it persist after change setpoint
for remove delay, please change in CTL_temp_change_inc
PID_force_update = 10;
to =>
PID_force_update = 1;
Author: Marco G. (stan)
I recommend HTerm as terminal program for Windows:
http://www.der-hammer.info/terminal/
Thanks Marco !
Thanks for the hints Jiri:
PID_force_update = 1; forces update
But we want prevent update during wheel move:
This prevents "normal" update (every 4 minutes) until 10s after wheel
stops !
Author: Chris (Guest)
Hi!
How do I find the "correct" values for minimum and maximum vent position
(0x0A, 0X0C)?
Maybe a feature to "live-control" the valve would be nice.
Chris
- set Max=Center= Min+1, wait until heater is cool
- increase all params +1 until hater starts getting warm
- set Min e.g. 5 lower and center 10-20 higer. leave max at 80
You don't precision values for valve_min a valve_max. It is used only as
protection to not move valve to hard limits.
Does the adaptation which is done after mounting have any influence on
the min and max values?
Jiri just did some redesign on that, but I think NO.
Calculation in controller.c works with center position. Only I part
(sumerror) can't increase when MIN/MAX are reached ...
This is why I set the center closer to MIN ...
Jiri - do you simulate your PI ? Do you have an .xls maybe ??
Richard G: simulation you can find here rfmsrc/doc/PI_tuning.ods
Thanks Jiri, I saw that before, but there is no formula for the
simulation in the Excel sheet ??
BTW: Where do I find Karims latest Version of his openHR20Suite. I only
found Version 0.2.4.23954 posted on page 2 ??
Author: Karim L. (louk)
@Richard,
the last released Version V 0.2.4.23954 of openHR20Suite can be found
here http://embdev.net/topic/118781#1157863, but I think, it will not be
completely data compatibel. It seemed to me, that no body was interested
in this program and I had to do a lot of other stuff, so I had not the
time and motivation to keep it uptodate. But since I am still interested
in this project, I need to look, wether I am able to compile and flash
the latest Version of OpenHR20 firmware an check, what has to be
modified in the Suite SW. May be I can take a look at it on next
weekend.
Hi Karim, I have this Version runnning since last weekend. Execpt the
difference in the EEProm names it seams to work. But once I had a jam on
COM - no more data transfer, which just could be released by using putty
to send some manual commands...
The only thing, that bothers me a bit is, that I had to install .NET35.
Usally nearly every PC has some .net version installed. Very often it is
2.x ...
Would it be possible to parse the appropriate eeprom.h. This way one
could only copy this file e.g. into the program dir and would be up to
date. The second thing is that one has to configure which #defines were
set ..
Since the program uses WPF technology, it requires .NET V>=3.0. If you
want to see a flash movie, you have to install the appropriate flash
player, same for Silverlight or here .NET. That is how it works and the
installation is only once required. The installed .NET framework
versions can be found here C:\WINDOWS\Microsoft.NET\Framework and
generally you have anyway several versions on your PC.
It would be possible to read the eeprom.h file but it has a very
processing unfriendly format, which is errorness. It would be better, to
have an xml file, which contains the required definitions and on
modifications in eeprom.h, everybody could edit the changes to this xml,
which will be loaded by the Suite. Different versions of the eeprom
data/HR20 firmware could be handled by this method as well. But I can't
promise to program that one of these days.
@Karim: Would be nice ! Put your tool into trunk !!!
@Jiri:
My experience with 319 controller in a 15m² room during some nights with
no persons in it and predifined Params (except MIN=52,CENTER=60):
1 I Part takes about 2 hours until reaction is seen on temp. Maybe I can
be increased ??
2 I think it is important to set the MIN value close to the real CLOSE
of the valve, beacuse this limits I part
3 I is still increasing/decreasing even if the temp gradient has already
changed (from falling to increasing or vice versa) ...
4 suggestion:
Why don't we stop increasing/decreasing sumerror, as soon as the
gradient of the real temp changes to the wanted direction ?
5 D part missing:
In my case, the Valve runs on accu with permanent charge of 5mA via data
connection.
I need something, that reacts when e.g. a person enters the room or a
heating source like a PC is started ... waht do xou suggest ?
6 I have no idea of what is the impact/aim of P3 - can you please
explain ?
7 Regarding simulation: I saw the .ods before, but there is no formula
for the simulation in the Excel sheet ?? Do you have something like that
... how are you doing it ?
8 Am I right ? On COM we don't see every move of valve, because of
integer value ? Why not put valve*10 to display and COM ?
1. I thing not, you can just create oscilations
2. problem is that MIN value float after every calibration. And you need
value below to insure close and prohibit unlimited heating
3. do you have better idea to protect to windup and allow integration if
valve still in position and you have permanent offset ?
4. If you want it, please use version 1.0. Problem is, that it increase
oscilations on some situations (in my case only in one room)
5. D is removed because usually we have only batteries, and it have
problem with transport delay (it take more than 20 minutes till you are
able to see effect when valve close)
6 regulation characteristic of valve is non linear with unknown
"center". If you use big P you will get oscilations. If you use low P,
you are not sufficient reaction if calculated "center" (I part) is too
far for real. Therefore you need compromise, small reaction for small
errors and big for big.
7. .ods contain simulation formulas, you can convert it into excel
8. COM show final position on every valve move start
add to 4) I was wrong. It is realy used on release 1.0. I remove it,
because it not solve windup completely. Normaly you have more heat
sources (ex: sun) and it can create any temperature profile independent
to valve. It is replaced by another idea, but it is compatible. I plan
to use longer temperature history than only previous.
ad4) but you agree, that a further increase after temp gradient changed
leads to a unnecessary high I part ?
ad6) what is the max P3 before oscillation starts, can it be increased
ad7) I used excel2010 to open it, but did not see any formula. You say
convert ?? How ?
ad8) I thought smallest move is 0,75%
4) right, but with side effect, it slow down integration if you have
small offset to wanted temperature (ex 0.5-1 degree).
7) what is in rows P-V ? If just number please send compliment to
Redmond and download OpenOffice
8) it move valve in 1% steps. You need hysteresis to inhibit move for ex
from 40 to 41% if result of controller calculation is 40.49 and 40.51
4) but you inject one idea to my bain, thanks
Welcome ;-) looking forward to it
ad6) what would be the max for P3 before oscillation will start ?
6a) why one doesnt use P^4 /5 then ?
Jiri: R320 controller.c 151 ... still missing ... see: 2011-03-06 10:54
&& (PID_force_update==-1))
Please quick explain the change 319>320 ??? THX
Richard,
I made another (shorter in flash) solution for (PID_force_update==-1)
now. It is in SVN
about 319>320
Basic idea is:
after wanted temperature change or after real temperature crossing wanted temperate (error from + to - and vice versa)
=> interator get some credit for not successful error curve direction
- if abs(error[t]) >= abs(error[t-2]) then credit=credit-1
- if credit == 0 then not allow update integrator
- temperature change must have same orientation like valve change in near history. Otherwise integrator is not updated.
- integrator is limited on valve_min and valve_max
real code is litle bit more complicated, it must contain more boundary
conditions and it is optimised for small flash, but idea is eqal
THX - I will try it
R325: e.g. Temp is to high: Some time after temp is sinking it stops
integrating = OK, but then sun shines into the room and temp is
increasing agein. In this case it should continue integrating - it seems
that credit was already=0 at this time ?!
controller line 315
    lastAbsError = absErr;
    last2AbsError = lastAbsError;
should'nt this be the other way round ?:
Example:
D: d5 01.01.10 12:00:17 A V: 52 I: 2380 S: 1700 B: 2459 Is: 0000
D: d5 01.01.10 12:04:17 A V: 52 I: 2390 S: 1700 B: 2459 Is: 0000
D: d5 01.01.10 12:06:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: 0000
D: d5 01.01.10 12:10:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: fd60
D: d5 01.01.10 12:14:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: fac0
D: d5 01.01.10 12:18:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: f820
D: d5 01.01.10 12:22:37 M V: 56 I: 2382 S: 2300 B: 2459 Is: f820
D: d5 01.01.10 12:26:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: f580
D: d5 01.01.10 12:30:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: f2e0
D: d5 01.01.10 12:34:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: f040
D: d5 01.01.10 12:38:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eda0
D: d5 01.01.10 12:42:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 12:46:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 12:50:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 12:54:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 12:58:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 13:02:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00
 I think latest here credit should be set to max_credit
D: d5 01.01.10 13:06:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 13:10:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 13:14:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00
e.g. something like:
if (((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) || (error16==0)
|| (absErr>last2AbsError))
 { //sign of last error16 != sign of current OR error16 == 0
Richard G:
Thanks for  last2AbsError=>lastAbsError order problem. Fixed.
But I can't set credit to max_credit on (absErr>last2AbsError)
condition. This is exactly condition which must be "pay" from credit.
Otherwise we will see windup again.
Prob is, that the error persists right now. Is stops about e000. The
influece of I&P is to low this way. Heater keeps on heating ... room is
getting hotter  ... with last2error > error it would only wind up if the
error is getting bigger and in this case we must do something about it
Is 327 just the copy prob or did you have a new idea ;-)
maybe we can do something like
if ...|| (last2error>(error+hysteresis(optional))) { if
credit<max.credit) credit+=1
on one valve since 2 day (since 321) I very often get E3 after flahing.
In this situations the valve head (sitting on the heater) is fully open
before installation.
If I set head valve manualy somewhere between open&close before
installation, the error is gone ... any idea ???
old questions:
6a) why one doesnt use P^4 ^5 instead of p^3 ?
Richard G:
Example1 for (absErr>last2AbsError) condition:
Wanted temperature is 18 real is 18.5 valve for this is 40% (just example)
Whats happen when sun shine directly into room?
Temperature will grow. This mean, that error grows. In this case (absErr>last2AbsError) is true independently to valve.
You will integrate this error typicaly 2-3 hours and result is too low unreal value of integrator. Name for this is windup.
Example2 for (last2error>(error+hysteresis(optional)) condition:
You have wanted 21, real 21 and you will change wanted to 18.
Valve will closed to valve_min and temperature descends 0.3 degree/hour.
When temperature drop to 19 (just example) valve will compensate temperature drop.
Temperature will descent slowly because come warm air from other rooms (ex 0.1 degree/hour)
But it unblock integrator limitation.
Condition from example2 is true therefore integrator drops down, it will move valve back to limitation.
And temperature descents more, therefore valve will compensate .... and cycle repeats.
Result is unreal value of integrator, again.
Both example situations are from real life.
Hi!
I'm using v1.0.
I too have the E3 problem in one room. I swapped the hr20 (but not the
part which contains the blue wheel) without success. Now I swapped that
part too. Tomorrow we will see if that helped.
Next problem is in the morning when the system heats up with water
temperatures up to 80 celcius.
Wanted temperature is for example 16 celcius, but room temperature goes
up to 19 celcius because the vent does not close fast enough.
In other rooms, wanted temperature is set to 21 celcius, the room goes
up do 23-25 celcius.
If I change wanted temperature (even from 16 to 16,5 celcius) the vent
starts to close.
Idea: Whatever is being reset when doing this, it perhaps should be done
as soon real temperature crosses wanted temperature?
Other idea would be to add some kind of temperature prediction, so that
openhr20 monitors if temperature rises and how fast it rises, and then
calculate 30 minutes into the future to compensate inertia of the
radiator.
Chris
Chris:
If you have E3 problem on one valve, it probably have problem with
"smooth" move. Solution is simple, set faster motor movement. It is more
nosily, but safe. In version 1.0 its setting "14", change it in service
menu.
Where you have valve and where you measure temperature? I was use
controller same as in 1.0 over year, without problem.
Temperature prediction would be nice. Problem is that we don't know
"transfer function" for all many different valves and it is imposible
implement Laplace transform (flash is too small and space is almost
gone).
If anybody have any idea, please feel free to do it. It is GPL code :-)
some update to motor speed setting info: for faster, you need LOWER
number
Jiri I will think about it ... but my feeling is: It is better to accept
windup in situations where Error grows and just block integration when
error gets smaller ...
Do you have explanation for this E3 phenomenon ?
On one valve since 2 day (since 321) I always get E3 after flashing when reinstalling it.
Richard
windup is not acceptable, integrator value outside reality make slow
reaction of controler (hours to start heating). Too slow and resulting
error is bigger compare to "permanet error". Please accept that less
than 1 degree of error is nothing compare to measure precision
(+-2degree, try compare 2 identical valves)
Except this you must compare it after may hour of operation when it
stabilize.
Another way to solve it is reset integrator after any change like in 1.0
release. But it need bigger I_factor (rel 1.0 use another scale than
current SVN). Problem of this is oscilaton in some condition (real
example from my one room:  t<-15 degree outside make oscilation
+-1degree inside with 2 hours period. valve oscilate +- 5%)
OK: R327 see this log from last night - error stays ...
Please comment on my E3 situation. Sometimes ADJ 1 stays longer then
usual ... on this valve
Richard you have 0.37 degree difference ;-)
And it will be better after few changes of temperature, because you will
have integrator more close to reality.
Calibration:
"Ad 1" is delay before real real calibration start
"Ad 2" open till motor slow down hard end. "Slow down" on this end in
reality is almost impact.
"Ad 3" close till motor is not possible keep it on wanted speed and slow
down over threshold (force to continue is too big)
Result is motor range in pulses. You can see it in service menu or Txx
command (see to watch.c)
If measured volume of impulses is <100 or >1000 it create E3 error
Usual volume of pulses is around 500
THX:
1 but how come that ADJ 1 then sometimes stays longer in the display ??
2 that error disapppears, if head (part mounted on heater) is adjusted
between open and close before installing valve
Jiri: In my case E3 typical comes under the following 3 conditions:
1. If I set the haed (blue wheel) to fully open and mount the valve. E3
comes directly after ADJ_1. This sometimes also happens on other
heaters/valves and seems to be a software prob.
