This is the new Thread about the OpenHR20 Firmware from http://openhr20.sourceforge.net . For generic Questions about the HR20, please look&ask in Beitrag "Honeywell Rondostat HR20E per AVR steuern und konfigurieren" Please write in English, thanks!
Posted on:
SVN revision 100
- improve motor control
- check EEPROM layout on startup
From this version EEPROM layout is fixed. This mean that you can enable
"preserve EEPROM" fuse and your setting can be saved.
Change EEPROM layout case is tested on code. You will see "EEPr" on LCD
after restart, startup is blocked. With empty EEPROM you will see same
message.
*I don't know any missing functionality or bug at this moment.*
Permanet problem is missing documentation generated from sources. We
need it to document "magic indexes" on setting (Gxx and Sxxxx commands)
or watches (Txx command)
Changelog:
http://openhr20.svn.sourceforge.net/viewvc/openhr2...
Posted on:
Known problem for Rev100: After change of PID constants you must change wanted temperature. Problem is teoretical internal value overload. I never saw this problem, but I found it on code review.
Posted on:
SVN revision 101
- optimizations
- overload check in pid.c
- change default setting for PID
Posted on:
SVN revision 103
- motor stop threshold for calibration / runtime can be different
EEPROM layout is changed, you can't preserve old contend.
Posted on:
@jdobry: very busy weekend! gonna try your latest release tomorrow when i have a JTAG-adapter again. gonna give you feedback about how the firmware works. will try to get familiar with the general firmware architecture then, for example questions like "how can i issue a task evry sixty seconds" which shall be the RFM's staus broadcast in sooner future... so long!
Posted on:
@ Mario Fischer: execute task every second: add it into "if (task & TASK_RTC)" section on main.c execute it every 60 second have many choices - use own counter inside "if (task & TASK_RTC)" (worst) - same section as before, but inside new "if (minute)" condition (better) - same section, add condition "if (RTC_GetSecond() == config.network_addreess)" (best) For interrupt from RFM you must add code inside "ISR (TIMER0_OVF_vect)" and set "task |=TASK_RFM12" inside. Make code inside interrupt small as is possible and move real functionality inside main.c "if (task & TASK_RFM12) task&=~TASK_RFM12; ....." f you have some code sniplets, please contact me by email. It have big priority for me at this moment.
Posted on:
Hi Jdobri!
(what is your first name? I dont know if "Hi Jdobri" is correct ;)
ok, ive downloaded the OpenHR20-rev 103 and started to play with it...
I will try to integrate a RFM status sender for first approach.
I can say now, i will have to make changes in several files. For example
main.c in
if (task & TASK_RTC) { ... if (RTC_GetSecond() == g_RFM_devaddr) ...
and so on.
I would try to encapsulate all RFM-stuff in #ifdef RFM-blocks, so a
project-fork wouldnt be neccesary.
But im not sure if i can guarantee that it will be possible to
distinguish RFM and notRFM-code clearly in all future.
So, what do you want to do?
Can you give me an SVN-Account for the project? Im sure you will be
anoyed very soon if i start to mail you my code all the time...
So, tell me your plans!
Greets from Munich,
Mario
PS: First Request: I'd like to have the global variable uint8_t
g_RFM_devaddr to be adjustable by menu (1-254, others reserved for
broadcast or future usage) and storable in EEPROM. Since youre master
of the menue it shouldnt be too difficult? ;)
Posted on:
Plan is keep latest STABLE version in main trunk and create branch for next development. By this way we can made anything include crazy ideas. You don't need change anything on menu. Simple add line into eeprom.h structure config_t and line into ee_config array. Don't forget change eeprom layout map version to something for development (exaple #define EE_LAYOUT (0xd0) ). You can read it by config.g_RFM_devaddr and change it by service menu (long press all buttons -select configuration press PROG change value and press PROG)
Posted on:
Question about the Config-Menue: Did i get this right? I can edit the Variables in eeprom.h via: 1. Pushing [AUTOMANU + TEMPSUNMOON + PROG] for 3 seconds. 2. Then display shows XX:YY, ourbar shows all bars, XX blinks 3. with the scroller i select variable number XX, then i push [PROG], then YY blinks and i can set XX's value (within the range given in eeprom.h). now its getting unclear: it looks like if i push [PROG] i'm back in selecting a XX again. is the other value now stored? or how can i cancel it (i guess via AUTOMANU] )? and what's happening if i push [TEMPSUNMOON] ? hourbar except one bar blinks, scroller selects a horbar, XX:YY shows thigs i dont understand... [AUTOMANU] always exits eeprom-edit-mode? regards!
Posted on:
Feature Request: in normal mode, [TEMPSUNMOON] shows current temp, valvepos, RTCtime, default display. i think that the RTCdate would also be interesting for a common user. regards!
Posted on:
Service mode: 1. Pushing [AUTOMANU + TEMPSUNMOON + PROG] for 3 seconds. 2. Then display shows XX:YY, ourbar shows all bars, XX blinks 3. with the scroller i select variable number XX, then i push [PROG], then YY blinks and i can set XX's value (within the range given in eeprom.h) 4. press PROG save selected value and go to step 2 any where on service menu: AUTO - escape service menu without save C - change service menu from EEPROM setting <-> watched variables and back Watched variables - see to watch.c. In this mode ALL segments are on, except 16-bit hex value on numbers and except one blinking segment on hourbar. Blinking segment indicate with values is on view. Ekvivalent COM command is "Txx<enter>"
Posted on:
RFM Pin wiring: you wired yor RFM like ths: rfm_sck = atmega169_pf1 //solder direct to atmega :-( rfm_sdi = atmega169_pf0 //solder direct to atmega :-( rfm_nsel = atmega169_pa3 //solder direct to atmega :-( rfm_sdo = atmega169_pe6 //crop via on backside of PCB as shown in picture rfm_nirq = open as discussed yesterday, rfm_nirq = open, because rfm_sdo can serve as irq-notifier. we will read the sdo-state after we drove rfm_nsel low. i assume that it will be high when the rfm is still busy sending, and edging low when ready (irq-event like "byte sent over radio in txmode or fifo-filled in rxmode). we need to clarify when we go into the sleep mode then and how we wake up/resume in main-loop. ... ive looked once again on pCB and schematic, it really looks like that there is no other way than soldering 3 pins directly to the atmega169? this is really a VERY sophisticated soldering job. is it possible to disable the atmega's jtag-interface during runtime only? that would make the soldering job really easy, we could even wire the RFM externally so that people dont have to open the HR20. of course, disabling jtag via fuses requires a working bootloader and is (as far as i know) not reversible... are there any alternatives than soldering to those tiny nasty atmega-pins?
Posted on:
RFM Wake up will be done by interrupt PCINT9 and setting task|=TASK_RFM. When we process this event, we must to do task&=~TASK_RFM and it will allow sleep in main loop. Connection RFM to ATmega we have only by 2 ways and both is similar, can be changed by compile option (different is only signal names). 1) connect wire directly to ATMEGA as in my pictures 2) use JTAG pins. JTAG is possible disable in runtime and it is also possible to use it for programming but for it we must hold reset signal. It is not problem. But it is no possible share this pins for debug. Therefore it can be possible way for end-user, not for development. Benefit is that it can be connected outside without open HR20. JTAG disable by fuses is not reversible by JTAG interface because it is disconnected. But this configuration can be changed later in runtime and we can reenable it by hold reset signal.
Posted on:
Hi, disable JTAG: i have googled it but couldnt find something useful. the only rumor i read was that "disabling JTAG at runtime doesnt mean setting the DisableJtagFuse" which would be very good because this could really cause trouble when the frmware crashes and cant execute any "ReEnable the JtagFuse again" command. do you have a sniplet how to use JTAG-Pins as IOpins at runtime without messing with the fuses? I would like to get this working soon, because i cant solder my RFM to the Atmega's pins directly - these ones are too small for me :( Idea: Is a "mixed version" of RFM wiring (JATG vs. internal pins) possible as well? That eans using JTAGpins<=>RFM except RFM's nSEL, which we wire to PE6 - that is the pin that is reachable by cropped via on PCB, so its possible to solder. Idea: In JTAGmode PE6 is HighZ => RFM's nSEL is not tied to GND and not SELected => RFM's other pins should be HighZ (gotta look that up...) which means the RFM shouldnt disturb the Programming Traffic between JTAGprogrammer and Atmega => no need to unplug the RFM when JTAGging. Security: I checked in a security.c module. mainly uses XTEA (yet written in C) for en/decryption in cipher feedback mode. has the nice side effect, that we dont need the code for XTEA-decipher (see http://en.wikipedia.org/wiki/Block_cipher_modes_of... ). i also abused the XTEA-code for a hash function in for chall-resp-authentication. code not yet tested but function interface shouldnt change.
Posted on:
Disable JTAG only for runtime: write one to the JTD bit in MCUCSR. Datasheet chapter 9.8.7 We don't have any reason to mixed version of wiring. In this case we will lost JTAG and we must solder inside HR20. It is not possible share one pin on JTAG interface. JTAG can be completly disabled, nothing more. Problem with share JTAG pins it not programing, but debug. Security: Yes, we can use XTEA encryptor on feedback mode to generate key to encrypt data. see to https://roulette.das-labor.org/trac/browser/microc... But it have problem. Cipher on RX and TX side must by synchronized otherwise is not possible to decrypt data. On wirelless is usual lost same data, therefore in this case we can lost synchronization. It is complication.
Posted on:
Hi! Disable JTAG: ok will check that register in the atmegas manual. thanks! mixed wiring: yes youre right, JTAG-firmwareupload is possible (if RFM's pins are really HighZ when nSEL=High) but debugging is not possible. i think it's ok as it is - you can use your directly soldered pins and i the JTAG (and cant JTAGdebug, but i dont need that often). its just pin definitions (see my rfm code its completely adjustable with some #defines). security: dont worry about the syncing! the CFB resets with every sent-out datagram again. it is just feedbacking within one datagram. otherwise it would be impossible for a receiver who was offline for several datagrams to resynchronize. id suggest this data format: payload = [rand,currtemp,wantedtemp,valepos] enc_payload = security_encrypt(payload) packet_nocrc = [deviceID,enc_payload] length = sizeof(packet_nocrc) + 1 // + 1 for crc crc= crc8([length,packet_nocrc]) rfm_send([length,packet_nocrc,crc]) if you want to you can encrypt the deviceID as well. but point is that we must use additional crc for checking air damage (crc is better for that than any hashes). rand is a random number that "salts" our security_encrypt => equal payload (except different randoms) will produce completely different enc_payloads. so its not possible to create a codebook. this salting rand could be also used for chall-resp-authes.
Posted on:
i was just thinking ... do we need a hash-function at all? if the master authenticates via sending the rand value back within an encrypted message, then the master has proofen that he knows the shared key. so scenario: 1. hr20 status broadcast every minute (length,devID,encrypted[rand,currtemp,wantedtemp,valepos],crc) 2. master receives that, decrypts packet and has rand in plain format. when master wnts to send a command to the HR20 he sends (within one second after HR20's broadcast): (length,devID,encrypted[rand,CommandTotheHR20],crc) 3. HR20 unpacks that datagram, checks rand, and if it is equal to the rand from (1.), CommandTotheHR20 is executed 4. HR20 sends back (length,devID,encrypted[ResultCommandTotheHR20],crc) 5. HR20 listens another second for a further command (again with rand included), and if not occuring, HR20 waits a minute till (1.) what do you think? rand is encrypted in all air messages and different in every (1.)
Posted on:
@Mario Fischer: Your proposal looks good. I would like want only this modifications: - use upper bit of length or devID to indicate HR20->master or master->HR20 communication (benefit: we can reject unwanted packes before decoding) - remove step 5. After step 4 we can go back to 2. It have benefit that we don't need keep receiver alive 1 second. Timeout can be smaller (max aprox 100ms) - use SYNC byte before communication, RFM support it in HW. It can filter possible noise from others wireless comunications. I am sure that you know this RFM feature but you forget write it in proposal. And some technical notes: - If you wan't, I can integrate RFM SPI layer into current code (interrupts, create task etc.) - It will be nice reuse/modify current COM code (same commands, same results). -- We can modify numbers in commands/responses to "compressed" version (not use hex coding but raw format) -- wireles layer will encapsulate COM packets and manage encryption. -- it not need \n as command termination char (size of wirelles packet is known)
Posted on:
We need hash or XTEA feedback hash. Without this it is easy decrypt ((packets) xor (fixed key)). Therefore we cant restart hash function for each "status" packed from HR20. It is just variant of fixed key. What we can to do: step 2 on master: we must reply to HR20 with command or empty packed (length,devID,encrypted[rand],crc) step 2 on HR20: after success on receive calculate next step of hash function to generate packed key What can happen (success): -step 1: HR20 will transmit packet with packet key generated from hash (PK1) -step 1: master receive it and decrypt it with PK1 -step 2: master transmit packet with PK1 and calculate PK2 -step 2: HR20 receive packet, decode it by PK1 and calculate PK2 What can happen next (fail): -step 3: HR20 will transmit packet with packet key generated from hash step 2 (PK2) -step 3: master receive it and decrypt it with PK2 -step 4: master transmit packet with PK2 and calculate PK3 -step 4: HR20 fail to receive packet, PK3 is NOT calculated -step 5: HR20 will transmit packet with PK2 -step 5: master receive it and try to decrypt it with PK3 it fail, but will be successfuly decrypted with PK2 -step 6: master transmit packet with PK2 ( calculation of PK3 not needed) -step 6: HR20 receive packet, decode it by PK3 and calculate PK3 What can happen next (another fail): -step 7: HR20 will transmit packet with PK3 -step 7: master fail to receive -step 8: HR20 will transmit status packet next minute with PK3 -step 8: master receive it and decrypt it with PK3 -step 9: master transmit packet with PK3 and calculate PK4 -step 9: HR20 receive packet, decode it by PK3 and calculate PK3 ...... I hope that it is clear. PK numbers is not significnt (PK[n+1]=hash(PK[n])). But we need to solve resync after HR20 or master is restarted (some initial fixed key)
Posted on:
I thinking. (some initial fixed key) must not be fixed. It can be fixed part + something from user for every init. In this case, user must read one or two bytes from master and enter it manualy into HR20. It just only idea .....
Posted on:
Hi! well, SPI is not the problem, the SPI-function itself is very very fast, Problem is as discussed the waiting between SPI and SPI. if you could write some code where i could integrate something, would be fine! Air-Protocol: In my implementation i had an additional byte "flags" with several useful values (contains ReceiverAddress, LoBatt, IsEncrypted...). I left that away in my sketch but a concrete implementation will contain sth like that. "1 second" is of course a too long time period. we could shorten it. Dont let us mix up all those SYNCS: you meant the sync-pattern the RFM sniffs to (and when he detects it he loads everything following into the RxFIFO) - Yes the Sender must Send Sync and 0xAA0xAA-Preamble before (and trailing 0xAA as well!). i also left that away in the sketch for keeping it simple. Commands: yes com-proto-reuse would be nice but ascii-over-air makes datagrams too long - too dangerus. we must compress/binarize it somehow. also sending multiple commands without delimiter if fixed length in one packet is good - then we can leave away the relisten for one second from step 5. Ok, gonna handle your latest post with security leak now...