It can be cured by setting the head somewhere between fully open &
close...
2. It comes directly after calibration (after ADJ_3), when the valve
should move to its 1st position.
3. It comes during operation ...
I wanted to find out the cause for my E3:
So I exchanged the motorunit (not the PCB) and the mounting head (blue
wheel). E3 is still there.
Facts:
A. It looks like theese E3 only occure, when the valve wants to start.
B. It has nothing to to with "smooth move" of the motor unit, but maybe
with the PCB.
C. The force needed to move the valve on this heater seems to be higher.
D. I am running on accu. So VCC is only 2,4-2,6V
Questions/Conclusions:
1. Is there a timeout after motor_start that can leed to E3?
2. Is there something like a torque_limit that can leed to E3 on
startup?
3. Can we give the motor more torque (boost) during start up ?
4. which eeprom parameters (e.g. light eye) also can leed to this
problem, please explain ?
5. I found a lot of E3(CTL_ERR_MOTOR) in the source code. It would be
easier to determine what caused E3, when we sepearate E3 into different
errors like E3a, E3b,....
Richard G:
answers to Q:
1) yes, (motor.c line 241)
2) no, it not detect torque_limit. It detect stop or slow down.
3) yes, but it have compensation to battery voltage (motor.c line 253)
4)
- motor_pwm_min  - minimum PWM for motor
- motor_pwm_max  - maximum PWM for motor
- motor_end_detect_cal - define maximum time between two impulses to
detect end in % of motor_speed - calibration (motor.c line 237)
- motor_end_detect_run - same as previous, but for normal run
- motor_speed - time between 2 impulses - simple controller keep motor
in this speed
- motor_speed_ctl_gain - speed controller gain
- motor_pwm_max_step - speed controler max step on PWM
- what do you think could cause the prob ?
- what steps should I try next ?
- what about 5. ?
You can try motor_pwm_max=0xff
you can try change line 241
you can try higher motor_end_detect_cal (default is 130 - you can try
200, but "touch" on the end of range will be little bit strong)
you can speed up motor_speed (default is 168, you can try for ex 100)
You can in debug.h "#define DEBUG_PRINT_MOTOR 1" and see serial console
(recommended, but it is just numbers because speed on this line is
limited)
It is many choices. But I can't found where is problem because it works
more than year for me without problem.
Jiri THX for your hints !!!!!!!!!!!!!!!!!
I built in E31-E35: Usally it is this error:
    if ((MOTOR_calibration_step == 0) &&
        (MOTOR_PosMax<MOTOR_MIN_IMPULSES)) {
        MOTOR_calibration_step = -1;     // calibration error
        CTL_error |=  CTL_ERR_MOTOR;
The causes are:
week accu about 2,45V, new head which leeds to more torque needed
I suggest following solution:
1. Change back motor speed
 /* 15 */  {184,       184,       10,      255},   //!< motor_speed
2. Change battery compensation to 2,7V
                MOTOR_pwm_set((int16_t)(((uint16_t)config.motor_pwm_max
* 256) / ((bat_average)/(2700/256))));
3. The cause for the longer adj_1 in the display could have something to
do with bat calculation ...
Anyway, do we have enough time to calculate the bat average after boot
to secure bat compensation before calibration starts ?? Sometimes I saw
wrong values over COM like 4V... It also seems to be part of the problem
Can we secure and validate bat calculation AND compensation
Only one question: are you sure to slowdown motor? 184 is bigger time
for one pulse = slower
yes, because it is OK as long as battery is fine. I think the prob has
to be cured somewhere else ;-)
Just an example of wrong battery calc (accu has 2,4V):
#Connection opened @ COM1, 9600, 8N1, DTR:On, RTS:Off
>V
V:OpenHR20 (10*16+3).( 2*16+7) Mar 14 2011 20:21:46 101
>D
D: d5 01.01.10 12:13:56 A V: 52 I: 2524 S: 1700 B: 3969 Is: 0000 E:08 X
>D
_____________________________________________
D: d5 01.01.10 12:00:17 A V: 80 I: 0000 S: 1700 B: 0000 Is: 0000
D: d5 01.01.10 12:04:17 A V: 52 I: 2530 S: 1700 B: 4207 Is: 0000 E:04
We have enough time to calculate the bat average after boot.
bat_average cant be > 0 till we have AVERAGE_LEN measures (adc.c line
92)
and calibration can't start (main.c line 295)
how come, that we have wrong voltage calculation then ? - accu=2,4V!!
D: d5 01.01.10 12:08:17 A V: 52 I: 2530 S: 1700 B: 4203 Is: 0000 E:04
D: d5 01.01.10 12:12:17 A V: 52 I: 2530 S: 1700 B: 4198 Is: 0000 E:04
D: d5 01.01.10 12:13:05 M V: 52 I: 2530 S: 2300 B: 4240 Is: 0000 E:04
D: d5 01.01.10 12:17:05 M V: 52 I: 2529 S: 2300 B: 4292 Is: 0000 E:04
It must be something different. Are you sure that you don't have some
parasite source of power? Usually it is 5V powered JTAG or serial
converter.
It you have 5V powered serial, 5V come from RXD signal to CPU. Solution
is simple, add one diode (example 1N4148 or any) anode to RXD on CPU,
katode to serial convertor.
JTAG is connected, but board has no power ... Serial comes from a
MAX2232 ... I will check that ! But anyway can we validate the calculate
voltage to sensible limits like 1-3,5V
Jiri: As most times - you were right. Seial and JTAG influence voltage
calculation... BUT the situation stays confusing:
- I made 3 versions ... bat. compensation with 2,6/2,7/2,8V
- I flashed 2,6V = Revision 327,
- disconnected everything
- accu (2,45V) out, wait 10s, accu in
- mount on head (heater)
- AD1, E3, motor was quite slow when it tried to start
- I flashed 2,7V
- same procedure, E3, no acustical difference when it tried to start
- I flashed 2,8V
- same procedure, WORKS OK, motor faster
- I flashed back 2,6V
- same procedure, WORKS OK, motor as fast as at 2,8 ???????????
- I took accu out for abot 10min.
- AD1, E3, motor was quite slow when it tried to start  ???????
- I flashed back 2,8V
- I took accu out for about 10min.
- same procedure, WORKS OK, motor faster ???????
during this test, most times I just flashed the Programm and not the
EEPROM (EEsave fuse is set).
- Are there any parameters stored in EEprom until calibration is done ?
- Are there any variables not initialised, that may stay in RAM ?
I am confused and frustrated now .. I need some fresh ideas .. pls help
voltage compensation is ONLY for motor start. After start it keep speed
on config.motor_speed value (define time for 1 pulse)
Jiri: I dont understand the connection to the prob from my last post ???
- Maybe 1 pulse is to short that motor reaches sensible speed ... ?
- but waht are your suggestions regarding the confusing E3 situation
described in my post ?
Jiri any idea ??
Jiri: The Prob comes to 99% from a wrong ADC bat value. Waht did I do:
Reboot over COM and imediately disconnect COM (Diode implemented) from
valve:
D: d2 02.01.07 00:38:59 M V: 52 I: 2421 S: 2300 B: 3385 Is: e3f8 X
D: d2 02.01.07 00:39:05 M V: 52 I: 2423 S: 2300 B: 3386 Is: e3f8 X
D: d2 02.01.07 00:44:23 M V: 52 I: 2426 S: 2300 B: 3387 Is: e3f8 X
BD: d2 02.01.07 00:44:56 M V: 52 I: 2430 S: 2300 B: 3391 Is: e3f8
B1324
V:OpenHR20 (10*16+3).( 2*16+7) Mar 15 2011 07:05:51 101
D: d5 01.01.10 12:00:41 A V: 80 I: 2430 S: 1700 B: 4755 Is: 0000 E:08 X
D: d5 01.01.10 12:00:55 A V: 80 I: 2430 S: 1700 B: 4759 Is: 0000 E:08 X
D: d5 01.01.10 12:00:41 A V: 80 I: 2435 S: 1700 B: 4596 Is: 0000 E:08 X
D: d5 01.01.10 12:01:07 A V: 80 I: 2437 S: 1700 B: 4596 Is: 0000 E:08 X
D: d5 01.01.10 12:01:08 A V: 80 I: 2437 S: 1700 B: 4596 Is: 0000 E:08 X
D: d5 01.01.10 12:00:27 A V: 80 I: 2437 S: 1700 B: 3050 Is: 0000 X
D: d5 01.01.10 12:00:33 A V: 80 I: 2437 S: 1700 B: 3034 Is: 0000 X
D: d5 01.01.10 12:00:35 A V: 80 I: 2437 S: 1700 B: 3029 Is: 0000 X
D: d5 01.01.10 12:00:53 A V: 80 I: 2437 S: 1700 B: 4705 Is: 0000 E:08 X
V:OpenHR20 (10*16+3).( 2*16+7) Mar 15 2011 07:05:51 101 IsB1324
D: d5 01.01.10 12:01:16 A V: 80 I: 2437 S: 1700 B: 4708 Is: 0000 E:08 X
As valve thinks it has more than 4V it reduces PWM at motor start and
motor does not start ... what should I try next ??
Hi!
Replacing the electronic part or the mechanical part of the hr20 was no
solution for the e3 problem. I also changed batterys.
I'm now trying with lower and higher values for 14.
It only happens at one radiator, so I think it's moving to heavy.
Besides: It is the only rondostat which shows a voltage of 3,55V (or
above, the output is limited by 8 bit + offset of 1V because I'm using
my own systen to readout the serial data from the rondostats).
Hi Jiri,
I can confirm this:
I have no external voltage at my rondostat, only the two internal
batteries and I'm also reading too high voltages.
I do not provide any external power to the rondostates.
Richard, how old are your rondostates? I bought four new ones and used
only one of them, which then showed the E3 error. Then I started
replacing the rondostat, but always used the new ones... never tried one
of the older ones.
Maybe they changed something with the hardware?
1. Chris do you have the wrong voltage reading all the time ?
2. When does the error occure (after AD1 = ADJ2 ?)
In my case it sometimes is OK, but I did not find out the case for i so
far. It might really be a Prob of the PCB. Because as I wrote I tried to
exchange the motorunit, but the error stayed !
Got mine (I have 6)
http://www.amazon.de/gp/product/B003URRKP8/ref=ox_...
from amazon last month ... did you find a fabrication date somewhere ?
3. I attached You a Version ehich has implemented 4 different errors for
E3 = E31-E34 which correspond with the different locations in the code,
where E3 comes from !
3. I attached You a Version which has implemented 4 different errors for
E3 = E31-E34 that correspond with the different locations in the code,
where E3 comes from ! All my changes in code are marked //jr
Most times I get E34.
It looks that we have problem with motor start you can try:
- change "#define MOTOR_IGNORE_IMPULSES 2" to bigger. It define number
of motor pulses ignored on start to control speed.
- change motor.c line "motor_timer = motor_max_time_for_impulse<<2;" to
multiply by more than 4. Ex "motor_timer =
motor_max_time_for_impulse<<3;" multiplies by 8
- enable "DEBUG_PRINT_MOTOR"
Richard G: battery voltage measurement is one of oldest part of code.
(more than 2 years) and I have not any problem with this. Please found
where is problem, it can be useful for others.
Ex "motor_timer = motor_max_time_for_impulse<<3;" I tried that some time
ago. It did not help.
Prob is wrong voltage and this PWM calc:
MOTOR_pwm_set (config.motor_pwm_max * 256) / ((bat_average)/(2800/256))
If valve thinks it has 4V: PWM=175, 2,4V: PWM=291(will lead to 255)
Is voltage calculated with the same adc like temp ? It must have
something to with the adc or something is wrong with pcb.
PWM value will not lead 255, see too MOTOR_pwm_set function
will lead to pwm_max of cause ... ;-)
How many pulses are needed for 0,5% move (can be max ignored), so that
we dont drive to far ?
typical 100% is 500-550pulses
1. so we should not ignore more than 5 (MOTOR_IGNORE_IMPULSES ) pulses ~
0,5%... right ?
2. Can you pls quick explain the 6 states of task_ADC. Is noise
cancelation only done for temp (  case 3:
update_ring(BAT_RING_TYPE,ADC_Get_Bat_Voltage(ADCW)))
you can use bigger value for MOTOR_IGNORE_IMPULSES. It is only for motor
speed controller, motor will be stopped on wanted position independent
to this.
Tip for test: use config.motor_pwm_max=config.motor_pwm_min=0xff and see
whats happen
AD steps:
1) (start_task_ADC) not used, just start ADC
2) battery, not used
3) battery, prepare for temperature
4) first temperature for compare
5) temperature, used only when result is same as previous, or repeat 5)
THX, so no noise canceling for bat.
Jiri do you have any further idea (except external power) where theese
wrong bat measurements can come from ...
Is there any chance to read the voltage directly an the valve ? (like
watch...)