Posted on:
Hi i was quite busy in the last days, so i had no time to answer. I don't have much time, but my business is embedded security. Also i am often in das-labor.org, which is located near my home (about 5 minutes walk) Mario Fischer wrote: > do we need a hash-function at all? > if the master authenticates via sending the rand value back within an > encrypted message, then the master has proofen that he knows the shared > key. Encryption != Authentication. I will show you the error in your proposal: An Attacker would receive from HR20 > (length,devID,encrypted[rand,currtemp,wantedtemp,valepos],crc) He is not able to dencrypt this, but the master will anser e.g.: > (length,devID,encrypted[rand,CommandTemp=20],crc) Note: the attacker is not able to dencrypt this. But he can se, which part of both encrypted parts is the same. So he knows enc(rand). Now what the attacker can do some days later: The HR20 sends: > (length,devID,encrypted[randnew,currtemp,wantedtemp,valepos],crc) The attacker can replay the old command: > (length,devID,encrypted[randnew,CommandTemp=20],crc) There are many ways to avoid this. This can be done by using different keys for encryption on both sides (key_H2M: HR20=enc Master=dec, key_M2H: Master=enc HR20=dec). Better it would be to use a MAC like CMAC[1], which can be done with the Block-Cipher. If you have some requirements, i can assist you in designing the secutity functionality. For cipher i would consider to think about using XTEA. Alternatives are AES (about 1000 Words) or (better) PRESENT [2]. PRESENT is optimized for very small hardware, but I think it should also be quite small on the AVR. Nevertheless also XTEA would be OK. [1]http://en.wikipedia.org/wiki/CMAC [2]http://crypto.rub.de/imperia/md/content/texte/publ...
Posted on:
Hi guys, ok im also thinking about the auth&encrypt stuff again. some facts: - we already decided for XTEA, seems secure "enough" (yes sounds sleazy but code must be short => XTEA is excellent trade off) - and we cant use long keys, digests or random numbers over air since radio packets MUST be short. the counterpart to short key is that our "slave" only accepts auth-tries every minute at all, so we must primary defend offline-attacks. - the amount of packet-ping-pong between auth/chal/comd/reply must be short for battery. - we can not use any circulating P[n] -> P[n+1] tokens because master or slave can be offline for a while. Token or n might get lost. - yes encryption alone doesnt replace auth or protects from playback. let me ask you guys again about the leak here, i still dont see it: 1. Slave sends (simplified): Encrypt( [rand1,statusinfo] ) 2. Master sends Encrypt( [rand2,rand1,command] ) 3. Slave sends (if rand1 was recognized) Encrypt( [rand3,rand2,result] ) i agree with dario that attacker could see enc(rand). so i putted a rand2 on start of message in 2 which will scramble all the rest of the packet (->CFB mode) (lesson learnd ;) beside, even if the attacker could catch a rand/enc(rand)-pair, then he couldnt offline-calc the key: rand is shorter than the key so many keys would produce the same rand. and the attacker would have to run thru the key-span (big) and not thru the random-span (small). ok, whats the weakness in this protocol? we have lots of power/packetsize/battery/pingpong-constraints guys, we must keep it simple!
Posted on:
Another thing: to distribute the keys in HR20 (Slaves) and Master we should think about the possible solutions: a) Keys are compiled in the Software b) Keys in EEPROM - can be entered using serial interface - can be entered using Service mode I would prefer to enter the keys in EEPROM. For maxium Security the key must at least 64 Bit, better 80 Bit. So it would consume 8 to 10 Bytes in Configuration Memory. A key exchange between Master and Slave is only possible, when we would use asymmetric functions like Diffie-Hellman. All other key exchanges are not secure, when they all use the same (master)key for all HR20s. Dario
Posted on:
@dario: key distribution: already done. its stored in eeprom and changeable via HR20's LCD/Button/Wheel-interface. Jiri did a great job with his extensible interface! => key distribution is no problem. i coded the keysize variable length. if shorter than xtea-key it will be padded (no user wants to enter a 16-byte key in every HR20 so i think padding is ok. it's not home-banking ;) i think i see now the point you wanted to show with your "a few days later": but thats a tradeoff we have to accept: if the rand is only one or two bytes long than it will some day repeat. again a trade-off for short-radio-packets. but even if the attacker has an old packet with matching rand. then he could inject a packet of which he doesnt know what it will do.
Posted on:
@dario: if you are interested, you can look at the current state-of-the-code in the http://openhr20.svn.sourceforge.net/viewvc/openhr20/rfmsrc/ branch of the project. new files are rfm.* and security.* security is as mentioned still in a draft state. i will think about the "do we need hash function if we have symetric-cfb-encryption?" again... i still think we dont need hash because cfb-enc kills all plain-cipher-pair-recognition-possibillities ...
Posted on:
@Dario C: You are right. For clarify: If attacker have 2 encrypted data with some KEY and know information that it contain common par of source data (rand) it is security hole. Attacker can easier calculate key. And from PK(n) can calculate PK(n+m) (with hash it is simple, with XTEA in feedbak it can be nightmare). (Example in history is repeat random part of KEY in encrypted communication used at ENIGMA - decrypted in Poland 1934 by Rejevski) we must have something like protocol specification before coding. From my side exist only small chance to do something till Xmas (I am quite busy). Therefore we have time to thinking about it.
Posted on:
Mario Fischer wrote: > let me ask you guys again about the leak here, i still dont see it: > 1. Slave sends (simplified): > Encrypt( [rand1,statusinfo] ) > 2. Master sends > Encrypt( [rand2,rand1,command] ) > 3. Slave sends (if rand1 was recognized) > Encrypt( [rand3,rand2,result] ) I think you gonne send many data, which is not needed. You saied, that radio packets MUST be short. 1. Keysize does not affect packetsize. 2. How long would your random mumbers be? 3. I think there are many better solutions, when we think a bit about it. 4. Security can be added later, you can implement 2 Dummy functions on each side generate_msg and verify_msg, which can be filled later. I have to think about it, but for me it seems to be a "Homebrewn" sollution which is not the best we can have. Also XTEA is very old, PRESENT is much newer and provides better security. I think it should not be bigger than XTEA; > we have lots of power/packetsize/battery/pingpong-constraints > guys, we must keep it simple! I Agree, but we should keep it smart, and simple. And in your proposal i see that many random numbers are send, which leads in big overhead, at least double rate
Overhead
============
Security
|
Let me ask a Question, befor i start to think about a better solution: Who is the Master? - How much memory - What computational power If the HR20 shall talk to each other without a master, than we have a problem. If not i think that the Master can recover missing sync information, so that we don't need to send the useless rand information. We would need to send some additional Bits (32 to 80) for authentication. But I have to think about it. Dario
Posted on:
Mario: "we can not use any circulating P[n] -> P[n+1]" NOT we can't do it like this. It big secutity hole. When one of station is offline it is not problem. See to my comments from 09.12.2008 23:48 But Dario is right, we cant repeat same data with 2 packet with same key.
Posted on:
Mario Fischer wrote: > i think i see now the point you wanted to show with your "a few days > later": No, when a few days later another rand (randnew) is send, i can replay the old command, which was the response to the old rand. I think when we use 1 or 2 Byte rands, than it is better to use no security at all, because it can be very easy broken. But I think by adding 4 Byte additional data to the frame, than we can get the security of 4*8=32 Bit and by adding 8 Byte we have 64 Bit security. But i have to think about it, i will write a purposal document for security when i am not so busy (during the holidays). Dario
Posted on:
@dario
- i diddnt know PRESENT but a first google shows me that it has s-boxes
... thats way to expensive!
- xtea is old, but look at known weaknes of it ...
- are there any other well-known and analyzed algorithms as short as
xtea?
- no hr20-hr20 communication.
- only hr20->master->hr20 talks
- master ... dont know... a linux-box, a atmega32, ... but doesnt play a
role: the computing-power-bottleneck is the HR20.
- random number lengths: i would guess 1 or 2 bytes. i know its short.
but be realistic: anyance over a shorter living battery from long radio
packets is more likely than someone who records about 256 or 65536
commands (there is NOT a command EVERY minute!)
> But Dario is right, we cant repeat same data with 2 packet with same
key.
do you really want some session-key-generation-protocol? this requires
lots of traffic!
the whole send encrypted random vice and versa is not my idea. i thik
its occuring similar in kerberos (let me look it up) but its not my
invention...
Posted on:
Dario C: I know about PRESENT but it is too expensive PRESENT - AVR C implementation - 1514 bytes of flash and 256bytes in RAM XTEA - AVR C implementation - 754bytes of flash, 0 bytes in RAM XTEA - AVR ASM implementation - 504bytes of flash 0 bytes in RAM source: http://www.das-labor.org/wiki/Crypto-avr-lib/en We have aprox 3kB of free flash in current SW. Save every byte is fine.
Posted on:
Mario: you dont need any session-key-generation-protocol It is simple. You have key for packet (PK) , and master key (MK) And you ca to do: //have function encrypt(data,key) PK(n+1) = encrypt (PK(n), MK); You can calculate it on both sides withou any session-key-generation-protocol You must only keep synchronization you cant decrypt PK(324245) encrypted packet by PK(6756324)
Posted on:
Jiri: im still trying to understand your post from 09.12.2008 23:48 - could you summarize that all a little please? how many transmissions each minute? what is transmitted in every packet? and im still insisting, that after one minute everything must be reset. there may be no references to any randoms or packetkeys that occured one minute before. master or slave can be offline always and the other doesnt know it! so after one minute, everything has to start from scratch. so long guys, i fall asleep now!
Posted on:
Mario Fischer wrote: > - i diddnt know PRESENT but a first google shows me that it has s-boxes > ... thats way to expensive! Yes one 4Bit-to-4Bit S-Box = 16 Byte. > - random number lengths: i would guess 1 or 2 bytes. i know its short. > but be realistic: anyance over a shorter living battery from long radio > packets is more likely than someone who records about 256 or 65536 > commands (there is NOT a command EVERY minute!) But when we use 1 Byte an attacker needs 128 tries for the chance of 50% to change the next random number and so to destroy any further communication. The attack is on: Encrypt( [rand2,rand1,command] ) The attacker would send some random data, to the HR20 as response. When the HR20 decrypts this data and the second byte is accidently rand1 (which is 50% for 128 Tries), it would save rand2 as new value, which the master (and the attacker) does not know. => After that no further communication is possible. I will think about a solution to provide security with additional 4 to 8 Byte each packet. > do you really want some session-key-generation-protocol? this requires > lots of traffic! I asked how the keys will be distributed, as they are in the EEPROM this is not an issue anymore.
Posted on:
im almost in bed, but let me shot comment
> destroy any further communication.
thats why i insist on "reset everything every minute"
destroy any further communication would otherwise also be possible if
only one minute's session fails - then both wouldnt be synced.
let me clarify: all my rand0,rand1,2,3.... are diced every minute from
new!
in general, it is always possible that an attacker records a packet and
playbacks it every minute - after latest 256 or 65536 minutes it will be
considered as valid.
i can accept the threatof such an scenario, since long packets are very
battery-consuming. i measured the rfm's current consumption during
sending with shunt+osci, thats why 4byte-randoms are too expensive to
me.
Posted on:
Mario: how many transmissions each minute? - not change from your proposal what is transmitted in every packet? - not change from your proposal You don't need sedn any aditional data for key change. Becasuse you can calculate PK(n+1) from PK(n) if you know master key (stored in EEPROM) You only must try for decryption use PK(n) and when you have not success PK(n-1). If you have not success with PK(n), it mean that one or more packets was lost and second side not change PK
Posted on:
Hi guys, i followed this and the other threads a long time. what i read out since now is that in between there is an open firmware available. now, you want to get/send data from/to the HR20 via a rfm module. but why should this be encrypted? the WHY is here missing. since now i thought it should be an OPEN firmware? Maybe i didnt understand a block or i missed one? cu, olly...
Posted on:
Open: The firmware's source code including encryption algorithms is open source. The encryption key is selectable by the user. Encrypted radio Traffic is to protect your HR20-valves from unauthorized people to control your room temperature or even detect from outside that your room temperature is cold (so you might not be at home and they could break in). No fundamental discussions about "who is interested in controlling my valves?" please! Protecting the system is not much code but always worth some thoughts about!
Posted on:
Guys, one Question: If our radio packets are always smaller than a XTEA blocksize, then the whole CFB or OFB modes dont make sense: Because in both modes, the first plainblock is just XORed with XTEAencrypt(Key,Initvector). This means that the whole plainblock is just XORed with a constant bitpattern. This would mean that even one captured Plain/Cipher-Pair would disclose this constant Key. So i would suggest CBC mode or no modes at all if all radio telegrams are < 17 bytes (what i would recommend). on the other hand, telegrams smaller than 16 bytes would have to be blown up to a XTEA-block.
Posted on:
@Mario Fischer Datum: 10.12.2008 16:19 plainblock is just XORed with a bitpattern. But this bit pattern is different for each packet.
Posted on:
Hi Jiri and OpenHR20-Team,
today I managed to make the HR20 send a radio frame with the RFM12
Module connected to the outside-accessible JTAG-Pins and PE2.
Well, almost -
I saw that quite often bytes are swallowed. For testing i let the HR20
send a bigger frame with increasing bytes
<preamble> <fifo start patt> 0x01, 0x02, ... 0x13 <dummy byte>
on the receiver side i saw things like
0x01 0x02 .. 0x04 0x50 0x60 ...
^^
in other words, sporadically swallowed bytes or nibbles and some noise.
Im quite sure its not the receiver which is swallowing the bytes, this
device im using for long time and it always worked.
I also looked at with the scope to the distances between the
SPI-16bit-Trains, their distances were not equal!
I suspect rather that the SDO line indicates the "ready to send next
byte" (TX flow control) event to early, multiple times, ... or the
InterruptRoutine sensing for SDO Edges somehow raises the "send next
byte" codition too often or to early ...
Im not sure where the problem is. In my other applications, I flow
controlled always with the IRQ line, which works fine.
The RFM datasheet tells us that the SDO line also is usamble for flow
control, so we want to use this line (to save IOports).
For test purpose i will connect the RFM's IRQ to the ATmegas IRQ (PE6)
and check wheather this is the cause of the stumbling TX flow control.
But im not sure, could be many sources
SDO not relieable for Flow Control,
OpenHR20's PinCHange-ISR has an error
main-task-loop has an error.
Updates will follow ...
Posted on:
Hi, I have a problem with my HR20E ordered at Conrad, it is the same problem at all three of them: They work fine in the Full-stroke mode. Yet, in the default-stroke mode, radiators stay cold after about three days, even though the HR20E shows a higher target-temperature. Removing the Rondostat and turning the blue wheel by hand, the radiators get warm. When it gets above the target-temperature, they are turned of properly and the Rondostat will work fine for another three days or so. This should not be a battery problem. The batteries are new and brand-products, and the Rondostat makes no sign of having a power shortage at any point. It should neither be a problem with the valves since the radiators get warm when I turn the blue wheel by my self, and since the problem does not occur in the full-stroke mode. It seems to me, that after a few days in the default-stroke mode, the Rondostat does not know anymore at which position it is, and does not open the valve as it thinks the valve is already open. Does anyone know a solution for this? In the Full-stroke mode, the temperature deviations from the target-temperature are too high since my radiators heat up very fast. Thanks for your answers, Robert
Posted on:
Hi just managed to flash the first HR20. I used the Atmel Eval Boarad from Pollin modified according to the Evertool LIGHT by Rainer Rakow. Starting test now... Is there any readable user manual or anyone working on it? Robert, i ordered 8 HR20 from CONRAD and had no problems found. Did you rewind the blue weel before installing the head? But carefull - its easy to overwind! I read about similar problems in another thread - in one case some coins helped to reduce the distance between the nozzle of the valve and the regulator pin. Frank
Posted on:
@Robert: I have 5 valves (exacly same) and only one of them have same broblem. It not depend to HR20 unit, but on valve. With original SW you can only use "full stroke" mode. You not able change anything or discover it. And it is one of reason why I wrote another SW for HR20. In my case it is solved. @Mario Fischer: I will try discover where it problem tomorow.