I built it into watch.c.voltage is defenitly measured wrong on this
valve = same values as when connected to COM
D: d5 01.01.10 22:55:16 - V: 56 I: 2534 S: 2450 B: 3255 Is: 0000 E:04
Motor when error occures:
+ 0aeb ae
+ 0767 ae
+ 075f ae
+ 0764 ae
- 0a7f ae
 07db ae
AND of course no error when setting pwm_min=max
+ 029f fa
+ 05bb fa
+ 04c4 fa
+ 04aa fa
+ 04a0 fa
+ 049c fa
+ 04a0 fa
+ 049d fa
+ 0498 fa
+ 04b4 fa
+ 04b2 fa
+ 04b7 fa
+ 06d0 fa
- 054d fa
- 04ae fa
- 049c fa
- 04d3 fa
- 04f1 fa
- 0504 fa
- 0502 fa
- 0509 fa
- 0501 fa
- 050a fa
another error situation:
V:OpenHR20 (10*16+3).( 2*16+7) Mar 16 2011 17:55:45 101
+ 08b7 96
- 0fcd 96
and after connecting and disconnecting JTAG voltage is measured OK ????:
+ 076e fa
+ 0501 fa
+ 05db fa
- 0515 fa
- 04b6 fa
D: d5 01.01.10 12:00:56 A V: 80 I: 2457 S: 1700 B: 2529 Is: 0000 E:04 X
After taking accus out/in voltage on valve (nothing connected) is wrong
again - valve starts but stops short after:
D: d5 01.01.10 12:01:17 A V: 80 I: 2457 S: 1700 B: 3428 Is: 0000 E:08 X
+ 05aa b9
+ 0760 b9
+ 06f2 b9
+ 0722 b9
+ 0727 c3
+ 06c5 cd
+ 063f d5
+ 05e2 d7
+ 05ab d6
+ 0598 d4
+ 05a1 d2
+ 05b7 d2
+ 05c5 d2
+ 05ca d2
+ 05d0 d3
+ 05ce d4
+ 05ba d4
+ 05b6 d4
+ 05c2 d4
+ 05c7 d4
+ 05ba d4
+ 05b9 d4
+ 05cb d4
- 099e ba
- 074f ba
 080d ba
nice, it is definitely compensation to wrong battery voltage.
I remember correct that you have Dragon? If yes, try it manualy.
Without start SW: Set AD reference to VCC, input channel to BadGap
reference and start measure. Result will be number representing known
voltage (1.1 badgap) on unknown scale (VCC). Calculate is easy. You can
compare this value to VREF pin on MCU (ADMUX must be switched to "AVCC
with external capacitor at AREF pin")
But this make one idea. VREF is "AVCC with external capacitor at AREF
pin" If you have different (bigger capacity) on VCC, it can create
problem with charge this capacitance after AD switch on (normally it is
in power down state). You can try add one or more "dummy" measures
before real or use code like for thermometer.
I repeated accu out/in noe several times and sometimes V is OK.
Interesting is, that the wrong measurements also differ .... Offest is
0,5-1,5V. I did not find this phenomenon on another valve .. but I just
tried reboot 5 -10 times....
1. Jiri can you please integrate a voltage display into menu (middle
button)
2. Do You have any idea to diagnose this wrong measurement and display
an error ???
3. Of Courese we could always start with MAX_PWM and it would work ...
but this way the users wont find out that they might have a defect valve
you can disable battery compensation completly and use simple:
MOTOR_pwm_set(config.motor_pwm_max);
same thinking, but error stays hidden this way...
@Jiri please enter voltage display at least with a #ifdef for me and the
novice software guys ;-) with middle button
@Chris: here is my "hack version" with voltage display on first watch
variable and , E31-34, 5 Ignore Pulses, motor_timeout*8
Jiri why did you or the others implement this bat compensation ?
What about 1 & 2 from last post ???
Battery voltage on LCD can be enabled on rev 330.
change #define MENU_SHOW_BATTERY 0
to #define MENU_SHOW_BATTERY 1
I am not able detect wrong battery measurement. How? We are not known
reason.
Good guy - THX !!!!!!!!!!!!!
Reason for battery voltage compensation was external power.
For debug and somebody for normal functionality use 5V power. With this
power it works, but motor is too strong on start.
With "normal" batteries one reason is bigger noise on motor start. We
can remove it or create option for this.
let us keep it for the moment and wait what Chrisis results are ... see
you  tommorow ;-)
@chris: please read/answer from post 9:44 on ...
@Chris: this is rev.330 with bat display (last Param on middle button)
including differentiation of E3 into E31-34
@Jiri: It would be quite usefull, if one could choose, that the
parameter menue (middle button) and the watch menues do not return
automatically to main menue. This way one could watch a specific
parameter without warming up the valve (by pressing the buttons all the
time) ... and it would be a lot easier during testing or valve setup ...
I hope to confice you ;-)
means .. something more professional than my quick hack:
if (( kb_events & KB_EVENT_NONE_LONG ) && (menu_state<menu_home2 ||
menu_state>menu_home5))
BTW: A little prob i have not figured out in menue is:
if I set a manual temp and enter menu_home2..5 and press AUTO/MANU
button to leave this menue ... sometimes my manual set temp is back to
auto again and sometimes it stays on manu - I think this has nothing to
do with my change !!???
Jiri:
1. Regarding my prob with changing to AUTO TEMP from last post (As I am
simulating the wheel with PLC, I am always on manual)
Why do we change_mode in menue_homeX keyboard.c ~260 ? Is this the cause
why temp is set to AUTO when pressing AUTO in this menue (sometimes) ?
if ( kb_events & KB_EVENT_AUTO ) {
                    CTL_change_mode(CTL_CHANGE_MODE); // change mode
                    menu_state=menu_home_no_alter;
                    ret=true;
                } else if ( kb_events & KB_EVENT_AUTO_REWOKE ) {
                    CTL_change_mode(CTL_CHANGE_MODE_REWOKE); // change mode
                    ret=true;
 why not just: menu_state = menu_home;
2. integratorBlock=6; means blocking for 6x4 minutes ?
1. Why not?  It is just alternate content of main screen
2. agree
mistunderstandig?!: If I want to exit alternate menue by pressing AUTO,
the wanted temp should not change, also the Mode should not change ...
in my case from "23,0 MANU" to "17,0 AUTO"... in some other menues AUTO
is also for EXIT without SAVE ! This is also bad for testing, because
integrator start all over again ;-)
BTW: The more I look into it, the more I am fascinated from the work
sticking in this source code !!!
Hi Jiri and Richard,
I'm sorry but I do not have my jtag programmer at the moment so I can't
flash the rondostates right now.
I just connected a logic analyzer to tx of the rondostat to see the
serial output and I get this: "B: 4446". Real voltage is 2,88V...
At the other rondostates, they report 2,62V to 3,34V. The one which
shows 3,34V is aprox. at 2,8V too in reality.
Interesting: When I used a multimeter to meassure the voltage, I caused
a short circuit between vcc and ground, so the rondostat did a reset.
Back in my room, where my laptop shows all rondostates, it says 255
which is <=3,55V. And: The rondostat sowed e3 after the reset.
ups, the last line should be:
which is >=3,55V. And: The rondostat showed e3 after the reset.
Btw: This is one of the newer rondostats, it still has the foil on it
which protects the display against scratches...
Out of 4 rondostates, only one showed a voltage of 2,8V as expected.
The others showed something between 3,5 to 4,4 volts....
The one with 4,4V shows E3.
Chris: Are you sure that you don't have other power source than
batteries? (Ex: serial cable powered by 5V, JTAG, anything)
You can try code from SVN. It contain EXPERIMENTAL improvement on
battery measure.
PS: it is strange that you measure invalid battery value. This
functionality need only MCU and capacitor on VREF pin.
Chris an I measure the same symptoms... I have just one valve that
behaves like this. Chris, when wiil you programm new code ??
Jiri:
1 mistunderstandig?!: If I want to exit alternate menue by pressing
AUTO, the wanted temp should not change, also the Mode should not change
... in my case from "23,0 MANU" to "17,0 AUTO" (I am always on MANU
because of my wheel simulation;-) ... in some other menues AUTO is also
2. What about putting integrator_credit on "D" line for COM ... at least
during our testings ??
ad2) OK?
#if DEBUG_PRINT_I_SUM
  print_s_p(PSTR(" Is: "));
  print_hexXXXX(sumError);
  print_s_p(PSTR(" Ic: ")); //jr
  print_decXXXX(CTL_interatorCredit);
#endif
3. How can I set Is after reboot manually to a certain value (necessary
during testing). Do we have a COM command or any other way ... ? Can we
use the EEprom edit mechanisem some how ??
Richard,
I almost accept your notices. Only one difference is hex output for
CTL_interatorCredit, reason is missing support for decimal numbers<0.
Jiri
Jiri did you accept 1 & 2 ???!!!
(I thought credit is only poistive ...)
How can I achieve 3 ??
4. How come - see sumerror
D: d6 19.03.11 09:41:08 M V: 56 I: 2317 S: 2300 B: 2707 Is: e1f0
D: d6 19.03.11 09:45:08 M V: 56 I: 2317 S: 2300 B: 2706 Is: e168
D: d6 19.03.11 09:49:08 M V: 56 I: 2317 S: 2300 B: 2705 Is: e0e0
D: d6 19.03.11 09:53:08 M V: 55 I: 2324 S: 2300 B: 2702 Is: e020
D: d6 19.03.11 09:57:08 M V: 55 I: 2324 S: 2300 B: 2701 Is: df60
D: d6 19.03.11 10:01:08 M V: 59 I: 2324 S: 2300 B: 2694 Is: ff40
D: d6 19.03.11 10:05:08 M V: 59 I: 2330 S: 2300 B: 2701 Is: fe50
D: d6 19.03.11 10:09:08 M V: 59 I: 2330 S: 2300 B: 2701 Is: fd60
around 10:05 valve started calibration ??? why ? today is saturday
THX: just verified the changes ;-)
bat voltage display has a prob = shows only 2. instead of 2.123
        LCD_Print
Char
(bat_average/1000, 2, LCD_MODE_ON);
        LCD_PrintDec(bat_average/100, 2, LCD_MODE_ON);
        LCD_PrintDec(bat_average%100, 0, LCD_MODE_ON);
Jiri please stay with /100, because this way I see wether accu is
charging or discharging earlier (I charge them from PLC) THX
pls comment on 3 & 4
Regarding alternate and service watch from one of the last posts should
no be left automatically (because we want to watch a certain parameter
for a longer time ;-) menu.c 125:
        } else if (( kb_events & KB_EVENT_NONE_LONG ) &&
           ! (menu_state>=menu_home2 || menu_state<=menu_home5 || menu_state==menu_service_watch)) {
@Richard: I have to wait until I get my jtag programmer back.... don't
know how long it will take....
BTW: The rondostat at which I caused the short circuit keeps running
into E3 error.
Question: When is battery voltage meassured? For me it looks as if it is
read only at startup, because that coult perhaps explain the wrong
voltage (?)
@Jiri: There is no other power source:
- At the other rondostats which are mounted at the radiators, there is
an external circuit connected which captures the serial data and sends
values using rfm12. It gets its power from the rondostat. So it will
perhaps add capacity, but it definitly is no power source ;)
- The logic analyzer is connected to gnd and tx pin, but it has high
impedance inputs, no pullups and so on.
battery is measured quite often (<10s)...wait until you have your
programmer back. there is a bat display in alternate menue already ;-)
batt voltage show only 2. ? For me it is correct, show 2.55.
You don't need 3) it is almost equal to config.valve_center. Difference
is only in units. Problem is that we don't have free flash for any
useful idea.
Every Sat on 10:00 is automatic recalibration. It is useful also for
keep valve heath.
I change battery voltage in LCD back to mV without decimal point.
battery voltage is measured every second. Presented value is average
from last AVERAGE_LEN (= default 15) values
men you are fast THX "mV"
for a longer time ;-) menu.c 125:        } else if (( kb_events &
ad3) in my case different heaters have quite different valves, so for
testing purposes it would be great to start with manual set Is by COM or
LCD. I thought during debuggin it would be quite helpfull to be able to
manipulate static variables or variables from service_watch
Richard,
add to your sumErr log (4): I down know why, it looks strange.
here it is. around 7pm, 9pm, and today 5am and 7:40 there is a temp
update with same temp=23.0
Jiri Bat display does not work for me with CHAR. I press middle button
right after version string and DATE skip define is set ! Display shows
10:00 (no clear screen) and when first bat calc is done the left 0 looks
like this
                    if (((CTL_error &  (CTL_ERR_BATT_LOW | CTL_ERR_BATT_WARNING)) == 0)
                  && (RTC_GetDayOfWeek()==6)
                && (RTC_GetHour()==10)
                && (RTC_GetMinute()==0)) {
                        // every sunday 10:00AM
                        // TODO: improve this code!
                        // valve protection / CyCL
6 .. then is saturday and not sunday as stated in comment ???
I connected a rondostat to a variable power source. When it callibrates
and I change power, the motor of the rondostat gets slower or faster,
but it returns to its normal speed after a very short time (a second or
so).
So the voltage messurment seems to work.
Strange1:
I set it to 3.0V, but it displays "batt". Why? Is this condition cleard
automatically when voltage rises, or only at reset or button-event?
Strange2:
Serial Output reports a voltage of 3,06V now.
Multimeter says 3,06V too (hm, very precise, it was rather cheap....)
Power-Supply is set to 3,0V.
=> All correct.
But when it was on batteries, the same rondostat showed 3,2V (serial)
while real voltage was 2,8V.
I set power supply to 2,8V now. Serial reports 2,87V now.
I set power supplay to 3,5V, serial reports 3,5V.
Connected batterys while power supply is still connected to prevent
reset, then disconnected power supply. Serial shows 2,8V, real voltage
is 2,8V. Still shows batt.
Removed and reinserted batteries to do a reset. Real voltage is still
2,8V
. Batt-Message is gone, serial output reports 3,55 or more volts. Motor
speed seems to be lower and when it starts the boost is barely there.
Switched on power supply (3V), batteries still in the rondostate. Serial
still shows 3,55V or greater.
bat displays are not reversible (except reboot or #define). Once voltage
droped below 2,4 bat warning comes on. Low bat is 2.0.
On my defect valve I also could not reproduce the situation ... I gues
if you try it several times (powerless in between each time!!) with
powersupply you will get wrong readings there as well
- battery warning and error is not reversible by good reason. Battery on
end of life usually refresh voltage without stress. In this situation is
show low voltage information only when motor runs.  I want to keep this
information.
- I fix "char" problem on voltage on LCD.
Richard: You are right about mistake in comment about Saturday automatic
recalibrate.
Chris: I don't have any idea why batteries is measured wrong and
external power supply is OK. I am not able repeat this problem. Maybe
some difference on PCB? Just idea, can you compare your PCB with photos
and other documentation?
Jiri: 339 bat display OK, but we have a : in display (before we had a .)
a) Do we realy need the Highword of summerror .. it is FFFF or 0 and if
it is ffff the lowword will start with f..a anyway ?? But it is cleaner
code of course ;-)
b) It would be quite usefull, if one could choose, that
alternate menue (middle button) and watch menue do not return
time) ... and it would be a lot easier during testing our valve setup
I hope to convice you ;-) menu.c 125:
c) did you find anything in my log ?
":" in voltage fixed
a) it could be 0x00012345 or 0xffff2345. Low word is same, but meaning
is different
b) I want to have automatic return to main_menu. You can create change
on your sources and it will kept after "svn update" command.
c) what is wrong on this log? PS: create chart in OpenOffice or Excel is
sometimes useful.
a) What was your maxsumerror so far ? mine typ. stops at ffff a/9
b) I tried snv commands some time ago, but it doesnt work in some of my
network surroundings (proxy,firewall,...), so I have to patch al my
changes all the time
hope to convince you at least to:
#if NO_AUTORETURN_FROM_ALT_MENUES
           && ! (menu_state>=menu_home2 || menu_state<=menu_home5 || menu_state==menu_service_watch))
#endif  {
c) I dont understand, thought you mentioned something strange  ...
strange is this part:
what happen at this time?
I thought sat 10:00 auto_calibration, main.c 241
                        // every saturday 10:00AM
                       sumError=0;
sumerror=0 should not happen here ! right ? should only happen if valve
is taken from head (E2)
Richard: right, I must fix it
1a ... I hope I may be looking forward to my bonus ;-)
"#if NO_AUTORETURN_FROM_ALT_MENUES"
R341: Jiri, why should autocalib need new sumerror. 99 times out of 100
;-) calib stays about the same ! This way every saturday it gets to hot
or to cold at 10:00. I think giving credit is good enough !!
Only if valve is taken from head (E2) we should reset sumerror ...
max sumError if defined on controller.c line +-319 (max inpact to valve
is 50%)
option NO_AUTORETURN_FROM_ALT_MENUES is added
Richard,
Calibration is same only on same conditions. But normally last
calibration is 1 week old. And it depend to battery, heater tempterature
atc.
But you are right, last value can be better than 0. I will create option
for it.
THX and a beer for R342:
Yes regarding impact of max 50%, but you agree that most times autocalib
will bring about the same results ... so we do not need sumerror=0 here
!! giving credit to adapt little changes will be good enough. (in my
case 5% change mean 1-2°C more/less in the room. min/max/center are
quite different on my heaters; they also have different valvetypes)
Only if valve is taken from heater (E2) we should start all over again
with sumerror=0
R343: Why not ?
#if CyCL_RESETS_sumError
sumError=0; // new calibration need found new sumError
CTL_interatorCredit=config.I_max_credit;
integratorBlock= DEFINE_INTEGRATOR_BLOCK (or eeprom)
#else
#endif
When do we need the block ? Also here ?:
    if (mont_contact & KBI_MONT) {
        CTL_error |=  CTL_ERR_MONTAGE;
    sumError=0;
suggestion:
#endif
______controller.c
   if (CTL_interatorCredit==config.I_max_credit) {
      integratorBlock=DEFINE_INTEGRATOR_BLOCK (or eeprom)
   if (updateNow) {
Try R327
you mean 344 ;-) ... tommorow ... my girls are waiting ... see you
Jiri, I verified all the changes compared to 339:
!!! VERY VERY  WELL DONE !!!
Suggestion regarding controller:
1.Your new idea from last weeks regarding I part works well. But
sometimes an offset 0,1-0,2 stays. I know that is not much ;-). My
suggestion is to give credit, if error is around 0 (instead=0). Existing
code
     if (absErr >= last2AbsError) { // error can grow only limited time
will prevent growth of sumerror anyway.
An Option could be to give the "tollerance credit" just once. But this
would produce more code ;-). This is why we should try this first:
      if ((error16 >= 0) ? (v0 < config.valve_max) : (v0 > config.valve_min)) {
            ((absErr==last2AbsError) && (absErr<=I_0_TOLLERANCE))) { //sign of last error16 != sign of current OR abserror around 0
          CTL_interatorCredit=config.I_max_credit; // give credit
#define I_ERR_TOLLERANCE_AROUND_0 15 // unit 0,01°C. Set it quite
restrictive !
2. I suggest a define in controll.c 303:
            CTL_interatorCredit-=(absErr/I_ERR_WEIGHT)+1; // max is
1200/25+1 = 49 impact of error on I part
#define I_ERR_WEIGHT 25 //impact of error on I part
Hi Jiri,
I logged temperature and vent position in one room to see the
overheating in the morning. Here it is.
Any idea what causes the wrong battery messurements? Why is is it after
reset and not before with the same rondostat? Strange.
Chris
btw: The "own sensor ic2" does not messure room temperature. You can
ignore it.
I got my jtag programmer back and flashed rev 344 (without rfm12).
I hear the initial boost of the motor (I see you disabled compensation
in config.h, so wrong battery messurements should not be a problem any
more?)
Bat on lcd shows 3281, multimeter shows 2,89V.
Csn I use rev 344 as "productive" version, or won't it work?
Chris
I also use it with the mods from above - no prob so far
I took the batteries in and out several times. There was nothing else
connected to the rondostat and I did not mount it. Here is the batt
output:
2,8V (ok)
3,5V
4,4V
5,4V
2,8
2,9
2,9
3,1
2,9
2,9
2,9
2,9
2,9
same on my defect one
Could it be a bug somewhere in the firmware (ad-init?) or a bug of the
atmega itself?
I don't think it is a "defect" in hardware because it occurs only
sometimes and changes only on reset (not sure about this... I never
watched a rondostat whith wrong messurements correct itself without
reset... did you?)
I habe 6 rondostats with openhr20 that work like a charm (except for the
overheating problem in the morning which is in all rooms).
And I have 4 rondostates which are not mounted because auf E3 problem /
wrong voltage problem or wrong callibration byte so serial data is not
working. (how can I correct this?)
I agree but have no idea how to get closer to the reason
Chris, comments to your values:
You have externaly disabled heating and SW wan't to fix this error.
Mechanism to do it is integrator (old name was "zero error
compensation")
Problem is that current version of windup protection not help in this
situation (I will improve it later).
Soloution for you is set I_Factor to 0 and set valve_center very precise
manualy.
Chris, I have idea how to solve your problem. Please wait till tomorrow.
I thing that problem with regulator windup on "central heating off" can
be solved on Rev345. It need tests.
I have NO idea where is problem with bad battery measure. But I create
some debug, please enable DEBUG_BATT_ADC in debug.h and report me
result. (need SVN rev 346)
Jiri, men you are fast - when I was ready with patching 349, you were at
350 already. I take this for the night ;-)
Jiri add this to com.c ?!
  print_hexXXXX(sumError>>16);
  print_s_p(PSTR(" Ib: ")); //jr
  print_hexXX(CTL_integratorBlock);
  print_hexXX(CTL_interatorCredit);
  print_s_p(PSTR(" Ie: ")); //jr
  print_hexXX(CTL_creditExpiration);
#endif
Jiri could you please explain the changes regarding controller since 344
It s simple:
- when integrator credit is empty or temperature change I compare
current error with error on last change. If it isn't smaller than 1/2
change on integrator is reverted.
- integrator credit have limited lifetime
1. OK. Isnt the aim of CTL_interatorCredit and CTL_creditExpiration the
same. Both expire. The 3rd function is revert (I think its a good idea).
All 3 mechanisems have the same goal = prevent windup = right ?
This is why I dont understand why we need CTL_creditExpiration - pls
explain?
2. When do I have to change I_ERR_WEIGHT and when I_Factor ?
ad2) log from last night: Impact on I at errors <0,5°C is to low / to
slow ...
Author: Jiri Dobry (jdobry)
too slow? Try create chart in excel. I can't be better. :-)
We need 2 different
CTL_interatorCredit - allow maximum change volume, depend to integrator
change size
CTL_creditExpiration - allow maximum time
Author: Richard G. (gggggg)
Jiri, I nearly expected your answer ;-) ... I am perfectionist ...
as you know ...
But right now I have the prob, that Summeroor, Ic and Ib in bathroom is
= 0 (I dont know Ie). Instead of 24 I have 26° = just P part active .. I
have no log and no idea so far ... maybe the gap is too big, as that it
is closed during credit/expiretime
2. When do I have to reduce I_ERR_WEIGHT and when increase I_Factor ?
Jiri:
a. if (absErr>=(lastTempChangeErrorAbs/2)) reverts too often ...
If just by chance the error is quite small we freeze wrong I part value
"forever". E.g. in some of my rooms (e.g.bathroom) I have a floor
heating as well. So it is not valve on its own who tries its best, doors
to other rooms sometimes stay open the whole day,...). In R351 valve
reverted quite often and ended up beeing controlled by P part close to
center. Bathrooom has 26 instead of 24 this way. So this "one time small
error" might be quite wrong, because it was produced by external
influences !!
Generell revert aim is to prevent wrong summerror produced by external
influences (shorten the time to correct I part). So aim is, to just
revert if really necessary ...
Suggetsion: revert if:
(absErr>=lastTempChangeErrorAbs) && (absErr>=I_REVERT_TEMP_THRESHOLD) &&
(lastTempChangeSumError>=I_REVERT_ERR_TRESHOLD)
#define I_REVERT_TEMP_THRESHOLD 50  //unit 0,01°C, revert only if error
is larger than e.g. 0,5°C. Dont go for small errors that by chance might
have been produced by external influece and will be stored "forever" !
#define I_REVERT_ERR_THRESHOLD 0x1000 //revert only if sumerror has
impact on valve move = do not revert on small values that have no impact
on valve position. This way even wrong sumerrors will be corrected
during the first periode, where external influence is gone.
b. expiration credit: do we relly need this ?
I understand, that aim is to stop valve during non heating periodes: If
no temp change occures, I part should be frozen to stop valve from
moving.
This is why I would like to set it to 24hours (no tempchange a whole
day) =24x60/4=360 but max is 255 ;-)
c) please answer 2. from last post...
a) must be:
.. && .. && (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD)
Idea for "revert" is solve 2 situations:
Ex1: you want to heat more, but central heating is switched off.
Integrator will move valve. And we need detect this situation: we are
not able to heat up, valve position have no effect
Ex2: you need lower temperature, but temperature declines too slowly
(open door, external heat source) Situation is same, any change on valve
can't help. See too attachment
I both situation: any integrated change of valve is invalid, because it
can't have any effect
expiration - Lets this situation:
22degrre in room, wanted temperature is 18. It take many hours to pass
20degrre and it leave valve_min position. Now valve slowly grow and
follow temperature decline. Without expiration, integrator will decline
valve without reason again to valve_min.
expiration in other words: If valve change have not effect in defined
time (default 2 hours!!!) we can't believe that measured error depend to
valve position. We must have impact from another source. Maximum
expiration is (255*4/60) = 17 hours Do you believe that measured effect
after 17 hours is caused by valve change?
But you are right, condition (absErr>=(lastTempChangeErrorAbs/2)) can be
too strong. I will change it.
(absErr>=I_REVERT_TEMP_THRESHOLD) <= bad idea, compare it mainly with
Ex2, it will not work in this situation
(abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) <= tell me why?
What is a goal?
"When do I have to reduce I_ERR_WEIGHT and when increase I_Factor?"
A: Anytime, and see whats happen. Frankly spoken, I don't know ideal
setting for this. It is too new, I have only limited data (only my
valves, only short time).
Ideal solution for enable/disable integrator update is put all magic
like "credit" to trash and use "regression analysis" to determine rate
of valve change to temperature. It is perfect clear solution. But we
have limited resources in MCU. If you enable all options on code, free
space in flash is less than 0.5kB (less than 250 assembler
instructions!!) This is reason why I disable program/time settings by
valve wheel on wireless case. Now I have 1432bytes free flash. It make
it possible.
I will try create better mathematical model of valve (not just
calc/excel sheet) and try press some "regression analysis" into code.
But I am sure that end of heating season will be faster.
also today bathroom was reverted the whole day ....
idea a) and b) work togehter !
ad (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) <= tell me why?
This way we just do a revert if the sumerror which we take for revert
has an impact on valve (the effect should be >= 1% ...)
e.g. we have stored a lastTempChangeSumError=0x050 at a
lastTempChangeErrorAbs=0,1°C. But those values were influenced by
externel source.
R351 will revert all the time 0x050 because abserr will be >
lastTempChangeErrorAbs=0,1°C most time. And when the ext. source is gone
abserror will get larger all the time ... As I is small 0x050 it has no
impact ... and I part is OFF "forever".
(abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) secures that we
just revert sumerrors that have a real influence (e.g. >=1%) on valve.
And if this lastTempChangeSumError was wrong (because of ext. influence)
it will lead to a larger error, which will not be reverted again because
of my condition a) !!!!!!!
I think A&B together will work for both examples, because we revert on
large errors.
my explanation was not quite OK.
b) on its own secures: Only revert values (e.g >0x1000) that have real
impact. So if stored values were wrong, the error will get worse and I
part will start working
a) if stored values were wrong, one of the next periodes for sure will
be able to reduce the error below 0,5°C(I_REVERT_TEMP_THRESHOLD) ... and
reverting will stop
I gave a&b a try for tommorow in bathroom
ad b) when I say "I part eill start working" I mean this part !