Posted on:
@jdobry: meanwhile i looked a little closer at the distances of the SPI-RFM-SendByte-Commands. I let every time such a write-command occured toggle a pin and looked at it with the osci, and their distances looked good. im not sure if the problem is in the receiver. it might have been false what i wrote in my last posting, sorry. but i will test it a little more today and know more. Full-Stroke-Issue: I have a general question: The HR20's Manual sais, that the HR20 knows a Default and a Full-Stroke-Mode of turning the Valves off and on. When coming out of the Box, HR20 is in Default-Mode. What is the use of this so called "Default-Mode"? I thought, the HR20 works like this: * When HR20 is screwed on Valve (detected by switch), then ... * HR20 turns on Motor to rotate left, until the light eye doesnt pulse any more (gearwheels block) * Set a lighteye_pulsecounter=0 * Turn on Motor to rotate right, until light eye doesnt pulse anymore and count pulses in between. Then set lighteye_pulsesmax = lighteye_pulsecounter * Now the mechanic is in a defined state (valve=100%) and we know that [Valve0% .. Valve100%] <=proportional=> [0 .. lighteye_pulsesmax] Which this knowledge and pulsecounting, we can put the Valve to any % we want. I guess this is the full-stroke mode. So, whats the Default-Mode? What would be the meaning/benefit of it? Whats the use of having a water tap that you dont open or close completely?
Posted on:
@Jiri: My Description of the Valve-Calibration - is this like your Calibration Algorithm? And if so, how do the described Phases correspondend with your "C-1" "C-2" "C-3" Calibration Messages? Your Code looks like if there is a "Manual Calibration" and a "Auto Calibration", but i couldnt find out when which mode is driven, and what's Manual at the manual Calibration. And what are you working with PWM with the Motor? I thought only the direction of the Motor is important when Setting a Valve-Position (which is selected by the 4 H-Bridge Transistors next to the Motor i guess), but why is Motorspeed interesting? Could you tell us some words about these things? We will need this text snipplet later probably for the User Documentation. Thanks! Mario
Posted on:
Attached files:Hi at all, today I finished the first (Christmas) release V 0.2.2.25740 for the openHR20 Suite which allows comfortable managing of the module settings. Since I was very busy adding functionality, not all things are well done and some problems may arise (if you find some, please report). The SW is based on .NET Framework 3.5 and uses WPF instead of Windows Forms windowing. It was developed on a Vista notebook but should also work with XP. The 3.5 .NET Framework is not contained in the installer. If you don't have it already installed, you must obtain it from MS. Basically WPF GUIs are very pale but the design can be changes tremendously. If anybody here has Expression Blend and has experience with good design, may contact me. Only one hardware platform was used, so I can't say which problems may arise on others. Unzip the attached setup and install the SW. Connect the HR20 via serial Port (or USB to Serial adapter as I did it), choose the correct COM Port and connect to it. You may read or set all/single Timers or Eeprom Data and save/load it to/from a File. You can also send manual commands, sync the date/time with the PC or log the traffic to a log file. The other functions are self describing I think. The SW works with REV 103 of the HR20, but may also operate with elder versions. Have fun with it. Karim
Posted on:
Attached files:A picture of the user interface is attached. At first I would like to make the SW stable before I add functions if I don't lose mood (e.g. script executing, graphical data logging, several Tabs for each connected module, connection via WEB Service, and what ever ideas comes).
Posted on:
Wow this looks good! Will try it soon! Karim, could you assure in your code, that the COM-port-stuff is not too much nested to the GUI-stuff. This would make it easy to port your application to wireless HR20 control. Would probably require some Addressing-Layer in your Programm. Communication would the go to a "RFM-Gateway" (= FTDI<=>Atmel<=>RFM), which would probably not be totally transparent to your Programm. The RFM-Gateway could do of course the HR20-comm totally transparent (especially since FTDI is a Comport) but a more generic firmware in the Radiomodem could make it a litte more flexible (use it as remote-therometer-receivre as well etc). But your Screenshot looks good! Will try it soon, wish i could code in .NET ;-)
Posted on:
I wrote a short Status-Update about the Wireless-Branch in the Project's Artice Page. http://www.mikrocontroller.net/articles/Heizungsst... (@Jiri: sorry it is in german, but it contains nothing you do not already know anyway)
Posted on:
Hi Thank you for your answers. @Frank: I am sure the wheel was on the "all open" position, before I mounted it on the valve. I am not sure whether the problem can be solved by coins. If the distance would be too large, the pin of the valve would be out and the valve open. In my case the valve is closed after three days. But still I can give it a try. @jdobry: I am not sure I correctly understood what you ment. What is a SW? And how did you change it? Thanks a lot, Robert
Posted on:
@Robert: Original software in valve is 2.04 from Honeywell. We don't know how to set it via serial line, how to bugug problematic situation etc. Therefore we wrote complete different SW for this valve. It have some extensions for debug and some more functionality. And don't have "cold valve" problem as is discoverd by you. For change SW you needd JTAG programer, see to this thread history.
Posted on:
@Karim L. I was try your SW 0.2.2.25740 version. And this is result: - not able to run under MONO, It use too many non implemented functions in mono. - it always use anti-aliased fonts and don't respect setting in windows. It is hard to read on hudge monitor with high resolution - layout have fix size, unable to use bigger window - About dialog contain information about GPL II license, but where it sources? Thanks for this SW, it can be useful. It's pitty that it can run only under MS Windows. Many of us have another system.
Posted on:
@Robert: If you dismount the head you can check the position of the blue weel - is the pin all in or all out or in between? You can get mor Information when you connect yor PC to the serial port of the HR20. But keep in ´mind that ist side is in 3,3V-logic. By the way, what is the easyest way to connect the HR20 to the serial port of a PC? Found this Beitrag "1 Transitor + 2 Widerstände = Verwirrung", intended for I2C but should work on RS232 too (?). @Karim: very fine - it runs on my XP but not yet connected (s.a.). Could your progy also work on an I2C-bus? I have 25 m cable going along every radiator in my flat. It would save me from laying my hands on every HR20 twice on each holyday :) Frank
Posted on:
@Frank: easyest way to connect the HR20 is use MAX232 for serial line or another cheap solution is use USB cable with USB->serial convertor for mobile phones. (Ulder mobile phones don't have USB and this cable not contain level changer for RS232 line, but use 3.3V logic). Example is (tested) KQ-U8A cable ( http://stephane.aubert.free.fr/KQ-U8A/ ). I buy each by aprox 3.20 EUR I2C-bus is not supported on OpenHR20 software. Except this I can't recomend I2C bus over all valves. This bus is not protected to noise and cables will be too long.
Posted on:
Hey Karim first look on your tools is all great. It works fine - but: were can i select the temperature for each on/off-time pair (snow/moon/sun on LCD)? Great work! Frank
Posted on:
@Mario, the COM Interface is placed in an one class. I will add an SW interface to it, which all communication classes has to implement, so that a seamless integration of any interface will be possible. @Jiri, the Suite is for me also an interesting technology project, since I have not written until yet a WPF application and I did like to use other technology stuff like reflection, data binding, user controls, which the .NET Framework offers, because I will need it at work next year. - MONO is always behind the latest technology. It takes a while until a full implementation is available but if I interpret it right, as I even so they offer already the .NET 3.0 function set. I reduced the level of .NET in the project to 3.0 and until some minor changes, it works as before. So the next release will require only .NET 3.0. Hope this helps for the Mono user. But I have no experience with Mono. - The code will be made public after I have added comments and reorganized the code a bit. May I add the code into a new folder in the SF openHR20 project? Would that be ok for you? - The size of the windows is currently fixed, because I don't know how to change it yet. It is different from Windows Forms but I think still not difficult. But that is on my list for change as soon as I know how to do it. What monitor resolution do you use. My one has 1680x1050 and I can read it well. Windows is the most used OS platform and .NET is quite powerful. Since I know how to program in .NET, it is the fastest way for me with acceptable effort to get a complex program although it is still a lot of work. And with Mono, even if it might not be possible yet, will open the door for other platforms. Hope you can live with that point of view. @Frank, the level shifter would allow to connect the RS-232 in parallel, but a special protocol would be required for communication which the I²C Bus (TWI-Two Wire Interface) has already implemented (master/slave, clock, addressing, collegian handling...). But in principle not a bad idea to use a level shifter plus a special protocol. I have also installed a cable ring to all heaters but planned to use I²C bus. The Atmel controller supports I²C bus. And the nice thing is, the needed TWI Pins (SCL (same as TCK, pin 4 of the connector), and SDA (TMS pin 3)) are already routed to the module outside connector. What we need is an interrupt routine which roots the traffic and at the PC a TWI to Serial or USB converter. An additional option is the 3 wire USI connection. But Jiri might be right, that long wires can be a problem for the signal edges although the overall speed can be as slow as wished. We will see. The temperature can be set in the eeprom block (temperature0-3), but it is not a nice way because of the required calculation of the necessary value. Also missing is the possibility to assign this temps to the switching time. I will add both later.
Posted on:
@Karim An I²C-Bus slave for Attiny was in the last issue of Elektor in germany: http://www.elektor.de/jahrgang/2009/januar/i2c-sla... The best is, no special port is needed for it. We could use any line - especially the serial lines, replacing the RS232 by the I²C. By the way, in the same issue there is an article about to conntect a RFM12 to AtMega. @jdobry I²C-Bus as a house-bus you find in Funkschau 9/2004 or at http://www.hauscomputer.gmxhome.de/. It seems very simple. My idea was to connect each rondostat with a power-line instad of batterys, I²C-Bus for Comunication and a PIR-switch. The later is to overide energy-save-mode if a person is in the room (e.g. school ends earlyer). PE2 is still free!?
Posted on:
I2C have some problems. Generaly it have open-collector bus. This mean that logical "1" is defined by resistor. On long cables, it have slow edges and mainly it have zero protection for noise. This problem can be fixed by active current injection on level change, but it need special chipset. Except this we can't use hardware support on HR20, because it need pins PE5 and PE6. Pin PE5 on HR20 is connected to ground, and it is not possible disconnect it without remove chip. SW implemented I2C is possible but I thing that RS485 is better for cables in home. RS485 HW is extremely simple, see to http://www.datasheetcatalog.org/datasheet/maxim/MA... But you can to do anything that you want, Source is GPL and you don't have any restriction. But because I have not cables, I must use wireless comunication.
Posted on:
Experience after 4 weeks on 4 valves - valve have more actions compare to original SW. It must be improved. Have anybody any idea? - battery low detector is not sufficient. At low battery SW usualy detect flase Error3 before battery low. I have some ideas how to imrove it, but your ideas is also welcome. - current temperature measure convert each measure to tempereture and calculate average from last minute. Result after average have better precision than is measured (overscan). But it can be reason to many action on valve. I will try prepare version with average from RAW ad data and calculate temperature from result. Overscan can be used or not, i don't know what is better.
Posted on:
HI @ all, i have some questions. is there an bootloader also implementated, so it is possible to flash a new Firmware over the Uart? The problem is, that i have the JTAG-Ice-MKII debugger only for the next seven days, and than i have to give it back. The next think, i want to know. Is there a posibility to use the SPI, i want to connect a can tranceiver to it, i saw that the pins PB0 to PB6 are use for the buttons and the engine. wbr Peppe
Posted on:
@peppe: It is possible use bootloader to flash this device. But I am do not use it. SPI: It is near ti impossible reconnect buttons to other pins. Therefore only one chance is SW implementation of SPI protocol. See to branch for RFM12 wireless communication (on development, not work now)
Posted on:
Idea: PE2 is free to use and avail on the connector. I'll try to connect it to a PIR motion sensor. If there are some events (PE2 is PCINT1 and can serve as an interrupt source) within a given time, the room is known as used and the temperature will be set to "comfort". If no motion is detected, temperature wil go to normal value given by timer. I will modify a cheap motion detector whith a relay. I think i will need a timer for it - Timer1 is not used yet? By the way - how are you using the simulator? Is it possible to simulate the switches too? I only reach "E2" due to PB0 is always going back to 0.
Posted on:
@Frank E. If you are not using RS485, PE2 is free. (used for debug, disable it on debug.h) Timer1 is free and it is disabled (you must remove this power save feature) I am not using simulator, just JTAGICE debuger connected to real HW. But on simulator you can manualy change pin status when SW is stoppend, or you can create input files, see to atmel docs. But I thing, that it is too complicated. Jiri
Posted on:
Hello Jiri and all, in my holidays I modified the code to work with the Thermotronic thermostats. I did this by using #if - #endif stuctures to make the code working for HR20 as well. Maybe you want to include my modifications in the SVN - a new branch should be unnecessary. The important differences between HR20 and Thermotronic are: -different pins for switches etc. (scheme of TT can be found in another thread) -no enable-pin for motor-pwm -hardware USART used for motorencoder (so i actually disabled all debug functions) -different thermistor - I modified the values but I´m not sure they are correct. Maybe the have to be updated in future. The Thermotronic doesnt show the measured temp so I cannot analyze as described in doc. Thomas
Posted on:
@Thomas V Modification for Thermotronic would be nice. Please contact me by email for access to SVN or send me patch set. Schematic is here http://www.mikrocontroller.net/attachment/29357/sc...
Posted on:
Hi, first I want to thank you for creating this project! I do some home-automation and this is just what I was looking for. Yesterday I bought me a HR20, connected my spi-programmer to the corresponding pins and set the fuses to l:0xe2, h:0x9b and e:0xfd. Then I uploaded the firmware I compiled out of the current SVN rev. It worked immediately but very unstable (random hangups). So i took the hex and eep files from the repository and it works like a charm. Do you have any idea why my self-compiled version fails? I used the Makefile from the repo with only one little modification: my avrdude doesnt know the atmega169p so I hardcoded the atmega169 for avrdude (not avr-gcc). Environment is Linux with avr-gcc version 4.3.0. Best wishes Björn
Posted on:
Hallo! Das hier ist ja mal höchst interessant. Bin mittlerweile auch im Besitz eines solchen Reglers. Ich habe verdammt lange nichts mehr mit einem AVR gemacht! Wie bekomme ich mein Rondostat umprogrammiert? Mir steht ein STK500 zu Verfügung. So wie ich das hier gelesen habe kann ich das ganze nur mit einem JTAG programmieren, den das STK500 nicht hat? Bekomme ich das doch noch recht spontan programmiert? Gibt es eine Schritt für Schritt Anleitung? Gruß, gammla
Posted on:
@gammla Sorry, keine Anleitung bis jetzt - ist auch kaum möglich, da stark von dem vorhandenen Gerätepark abhängig. Ich bin so vorgegangen: 1.) JTAG Programer gebaut. Ich habe dazu ein ATMEL-Eval-Board von Pollin angepasst. Anleitung findest Du bei Evertool-Light http://www.siwawi.arubi.uni-kl.de/avr_projects/eve... Dort ist auch die Beschreibung, wie man die Firmware und die PC-Software beschafft und installiert. Achtung: Es muss ein anderer Quarz ins Board! Du brauchst auch nur den Teil fürs JTAG nachbauen - 1 Quarz, paar Widerstände, 1 LED und 1 Kondensator. Die Steckerbelegung am HR20 findest Du in der Analyse http://carluccio.de/images/e/e1/Hr20-analyse.pdf. Ich habe 2 5-polige Platinenstecker benutzt, wie sie in PC für die Gehäuseanschlüsse oft verwendet werden. 2.) Aktuelle Toolchain für den Compiler installiert (Win-AVR) und danach das Atmel-Studio 4 (Nicht Studio 32!). Hinweise dazu auf der Seite von ATMEL. 3.) Das Repository mit den Sources geholt -> siehe dazu http://www.mikrocontroller.net/articles/Heizungsst... 4.) Anleitung zum Übersetzen und Übertragen im Repository unter
Open HR20\trunk\doc\Anleitung AVR Studio HR20.pdf |
Das Device im Studio festgelegt als JTAG ICE. Aufwand: Recherche 4 Tage (kannst Du Dir hiermit sparen), Löten 2 Stunden, Software 3 Stunden (aber nur wegen der alten Version von Win-AVR). Sieht nicht gut aus, tuts aber...