CTL_interatorCredit-=(absErr/I_ERR_WEIGHT)+1; // max is 1200/20+1 = 61
Richard
but you compare integrated value, not change from last temperature
change. It can't work.
Or I understood wrong. Any chart ?
no chart ... log will come tommorow ....
goal of a)
Do not revert on small errors, this way valve can get out of REVERTING
by itself (it gets out of the trap if controller controls the error to <
0,5°)
If we dont limit the error REVERTING will last "forever" (e.g. if
lastTempChangeErrorAbs=0), because controller cant do any better. But if
the sumerror stored is wrong controller is in the trap!!)
b) only revert if I part has influence on controller. small summerrors
have no effect on valve position. Only P part works. Large values have
real influece on position. So if wrong (large) summerror will be
reverted, position will be worse then before (when the ext. source was
active). This way I part "if (absErr >= last2AbsError)" will start
working on this error and next time abserror will be <0,5 and reverting
will stop....
1. V starts with 43 (center= 58, Min=42) through P part
23.03.11 23:41:42 Ic is used up but V is 44 now:
So I_Factor should be increased to at least compensate the loss on P. We
should have V<42 there.
Jiri we should increase I to 35
2. 24.03.11 04:03:03 Tempchange to 2300:
summerror stays as Vmin is reached. room is heated up by floor heating,
no revert was necessary > no revert done > OK
another room: Vmin=52 Center=58 I set Vmin at 18:02:03 and Ifactor to 35
around 17:38
bathroom during last night: Vmin=40, Center=58, I=35
heater stops heating about V=41
At the beginning valve was warmed up from my hands... I think I is still
to low ?!
Richard, why do you set Vmin too close? This result is not surprise,
controller disable integration if valve is out of range and in your case
it usual situation. Except this, valve calibration depends to battery
status, and with this setting is easy to see valve on Vmin and heating
warming.
Jiri, I thought battery should not interfear, beacause we count pulses
Actually I set Vmin = VheaterOFF - 4. This way I part cant "wind down".
-4 was good enough so far to compensate the calibration tollerances
which usally are not more than 2.
If you read the bathroom logs, be aware that bathromm has floor heating,
hand towel hater (with normal valve, shuts down about 26°C) and the
heater controlled by hr20. And if door is opened temp slowly goes down
to 24. This room is perfect for testing the reverting prob I had with
R351 ;-).
Valve calibration depend to battery because maximum force depend too.
It is simple, motor controller try to keep same speed till slow down on
"close end" (Ad3 state). Problem is that maximum force depend to battery
state (maximum PWM is constant). I my valves valve range is ~600pulses
end to end with fresh batteries and ~480pulses with end of live
batteries.
(if you need exact position of valve, try to find "manual calibration"
in this thread)
Jiri,
- #define WATCH_N (10) should be (11) (values 0..0a)
- why dont we start autocalibration with searching CLOSE first. This way
one could manually set head to CLOSE, mount valve, valve checks that it
cant go any further and store this manually set CLOSE, then valve goes
to OPEN. This way we could reproduce the CLOSE position in automatic as
well .. ?
- why dont we store the positions found during automatic calib in eeprom
- e.g. by setting MOTOR_ManuCalibration |= 0x8000
0 ... no calib, >0 ... auto, <0 ... manu
WATCH_N you are right, fixed
Calibration starts to "OPEN" direction by few reasons:
- when valve is on "CLOSE" side, force to start closing depend to valve
position. I will create calibration depend to position on start
salibration.
- when valve is "CLOSE" side, it can be on position, where motor have
not force to reach. In another word, manually you can brace stronger
than motor.
Where is benefit if you store automatic calibration in EEPROM? If you
remove had from valve you must calibrate it anyway.
THX for explanation regarding calib start direction
Benefit - what I am looking for:
a) one would like to see, wether position ater valve install is about
the same like last time. So we can be sure everything is fine.
b) right now I always look at MOTOR_PosMax to see wether the number of
pulses are about the same (the gap so far always was < 10 pulses, this
is about 2% from 0x200 to 0x2d0 pulses on my valves.
c) one thing could be to set calibration data manually
Jiri,
1 I think we should give integrator credit when valve starts moving
because of p part e.g.:
D: d7 27.03.11 00:13:57 M V: 41 I: 2520 S: 2450 B: 2491 Is: ffffc900 Ib:
00 Ic: fd Ie: e2
D: d7 27.03.11 00:17:57 M V: 41 I: 2520 S: 2450 B: 2489 Is: ffffc900 Ib:
00 Ic: fd Ie: e1
D: d7 27.03.11 00:21:57 M V: 41 I: 2520 S: 2450 B: 2488 Is: ffffc900 Ib:
00 Ic: fd Ie: e0
D: d7 27.03.11 00:25:57 M V: 42 I: 2516 S: 2450 B: 2490 Is: ffffc900 Ib:
00 Ic: fd Ie: df
D: d7 27.03.11 00:29:57 M V: 42 I: 2514 S: 2450 B: 2490 Is: ffffc900 Ib:
00 Ic: fd Ie: de
D: d7 27.03.11 00:33:57 M V: 42 I: 2514 S: 2450 B: 2492 Is: ffffc900 Ib:
00 Ic: fd Ie: dd
D: d7 27.03.11 00:37:57 M V: 42 I: 2514 S: 2450 B: 2488 Is: ffffc900 Ib:
00 Ic: fd Ie: dc
controller.c 399:
  if ((lastCTL_interatorCredit<=0) && (pi_term16!=(uint8_t)processValue)) {  //give credit if p part moves valve
                CTL_creditExpiration=config.I_credit_expiration;
  return (uint8_t)pi_term16;
    lastErrorSign = (uint8_t)(error16>>8)&0x80;
    lastCTL_interatorCredit = CTL_interatorCredit;
2. REVERT http://embdev.net/topic/118781?goto=2120075#2116213
works OK. see log D: d6 26.03.11 21:34:12
ad1) integrator_block was missing:
                CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK;       //block to wait for p part impact
ad1)
   if ((lastCTL_interatorCredit<=0) && ((uint8_t)pi_term16!=(uint8_t)processValue)) {  //give credit if p part moves valve
I think its even better to block integrator after any change of valve
position caused by p part
  if ((lastCTL_interatorCredit==CTL_interatorCredit) && (uint8_t)pi_term16!=(uint8_t)processValue) {
    CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK;       //block Integrator if only p moves valve
    if (lastCTL_interatorCredit<=0) {  // if credit is expired
      CTL_interatorCredit = config.I_max_credit; //give new credit if p part moves valve
      CTL_creditExpiration = config.I_credit_expiration;
a better position to implement blocking after P change could be line
175, but then we need something like lastSumError ...
I took wrong variable: instead of process_value we have to use
old_result of course ...
   if ((lastCTL_interatorCredit==CTL_interatorCredit) && (uint8_t)pi_term16!=old_result) {
controller.c 312 uint8_t v0 = valveHistory[0];
why dont we use old_result here ?
my changes did well over the night ...also revert ... see LAST PART of
log: Vmin=36
PS: I set blocking to 3 to get faster results during testing phase.
credit_expiration=FF
PPS: Maybe we could give credit on each P Move instead of just if credit
is expired ...
log from normal room (16m²) Vmin=52/54
Jiri, did you or others ever think about or try replacing the thick
wires of the temp sensor by very thin ones to get faster temp respons
BTW: I am blocking integrator now after any move of valve
did someone ever try to move in smaller steps - is it possible to count
and stop 0,5% ?
hu hu ... any anwsers to my last posts would be very welcome ...
the attached jpg shows R354, reverting deactivated and integrator
blocked after any move of valve... as one could see in small rooms
(16m²) with outside temps >10°C our actual 1% valve step is too big for
me...
Heating was deactivatetd in the afternoon, because of sun ..
blocking I: controller.c 396
  if ((uint8_t)pi_term16!=old_result) {
    CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK;       //block Integrator on any valve move
1. did you or others ever think about or try replacing the thick
wires of the temp sensor by very thin ones to get faster temp response
2. did someone ever try to move valve in smaller steps - is it possible
to count
and stop 0,5% ?
2a what do I have to change  to try it ?
3. in the morning I want to boost temp 1-2° as fast as possible. The
actual controller is way to slow to get the childs room warm in the
morning. We need something like:
if the new wanted temp differs by more than e.g. 1°C from the actual
setpoint we have to open/or close the valve with another algorithm and
hand over to the actual controller one some time or if temp is within
0,3°C to the new temp wanted ...
1. Why? You don't need faster response. Frankly spoken, compare to
heating response it is fast enough.
2. motor.c function MOTOR_Goto replace 100->200. But you need check all
valve calculation, because after this same values can be overloaded. You
must also update LCD and COM functions for correct reports.
3. It if exactly reason for P3_Factor. It is "boost" for big temperature
difference.
Richard G, about "blocking I: controller.c 396":
It is interesting idea, I will test it too.
1. As heater heats up valve. the temp sensor is heated up via its wires.
With thin wires, see chart 06:30
hr20_1354_110401a_thin_wire_blocking_I.jpg the impact on sensor is less.
Sensor is still heated up, but just by air. This way we are closer to
real room temp. Newer valves from other manufacturers have smd sensors
with 0,2mm lines...
3. I implemented a boost function...quite preliminary still... just
using max and min positions of valve. This is the fastest way to heat up
or cool down... in the next step I will calculate boost_time depending
on error.. see chart 6:10 hr20_2354_110402a_thin_wire_boost.jpg
Description:
if setpoint is changed and gap is larger than setpoint_diff (50=0,5°)
and actual error is large enough (boost_error 30=0,3°) we start boost
funtion. boost sets valve to max or min position depending on error.
boost lasts for boost_time in minutes (15). boost ends earlier if actual
error is less than boost_error - boost_hystereses (30-10=0,2°). During
boost PID controller only calculates errors (no PID values) and
integrator is blocked.
eeprom.h
  /*    */  {50,           0,        0,      255},   //!< temp_boost_setpoint_diff, unit 0,01°C
  /*    */  {10,           0,        0,      255},   //!< temp_boost_hystereses, unit 0,01°C
  /*    */  {30,           0,        0,      255},   //!< temp_boost_error, unit 0,01°C
  /*    */  {15,           0,        0,      255},   //!< temp_boost_time, minutes
controller.c 150
    if ( minute_ch && (PID_boost_timeout>0)) {  //timeout in minutes (15)
    PID_boost_timeout--;
      if (PID_boost_timeout==0) {
      PID_force_update = 0;
        if (updateNow) {
//jr needed in PID update, so set it later      CTL_temp_wanted_last=temp;
      goto UPDATE_NOW; // optimize
        valveHistory[0]=new_valve;
      CTL_temp_wanted_last=temp;  //jr was after line "if (updateNow) {" before
       COM_print_debug(0);
controller.c ~310:
    if (updateNow) {
      CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; // do not allow
update integrator immediately after temp change
      testIntegratorRevert(lastAbsError);
      lastTempChangeErrorAbs = absErr;
      lastTempChangeSumError = sumError;
      if ((PID_boost_timeout==0) && (abs(setPoint-CTL_temp_wanted_last)>=config.temp_boost_setpoint_diff) // change of wanted temp large enough to start boost (0,5°C)
        && (absErr>=(int16_t)config.temp_boost_error)) {  // error large enough to start boost (0,3°C)
        PID_boost_timeout = config.temp_boost_time; // temp_boost_time in minutes
    } else {
controller.c ~360:
  lastProcessValue = processValue;
  if ((PID_boost_timeout > 0) && //choose position of code, because parameters like error are calculated above
    (abs(error16)<=(int16_t)(config.temp_boost_error-config.temp_boost_hystereses))) {  // error <= temp_boost_error-temp_boost_hystereses
    PID_boost_timeout=0; // end boost earlier, if error got to small (0,2°)
  if (PID_boost_timeout > 0) {  // boost active
    if (error16>0) {
      return config.valve_max;   //boost to max, no PID calculation
    } else {
      return config.valve_min;   //boost to min, no PID calculation
  if (config.I_Factor > 0) {
@Chris any new ideas about bat ADCprob ?? I am having it again ...
looks like adc meaeures x01bb all the time. But after reset (just by
programming fuses) the same value is interpreted differently:
batAD x01bb
batAD x01bb
D: d5 01.01.10 12:00:22 A V: 30 I: 2274 S: 1700 B: 2542 Is: 00000000 Ib: 06 Ic: 28 bo: ff E
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
D V:OpenHR20 (3*16+3).( 5*16+4) Apr  3 2011 12:33:06 101
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD x01bb
batAD xbat
batAD x01bb
D
batAD x01bb
batAD x01bb
batAD x01bb
D: d5 01.01.10 12:00:21 A V: 80 I: 0000 S: 1700 B: 0000 Is: 00000000 Ib: 06 Ic: 28 bo: ff X
batAD x01bb
batAD x01bb
batAD x01bb
D
batAD x01bb
D: d5 01.01.10 12:00:25 A V: 80 I: 2267 S: 1700 B: 3728 Is: 00000000 Ib: 06 Ic: 28 bo: ff E:04 X
batAD x01bb
@Jiri: still dont look through the ring buffer secrets ... but is it
possible that this
static void shift_ring(void) {
#if ! HW_WINDOW_DETECTION
  ring_pos = (ring_pos+1) % AVERAGE_LEN;
should look like that ????
deleted
average is definitely miscalculated: istead of 9b6 we get ee4
AV is calculated average, followed by the 15 values aof ring buffer
AV0ee4
009b6
109b6
209b6
309bc
409b6
509b6
609b6
709b6
809b6
909b6
A09b6
B09b6
C09b6
D09b6
E09b6
Should this:
static void update_ring(uint8_t type, int16_t value) {
  ring_sum[type]+=value;
better look like that:
  ring_sum[type]+=(int32_t)value;
It looks like sum is calculated wrong.. SUm is e910  this is 18 * 09b6
SUe910
AV0f89
009b6
109b6
209b6
309b6
409b6
509b6
609b6
709b6
809b6
909b6
A09b6
B09b6
C09b6
D09b6
E09b6
OK so the bugs are = corrected bugs look like:
a) static uint8_t ring_used=0;
b)
c)
  ring_sum[type]-=(int32_t)ring_buf[type][ring_pos];
  if (ring_used>=AVERAGE_LEN) {
The main reason is that update_ring is called more often than shif_ring
during the phase were ring_used is less than average_len
d) Another question:
switch (++state_ADC) means präfix ++
is this OK then for noise protection:
 state_ADC=3;
 state_ADC=5;
my preliminary adc.c - see attachement
in attachement find next step preliminary boost function with time
calculation.
description http://embdev.net/topic/118781?goto=2130451#2129904
I found, where was battery measurement problem. Normally it call
update_ring twice (one for battery, one for temperature). And shift_ring
only once after measure finish. But noise cancellation loop can cause,
that measurement repeats many time and next second pulse come earlier.