Posted on:
Attached files:Hi, I've written a little tool for the linux/*nix console to communicate with openhr20. It's very basic, just for my needs, but if there is interest, I will extend it. With it, you can set the current date/time, the wanted temperature and the mode. You can also get the status. To compile it, you need cmake. If chosen this as it makes it easy to compile software for different architectures. Björn
Posted on:
@ Björn Biesenbach nice tool! Do you wan't to place this project into SVN? If yes contact me by email.
Posted on:
Ok the tool can now be found in the svn under tools/
Posted on:
I made hudge experimental change in motor controller. Version before this revision use constant PWM for open and another constant for close. This experimental revision try to use constant speed and try to control PWM. Benefits: - we can use slower movement and it is more quite - I hope that it will more resistant to false "Error3" detections - speed is independent to battery voltage Second experimental change: limitation of "P" part of valve position controller. "I" part of this controller will found valve position inside regulation area. I hope that it will reduce motor movement outside valve regulation area. It save battery. It use config.P_max eeprom constant and it can be improved. Because it is EXPERIMENTAL, it is not in SVN main trunk. If you want to test it, please use "Rev 152" from rfmsrc branch. Change "#define RFM 1" to "#define RFM 0" in config.h If you want to help with development, PLEASE SEND ME LOGFILE FROM YOUR VALVE. Thans. Jiri
Posted on:
I forget to one warning. Rev 152 have changed numbers of settings in eeprom. Please see to eeprom.h
Posted on:
Hello Jiri and Forum! @Jiri: PWM: could you explain a little about, what the use PWM in motor control is at all? I thought, motor speed is not important at all because the valve position is not calculated by motorspeed (==PWM?) and motor's runtime - it is calculated (much more exact) by lighteye pulse counting - which is speed independant. Could you tell me/us a little about meaning of PWM in motor control? RFM: sorry, i did not have time for working with RFM last weeks. I hope i will find some time next week and/or the followings.
Posted on:
Rev 152 and 153 in branch rfmsrc is buggy (measure wrong motor calibration, will be fixed today, please wait.) Motor speed is not significant for valve position. But old versions use constatnt pwm for control motor speed. This has this problems: - high pwm constants are noisly - high pwm constatns have hard touch on the end of motor movement range - low pwm have problem with false "Error3" detection (motor can be too slow) - speed depend to actual battery voltage, therefore is near to impossible find this constants for open/close Jiri
Posted on:
Bug on motor calibration is on "manual callibration". It is fixed for rfmsrc branch in Rev 155 New motor speed controller looks nice and better than original constant PWM. !!! Bug is not fixed on main trunk now !!! I wan't to find maintainer for version 1.00 (main trunk) We need to integrate changes from Rev 155 (bug fix) We need to integrate changes from Rev 152,153 (motor speed controller) Any volunteer?
Posted on:
Hello, Motor speed controller is in SVN (Rev 158 in trunk / Rev 157 in rfmsrc). If you can, send me log frou your valve/HR20 combination. - If you will have problems (heating still cold or too hot) try to increase config 0x0b - If your motor speed is too high decrease config 0x12. - If your motor speed is too low increase config 0x12. Jiri
Posted on:
I have best results with "I" constatnt = 1 You can set it in service menu or by COM (S0601<enter>) Current default value is 3 Can you confirm this result? I will change default value. Jiri
Posted on:
Hi Jiri, ok the hex file from trunk/source 158 seems to work here. What log do you want to get? The output while adjusting or just any motor movement? I still have the problem that my self-compiled hex does not work :-( Don't you have any idea what the reason could be? Which compiler version do you exactly use? Bjoern
Posted on:
@Bjoern: I need complete log (motor calibration, and all motor movement, both have some significant information) About compilation: I know only gcc version, but significant is also version of AVR lib. Version? Distribution? You can try to disable "#define TASK_IS_SFR 1" to 0 (disable interrupt optimizations) and replace "OPT = s -mcall-prologues" to simple "OPT = 2" in Makefile Jiri
Posted on:
If you want to use rev 152-158 please change configuration 0b to 0x32 (hex) It contain bug (Valve can still close, same bug as original SW see Datum 21.12.2008 13:28 in this thread). I know why and I have solution. It will be fixed later. Jiri
Posted on:
Hi Jiri, thanks for your unrestless effort. Propably tomorrow I can send you a log file. In rfmsrc you moved some files but didn't check in the appropriate AVR Studio aps project file. The Studio claims about missing files. openHR20 Suite: Unfortuantely MONO does not support WPF (only Windows Forms) and there are no plans yet to do so although parts of the community see high need for that (otherwise MONO is ded on the long run). It would be possible to rewrite the Suite to run under Windows Forms instead of WPF, but since there is a Linux SW now available, it is not needed and the more flexible solution would be a WEB application. Nevertheless I extended the Suite between christmas and new year and this could be released in a few days, if anybody likes to have it. New is a script sending feature (for ease use, can be derived from log file), the assignments of switching time and temperature (0..3) can be done now, the temperatures can be set with more comfort and a bug fix was done. May I add the code to the SVN? You have been right, the pins for TWI are not routet out, I did look at the wrong port. Using RS485 is a good idea.
Posted on:
@Karim L: I thing that your tool in SVN will be welcome. Please add it into "tools" folder. @All: Please try Rev 159 and send me log. Current default "P" limiter (config 0b) in SVN is 100 (0x64 hex). But I want to test it with smaller value (ex 32 = 0x20 hex). Please change it. This will reduce motor movement outside live regulation arrea, but it is not fully tested. Bug from last rev is fixed (I hope). I want to have log file from 10 hours or more (integration of controller error is slow) Jiri
Posted on:
@Jiri, Yesterday I flashed REV 159, changed 0b to 32 and logged a calibration, window open/close and temp regulation over night. Log is still recording and I will send it to you in the evening today when I am back from work. But what I found in the morning is, that the switching times I set are not used. I can set them and read them back which shows the correct values but they are not used. Is this a bug or is there anything else to set? I have also a Thermotronic module and the code shows adjustments for this module which can be enabled per compiler switch. Is this implementation complete and does it work? Regards, Karim
Posted on:
@Karim L: switching times working without problem for me on all 4 walves with OpenHR20 SW. It has not in MANU mode? Strange, it may be new bug? Thermotronic: I thing that it works, but I haven't this HW to confirm it. This modification is done by Thomas V. and I only review it. Main difference from HR20 is missing communication (pin is used for something else) and no PWM control for motor (haven't support in HW). Can somebody confirm to me that original SW in Thermotronic not use SW implementation of motor pwm (HW is not possible)? Jiri
Posted on:
Hi Jiri, I will try to find out if the Thermotronic uses software PWM next week. At the moment i have less time. I hope I can finish my modification for new timeroptions next week, too. @Karim: except for missing communication and missing PWM my Thermotronic works quite well. I think modification for RFM12 will be possible. The RX-Pin of hardware usart isn´t used, too. So maybe it will be possible to implement an unidirectional communication over RS232 for configuration and so on. Another solution would be a software-uart, but this would need much memory... Thomas
Posted on:
@Jiri, I don't think that manual mode is set, but may be you are rigth. I will check that later. @Thomas, Thermotronic schematic diagram can be seen here Beitrag "elektronische Heizungsregelung mit Thermotronic", but you may know that already. Would it be possible, to release tx pin an use instead one of PE4..PE7? It would enable full communication as HR20.
Posted on:
Hi there, I'm going to try all the stuff as soon as my JTAG Adapter arrives! So far it sounds soooo nice. Meanwhile ... Do you think it's possible to take a new software branch for having more than 4 switching times, let's say 6 or 8 switching times per day? Additionally I'd like to have more than 2 temperatures, say 4 temperatures, e.g. 07:00-09:00 21 Celsius 09:00-16:00 19 Celsius 16:00-22:30 21 Celsius 22:30-07:00 18 Celsius How can this be achieved so that it doesnt conflict with all the radio/wireless approaches there are? Please gimme some helping hand, for what I've seen so far, I can change the software in C with some version of the AVR studio... Am I right? Having more than 4 switching times, together with more than 2 temperatures will surley let me reprogramm all the setup stuff etc. What do you think? Kind regards Thomas Reifferscheid
Posted on:
@reiffert, this work is already done. Thanks to Jiri and Dario, the OpenHR20 SW allows 8 switching times per day and 4 temperatures they can be assigned to.
Posted on:
Ok, the original Thermotronic doesn´t use PWM. I think it is possible to change pinconfiguration to use hw-uart but you have to do changes on the pcb so I think this would be a solution for only a few people. A better way would be to use a rfm12 wireless connection. Thomas
Posted on:
To integrate a rfm12 module, a user has to open the Thermotronic module an solder wires as well. Although it meight be a bit less complex than to cut a strip on the board and rearange a connection, still some wouldn't be able to do neither of both.
Posted on:
Attached files:Here is an updated version of the hr20cmd tool. It has the ability to get and set the timer slots now. Björn
Posted on:
Hello Jiri, Dario and the other guys from HR20 wireless! I read Jiri&Darios Wireless Spec and have some annotations about it, i'd like to give now. I hope it doesnt sound inpolite, it's for sure not meant that way! Ok, nice evening! *** *** 4.2. Sync Packets Did i get this right? the Master sends regulary Sync-Frames containing the current DateTime every :00 and :30 second? (:00 is enough anyway i think). Here i see a bootstrap problem: If a slave hasnt a synced clock yet (regardless if he knows that his clock isnt synced), he doesnt know when the time Slot 00 occurs: So he has to switch on the RFM receiver for about a whole minute, hoping he receives a Sync Frame, which is battery consuming and costing program space. I would rather suggest, that a Sync-Packet is just a SETDATETIME-Command, the Master sends to the Slave, after the Slave sent a BroadcastStatus packet (in his Timeslot with Second=OwnAddress). Then the slave's clock can be synced as well. I dont agree with your statement that Date&Time is needed for preventing replay attacks: A Timestamp is worse for replay prevention than a random number. 4 byte MAC Code is totally overkill! This is wasting battery! Beside, longer packets have a higher propability to get lost over the air. 5.2 Keys I agree that it isnt recommended using Masterkeys in encrypted Communication. But derived Keys like Kmac and Kenc make ONLY sense, if they are derived from the Master Key more than one time within the life time of the Masterkey!!! Otherwise it doesnt have any impact on security. If Kmac or Kenc is broken, Km is worthless as well! I think you mixed that with the idea of session keys. General Critic: The packets are too long, too many syncs from master the slave might not hear anyway, derived Keys that dont improve security. A nonce derived from a datetime and a packet counter is predicatable! A nonce = rand() is much better. What is the CRT ? did you mean CTR? Does all this fit into HR20 left codespace anyway?
Posted on:
@Mario: 4.2. - We need broadcast date/time for encryption also. - boot strap is not problem. It happen only ONCE afret battery change and price is 15mA on 30 second (maximum) It mean 0.002mAh - not problem - sync packet on 00 and 30 is not exactly same. It is needed for force communication from selected slave. Time slot 31-59 can be used as block for one slave long communication. - use random number rater than time is worst because it complicate protocol, try it and you can see. For security is ony byte random number nothing. Two bytes looks better, but if false feeling (http://en.wikipedia.org/wiki/Birthday_paradox) - 4 byte MAC code is nothing, you must calculate energy. Cost is 4.6e-5mAh per packet. This mean that 132000 status packets (one year average) take 6mAh. It is nothing. - For save energy we MUST have very accurate time synchronization. Enable receiver for 1 second have same cost like send 360 bytes! 5.2 I can't agree, that it not improve security. It is no way how to calculate Km from Kenc or Kmac. This mean that if you have Kmac you are not abble calculate Kenc nad vice versa. CRT is misstyping Jiri PS: It is not pollite for others discus this document on this thread when it is not public now. (it is not secret, we will add it on SVN later)
Posted on:
New revision 175: Changes: - controler use new configuration for linear "P" gain - controler configuration for quadratic "P" gain - new config option (0a) for min valve position (default 30%) - new config option (0b) for max valve position (default 80%) - optimization Improvemets: - linear/quadratic controller have best result for me (send me your log) - valve min/max setting save batteries because not all range of valve is active. If you have problems (valve still open or close) please change it. I am not abble to find algorithm to find it automaticaly (every idea have some condition when must fail. I belive that range 30%-80% is correct for major part of valves, but you can set narrower range and save more battery energy. If nobody found any problem I plan release Rev 175 as STABLE version 1.00. If you want to do something: - doxygen comments need improvement to generate USER DOCUMENTATION - create Thermotronic patch for rfmsrc branch - create schematics picture for RFM12 master HW (text specification is in SVN) - I want to find maintainer for stable 1.xx version. I have last one HR20 without RFM12 modification and I will not have HW for test this SW.
Posted on:
Hello Jiri and OpenHR20 Team, first of all, sorry if my comments on HR20 wireless spec were misplaced and sounded inpolite, both wasnt meant so! today i checked out the openhr20 from svn and tested the rfmsrc-branch: i could verify, that the (interrupt driven) RFM packet sending now works correctly, even for long packets (either my receiver was programmed wrong some months ago, or the old openhr20's sending code (non interrupt driven) swallowed some bytes), but anyway this looks good to me! but i got one strange compiler message, saying that this code
// rfm_config.h #define RFM_INT_EN() (PCMSK0 |= _BV(RFM_SDO_PCINT), PCINT0_vect()) #define RFM_INT_DIS() (PCMSK0 &= ~_BV(RFM_SDO_PCINT)) |
creates this warning: main.c:223: warning: implicit declaration of function '__vector_2' it looks to me like a typo (PCINT0 is hard coded beside that) and i wrote
// rfm_config.h #define RFM_INT_EN() PCMSK0 |= _BV(RFM_SDO_PCINT); #define RFM_INT_DIS() PCMSK0 &= ~_BV(RFM_SDO_PCINT); |
instead, raising no warnings, and running correctly ... until i mounted the valve for the motor calibration to start, which makes the HR20 reboot in infinite loop every few seconds. (reboot, running till blinking "2008", reboot, ...). it also showed this reboot loop with #define RFM 0 could this be a consequence that moror control isnt via PWM? any ideas? sorry i have no logs about that (yet). regards, Mario
Posted on:
This code:
// rfm_config.h #define RFM_INT_EN() (PCMSK0 |= _BV(RFM_SDO_PCINT), PCINT0_vect()) #define RFM_INT_DIS() (PCMSK0 &= ~_BV(RFM_SDO_PCINT)) |
is correct: 1) please don't remove branches around macro body or use ";" on end, it make problems if you use macro in expression 2) PCINT0_vect() is dummy call interrupt to insurance that no interrupt will be lost (signal is level based, interrupts is on edge) 3) If you want to remove this false warning, add this
void PCINT0_vect(void); |
into rfm_config.h Reboots: I thing that you are use external power not bateries. Right? Problem is that old code has problem with motor movement with older batteries and create false positive "E3". Therefore from Rev153 motor have "I" controller for speed stabilize and motor startup use config.motor_pwm_max value. This works amazing on batteries, but worst with external power (HR20 have not any capacitor for absorb power shock from motor start because it is not needed with batteries) With external power you must add big capacitor into power lines. If you use USB as power source it is worst, because USB have current limitter (USB specification) and power line shock is hudge.
Posted on:
New release candidate for ver 1.00 is Rev 180. Please test it. Changes: - fix setting to AUTO mode
Posted on:
Information about wirelles: Rev 181 is just proof of concept for bi-directional communication. It is not usable for real live, I must refactor some code and add real functionality. Jiri PS: I am not abble maintain 1.00 versions after release. I have not Hw and I have not time also. Any volunteer for maintain it?
Posted on:
Hello Jiri and the other guys from the 'development team'. Fantastic project, the code worked more or less 'out of the box' for me. No problems with compiling and exactly the features added to the original code that I missed. I have also been using the RFM12 in other projects and have tried that modification during the last days (external RFM12 connected via JTAG pins). After adding some code to get the necessary information like set value and measured value for temperature and the valve position sent via RF I can now at least log the data from one thermostat without cables or a notebook in the bathroom. I hope that this will help me to fix some problems I have with the regulation characteristics using the default settings. I use two HR20 in quite small rooms (toilet ~3m² and bathroom~10m²) and the regulation with OpenHR20 and default settings works much worse for me than with the original HR20 firmware. When heating up in the morning (step from 15°C to 21°C) this happens much slower than with the original software but there is also a big overshoot. Than i quite often see a big permanent difference between set value and real temperature without any reaction on the valve setting. Strange, but as already said I will now first log the data before telling too much nonsense. And I know that these small rooms are very complicated in terms of regulation compared to larger ones. The doors and windows are also permanently (or at least quite often) opened and closed in these rooms and this makes everything even worse. But as already said, the original software seemed to handle this much better. To correct problems like this or workon them, I first have to understand the code and function of the controller better. One comment on the 'RFM' version: I have a blank display after some seconds only with this software. When changing the set value with the wheel, the changed value is displayed correctly again and then after some seconds it disappears again. The 'normal' version without RFM12 works ok. That's it for now, keep on the good work. And maybe someone has a suggestion, which parameters I could touch to improve the regulation. BR, Jörg.
Posted on:
Hello Jörg, I can confirm, that the software does not regulate the desired value exact (about 0,8°C lower than set) and also it does not open the valve wide enough in my opinion to reach fast the desired temperature. In my 30m² living room I have no overshot of the temp. The current setup might be ok for a large heater in a midsized room, but it is not optimal yet. Problem may also be the different valves (where is it completely open and closed?). The SW was optimized by Jiri for less movements and saving battery energy. Further work is required. It would be good to have an algorithm, which adopts automatically to some parameter and may be also predict the temperature which will be reached on a valve setting. For that, a pulse response characteristic could help. Open the valve 100% for a short time close it completely. Measure how long it takes until the temp rises, until it reaches the maximum and how it does fall. Calculate the mathematical formula and use it ;-). Regards, Karim
Posted on:
@Jörg Becker: thank you for feedback. I know that default setting after last modification is not perfect. It works for me (used on 4 rooms, bathroom still use original SW for comparation) Karim have true, we have to many different conditions (valves rooms etc) but too less data for final setting (send me you log). You can try change setting: PP_Factor (05): proportional gain for quadratic error P_Factor (06): proportional gain for linear error I_Factor (07): gain for integrated error Try increase I_Factor, it can solve problems with small rooms. If you can, send me log file. RFM12: this state still in pre-apha state. Too many parts is changed, but not finished. Could you send me your modification on RFM12? May be I can use some part from it. Current code will need some special SW/HW called "master" to control wireless network and for encryption. It make it incompatible with simple wireless listening and loging. @Karim L.: I fully agree, that current controller part can be improved, but it need some suficient matematical model. We not have it.
Posted on:
Jiri, I am sorry, I simply do not have enough time at the moment. My logging attempts were not successful partly because I have problems with my circulation pump not working correctly (no, not with mine, but with that of my heating system :-) ). When the pump works ok and the water temperature is not too high (dependant on outside temperature) the regulation with default values is not so bad, although I still sometimes (?) see permanent differences of nearly one degree like Karim. One of the reasons why I want to have the RFM12 solution is, that I want the thermostats to do the regulation only when the circulation pump is running. And this is 'intelligently' controlled by my heating controller (Schäfer Domoxxx something). In times when the pump is stopped (variable interval at night with start time in the morning depending on outside temperature) the thermostats shall go into off position. The same goes for times when the pump is completely stopped due to high outside temperatures (programmable, set to >17°C in my case). Regarding code with RFM12, I used your code nearly 100% and just added some extra bytes for sending set temperature, real temperature and valve position every two seconds. Worked ok more or less as I did not 'know' (or understand the code enough) that this software does not switch the temperatures to the preset values like the normal software does in automatic mode. It seems to be waiting for a master command to set a new value? So my remote (RF) logging attempts were not successful. Have to dig deeper into that code first (or wait for your solution :-) ). BR, Jörg.
Posted on:
I have a problem with version 180. I had the valve behind a curtain. So it was very hot but the valve was full open! The temperature was shown at 9 °C (I measured about 40°C with another thermometer). I pulled off the HR20-head and watched the temperature, while it cooled down. It decreases from 9 to 0.0 °C and then it jumps to 25.5°C (in my opinion the real temperature at this time). Is there a problem with high temperature measuring? Ronny
Posted on:
@rhb: thanks for bug report. I was repeat it and this bug is real. I will fix it.
Posted on:
Hello Jiri, on last Sunday I flashed REV 180, but couldn't log long enough to make some effects clear. Today I discovered also a jump in the temperature, which I couldn't explain (within a few minutes from 16,76 to 17,26 then back to 16,76, 17,76, 17,30 and 16,82 which looked strange to me. I have the feeling, that the temperature send to rs-232 and internally used are different, which could be the reason for the temp difference of about 1°C which I still can see. When I increase the set temp from 17,5 to 18,5 °C the valve will be set to about 50 which still does not open the valve (at least not much) and even after 30min the valve will only be opened slightly to 52 or 53 which is still not enough. As I have that logged more clearly I will send you a log. Concerning a new regulator model, I have unfortunately no experience and would have to do a lot of experimenting and development work to get something reasonable to work. Regards, Karim
Posted on:
Rev 192 is bug fix for measured temperature > 25.5. - temperature was measured correctly - Rev192 is new release candidate for 1.00 version @rhb: I was found bug only on LCD value, can you explain it better? What was valve value on LCD on "%". Jiri
Posted on:
@Karim L: internaly used temperature and RS232 log is SAME values. It is past 15 second average. Only one exeption is debug output (DEBUG_PRINT_MEASURE). This is RAW values before 15second average. This debug is DISABED in default compilation.
Posted on:
@Jiri: Please take a look to the following source code lines. From my point of view the type of the variable valve is changed too often and may force neagative effects.
controller.c line 57:
static uint8_t pid_Controller(int16_t setPoint, int16_t processValue, int8_t old_result);
controller.c line 70:
int8_t CTL_update(bool minute_ch, int8_t valve) {
controller.c line 137:
valve = (int16_t)pid_Controller(calc_temp(temp),temp_average,valve);
controller.c line 225:
static uint8_t pid_Controller(int16_t setPoint, int16_t processValue, int8_t old_result)
|
Artax
Posted on:
@ Artax: All this lines is correct: temperature can be measured - unit is 1/100 degree(int16_t) temperature can be wanted - unit 0.5 degree (uint8_t) - calc_temp() macro change it into 1/100deg unit and int16_t type. valve position have int8_t variable and range 0-100 PS: I know that it is not best practice change types often. But we don't have a choice, because it was save many bytes in RAM and Flash. Current situation : incomplete RFM code take 15102bytes form 16KB Flash. This is one of many "ugly" parts of code. Most ugly is non existed division into layers and interfaces between this layers. We dont have space for it.
Posted on:
@ Artax: signed values on valve is remaining code from old valve renage (-50 to +50). It can be cahnged to uint8_t Ex:
uint8_t CTL_update(bool minute_ch, uint8_t valve);
|
And it can save 4 bytes in flash.
Posted on:
@jdobry measured temp is ok in rev. 192, thanks for your very fast response! The overheating was my fault, your question was the right hint: the default min. valve position in eeprom (30%) was to high for this small room and valve. Now I set it to 5% and everything is ok. Ronny
Posted on:
@rhb Valve limitation is not depend to room size but only on valve type. Every valves have wider range than active part. This is for my valves. 0-45 - valve is closed, when I try go from 45 to 0 force for movement growing and this have not efect for regulation but big effect to battery live and gears abrasion. 45-70 - this is active part of valve, in this change valve position have effect to water stream 70-100 - valve is open, movement of valve have effect near to nothing. All this values are not exact and it depend to valve type.
Posted on:
"All this values are not exact and it depend to valve type." Not only valve type but even more on the pressure the water pump for the heating water builds up. Especially modern self adjustable water pumps can be a real nightmare in this sence as the pressure in smaller rooms can be quite different depending on how the other rooms behave. I had the situation where the water pump would detect night shutdown for some reason and reduce its power significantly without obvious reason. Turning this feature off reduced my problems, however I did not even know it had this feature as I had to open the pump to get to some small dip switches to control this. Axel
Posted on:
Hello I have buy an other HR20 www.thomas-peterson.de/h20/front.jpg www.thomas-peterson.de/h20/back.jpg I will draw a new circuit diagramm for this.
Posted on:
@Thomas Peterson: It looks like Thermotronic. Compare it with this picture: http://img407.imageshack.us/img407/8021/thermotron... Schematics is here: Beitrag "elektronische Heizungsregelung mit Thermotronic"
Posted on:
Hello Jiri, Karim L. and the other team-members from the 'development team'. Very good, phantastic project, I´m not a electronic specalist and a managed to flash 3 hr20 (original v2.04) with the guidance in this forum, (currently I use the latest F0.97 rev.192 without rfm) for me it works fine so far. But i have also an older hr20 (original v1.xx) and with the same interface cable it was not possible to get a connection, it works only with the newer HR20. For setting the hr20 i used the openHR20suite dated 22.12.2008) from Karim L. The program works in general fine, sometimes I have a longer waiting time for read / write the data’s but maybe this is related to my interface cable. If a new version of openHR20suite is available I would be interested to test it. I had some problems with the valve range adjustment (30-80%) in openHR20suite, this I could not find in the openHR20suite. many thanks and best regards reinis
Posted on:
@Reinis, since the eeprom data arrangement did change, the first openHR20 Suite release is not fully compatible. But I have a newer version, which I can offer next week (I will return on Monday evening home, so that hopefully till Thursday a new release can be provided). It has several new features and supports the latest eeprom layout. Karim
Posted on:
Karim, it seems that you activate RTS as well as DTR in your openHR20 Suite (both lines show ~+12V). Would it be a big deal to make these settings variable with maybe two check boxes? I am using a 'standard' RS232 to TTL converter with optical isolation, which draws the power from the RS232 lines and needs RTS activated and DTR deactivated. Maybe I am not the only one with such a special wish :-) BR, Jörg.
Posted on:
@karim, that would be very nice if you can provide an updated Version of openHR20suite matching the latest eeprom layout. Can you give me a hint how i can log the data's from HR20 (Valve Pos., SW Temp. and Act. Temp.)i saw some recordings? Was this done with openHR20suite (e.g. i have a recorder which would work with DDE-Link if you provide this to other applications) or is it a other program? thx + br Reinis
Posted on:
Hello, I'm new to this forum and I have been playing around with the new firmware for the HR20E for some time. I just want to say that you've done a really good job. But I've also found some minor problems: - the parameter of the RTC_Setxxx functions has changed from int8_t to uint8_t. At least for hours and seconds this was not a good idea. The parameter can be negative if you set the values with the wheel and turn it anti-clockwise. E.g. for minutes you get the sequence 01-00-15 instead of 01-00-59. - setting of DEBUG_IGNORE_MONT_CONTACT to 1 doesn't work. In line 196 of keyboard.c ( mont_contact= 1; ) the value should be 0. The 1 is forcing the E2-Error instead of ignoring it. - After a reset setting of the year manually is sometimes wrong: If you don't touch the wheel and confirm the standard value of 2009 with the PROG key the stored value is sometimes 2008 and sometimes 2009. It depends on the current position of the wheel. At one position PB5 and PB6 are both LOW and at the next position both are HIGH. The variable state_wheel_prev is initialized with zero and so it doesn't reflect the HIGH values of PB5 and PB6. In this case when you press the PROG key a wrong KB_EVENT_WHEEL_MINUS is detected. I've found a solution for this but I'm not very happy with it. But here it goes: I've added the line
state_wheel_prev = (~PINB & KBI_ROT1); |
to the end of the init function in main.c. It must go behind the call of task_keyboard() in order to not being overwritten. I've also defined state_wheel_prev as extern in keyboard.h. Regards, Ulrich
Posted on:
@Ulrich Wilkens: Thanks for bug report! 1) RTC_Setxxx and overflow: It look like bug in compiller. I know that code mix signed and usigned types. And it is correct for 8-bit aritmetics. For example minute 00-1 is 255 and (uint8_t)255+(uint8_t)60=59. But compiler use 16 bit aritmetic to add 60 and I don't know why ((255+60)%60=15). This function:
void RTC_SetMinute(int8_t minute) { RTC_mm = ((uint8_t)minute+(uint8_t)60)%(uint8_t)60; } |
is compiled wrong to:
37 .global RTC_SetMinute 39 RTC_SetMinute: 40 .LFB8: 41 .LM3: 42 /* prologue: frame size=0 */ 43 /* prologue end (size=0) */ 44 .LVL2: 45 .LM4: 46 000e 90E0 ldi r25,lo8(0) 47 .LVL3: 48 0010 CC96 adiw r24,60 49 .LVL4: 50 0012 6CE3 ldi r22,lo8(60) 51 0014 70E0 ldi r23,hi8(60) 52 0016 0E94 0000 call __divmodhi4 53 001a 8093 0000 sts RTC_mm,r24 54 /* epilogue: frame size=0 */ 55 001e 0895 ret 56 /* epilogue end (size=1) */ 57 /* function RTC_SetMinute size 9 (8) */ |
Compiler use 16 bit aritmetic to adition but this code
void RTC_SetMinute(int8_t minute) { RTC_mm = (uint8_t)(minute+60)%60; } |
create correct result:
37 .global RTC_SetMinute 39 RTC_SetMinute: 40 .LFB8: 41 .LM3: 42 /* prologue: frame size=0 */ 43 /* prologue end (size=0) */ 44 .LVL2: 45 .LM4: 46 000e 845C subi r24,lo8(-(60)) 47 .LVL3: 48 0010 6CE3 ldi r22,lo8(60) 49 0012 0E94 0000 call __udivmodqi4 50 0016 9093 0000 sts RTC_mm,r25 51 /* epilogue: frame size=0 */ 52 001a 0895 ret 53 /* epilogue end (size=1) */ 54 /* function RTC_SetMinute size 7 (6) */ |
Could me somebody tell WHY? 2) DEBUG_IGNORE_MONT_CONTACT - fixed, thanks 3) wheel error, I was know about this bug, but it has not priority. Thanks for bug fix. ***************************** fixed in Rev 195 version 0.98 ***************************** This fixed code is not tested, tell me if it solve problem.
Posted on:
Attached files:Since I had my notebook with me and a bit time, I finished the next release of the openHR20 Suite V 0.2.4.23954 today. See the readme.txt for the made changes after installation or the text below. @Jörg, you may change the RTS/DTR signal state via the openHR20suite.cfg. Install the program, chut it, modify the new cfg and restart the program. Currently I did not like to add this settings to the GUI. Report problems and errors please. 23.02.2009, V 0.2.4.X Current day in switching time table has style bold instead of italic With # in command window, comments can be added for better documentation of the log file A detected open window will be shown in status bar For com interface DTR and RTS signal state can be changed via openHR20Suite.cfg XML File. Log File can be renamed as *.scp and used as script file Readme.txt added to installation New eeprom layout of REV 180 supported (Attention: Incompatible to old layout) If an expected response is not received, an error comment is displayed in terminal 28.12.2008, V 0.2.3.X Not released IsTemp progress bar is green when Target Temp is range +-0.5°C, below blue and above red. Aktive day is shown in italic Bugfixes on loading an saving data Resizebale window, application starts with last size Temp 0..3 can be set Temp assignment to switching time possible script execution added (see tooltip of command box) Data names in data files changed -> incompatible 22.12.2008, V 0.2.2.25760 First release
Posted on:
@Karim, i just tried your latest version of openHR20suite, excelent !!! It works much faster with read/write as the older one i used and data-tx is now much more reliable. Also your idea with the red error line is good. thanks and br Reinis
Posted on:
Karim, thanks, works perfect for me!!! BR, Jörg.