It restart measures. It repeat update_ring without shift_ring and this
situation with (ring_used<AVERAGE_LEN) create this problem.
Fixed in rev 355, change is here:
http://openhr20.svn.sourceforge.net/viewvc/openhr2...
Option BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE added
Option BOOST_CONTROLER_AFTER_CHANGE added.
Richard, please check it (contain one small difference to your code)
Jiri, THX
switch (++state_ADC) ..... ++ here means increment before operation !!
 state_ADC=3;
 state_ADC=5;
I will check the new code tommorow ...
BTW: After 10-15 hours I had this error today .. what is the typical
reason for ir ?
    if (motor_timer>0) { // normal stop on wanted position
            if (MOTOR_calibration_step != 0) {
                CTL_error_jr =  1; //jr CTL_ERR_MOTOR;
(++state_ADC) is correct, next call not execute step 3(5) but 4(6)
Reason for your error is overload maximum volume of pulses during
calibration. (see to MOTOR_MAX_IMPULSES)
Battery voltage error fix was not complete. Updated.
"Reason for your error is overload maximum volume of pulses during
calibration. (see to MOTOR_MAX_IMPULSES)"
Can it be another reason, because there was no clalib sceduled after
valve was installed ????
- Maybe it started calib for another reason (not saturday 10:00) - why
would it do that ???
- It might have something to do with the boostfunction. It moves valve
to MAX and later back to MIN ????
R359 THX Jiri:
1.adc I dont understand the -1, because we want to fill all 15
positions(0-14) before we calc average. ring_used runs as ring_pos from
0 to 15 !!!
With -1 we start calculating after 14 (pos=0-13) entries. So pos[14] is
still=0. This way the first calculated average will be wrong ???
if (ring_used>=AVERAGE_LEN-1) { // note for "-1", last measurement can
update ring_average
2.controller line 171 has to be moved after line 200, because
boostdedection needs temp_wanted last see line ~334
line 200      }
       COM_print_debug(0);
3. See last post. I still dont understand where my E3 can come from. As
I marked the different E3 errors with E31-E34, it must be the one I
posted... Why should it calibrate ? why should this gi wrong then ? Low
Voltage on a long valve move ???
1. It is simple. In this case, we have 15 complete measurement. In table
(0-14), ring_pos=ring_used=14. But ring_used will be incremented later.
It is reason to compare with 14, not 15.
2. Changed in Rev 360
3. calibration is not start after set position to min or max. I start
after valve mount  reboot  every Sat 10:00 Never else. And see to
condition for this error (MOTOR_calibration_step != 0) it means
calibration on progress or calibration error before this.
New idea for reverting:
Build a moving average of sumerror from max. n(should last for a week or
so...e.g. 255) values. Only use an sumerror for average, if error is
small (<0,3) and stable.
Average is built only after update (typ. 1-4x per day). I need your help
on a simple idea to handle it like the temp_ring_average !!
    if (updateNow) {
      if ((absErr==lastAbsError) && (absErr<(I_ERR_TOLLERANCE_AROUND_0<<1)) //stable error & error < 0,3°C)
        && (average_sumerr_count<=255) ) {
      average_sumerr_count++;
      lastTempChangeSumError += (sumError-lastTempChangeSumError)/average_sumerr_count; //average of sumerrors
Revert only is done, if the error could not be reduced by 25% and the
error is larger than 3.g. 0,3°C
static void testIntegratorRevert(uint16_t absErr) {
  if (absErr>=(lastTempChangeErrorAbs>>2*3) && absErr > (I_ERR_TOLLERANCE_AROUND_0<<1)) {
  // if error could not be reduced to 3/4 and Error is larger than 0,3°C
  // if (absErr>=(lastTempChangeErrorAbs/2)) {
    // revert Integrator to previous state if current error is not smaller than 1/2  of original
    sumError=lastTempChangeSumError;
  lastTempChangeErrorAbs = 0xffff; // function can be called more time but only first is valid
Richard:
first - we don't have space for average buffer (used 685 bytes (66.9%
Full) but without unknown stack size on top)
second - something like "stable" error not exist. See here to real data
http://embdev.net/attachment/102842/1.png
third - exist only one correct way. This mean make model function and
use regression analysis to find unknown parameters on real time.
testIntegratorRevert is updated
note: price of this change is 80bytes in flash (0.5% of size)
OK,
1. of course I am looking forward to your math model !!
I know that there is no real stable error....
Actually  the posted version works without ringbuffer anyway (less
code). But I have to think about a better moving of the average... right
now moving stops after 255 values...
2. in line 308 it was (I_ERR_TOLLERANCE_AROUND_0<<1). This way it only
revert on errors >= 0,3°C ...
3. Jiri why did you solve that with so many #if #else ?? is it less code
? Because this simple change based on 359 was easier to undestand (for
me;-) ...
        if (updateNow) {
        if ((PID_update_timeout == 0)) {
      UPDATE_NOW:
            PID_update_timeout = (config.PID_interval * 5); // new PID pooling
      uint8_t new_valve;
                new_valve = config.valve_max;
            } else {
                new_valve = pid_Controller(calc_temp(temp),temp_average,valveHistory[0],updateNow);
        int8_t i;
        #if BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE
          if (valveHistory[0]!=new_valve) {
            CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK;       //block Integrator if valve moves
        #endif
        for(i=VALVE_HISTORY_LEN-1; i>0; i--) {
          if (updateNow || (new_valve <= config.valve_max) || (new_valve >= config.valve_min)) {
            // condition inside loop is stupid, but produce shorter code
            valveHistory[i]=new_valve;
          } else  {
            valveHistory[i]=valveHistory[i-1];
2. ???? Where is problem ?
3. I know that it is little bit complicated. But try it and you will see
difference in code size. This code is significantly smaller for
BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE = 0
ad2) I_ERR_TOLLERANCE_AROUND_0
<<1
 missing
<<1 why?
"<<1" opps, I see, fixed
a) I am curious why you used *2: Does <<1 not work with constants ?
another C thing:
b) When do we declare variables "static" in HR20
c) is an "extern" declared variable automatically "static" ? example is
"lastTempChangeSumError" is static, but as I wanted it beeing sent over
COM I had to declare it extern ...
deleted
a) *2 is better for reading. Because is is constant, it is not need
optimize it for execution.
b) "static" is for local only variables and function. "static" function
have one more benefit, it can be linked into call point and it is nice
for compiler optimization.
c) if you need use variable or function outside "C" file it can't be
static.
THX:
     #if ! BOOST_CONTROLER_AFTER_CHANGE
      if (updateNow) {
172 CTL_temp_wanted_last=temp;
    #else
      if (updateNow||(PID_update_timeout == 0)) {
    #endif
            uint8_t new_valve;
            if (temp>TEMP_MAX) {
            } else {
                new_valve =
187 #if BOOST_CONTROLER_AFTER_CHANGE
188 if (updateNow) {
189  CTL_temp_wanted_last=temp;
     #endif
Jiri,
a) I think line 172 (CTL_temp_wanted_last=temp;) can be at the end
=line189 in both cases... (I checked that already)
b) so we can also forget the #if from 187
c) and the if in 188 is not needed. It does not matter if
CTL_temp_wanted_last is set under any condition more often...
OK I clean up this code.
note: price of moving "CTL_temp_wanted_last=temp;" line is 8 bytes. We
has code bigger than flash already. Current code uses MANY hack to
optimization.
Jiri you can also keep it, your decision, I can live with it,
Then just delete the if from line 188...
THX Jiri
R362:
Program:   13398 bytes (81.8% Full)
Data:        485 bytes (47.4% Full)
EEPROM:      392 bytes (76.6% Full)
R363:
Program:   13392 bytes (81.7% Full)
Jiri, I had this E31 error again - please comment on this
When I mounted the valve it was nearly fully open (12 pulses) .. when
the error came up it was fully closed (i nearly could not move it any
further by hand)
Values when E31 came up:
MOTOR_PosMax=12
MOTOR_PosAct=fde9
MOTOR_PosOvershoot=1
MOTOR_counter=23b
The next time calib was OK:
MOTOR_PosMax=2c6
R363 with RFM and normal "wheel" settings
Program:   16022 bytes (97.8% Full)
Data:        690 bytes (67.4% Full)
EEPROM:      400 bytes (78.1% Full)
but with CTL_temp_wanted_last=temp; like previous versions
Program:   16014 bytes (97.7% Full)
16022 means 362bytes free and it is less than 181 AVR machine
instructions.
Not nice.
I think we could save some bytes, because with I_ERR_TOLLERANCE_AROUND_0
we have covered this good enough ...
if ((error16 >= 0) ? (old_result < config.valve_max) : (old_result >
        if (  // ((lastErrorSign != ((uint8_t)(error16>>8)&0x80)))
        ((absErr==lastAbsError) && (absErr<=I_ERR_TOLLERANCE_AROUND_0)))
{  //abserror around 0
and please set the error variables to an invalid value and they have to
be different
please comment on my E31 from above
the post timed out...  and please set the error variables to an invalid
value and they have to be different:
static uint16_t lastAbsError = 0xFF;  //set invalid
static uint16_t last2AbsError= 0xFE;  //set invalid and different to
lastAbsError
E31 means here ?
                MOTOR_calibration_step = -1;     // calibration error
                CTL_error |=  CTL_ERR_MOTOR;
Strange. MOTOR_PosMax-MOTOR_PosAct = 552[dec]
But mininum posion for this error is  (MOTOR_PosMax-MOTOR_MAX_IMPULSES)
= -982 = 0xFC2A And this position was not reach.
Motor stops in 2 conditions:
- reach to final positon (not happen)
- motor slow down or stop mechanicaly, but in this condition is
motor_timer==0
This mean, that it can't be this error, or we have some bug in code.
what was in motor_diag (trace variable 0x05)
menu.c ...E35 is spare
                } else if (CTL_error & CTL_ERR_MOTOR) {
                    if      (CTL_error_jr==1) {
            LCD_PrintStringID(LCD_STRING_E31,LCD_MODE_ON);
           } else if (CTL_error_jr==2) {
             LCD_PrintStringID(LCD_STRING_E32,LCD_MODE_ON);
           } else if (CTL_error_jr==3) {
             LCD_PrintStringID(LCD_STRING_E33,LCD_MODE_ON);
           } else if (CTL_error_jr==4) {
             LCD_PrintStringID(LCD_STRING_E34,LCD_MODE_ON);
           } else if (CTL_error_jr==5) {
             LCD_PrintStringID(LCD_STRING_E35,LCD_MODE_ON);
                } else if (CTL_error & CTL_ERR_BATT_WARNING) {
LCD.c... in any language
      {32,14, 3, 1},    //!<  " E31"    LCD_STRING_E31
      {32,14, 3, 2},    //!<  " E32"    LCD_STRING_E32
      {32,14, 3, 3},    //!<  " E33"    LCD_STRING_E33
      {32,14, 3, 4},    //!<  " E34"    LCD_STRING_E34
      {32,14, 3, 5},    //!<  " E35"    LCD_STRING_E35
      {32,14, 4,32},    //!<  " E4 "    LCD_STRING_E4
it is this code position for sure 99,99% ... I used the motor diag watch
for something else ;-)
it seems like it happens only after I flashed a new programm and had the
batteries out ... can this be a trace ??
I just tried to dismount, batteries out/in, remount 5 times ... no error
when calib goes OK. motor_diag on this valve runs typ at 5c0 and at the
close position it is 784
OK. But what is E31?
I have 4 different error messsages for the 4 different code lines of E3
(E31-E34  see last posts)
E31:
                CTL_error_jr =  1; //jr CTL_ERR_MOTOR E3(1)
...menu.c
Any idea how I can reproduce the prob. ??
see to my post from 2011-04-08 16:51
1. I think we could save some bytes, because with
we have covered the sign change as well ... delete highlighted line
  if (
 // ((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) ||
     ((absErr==lastAbsError) && (absErr<=I_ERR_TOLLERANCE_AROUND_0))) {
//abserror around 0
2. please initialize the error variables with an invalid
lastAbsError
3. I use a moving average for reverting ... this way the problem of
short periodes (some days, depending on I_SUMERR_CHANGE_WEIGHT ) with no
heating looks quite well ...
    if (updateNow) {
      if ((lastAbsError==last2AbsError) &&
(lastAbsError<(I_ERR_TOLLERANCE_AROUND_0*2))) {//stable error & error <
0,3°C)
      lastTempChangeSumError += (sumError-lastTempChangeSumError)/I_SUMERR_CHANGE_WEIGHT;
      //imapct of SumErr changes on lastSummError, averaging for integrator revert
      // lastTempChangeSumError = sumError;
#define I_SUMERR_CHANGE_WEIGHT 10  // impact on lastSumError which is
used for reverting
1) I thing that it is not covered, this is reason :
(absErr==last2AbsError). See here
Except this I thing that zero cross is better than something
with(absErr==last2AbsError)
2) You are right, it is best practice. But because situation in flash
space is critical, I will use it only if it really needed. I thing, that
0 not make any problem.