Posted on:
Hello Jiri,
I've tested your fixes and they are working for me. Thanks a lot.
Regarding your compiler question: I'm not a compiler expert but I've
found this one:
Beitrag "Re: reihenfolge der bits in einem byte umdrehen"
In short, it states out that gcc is doing calculations in a way that
intermediate results are at least of type int (16bit). This is requested
by the C standard and casting the parameters to 8bit types doesn't
change this behaviour.
Another thing is that avr-gcc is working internally like a virtual 16bit
machine and treating with 8bit values is defined specially.
This could be the reason that your second example with casting of the
end result is working.
Regards, Ulrich
Posted on:
Karim, I found some problems with your OpenHR20Suite, but maybe this is just because I do not use it correctly or I do not understand something. If I read out temperature values, i get the reading 68:15 for empty entries (--:--) in the thermostat. If I enter --:-- in the program and 0 0 for the temperature settings, the program just closes if I press 'set'. Next, if I enter new values directly in the thermostat and then read the timer settings again, nothing is changed on the screen. But the new settings are clearly present in the thermostat. Any idea what I am doing wrong? BR, Jörg.
Posted on:
Karim, now I see that you only show the timer entries for the individual days and not for settings the whole week (I use setting 1-7 on the thermostat). I thought that the settings for (1-7) would be copied to the individual days. BR, Jörg.
Posted on:
Hello Jörg, thanks for the hints. Week mode operation is not well supported in the program. That is one of the open points for the next release. If I don't want to use a switching timer, --:-- is to be set at the module by the wheel. If I read then the time via program, I get x5A0, where x stays for the temps 0..3 to be used and 5A0=24:00, which marks not to use this switch setting. The default in eeprom (see ee_timers in eeprom.h) after flashing is for not used switching timers xFFF=68:15 which is different from above after manual setting. 68:15 is not replaced by the suite with --:-- yet. And even worse, if you try to enter an invalid time, the program crashes. But I know that and in the About window I made a hint to not enter wrong values. I plan to add a check for all entries and I would like to use masked text, but here MS made it not very easy to have a nice implementation. This subject is more complex to solve as you would assume and I need time to acquire a solution. So don't enter an invalid time, only this range is allowed [00:00...23:59, --:--]. Don't try to set a displayed 68:15 red from device, because it lets the program crash. You can switch from week to day mode by setting the timer_mode from 0 to 1 in the eeprom data block. The week times can be set via R00..R07 command. But I will make that available by direct setting in GUI. @Jiri, is it required to have xFFF as default in ee_timers for not used switches and could this values be changed to x5A0? BR, Karim
Posted on:
@Karim L. For not used timers I need any invalid time. x5a0 is also correct.
Posted on:
@Jiri, ok, I will do a fix for that in the next release.
Posted on:
Hi Jiri, I still see some permanent differences in set value and real value without any reaction of the controller. Now I took a HR20 with newest firmware on my desk and waited until the real temperature reading stabilized to 18.32°C (with a set value of 19.0). Then I made some changes on the I value. But i do not understand the result. Do you have an explanation?
20:38:54.515> D: d4 26.02.09 20:38:54 A V: 51 I: 1851 S: 1900 B: 3312 Is: ff03 I value = 3 (default) 20:40:54.515> D: d4 26.02.09 20:40:54 A V: 52 I: 1845 S: 1900 B: 3312 Is: ff3a 20:42:54.421> D: d4 26.02.09 20:42:54 A V: 54 I: 1838 S: 1900 B: 3312 Is: ff78 20:44:54.421> D: d4 26.02.09 20:44:54 A V: 54 I: 1838 S: 1900 B: 3312 Is: ff78 20:46:54.421> D: d4 26.02.09 20:46:54 A V: 54 I: 1838 S: 1900 B: 3312 Is: ff78 20:48:54.453> D: d4 26.02.09 20:48:54 A V: 55 I: 1832 S: 1900 B: 3312 Is: ffbc changed I value to 6 20:50:54.453> D: d4 26.02.09 20:50:54 A V: 55 I: 1832 S: 1900 B: 3312 Is: ffbc nothing happens 20:52:54.453> D: d4 26.02.09 20:52:54 A V: 55 I: 1832 S: 1900 B: 3312 Is: ffbc nothing happens, change I to 10 20:54:54.593> D: d4 26.02.09 20:54:54 A V: 51 I: 1832 S: 1900 B: 3312 Is: ffbc valve closes!!! 20:56:54.593> D: d4 26.02.09 20:56:54 A V: 51 I: 1832 S: 1900 B: 3312 Is: ffbc no change 20:58:54.593> D: d4 26.02.09 20:58:54 A V: 51 I: 1832 S: 1900 B: 3312 Is: ffbc no change |
I thought that increasing the I value would help the controller to get rid of the permanent difference by opening up the valve, but the opposite happens. Ok, I wanted to watch this a bit longer, but after some minutes the automatic timer changed to 15.0°C and the valve closed down completely. I am a bit puzzled. BR, Jörg.
Posted on:
I was try the best algoritmus with my valves in my flat. From feedback I know, that it is not perfect for everybody. (info from Karim L.) I will be changed soon (this wekend probably). I will describe better current situation:
e = error = current_temp - wanted_temp
temperatures is in fixed point, unit is 1/100 degree
abs(e)*e*PP_Factor/256 + e*P_Factor + Is*I_Factor
valve = ------------------------------------------------ + 50
256
where "Is" is integrator with this limitter:
256*50
maximum Is change in one step = --------
P_Factor
if ( ((current_temp<last_temp) && (current_temp<wanted_temp))
||((current_temp>last_temp) && (current_temp>wanted_temp))) {
// update integrator
Is+=e;
}
|
You can see consequences: - if current temperature is not changed from last, integrator is not updated - if temperature grow and current_temp<wanted_temp (and vice versa), integrator is not updated This limitation I was add to limit motor movement around wanted position. Without this, near to every 4 minutes SW will move motor back and forth. It have devastation consequence for battery live. Another reason is hijacking of integrator. Why? Please fancy this situation: wanted temperature is 17 degree, real temperature is 19 degree, we have opened door from heated space. In this situation, valve is fully closed. But without limitation, error value must be -3 (-300 in 1/100 deg unit) and integrator will integrate this value every step. Result after few hours is clear. Integrator will be on limit and not allow motor movement when you change wanted_temp. Valve changes < (pid_hysteresis/265) is ignored (noise protection) (default pid_hysteresis is 120) At this moment I thing that this limit conditions is too hard. ---------------------------------------------------------------- @Jörg Becker: Is: is integrated value ffbc mean -68 decadic. If you increase I_Factor, valve must be closted, see up to formula. Small changes of I_Factor needn't change of valve because it's smaller than (pid_hysteresis/265) Try calculate formula from up. ---------------------------------------------------------------- What I can do? (and probably will do): - I can change comparation in "i" change consequences from ">" to ">=" (and vice versa) After this it will be more sensitive to hijacking of integrator. - Itegrator can be reset after every change of wanted_temp. It is usual in numeric PID controllers. But after this change temperature stabilization take more time. It can be improved with default "zero error" position in EEPROM (current value is hardcoded 50% - see to formula, new default value can be around 55%) (@Karim L. > it need change of EEPROM layout) ---------------------------------------------------------------- PS: If this explanation is not clear don't worry ask me. Jiri
Posted on:
I forget in "What I can do?" part: (update) - I can change comparation in "i" change consequences from ">" to ">=" (and vice versa) After this it will be more sensitive to hijacking of integrator when valve is fully closed or open. And it will better to repair temperature offset. It can be abble repair hijack, but it take long time. - Itegrator can be reset after every change of wanted_temp. It is usual in numeric PID controllers. But after this change temperature stabilization can take more time. It can be improved with default "zero error" position in EEPROM (current value is hardcoded 50% - see to formula, new default value can be around 55%) (@Karim L. > it need change of EEPROM layout) Reset interator will solve part of hijacking problem. After this "hijacking" is possible only for constant wanted_temp without any changes in long time when valve is fully closed or open. I don't have any idea to solve this. Motor calibration on Saturday 10:00AM will cancel this hijack, but it can be too late in some situations.
Posted on:
Hi Jiri, I will take a closer look at it at the weekend. Don't worry about eeprom layout change. I do only have to copy the new Layout into my code, the rest is don't automatically per reflection mechanism. The only disadvantages are, I have to release a new version and that stored eeprom data in a file can't be used without problems. Maybe I add a feature to load the eeprom structure from a file to have more flexibility for different versions. If not already implemented, you could add a hysteresis, which allows lets say 0,2°C deviation before trying to regulate, to reduce motor movements. And the Is value should be limited for keeping the contoller responsive even if it is what you call hijacked. During the day (from 7:20 on), the wanted temp is set to 15,5°C, but my living room is always warmer, because of good isolation, solar radation and heat comming through the wall and floor of my neighbors ;-). The temp during the day can go up even in cold winter day to 21°C without having heater on. But in the evening it is getting colder, but most of the days not below 16°C when heater keeps off. Thats to cold for me. Therefor I programmed my controller to heat up to 17,5°C at 17:30 till midnight which results in about 19-20°C where I sit. Under this conditions the integrator will sum up to the rangellimit when wanted temp is 15,5 during the day and after midnight. So far that to the conditions I have.
Posted on:
@Karim L. I was try to add hysteresis which allows deviation before trying to regulate. But is was unstable solution. System was overregulated for any constant setting. (I can't remember if I commit this try or not, but I was try it) I will try to use same "hysteresis" but only for integrator update condition. Do you remember to ">" or ">=" in my text from 2009-02-27 10:35? We can use ">" around wanted temperature +- tolerance and ">=" or none condition outsite tolerance. I would be better. Is value is already limited to (256*50/I_Factor). This mean that maximum effect is +-50% on valve. I can move this setting to EEPROM, but I don't belive that it is major problem. PS: You have perfect conditions to "hijack" integrator. Well isolated room, where is external source of heat. And lower wanted temperature than natural in long time. Jiri
Posted on:
"ffbc mean -68 decadic. If you increase I_Factor, valve must be closted, see up to formula." I see from the formula that this is the way it works, but does this make any sense? As you wrote, a negativ value means that the real temperature is lower than the wanted temperature. In this case Is becomes more and more negativ with time and the valve closes more and more. This is not really the desired effect. Is this a bug in the formula or a misinterpretation from my side? BR, Jörg.
Posted on:
@Jörg Becker I thing that is correct: ff03 is -253 ff3a is -198 ff78 is -136 ffbc is -68 Negative values can be calculated by (dec(value)-dec(0x10000)) Jiri
Posted on:
Jiri, i know about representation of negative values. The problem is that your description in the mail from 10:35 is not 100% correct and is not the same as in the program code and that mislead me. you wrote "e = error = current_temp - wanted_temp" and that means that e is negative if the set value is higher than the real value. Together with the term "Is+=e" this would mean that in my example the negative value of Is should get more and more negative, what it obviously does not do! In the program code we find that: " error16 = setPoint - processValue;" which has opposite sign than e and " sumError += error16;" which leads to the correct behavior that Is gets more and more positive over time if the real value is lower than the set value. So the code is correct. The only problem is, as you explained, that you only change Is if the temperature value changes. So, in my example, if I only had waited some minutes longer and the temperature would have changed just a bit, Is would have become positive and the valve would have opened. Thanks for your help to understand the code a bit better! BR, Jörg.
Posted on:
@Jörg Becker: OPPS! I was make mistake in my test. You are right. Correct error formula is
e = error = wanted_temp - current_temp |
Jiri
Posted on:
Hello How can i resive the data from termotronic?
Posted on:
@Thomas: Thermotronic version of SW don't support serial communication due to hardware limitation. Serial line pin is used for another function. You can have two choices: - wireless comunication - rfm12 - now exist on pre-alpha state, it is not prepared for end user, wait aprox 1 month - prepare another type of communication or simulate serial line on SW (not exist now) Jiri
Posted on:
@jdobry Ok when i buy the rfm12 and connect it, what must i do on the receiver site? Have you an Link? Thanks for all :)
Posted on:
@Thomas: On receiver side you need another rfm12 and simple board with ATMEGA16. Sorry but I don't have better documentation than text specification in SVN now. Jiri
Posted on:
Rev203 have improved integrator consequences. It can be less sensitive to ingegrator "hijack". Please test it. *********************************************************** It is no fully tested now, last stested version is Rev 192. ***********************************************************
Posted on:
Hi Jiri, I tried the new version with temp-tolerance set to 0.3°C and it works really nice for me. No big permanent deviations any more, that's good. Congrats! I still have problems with my very small toilet room with oversized radiator. The temperature overshoots very much. One thing that helps is to decrease the PID interval (I have set it to 1 minute now). But I have no logging data, so I am still very uncertain about the effect. After playing around with the various versions for some time now, I have one remark (not complaining, just asking for your opinion :-) ): - After a reset (e.g. battery exchange) I have to 'type in' the whole date and time setting starting from the default value (01.01.2009). I would like it much more if at least the year, the month and the day would be stored to eeprom on every change (even for the day that means just 365 write accesses per year and the time and Ah needed are negligible). I have done this on a project where I want to be sure that after an erroneous reset (spikes, ESD) the system still has a date/time that is at least nearly ok. I also store the last hour value to eeprom and have the minute and second value uninitialized at startup (I just test if the value is reasonable, means in 0..60), so that in most cases I only loose some seconds. BR, Jörg.
Posted on:
@Jörg Becker: Toilet room: without log I can tell nothing. But log from this extreme situation can be helpful. Date in EEPROM: nice idea, you can me send patch. For me it is not significant, because I am use date/time setting from wireless network (rfm12). But it can be useful for others. PS: I haven't erroneous reset. Do you use batteries or external power? Jiri
Posted on:
I am just going through the RTC routines:
bool RTC_IsLastSunday(void) { if (RTC_DOW == 7){ // sunday ? return 0; // not sunday } .... |
shouldn't that be:
bool RTC_IsLastSunday(void) { if (RTC_DOW != 7){ // sunday ? return 0; // not sunday } .... |
Regarding your question: No, I did not experience resets with this project except during battery exchange. BR, Jörg.
Posted on:
@Jorg: OPPS! Thanks for bugfix. You are right, it is bug. Jiri
Posted on:
Just for your info, this is my (very simple) routine for RTC from one of my other projects:
void RTC_add_one_second(void) { static const uint8_t days_per_month[12] = \ {31, 28, 31, 30, 31, 30, 31, 31, 30, 31, 30, 31}; if (++sec>59) { sec = 0; if (++min>59) { min = 0; if (++hour>23) { hour = 0; // recognize leap year (correct until 2099!!!) if (((year&0x03)==0) && (month==2)) // if year can be divided by 4 { days = 29; // it's a leap year with 29 days in Febr. } else { days = days_per_month[month-1]; } if (++day>days) { day = 1; if (++month>12) { month = 1; year++; EEPROMwriteB(13, year); } EEPROMwriteB(12, month); } EEPROMwriteB(11, day); } EEPROMwriteB(10, hour); } } } |
BR, Jörg.
Posted on:
@Jorg: I know that current implementation isn't optimal. This was not my code and abble to see many point to optimize (some function can be "static" and more). But I has many more significant tasks.