3) Why? You don't need make any average from stable value. If this value
is not almost stable, something is wrong. We need solve causation, not
mask result.
ad1) (absErr==last2AbsError) this prevents, that we give credit, if
temperature rushes up/down = ext. influence. In your example I guess it
was P part and not integrator moving the valve. So a fast change of sign
should not be handled by I-part and a slow change is covered by
"dedection around 0"... I live quite well for a while without the sign
dedection, but loosened the restriction (absErr==last2AbsError) to
(absErr==lastAbsError)...
ad2) well, directly after boot, temp is updated and comparisons like
this go wrong then.. but I can live with that ... your decison...
0,3°C)
        // && (average_sumerr_count<255) ) {
ad3) Because right now - in times where heating is deactivated temporary
by high outside temps during day or night ... the actual code
produces more wrong reactions (I-parts) than a continous averaging:
(sumError-lastTempChangeSumError)/I_SUMERR_CHANGE_WEIGHT;  // weight
e.g.=10
I thik this is a compromise (with liitle code) until we find a better
(math) solution for revert
here is a quick status from my side which includes:
NO_AUTORETURN_FROM_ALT_MENUES=-DNO_AUTORETURN_FROM_ALT_MENUES=1
BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE=-DBLOCK_INTEGRATOR_AFTER_VALVE_CHANG
E=1
BOOST_CONTROLER_AFTER_CHANGE=-DBOOST_CONTROLER_AFTER_CHANGE=1
and a modified code for reverting (posted above, value Isl in the chart)
Valve MAX=80, MIN=CENTER=52, Credit_expiration=255
I changed MAX to 96 around 13:00, 80% did not open the valve wide
enough. This way boost function works more effective.. room gets warmer
about 0,7° within 1 hour ... during this valve reverted SumError=Is
(vlack line) to lastSumError=Isl (moving average with 10% impact of
SumError ... see black dotted line)
Heating was OFF from 22:00-4:30..
@Jiri:
I found some bugs in my code (BOOST) and deleted unnecessary EEprom
variables ...
Could you please integrate the changes from OpenHR20_R363_mod110417.zip
in a new revision ... THX
Jiri:
I mailed the changes to you... as your mailbox seems to be full I add
the .zip here ...
Also my last MAil returned .. so I post the changes here: The files are
zipped in my last post ;-)
com.c 309
 print_s_p(PSTR(" bo: ")); //jr
 print_hexXX(PID_boost_timeout);
 print_s_p(PSTR(" Iac ")); //jr
 print_hexXX(average_sumerr_count);
 print_s_p(PSTR(" Isl "));
 print_hexXXXX(lastTempChangeSumError>>16); //jr
 print_hexXXXX(lastTempChangeSumError); //jr
controller.c:
60:
 uint8_t PID_boost_timeout;  //boost timout in minutes
 uint8_t PID_boost;  //boost value, either valve max or min
#endif
183: cosmetic:
      CTL_integratorBlock=CTL_INTEGRATOR_BLOCK;       //block Integrator if valve moves
248:
   PID_boost_timeout = 0; //to disable boost change mode, then change setpoint and change back mode
271:
static uint16_t last2AbsError= 0xFE;  //set invalid and different to lastAbsError
290:
static uint16_t lastTempChangeErrorAbs=0xffff;
int32_t lastTempChangeSumError=0;
uint8_t average_sumerr_count=0; // counting # of averages, just for diagnosis purposes
296: just comment:
  // if error could not be reduced to 3/4 and Error is larger than I_ERR_TOLLERANCE_AROUND_0*2 °C
320:
    CTL_integratorBlock=CTL_INTEGRATOR_BLOCK; // do not allow update integrator immediately after temp change
    if ((lastAbsError==last2AbsError) && (lastAbsError<(I_ERR_TOLLERANCE_AROUND_0*2))) {//stable error & error < 0,3°C)
     average_sumerr_count++;  //just for diagnosis, how often do we average
     if (absErr>=(int16_t)config.temp_boost_error) {  // error large enough to start boost (0,3°C)
    if (error16 >= 0) {
     PID_boost = config.valve_max;
     PID_boost_timeout = config.temp_boost_time_heat;
    } else {
     PID_boost = config.valve_min;
     PID_boost_timeout = config.temp_boost_time_cool;
    PID_boost_timeout = (uint8_t)(MIN(255,abs(error16)/10*(int16_t)PID_boost_timeout/CTL_BOOST_TEMPCHANGE)); //boosttime=error/10(0,1°C)*time/CTL_BOOST_TEMPCHANGE(0,5°C)
340:
 this prevents, that we give credit, if temperature rushes up/down = ext. influence. In your posted example I guess it was P part and not integrator moving the valve. So a fast change of sign should not be handled by I-part and a slow change is covered by "dedection around 0"... I live quite well for a while without the sign
dedection
    if (  // ((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) ||  //sign of last error16 != sign of current
    ((absErr==last2AbsError) && (absErr<=I_ERR_TOLLERANCE_AROUND_0))) {  //abserror around 0 with slow change
370:
  return PID_boost;  //return valve_MAX or MIN
  #endif
eeprom.h:
~100:
 /*    */ uint8_t  temp_boost_error;
 /*    */ uint8_t  temp_boost_time_cool;
 /*    */ uint8_t  temp_boost_time_heat;
#endif
~250:
  /*    */  {30,          30,       10,      255},   //!< temp_boost_error,start boost if error to new setpoint is larger than this,unit0,01°C
  /*    */  {64,          64,        0,      255},   //!< temp_boost_time_cool, minutes boost should last during heat up, if error = CTL_BOOST_TEMP_CHANGE(0,5°C)
  /*    */  {48,          48,        0,      255},   //!< temp_boost_time_heat, minutes boost should last during cool down, if error = CTL_BOOST_TEMP_CHANGE(0,5°C)
#endif
controller.h
~63:
#define CTL_INTEGRATOR_BLOCK 6    //jr was=6
#define I_ERR_TOLLERANCE_AROUND_0 15 // unit 0,01°C. Set it quite restrictive !
#define I_SUMERR_CHANGE_WEIGHT 10 //imapct of SumErr changes on lastSummError, averaging for integrator revert
#define CTL_BOOST_TEMPCHANGE 5 //unit 0,1°C, estimated change of temp during boosttime, for calculating boost time
80:
extern uint8_t PID_boost_timeout;
extern uint8_t CTL_creditExpiration;
extern int32_t lastTempChangeSumError;
extern uint8_t average_sumerr_count;
motor.c: 111
watch.c:
    /* 00 */ ((uint16_t) &sumError) + B16,
    /* 01 */ ((uint16_t) &CTL_integratorBlock) + B8,
    /* 02 */ ((uint16_t) &CTL_interatorCredit)+ B8,
    /* 03 */ ((uint16_t) &PID_boost_timeout)+ B8,
 /* 04 */ ((uint16_t) &average_sumerr_count) + B8,
    /* 05 */ ((uint16_t) &lastTempChangeSumError) + B16,
 /* 06 */ ((uint16_t) &MOTOR_PosMax) + B16,  //12  az:2c6 bad:22c
 /* 07 */ ((uint16_t) &MOTOR_PosAct) + B16,  //fde9  az:18d bad:c4
 /* 08 */ ((uint16_t) &MOTOR_PosOvershoot) + B8, //1
#if DEBUG_MOTOR_COUNTER
 /* 09 */ ((uint16_t) &MOTOR_counter) + B16,  //23b
 /* 04 */ ((uint16_t) &motor_diag) + B16,
// /* 0a */ ((uint16_t) &MOTOR_counter)+ 2 + B16, //0
#endif
Hi Jiri - are you still there ? - I would like to finish up, before the
summer comes and I forget everything .... ;-)
RE: "Can you generate "diff" file? (for ex in TortoiseSVN)"
Sorry, no know how in those things ...
a) either you instruct me or
b) I could also edit the changes into R363 files and send you those ..
Author: jdobry (Guest)
I am still here. But I am too busy on another tasks till end of may.
Ok .. then we'll clean up end of May/June ... BR .. Richard
Author: transis (Guest)
Need some help. I receive following error msg during compiling:
**** Build of configuration Debug for project HR20 ****
make all
Building file: ../src/lcd.c
Invoking: AVR Compiler
avr-gcc -Wall -g2 -gstabs -O0 -fpack-struct -fshort-enums -std=gnu99
-funsigned-char -funsigned-bitfields -mmcu=atmega169p -DF_CPU=1000000UL
-MMD -MP -MF"src/lcd.d" -MT"src/lcd.d" -c -o "src/lcd.o" "../src/lcd.c"
../src/lcd.c: In function 'LCD_HourBarBitmap':
../src/lcd.c:627: error: r28 cannot be used in asm here
../src/lcd.c:627: error: r29 cannot be used in asm here
make: *** [src/lcd.o] Error 1
**** Build Finished ****
lcd.c revison: 192
how can i fix this error(s)?
transis: Which compiler? Please try WinAVR-20100110.
it is already the compiler: WinAVR-20100110 !
I've also tried to compile it with AVR-Studio 5 => same compiler
error(s):
Error 1 r28 cannot be used in asm here ...\lcd.c 627 1  OpenHR20
Error 2  r29 cannot be used in asm here ...\lcd.c 627 1  OpenHR20
Error:
Fix-Proposal:
   modify line in lcd.c
     : "r14", "r15", "r16", "r28","r29", "r30", "r31"
   to:
     : "r14", "r15", "r16", "r30", "r31"
after this modification the compilaton will pass.
What are the side-effects of this fix?
(I'm not so experienced with assembler coding ...)
Problem is that this line not create any code. It just inform compiler
optimizer about used registers. If you remove it, ASM code rewrite this
registers and compiler will not know it. It will fail.
Are you sure that in compilation you use  WinAVR-20100110 ? It is tested
with this without problem.
yes, i am sure. It is the compiler "WinAVR-20100110"! But this errors
was also reported by AVR-Studio5. I think it is not a compiler specific
problem.
Hello again,
I've tried to compile it with "release" setup, and it is
compiling.(Before, it was in the "debug" setup => with this setup i got
the above mentioned errors.)
are the compiling options wrong?
release-setup:
   avr-gcc -Wall -Os  ...
debug-setup:
   avr-gcc -Wall -g2 -gstabs -O0 ...
After some further testing....
The parameter/option "-O0" raise this errors. When i am select one of
the other optimization levels "-O1..3" the errors are not occured.
Can someone explain me this crazy behavior?
Author: Marco G. (stan)
-O0 means no optimization, so it seems that without optimization these
two registers are necessary for the C code and then the compiler
complains.
Author: transis __ (Company: manmen) (transis)
sounds plausible. ;-)
What will be the workaround/fix (is it a bug?)
Why this error was only reported/seen by me (i think the compilers with
same options should report same errors...)?
I any way, compile it for debug with -O0 have not solution. Simply
before code will be too big for only 16kB flash.
Hi Jiri, hope you have/had a good summer ... can we continue to
integrate the changes from post http://embdev.net/topic/118781#2153401
BR Richard
@ Richard G.:
I review this changes, and it is not possible use as is. It contain many
other changes that only core. It is not encapsulated into ifdef. And I
has not time to rewrite it.
Please send me it as "patch", or I must say sorry for this moment. I
have some urgent concern to solve.
Jiri
Jiri, what you mean with patch ? example please
Author: Chris (Guest)
Hi!
I flashed 7 rondostates with the firmware of 29.8.2011. It seems to me
that the vent does not open, even if the room is too cold.
Example: Temperature is 18,7, wantet temperature is 20, Vent is about
55-60%. (max vent position 96, min position 30).
Maybe I have to set min position to a higher value, because the vent
closes at about 45%?
Chris
Author: Holger T. (holgert)
I plan to buy RFM12(x) modules to use with HR20E. What are the correct
types to use?
Currently I prefer:
RFM12 for MASTER (because it is specified for 5V)
RFM12B for all (Rondostat-) slaves  (because it is specified for 3,3V).
What frequency should be used: 433MHz vs. 868MHz?
What types are supported by current existing SW? (I didn't find any
switch in source code to choose B-Type or 433/868MHz)
Thank you for some useful suggestions.
-Holger
Author: Frank (Guest)
I want use some HR20 as central control. Temperatures are measured
externally. To to this i have extended the firmware:
1. Improved input operation in com.c
2. Serial Bus mode Ixx enables the communication with ID=xx all other
devices are silent.
3. Override measured themperature via Oxxxx
4. Debug prints free RAM
With 2. i have an problem. Variable 0x27 holds the bus id but i cannot
change this. 0x27 is allays set to 0xff
By the way:
5. i can communicate only with 1200 baud when i set COM_BAUD_RATE to
1140 on higher speed i receive no correct characters.
6. the hr20 prints 22.6°C while an DS1820 messures 24.87°C
7. i have changed the boot loader to fastboot. With lboot i can flash
with 115200 baud
@Holger T.: I use 868MHz modules. RFM12B is improved version of RFM12. I
recomend new.
@Frank: Thanks for patch I will try it later.
add 5) see to http://atmel.com/dyn/resources/prod_documents/doc2555.pdf
add 6) HR20 use only cheap thermistor. But you can calibrate it in
EEPROM
add 7) I don't use bootloader. Reason is some temporary problems with
flash space and in this case, every byte is needed.
Hi Jiri, as wanted here is the Tortoise SVN patch...
Only those chenges are relevant:
http://embdev.net/topic/118781?page=4#2153401
Explanations start here http://embdev.net/topic/118781?page=4#2140184
I have written an r/c clock calibration code. I uses no timers other
than rtc and no interrupts. I thin this code is good enough to call it
periodically to avoid communication problems while voltage or
temperature is changing.
Jiri, you remember I also had calibration errors last year.... again
this year on different valve..
It is the error from the else part (my ident CTL_error_jr =  2)
                    if (MOTOR_ManuCalibration==0) {
                        if (a >= MOTOR_MIN_IMPULSES) {
                            MOTOR_ManuCalibration = a;
                            eeprom_config_save((uint16_t)(&config.MOTOR_ManuCalibration_L)-(uint16_t)(&config));
                            eeprom_config_save((uint16_t)(&config.MOTOR_ManuCalibration_H)-(uint16_t)(&config));
                            MOTOR_calibration_step = 0;
                        } else {
                      CTL_error_jr =  2; //jr CTL_ERR_MOTOR;
MOTOR_PosMax 47, MOTOR_PosAct 47, MOTOR_PosOvershoot 2,
MOTOR_counter 5E6, motor_diag 779
How it happens:
1 I pressed a button and got E2 (valve not mounted, maybe I pressed to
hard ;-)
2 I took valve off
3 I set the heater valve head manually near full open
4 put valve back on
5 valve starts adapting and stops with the error on full open position
I took it off again and repeated from 3. Same error again ...
Then I took battery out and repeated from 3. No more error !
Hi Jiri,
I too experienced a E3 error and could not find any reason for it, but
it could be because I used empty batteries.
With current version, I have 2 main problems:
1: The window open function still triggers randomly, for example if the
central heating goes out for a few minutes and there is a slight drop in
temperature. I tried different eeprom settings to disable the window
open detection, but it still triggers.
2: With default settings, valve is always around 50%. Our water
temperature is only high enough to reach wanted temperatures, but only
if vents are at about 90%. So I increased the value for valve-center.
Problem is that valve is opend or closed with a too flat curve. For
example, when wanted temperature is 20 and real temperature is 21, valve
only closes a little bit, which is not enough.
I think I have to change impact of P-Part of the controller?
Chris
Author: Bernard K. (bernard_k)
Hi all,
I've been reading this, and the other German thread (through google
translate), along with the documents referenced in those, but still have
some questions.
I currently have one HR20 and one HomExpert HR20Style. As soon as I get
everything working I will purchase 7 more HR20Style (since they're
cheaper than the original HR20.)
My goal is to power and control the thermostats over wiring already
present for this purpose.
What I need to do is to set the desired temperature, and read the actual
temperature. Reading the valve state would be a plus.
I now have the HR20 hooked up (it's SW 204), and can read the
information it sends me (fe.: "K: 0b1 [0x0D][0x0A]>")
I cannot successfully send it any commands, I always get the message
"Error in command[0x0D][0x0A]>"
After a while any commands I send it are ignored. (I assume the device
has gone to sleep.) I have not found a way to wake it up.
Apparently all this is because the information I'm using concerns the
protocol of an earlier hardware version (with a NEC chip instead of the
Atmel AVR mine has?)
I have not found a protocol specification for the SW 204 specifically.
Is it possible to control the SW 204 in the same way as the earlier
edition? If so, could someone point me to the correct protocol
specification?
If not, then I assume I will need to flash the HR20 with OpenHR20? I
have a ICSP programmer, but as I understand it I cannot use this unless
I actually open up the HR20 and solder some extra wires to it?
So I've ordered a cheap AVR JTAG ICE from ebay (I figure I'll be able to
use it later for other purposes anyway, even if I don't need it after
all.)
If I'm correct so far, these would be the steps required to flash the
HR20?
* I will not be able to connect the JTAG connector directly to the HR20
and will need to make some wires to connect the right pins to the JTAG
connector.
* I will then use avrdude (I do not have any Windows) to upload the file
hr20.bin to the HR20 using the AVR JTAG ICE.
* Afterwards, I can use the OpenHR20 protocol to accomplish my goal.
I've checked out the svn repo, and have also downloaded the v1.0
zipfile.
I see no .bin files inside the svn repo.
Is the zipfile's original_sww/hr20.bin the file I need, or would you
recommend (considering my goal) to compile one from the latest svn
source instead?
If I need to compile a bin file, could you tell me how to do this? My C
knowledge is very limited, so the correct avr-gcc (if that is the
correct application?) command line would be very helpful.
All the thanks,
Bernard Kerckenaere
Author: Jiri Dobry (Guest)
Bernard K:
- serial protocol for original SW 204 is unknown.
- I don't known if HR20 style contain same HW as HR20. Please check it
ane tell us results.
- You are right ICSP can't be used without open valve and soldering.
- connector on HR20 have't same layout like AVR JTAG, you will need
special cable.
- I am not using Windows too. You need "avr-gcc" package. On actual
source directory simple start "make". I recommend do it in "rfmsrc"
directory and result hex files will be on "bin"
- Here is TESTED avrdude commands. You will probably need both in same
order. Without first is impossible rewrite EEPROM.
avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -U hfuse:w:0x19:m
avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -e -U flash:w:hr20.hex -U eeprom:w:hr20.eep -U hfuse:w:0x11:m
update: for compile under linux you need "gcc-avr" and "avr-libc"
@Jiri, @Bernard
I have flashd without soldering. All ISP pins are on the connector and
under the tree keys. The display can be easy removed from battery side.
With fastboot
http://www.mikrocontroller.net/articles/AVR_Bootlo...
the new firmware can be flashd via serial cable.
This is my modified Makefile:
--- Makefile.orig    2011-09-29 10:50:21.000000000 +0200
+++ Makefile    2011-09-29 11:02:07.015224003 +0200
@@ -37,7 +37,7 @@
 # MCU = attiny85
 # MCU = atmega2560
 # MCU = atmega1281
-MCU = atmega8
+MCU = atmega169p
 # Name of the Atmel defs file for the actual MCU.
@@ -50,16 +50,16 @@
 # files" and unzip it in the same directory as this Makefile.
 # Examples (select one of them or add your own):
-# ATMEL_INC = m168def.inc
+ATMEL_INC = m169def.inc
 # ATMEL_INC=m64def.inc
 # ATMEL_INC=tn85def.inc
 # ATMEL_INC = m2560def.inc
 # ATMEL_INC = m1281def.inc
-ATMEL_INC = m8def.inc
+#ATMEL_INC = m8def.inc
 # Processor frequency.  The value is not critical:
 #F_CPU = 14745600
-F_CPU = 8000000
+F_CPU = 4000000
 #     AVR Studio 4.10 requires dwarf-2.
 #     gdb runs better with stabs
@@ -68,11 +68,11 @@
 # Define the Tx and Rx lines here.  Set both groups to the same for
 # one wire mode:
-STX_PORT = PORTD
-STX = PD1
+STX_PORT = PORTE
+STX = PE1
-SRX_PORT = PORTD
-SRX = PD0
+SRX_PORT = PORTE
+SRX = PE0
 ####### End user presets ######################
This is my avrdude call. You need the EEPROM image from OpenHR20
sudo avrdude -c usbtiny -p m169 -u \
        -U flash:w:bootload.hex \
        -U eeprom:w:../OpenHR20/openhr20/trunk/source/hr20.eep \
        -U efuse:w:0xfd:m \
        -U hfuse:w:0x94:m \
        -U lfuse:w:0xe2:m
I am sorry, in avrdude commands I write invalid hfuse. Here is correct:
avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -U hfuse:w:0x99:m
avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -e -U flash:w:hr20.hex -U eeprom:w:hr20.eep -U hfuse:w:0x91:m
Thank you very much for all the information, I really appreciate it!
I'll wait for my JTAG programmer to arrive (it's on its way, and looks
to be a bit easier to use than ISP), and will then try and verify
whether I can flash and get the sought after results on both the HR20
and the HR20Style.
Again thank you!
Richard G: your patch file "richard363_111008.patch" is not possible
apply to fresh 363 revision. You probably made same mistake.
Jiri: I thought it might be a good idea to just include the files with
major changes. Otherwise you will also get beautifiing stuff ... do you
want them all ?
Author: rps (Guest)
Hi!
Did anybody consider adding 1-wire connectivity yet?
(Axel_5 mentioned something in other threads but no details.)
This could use the one free pin in the connector (PE2 I think). No need
for Hardware adaptions.
The device could mimic multiple "standard" 1-wire devices:
- a temperature sensor (RTC value)
- ADC (valve target position)
- EEPROM (non-volatile config)
- RAM (current state)
perhaps even:
- switch/PIO (for buttons) but this would possibly be missed when
polling is intentionally slow.
User interface would need the possibility to configure the address.
I'm thinking of semi-autonomous operation - current target mode and
timetable are uploaded regularly, temperature values are centrally
logged.
Full "slave mode", just using the temperature sensor, the valve actor
and the wheel and buttons for user requests and doing the rest centrally
would also be possible.
I plan to implement this, but would like to hear your thoughts.
Author: Bruce A. (bruce_a)
I got the first HR20-E flashed with JTAG last night. I'm very impressed.
So thanks. Now, my question, assuming this is the right forum for
this...
I also got an HR-25
(http://www.homexpertbyhoneywell.com/en-DE/Products...)
which has a very, very similar PCB to the HR-20. It has a MEGA329P on
board and a fancier LCD and only a couple of extra tracks/vias that I
can spot. I'm tempted to get more of these instead for the nicer LCD and
bigger code space.
Before I go reinventing wheels, has the OpenHR20 code been ported to
this, the LCD mapped out etc.? i.e. has anyone done work already on
supporting the HR25?
Author: Axel Laufenberg (axel_5)
I can upload my code tonight.
However I have forked this a long time ago, so maybe it is quite
difficult to merge this in the current branch.
Basically the temperature can be read as a simple 1-wire temperature
sensor, target temperature can be set. The value of the valve can also
be read.
However power consumption is quite high as I have removed all sleep
modes as the device is always powered through the cable. Also the
timetable is removed as this is now done by the central controller.
Best regards
Axel
Author: Jiri Dobry (jdobry)
@Axel Laufenberg:
If you want store your code into repository please contact me on
jdobry-at-centrum-dot-cz and send me your account name from sourceforge.
Is it based on trunk(I will not make improvements) or rfmsrc
(recomended)?
If it is encapsulated to "ifdef" preprocessor you can add this into
current code. Otherwise please create new branch in repository.
Sorry, I do not have time right now to add to the repository, I just
spent some time to translate most of the stuff into English. And I
recognized that I used a version from 2008, so I guess this does not
have too much in common with the current version.
Actually only the attached files are affected. The main.c only gets the
additional function to assign the values received and transmitted
from/to the onewire interface and gets the sleep mode disabled.
motor.c is changed because the external interrupt is used. This now has
to handle also the 1-wire edge handling. The file onewire.c handles the
timing for the onewire. I just recognised that the ISR is in the code
twice, once within the motor.c and once in the onewire.c. Actually it is
only used in motor.c as otherwise the interrupt routine may be too slow.
Actually you should be aware that the AVR needs to be clocked at 8 Mhz,
otherwise it is too slow to handle the onewire timing.
I tried to document as good as possible, so it should be no problem to
add this to the code.
If I find the time I can try to make this all a bit nicer and merge it
with the repository, but ....
So I hope this is in any case helpful to somebody, if you have questions
please feel free to ask.
Axel
Author: Rupert Schlick (rps)
@Axel:
Wow, thanks a lot - mostly what I hoped for. It's a pity that it will
need to run on 8MHz.
The code looks good and well documented too (and I have no problem with
the german parts ;-) ).
@Axel&Jiri:
When I have this running (which still might take me a few weeks), I'll
try to integrate it with the current version and into the repository.
Maybe I can even invest some of the effort saved into thinking a bit
more about the 1-wire-bootloader :-).
Rupert
I have got the LCD working on the HR25. It seems to work fine. I'll have
to wait until the RFM12s arrive before testing further. See
https://sites.google.com/site/slangey/misc/honeywell-hr25 for some more
details including pictures of the board.
I've done the changes against rfmsrc and it touches the Makefile,
lcd.c/.h and rs232_485.c/.h. I would appreciate if someone could please
review and give comments before (hopefully) getting this in to svn?
Bruce.
Bruce_a:
I made fast review and looks OK. Committed into revision 364.
PS: I made only small fix (compilation need remove one space in
rfmsrc/OpenHR20/Makefile) and modify rfmsrc/Makefile to create new
target platform files.
It looks that it can support hardware window detection and RFM without
any additional changes. But I am not create target files for this
because I can't test it.
Author: Knut Schwichtenberg (kschwi)
Is there any technical difference between HR20 and HR25 than CPU and
display? There is at least little space left in the 169 flash so it
might make sense to replace the CPU and take the HR25 SW-version.
Cheers,
Knut
Hi Knut,
It would appear just to be a CPU/LCD difference. Amtel's migration docs
suggest not much interesting has changed. The code would need just one
more target to specify the new cpu correctly. Be aware that the cheap
JTAG programmer I got off ebay doesn't program the 329 :( (see the link
in previous post). So I'm thinking RFM12b & serial bootloader... and/or
replacing the JTAG pins on the side with ISP ones.
Author: StuartP (Guest)
Hi All,
I've been watching this thread for a while now, and have taken the
plunge and purchased an HR20.
Could someone advise what is the best lowcost JTAG programmer to get
started with for the HR20.
Cheers
Stuart
Author: Bernard Kerckenaere (Guest)
I ordered this one:
New AVR USB Emulator debugger programmer JTAG ICE+Protecter for US
$10,90
Ebay-Artikel Nr. 200667489423
Thanks for the info.
Is anyone using linux to do development work & programming ? This would
be my preferred environment.