Posted on:
RTC_IsLastSunday bug was fixed in Rev 207 thx: Jörg Becker Jiri
Posted on:
Hello, Schematic for RFM12 "master" board communication can be found here in SVN: http://openhr20.svn.sourceforge.net/viewvc/openhr2... First alpha version of wireless comunication SW can be released very soon. If somebody will be create PCB for this, please send me one. Notes: not all supply pins (5,6,17,18,38,39) must be used. LED can be moved to another pin than PD7(16) but tell me it. RFM12 DATA pullup PB0(40) can be moved to another pin or we can use pull-up resistor, but tell me it. Jiri
Posted on:
Hi Jiri, it would not be a big problem to do a pcb for the master. But it would be nice if you could explain what the exact function or way of use of the master is. - Is it used as a stand-alone unit? What does it do then and how is the master itself configured? - Is it used as a sort of RF gateway for a PC? - Does it completely override the settings in all the connected HR20s? - It does not have any inputs (keys, door or window open detection, ...) at all, no display, (no power supply), no temperature sensor, no RTC Would be nice to understand that. BR, Jörg.
Posted on:
"master" have 2 functions: - It control wireles network access to shared media (air) and broadcast real time - it is gateway for Linux/Windows PC or linux based router (see to http://www.openwrt.org) I will completly control all connected HR20. It have not any input (it is not needed). It is gateway between serial line and RFM12. I have same pinout like HR20, it mean that we can use same programming cable and same serial level or serial USB convertor. Power supply must be wired to connector. SW on PC side have 2 parts: one is small daemon, second is web interface. Both is in PHP. It can run under Linux or Windows. Including Linux on small routers. It have amazing benefit for me, this router run 24/7 and need small power (7W). You can control heating from anywhere 24/7 including access from PDA.
Posted on:
Wireless RFM12 modification documentation is available on SVN http://openhr20.svn.sourceforge.net/viewvc/openhr2... - internal version is inside HR20. It allow to use debbugger. It is more compact. It is safer for childen etc. But it need expert skill of soldering. Solder wires "touch" to MLF package is nightmare. - external version is outside HR20 on system connector. It not need open HR20, easy to install. But not allow connect debuger to HR20. And it can be mechanicaly damaged. (thx to Mario) Jiri
Posted on:
Jiri, thank you for your explanation of the master functionality. I want to use the wireless HR20s a bit differently then you. Most of the time the units shall work independently with their own settings and I just want to override these settings occasionally, e.g. if I want to switch off the heating completely or the circulation pump is not running..... Then I want to add small wireless nodes that monitor windows and doors with a small reed contact. This is first just for monitoring and second to switch on and off the HR20s in the same room where I see an open window or door (for some minimum time off course). Next thing I already started is the wireless remote control of most of the internal and external lights and also some other electronic devices, all with the same RFM12 receivers (433MHz in my case). When all this is completed, I also need a gateway between PC and this wireless network. And then a WEB interface would be nice, too. These are the plans, I hope to find the time for it. BR, Jörg. PS: Since some weeks I have a very small problem compiling the 'wireless' version of the firmware. If I double-click the .aps file, I get a message about missing files and I see that the file path of these files is 'C:\jirik\hr20\rfmsrc\...'. Am I doing something wrong with the SVN update? I know that I can simply 'locate' these files on my HR20 folder, but every time I update I have to do it again.
Posted on:
@Jorg: Don't worry about missing file. .aps file is not used for compilation, just for debug and edit (I use Kate and PSpad for edit). Compilation use Makefile. Jiri
Posted on:
Information about RFM12 SW: It is still incomplete and it is not prepared to use. I hope that first "Alpha" version will be prepared around 20.3. If you will want to use it, it is right time to buy/prepare HW. I will need testers ;-) Jiri
Posted on:
Apologies if this is in the wrong forum, but I would like to load up the software to my HR20. What is the easiest way to connect to pc? and what are the details of each of the pins which I must connect to RS232? thanks
Posted on:
@Bronco: To load up the software you need a Programmer that supports JTAG, e.g. AVR Dragon: http://www.atmel.com/dyn/Products/tools_card.asp?t... The details of the pins are described in the documentation.
Posted on:
Great. I will look up JTAG. I presume then I will need a JTAG to Rs232 if I want to communicate from pc to rondostat?
Posted on:
The software is not downloadable from sourceforgenet. Has the project been moved elsewhere? thanks.
Posted on:
Project is not moved. But we not release any final version. You must download it from SVN.
Posted on:
Hi Jiri and all the other HR20 users, I have just recognized a strange problem with on of my HR20s with one of the latest firmware versions. After mounting the HR20 and after the calibration run, I found that the valve opened at a readout value of about 41% valve position. I then corrected the minimum valve position to 38%. After a week or so I found that the temperature in the room was always to high and the valve already at its minimum position of 38. I could hear that the valve was still open. I therefor corrected the minimum valve position to 30% (default value) again. Yesterday evening I found that the valve was again wide open (24°C in the room) although the valve was at 30% position. After a calibration run the minimum position where the valve opened was again ~41%. (Strange thing is that this behavior is very similar to what I experienced with my very old HR20s from time to time.) Is there any chance that the controller misses pulses from the postion encoder? Did anyone else experience the same problems? Is this perhaps hardware dependent? BR, Jörg.
Posted on:
@Jörg Becker: Have you log file? I could be more than one reason. - you have some "noise" on impulse conter input and current noise filter fail (create log file it is helpful) - it is +-1 problem on ends. It can count false +1 on motor start or not count first pulse on movement. On worst situation after 100 movements you will have 100 impulses error on position but it is not probbaly (win in lotery it absolute sure compare to this :-) ). I would like to found where is bug. Because it can be problem on code. Can you create log (calibration + minimum 20 movements) Because we can't mesasure position without any error (motor start can create false pulse very easy), valve use automatic calibration on Sun 10:00AM. To break this problem, current SW don't stop motor inmediately after wanted pulses but it will stop motor with delay. Idea was stop motor ouside problematic position around motor pulse edge. You can tune this value (config.motor_eye_noise_protect, position 0x15 on trunk), default value is 40% of motor pulse cycle. Jiri
Posted on:
ok. got the avr dragon. could someone guide me on the steps to connect to the HR20? I assume a) connect JTAG cable from AVR Dragon to HR20 b) use AVR Studio (not sure how) c) load up hex file from svn repository to flash HR20 could someone help me with some details: a) do I need to set some JTAG pins? b) If I want to communicate with HR20 without flashing to getState is this possible? or do I need to flash (basically I am scared of flashing until I know exactly what I am doing). regards
Posted on:
@Jörg Becker: I saw the same situation, but I thought, that was my fault, because I played with the sources and sent the log/debug messages every second. So I thought because of this the motor loose steps. Unfortunately I don´t have any logs, because everything was fine until after a new calibration... Ronny PS: Has anyone also my (strange) situation: I have long-distance heating, but without a heat exchanger in my house - only a valve, that closes the whole system (every heater in every room), if the temperatur of the recirculation water is too high. That means, if one heater (in my case in the bath-room) produces too high temperature in the recirculation tube, the valve closes and also the heater in the the living room gets cold. I cannot change this behavior, because we rented this flat. So I tried the following: I putted a second temperatur sensor to the HR20 and tried to control the recirculation temperatur of any heater independently. Has anybody suggestions how/where this can be done? My idea: decrease at the end of the function CTL_update the valve value proportional to the recirculation temperatur.
Posted on:
I too figured out a problem regarding loss of pulses. Situation: Room was heated up to about 24°C, valve position displayed as 30% but valve was not closed (nearly open, seen after disassembly of Controller Head). After new calibration everything seems to be ok. But the question is - how long? In this context, could somebody give me a little explanation in how the calibration of the Motor travel works. It seems to be a little bit tricky. Especially the interaction the various subroutines. Ulf
Posted on:
I too figured out a problem regarding loss of pulses. Situation: Room was heated up to about 24°C, valve position displayed as 30% but valve was not closed (nearly open, seen after disassembly of Controller Head). After new calibration everything seems to be ok. But the question is - how long? In this context, could somebody give me a little explanation in how the calibration of the Motor travel works. It seems to be a little bit tricky. Especially the interaction of the various subroutines. Ulf
Posted on:
Most probaly is that SW not count one pulse add one false pulse when motor stop and run back later. WE NEED LOG FILE. A am not able replay this situation now.
Posted on:
!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !WARNING! Do not use "On" setting but some temperature only. It will pull valve position to physical limit every second !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! It will be fixed very soon. Touched Revisions on main trunk is 175-221
Posted on:
Update to Rev 222 is RECOMENDED. It was fix problem with "On" setting. PS: Motor position measure will be improved later
Posted on:
Attached files:Hello, @Jiri Dobry here are a logfile about the loss of pulses problem. I measured it from 22nd march at 00:00 till 23rd of march ~21:00. The valve was calibrated at the beginning of the measure. Now the log says 5% valve position, but the service menu (pressing 2 times -C-) says 10%. The environment: a small bathroom with a big heater and a strong spring in the valve (means: if I pull the head from the valve the valve opens itself - I have other valves in my flat, where the valve stays at the momentary position, if I remove the head). I have very agressive settings at this valve: update every 1,5 minutes and a small differenz between wanted/actual temperature. hope this helps to find the problem Ronny
Posted on:
what I forgot: this is release 198 Ronny
Posted on:
Thanks for LOG file to everybody. At this moment I have new valve position measurement. It works, but need some cleanups. It will be prepared for SVN tomorrow (I hope). @Ronny: Can you send me your valve range? You can get it by command "T08" and absolute valve position (command "T09"). Valve position on log is what you want to have (can't be change live on motor movements), valve position on LCD is calculated from absolute position and show live position. It use near to same equation, but 16bit fixed point aritmetic have some +-1 error. It is strange, that diffence between this two values is bigger than 1. Jiri
Posted on:
Hello, You can test latest method to count motor pulses. Any LOGs will be welcome. Revision with change is 225. This version is not tested on all conditions. If you want stable version on this moment, please use Rev222. Jiri EDIT: new pulses calculation - minor bug fix in Rev225
Posted on:
Hello Jiri, at first: thanks for your incredible work at this project! I´m not so familiar with microcontroller programming and it´s hard to understand for me what you did in the program - but I´m learning... And so I have to show respect to your work. Unfortunately I had to recalibrate my bathroom HR20 before I read your posting, so that the error isnt there now. I made a T08 and got T[08]=01dc and for T[09]=00e5. A log line is now D: d2 24.03.09 20:25:04 A V: 48 I: 2349 S: 2400 B: 3052 Is: 10aa and the valve position is identical in the service menu. Maybe I have to wait until the error occurs again, for my experience this will be in 2 days. Therefore I didn´t flashed your new version, because another hidden problem could be there Ronny
Posted on:
Hello, here is the problem on Version 198 again: Log-File says 5% valve position and service menu says 10%! D: d3 25.03.09 22:43:21 A V: 05 I: 2525 S: 2500 B: 3047 Is: ef56 X T[08]=01f0 T[09]=0033 D: d3 25.03.09 22:44:00 A V: 05 I: 2585 S: 2500 B: 3044 Is: ef56 D: d3 25.03.09 22:45:20 A V: 05 I: 2548 S: 2500 B: 3048 Is: ef56 Ronny
Posted on:
@Ronny: Strange. T08 and T09 values look correct for 10% (10.28%). Can you update SW to rev 225? I will look to this problem later. Do you change some values in EEPROM? Jiri
Posted on:
Hello Jiri, I will update to 225 now. I changed the following eeprom-value: /* 08 */ temp_tolerance; to 50h /* 09 */ PID_interval; //!< PID_interval*5 to 10h /* 0a */ valve_min; // valve position limiter min ;to 30h /* 0c */ valve_max; // valve position limiter max; to 3ch and s:ome strange settings - I cannot remember, that I changed this values /* 0d */ motor_pwm_min; //!< min PWM for motor; to fah /* 0e */ motor_pwm_max; //!< max PWM for motor; to 1e Ronny
Posted on:
I would like to inform you, that wireles communication works. Rev 227 is ALPHA version (http://openhr20.svn.sourceforge.net/viewvc/openhr20/rfmsrc/) Some notes: - PHP&sqlite is needed - It can run on PC or Linux based routers (for 24/7 access, low powered devices see to OpenWRT project) - linux instalation is without problem. Windows users must use "Serproxy" and connect daemon.php to localhost TCP port. - daemon.php come from communication test code. It is buggy and sometimes lost some request. User must make another request. I will not fix it but I will create complete new daemon. - It is need to setup serial port to 38400/8/1 (linux machines have "start" file) PS: it need to write HowTo setup document. (volunteer?) Jiri
Posted on:
PS: When somebody will create PCB for wireles "master", please send me one. Thanks. My current master is nest of wires. Jiri
Posted on:
Window open function looks buggy. See to my log. It have false "close" detection. I will try it improve. PS: table is from wireless extension, it is nice to monitor all valves near to real time. See to attachment
addr time mode valve real wanted battery error window force 17 2009-03-28 09:45:15 - 30 15.03 4.5 2.668 0 0 0 17 2009-03-28 09:44:55 - 30 14.78 4.5 2.663 0 0 0 17 2009-03-28 09:42:53 - 30 14.7 4.5 2.667 0 1 0 17 2009-03-28 09:41:15 - 30 15.13 4.5 2.663 0 0 0 17 2009-03-28 09:40:02 - 30 15.29 4.5 2.662 0 0 0 17 2009-03-28 09:37:14 - 30 15.44 4.5 2.661 0 1 0 17 2009-03-28 09:36:11 - 30 15.7 4.5 2.668 0 1 0 17 2009-03-28 09:33:14 - 30 16.29 4.5 2.668 0 0 0 17 2009-03-28 09:31:23 - 30 16.54 4.5 2.662 0 0 0 17 2009-03-28 09:30:15 - 30 16.5 4.5 2.668 0 1 0 17 2009-03-28 09:29:14 - 30 16.8 4.5 2.668 0 0 0 17 2009-03-28 09:25:34 - 30 16.99 4.5 2.662 0 0 0 17 2009-03-28 09:25:14 - 30 16.92 4.5 2.663 0 1 0 17 2009-03-28 09:24:17 - 30 17.13 4.5 2.669 0 1 0 17 2009-03-28 09:21:22 - 30 17.47 4.5 2.666 0 0 0 17 2009-03-28 09:21:15 - 30 17.43 4.5 2.666 0 1 0 17 2009-03-28 09:19:44 - 30 17.54 4.5 2.668 0 1 0 17 2009-03-28 09:17:15 - 30 17.97 4.5 2.663 0 0 0 17 2009-03-28 09:16:36 AUTO 45 17.77 17 2.667 0 0 0 17 2009-03-28 09:15:47 AUTO 30 17.6 17 2.669 0 1 0 |
Posted on:
Attached files:Wireless aplication screenshot
Posted on:
Attached files:Wireless aplication screenshot (false window close detection problem)
Posted on:
Attached files:Wireless aplication screenshot #3 (timers)
Posted on:
Hello jiri, your last inputs are very interesting. I think i have to upgrade to a wireless version now.... I use at the moment Rev. 192 and since 3-4 days i have problems with the time, each day the time changes with one additional hour (issue with sommertime ?? the actual time is e.g. 10:00 but HR20 shows 11:00 ,next day 12:00 and so on). regards reinis
Posted on:
@reinis: it look like bad XTAL. I have 6x HR20 and usual precision is better than +-2sec/day except one (8 sec/day). But with wireless extension it is not problem it is syncronized from master. And master can be syncronized from internet.
Posted on:
@jiri, regarding the 1 hour timeshift, i think it has something to do
with the follwing function:
void RTC_AddOneSecond (void)
Add one second to clock variables
Note:
* calculate overflows, regarding leapyear, etc.
* process daylight saving
o last sunday in march 1:59:59 -> 3:00:00
o last sunday in october 2:59:59 -> 2:00:00
ONLY ONE TIME -> set FLAG RTC_DS
reset FLAG RTC_DS on November 1st
over a longer time/several weeks the time was always correct on all of
my hr20. The problem started only last week and on all of the three
hr20. I resetted the time on the next day i had again a 1 hour offset
but only until today (summertime change). This morning the 1 hour
timeshift was not there anymore and i did a manual set to summertime
(daylight saving).
regards
reinis
Posted on:
reinis, before Rev207 there was a bug in the daylight saving routine (see our postings on 2009-03-04). As you are using Rev192, it is very likely that you hit that problem. BR, Jörg.
Posted on:
Attached files:@Jorg & reinis: Jorg have true. This bug was fixed and I was not abble to see that you are use too old version before bugfix. Wireles extension: New Rev 228 with graphs. I was not abble to find any library for lightweight XY grapg. All was too havy for embeded router. Therefore I was create one oprimized for this project. I will improve look&feel but you can see result from Rev 228 on attachment.
Posted on:
Hi Jiri, regarding the wireless version (Rev207), I have some questions: - when I compile it, I get
Program: 16478 bytes (100.6% Full) |
is this ok?
- how does the HR20 with this version behave, if I do not have a master
running? Does it use its individual settings then? Does it send the 4
minute reports wireless instead of via RS232?
BR,
Jörg.
PS: I quite regularly (but not always!) see that the temperature reading
changes by some degrees (1.5 to 2?)while the motor is running (all
firmware revisions). Is there any explanation for this? Can this cause
any trouble? I am asking because yesterday morning the bathroom was cold
and the display showing 'OPen' without any cause. Nobody had opened the
window nor the door and half an hour earlier the temperature had been
ok. I have never managed to get this response ('Open') by really opening
the window (not even with the original firmware). In most cases when I
tried this (open window), the temperature did not fall fast enough. So
it is even more strange what I saw yesterday.
Posted on:
@Jörg: Please use recomended compiler WinAVR-20071221 or disable something on debug.h Q: how does the HR20 with this version behave, if I do not have a master running? A: you can use RS232 connection in same way as before this modification. But if you use only wireless and master not runnig, software will save 4 minutes report to buffer, after buffer overload (it is small for maximum 7 reports) data will be lost. Q: Does it use its individual settings then? A: yes, setting is individual for each valve. But you can manualy change AUTO/MANU mode or wanted temperature easily from one page. Q: Does it send the 4 minute reports wireless instead of via RS232? A: yes, you can see example on screenshots Jiri
Posted on:
Jorg: Temperature reading during motor run: You are right, motor measure too big noise for exact measure. We will must change it. But till now I was not have any accident from this, because we are use 15 second average for temperature controler. But window open detector have noise filter only from 5 values. You can try change this filter setting it is config.window_open_noise_filter setting (0x23 configuration). But I wrote request to disable measure during motor run into TODO list. Jiri
Posted on:
Jiri, first of all, I saw your graph from Rev228. This is very nice! - Regarding the wireless version, I want to have reports via RFM12 without using a master, e.g. for logging. Means that the HR20 works exactly as with the normal version but with wireless reports instead of RS232. Have to find out how this works. The other question was whether the wireless version will use its own (stored in the HR20!) settings, if the master fails working (or is not present at all). I understand that if the master is running, it takes full control. - Regarding the temperature measurement, I do not understand why the ADC buffer is 60 entries long and only 15 are used for the average (compile time options, not changeable during runtime). Does this make any sense? BR, Jörg. PS: I still have a lot of questions concerning the code and unfortunately not enough time to go through it and understand it in detail. I am just busy working on my remote switches with RFM12. Got first PCBs and will try getting these to work during the next time.
Posted on:
Jorg: you are not abble use current wireless code without master. Simply before master syncronize communication an without master you are not abble use encryption. But I thing that master is extremely simple and cheap. If master fail, you are not abble communicate. Current code don't support communication between two valves (and we have not free flash). And mainly: "master" is interface between computer and valve wireless network. How you want to control this network without this interface? 60 measured items on table is used for window open detection. We need to compare current value and 1 minute old value.
Posted on:
For clarification. CurrentSW can be modified to direct communication between valves or between remote thermometer to valve. But it still need "master" for manage network and encryption. For direct communication without valve you need some caint of "MESH" network. It is possible if you disable some existing part of SW to save flash space (for example rs232 com). But it is more complicate than current communication. It need complete new protocol, complete different SW layer. And volume of work for RFM12 is sufficient university dissertation for few peoples (it is not only few lines of code). Another chance is buy some existing solution (and use another more expensive wireless modules).
Posted on:
New improvements for 1.00 version are in rev 229: - configuration for disable/enable ADC measure when motor run - bug fix for false positive window close detection Jiri
Posted on:
I have until now the problem with loss of steps (original version 225). I think that because of the strong spring in the valve the real valve position shifts a little bit every time the valve is closed. So I want to correct these "shift values" by a "partial" calibration to save battery. That means: I want to correct the actual valve position only by driving the valve to the real open position (until the motor stops). Has somebody a hint for me? Ronny PS: I have solved my problem of the recirculation temperature (see Post on: 2009-03-17 13:38) at the beginning of CTL_update I save lastProcessValue and sumError. After calling of pid_Controller I compare the recirculation temperature with a value stored in eeprom. If the temperature is too high (with hysteresis) , I close the valve and restore lastProcessValue and sumError from the saved values. This works for me in a reasonable way... But the problem of loosing steps exists also with the original software from the SVN.
Posted on:
@rhb: It is unbelivable for me, that Rev 225 can lost some motor steps. Absolutly strange. You don't want to use "partial" calibration, you can use current manual calibration mode. (Unmount head from valve, manualy close valve, this position will be saved as "close", press "C" and mount head to valve back - keep "C" pressed during this operation) After this calibration proccess on LCD will not show "Ad 1" etc but "A 1" etc. Motor recalibration will only touch to "open end" and go back to wanted position because know "closed position" - saved in EEPROM. Recalibration is done automaticaly every Sunday on 10:00, you can change it on main.c Return to automatic mode is same, butt preess and hold "PROG" button not "C". PS: I trust you this problem but I can imagine where is problem, it need LONG log file from Rev 225 or up. PSS: how you measure second temperature? !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! All: we still have problem with window open close detection. After last change it is better, but it can be false positive or negative again. I will completly rewrite this part later this week, I have idea how. !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
Posted on:
Hello Jiri, my "partial calibration" was only a thought for a workaround to automatically correct the actual position. I saw the part of the program, were the full recalibration is done on sunday 10am, but I wanted to save battery power... (Thank you for the explanation of the manual calibration, I didn´t figured out this from the source code - as I said, I´m learning) My theory is, that the the motor doesn´t lose steps, but because of the strong spring in the valve the motor is turned back a little bit AFTER it (and the "photo eye") was switched off and so the actual position is distorted. So maybe it would help to deactivate the "photo eye" a little bit later - what do you think? I started a new log today with original version 229, what do you mean with LONG time? 1,2 or more days? Or until the valve isn´t closed? Now this will takes longer because of the warm weather and mainly closed valve... Ronny PS: I measure in my "recirculation temp version" the second temperature by adding a second thermistor to pin 60 (ADC1) of the ATMEGA and GND (I don´t need the wireless part) and a resistor between pin 60 and pin 58. I know, that I decrease the precision of the measurement of the room temperature with this modification.
Posted on:
@rhb: manual calibration is almost equal to "partial calibration" as you want. Because range of valve is defined, every calibration in this mode is simple (go to "open end" and it's done)
Posted on:
Attached files:@Jiri here are the long log. At this evening the error happens again. The valve seems closed (30%), but the heater is warm. At the beginning (after the calibration) the valve is real closed at 40% and now the valve is a little bit open at 30%. The log was made with original version 229. I changed only the pid-interval to 120 seconds. Ronny
Posted on:
Due to problems with window detection I made completly new window open detection. You can test in Rev 232 Configuration options:
/* 22 */ uint8_t window_open_detection_diff; //!< threshold for window open detection unit is 0.1C
/* 23 */ uint8_t window_close_detection_diff; //!< threshold for window close detection unit is 0.1C
/* 24 */ uint8_t window_open_detection_time;
/* 25 */ uint8_t window_close_detection_time;
|
How it works: Program save temperature AVG every 15 seconds. For window open detection, program compare current actual value with higest value in selected interval. Interval is in 15sec unit in window_close_detection_time and detection threshold value is in window_close_detection_diff. Window open detection is similar. Default values is 0,5degC difference on 2 minutes interval. Maybe that we will need change it. Jiri PS to @rhb: thanks for log, I will analyze it today or tommorow.
Posted on:
@rhb: Strange, your log looks perfect. No problem. Where is your position where valve start opening? (normaly after restart) On start or end of movement you can found x/X and y/Y chars. This is signalization where motor stop (logical level). It must be "x" and "y" every time because we want to stop on low level. When motor move sometimes during eye is off, sometimes we will see "Y" after x. But it never happen. (except calibration, but it is due to HW movement limit)
Posted on:
Rev 234 contain paranoid filter for temperature measure (noise cancelation) You can try it Jiri
Posted on:
Attached files:Hello Jiri, I think, that I have a log with the error. At this evening the valve was open at 30% (after calibration it is closed at 40%, so the error is greater than 10). I set the eeprom valve_max to 90 and then I set the wanted temperature to 30° (see 06.04.09 20:12:38). The valve wants to open to 90%, but at nearly 86% the valve blocked and the scale jumps from 86 to 100% and went then to 90%. Ronny
Posted on:
@hrb: - I am surprised, you are realy losing pulses. But it is not on log. - Jump from 86->100 is correct and I wrote this behavior into SW. In this situation calculated position is 86%, but valve stop on hard break. This hard break must be 100% by definition, therefore SW fix current position to 100% and will continue go to wanted position 90%. This is partial recalibration initiated by error detection. Main question is WHY you losing pulses? Have you only one HR20? Can you try mount this HR20 into another valve? I have 5x HR20 with my SW byt never see situation like this. Strange. Problem is that your log looks perfect. Any pulse during motor run can't be lost becasuse in this condition we can see in log longer time for one pulse. (second column is time for one pulse) and it looks perfectly stable without glitches. Only one idea is, that your valve is too strong and it is abble change position when motor is stopped. Probably after opening. But in this case we will see sometimes "X" after "y" but it newer happen in your log. Strange, strange, strange. Jiri
Posted on:
Wireless extension: Have somebody "master" hardware already? I would like ask, before I will change used MCU from ATMEGA16 to ATMEGA32. Reason is RAM size needed for buffers. If somebody have deprecated hardware with ATMEGA16, please tell me it !!!NOW!!! (if it is not possible replace MCU in socket) Jiri
Posted on:
Attached files:Hello Jiri, sorry for the delay, but I tried a second (different) HR20 on the bathroom valve. But for the warm weather it tooks a little bit longer, because the valve was closed most of the time. But now I saw the same situation: I set the max position to 90% - the valve wants to set to 88% and came to the hard break and jumps to 100 - see the log. I have the same theory as you: the valve (or the valve spring) is too strong and can change the position, if the motor is stopped, maybe only a few seconds after the motor stops. Do you have an idea how this can be solved? Ronny
Posted on:
rhb: I have idea to keep motor eye enabled few secons after motor stop. But it will be done after few weeks, today I have more urgent tasks. Jiri
Posted on:
Hi, the RF-Modul sends at 433 MHz and you need a master to controll the units? Maybe the "Betty Remote" can be used to control the single units (or all). It has a cc1100 included. Take a loot at (german only): http://bettyhacks.com/wiki/index.php/Main_Page Greets torrz
Posted on:
I am using 868Mhz modules but it is easy use same modules but for 433. Problem can be that current SW realy need "master" board. Current communication protocol is simple and not support some "MESH" functionlity. !But! it is open project and your idea with "betty remote" is nice. Everybody can modify it to this way, but it is lot of work. Jiri
Posted on:
Hello, first a big respect to all members in this forum which do a great job to developing the new firmware. I was looking for an alternative and found a way to control my HR20 by my iPhone. Here a brief description: I use a master (ATiny2313) and a slave (ATiny2313) which communicate per radio (RFM12 modules) bidirectional. The HR20 is connected to the slave and the iPhone communicates via the master with the HR20. To set the temperature on the HR20 the uC (slave) is connected parallel to the encoder-pins of the HR20. To display the set and the current temperature the uC (slave) receives the information via the HR20-RS232-connector. Then the slave transmits the values to the master and then to the iPhone. For a better understanding watch: http://www.youtube.com/watch?v=w9R1_ee6c6Y It's only the first experimental step and the development is going on (pcb layout, control more then one HR20 and so on). But it works. Many greetings, puchti
Posted on:
@puchti100: I thing that control with WEB interface is more comfortable. Please find snapshots in this thread (example http://embdev.net/attachment/48705/status.png). It also works on iPhone, I was test it. It need any PC or embeded linux based router (it is cheap and power efficient) But you can create complete another solution, it is your choice and your time. Alternate SW you can drive directly via serial line; you don't need connect wires to encoder (It can work only on one encoder position as you know) PS: How you connect "master" (ATiny2313) and iPhone? Jiri
Posted on:
At my home I've been controling all my audio and video equipments and also lights per iPhone since one year. I use the iPhone app "CF iViewer" and the controller of the manufacturer Crestron. It could also be a PC-application, web interface or a Touchpanel-PC. In the past I had the wish to integrate the HR20 into "my system". That's why I looked for a way to do this. I added a schematic to show how the communication works. puchti100
Posted on:
Attached files:sorry! here the schematic...
Posted on:
Attached files:sorry again... to fast... here the correct schematic (copy-and-paste mistake in the HR20-symbol)
Posted on:
@puchti100: nice, it is solution. I have few technical notes: - RFM12 can be connected directly to valve but it will need modification to your wireless protocol - be careful if you use battery power, wireles communication is hungry - alternate SW have public protocol on RS232, you can drive it direcly without connection to encoder.
Posted on:
good evening everyone, Can someone please tell me where a user can find generic celebrex online without a prescription? I've been referred to http://www.drugpricegrabber.com but I'm unsure how to determine whether their site is trustworthy.
Posted on:
Hi, I have connected the rondostat to avrisp, via JTAG cable. I am trying to use AVR Studio. Which Amtel chip does the rondostat have? How can I check? thanks
Posted on:
Chip is ATmega169P. Programmer can read and check chip signature without programming.
Posted on:
I'm about to buy some HR20s to join this very interesting HR20 development. However, I got a few questions. 1) there is HR20E and HR20N. The HR20N seems cheaper. What's the difference? Are they both ok for OpenHR20? 2) are there different versions of HR20? are they all ok for OpenHR20? (like the Linksys WRT54G with a lot hardware difference for different versions) 3) I plan to add a Zigbee tranceiver. Has anyone already done this? The PCB size is about 20mm x 30mm x 3mm. Is there such room inside the valve? Many thanks David
Posted on:
Hi, This thread seems a bit quiet recently, maybe, because the weather is still warm and there is not much need for heating. Anyway, after a few days research, I plan to do the following based on the current code/design; - Add a different wireless transceiver (client). It is going to be an A7105 based transceiver. The reason for different transceiver is that it works at 2.4G and hence smaller antenna and faster data rate. Also, it takes 3 wire SPI instead of 4. So I can use the PE2 (Sorry about the PIR idea. But I think it can go with another A7105 transceiver.), RXD and TXD. They are a lot easier to solder. - Build a, maybe too ambitious, server. The server will have, 1. Graphic LCD 128x64; 2. A keypad and dial; 3. AVR MCU; (can be ARM but I do not want to involve another different tool chain) 4. Two A7105 tranceivers: one for normal using; one for alternative channel when there is jam; 5. One Blutooth module with the RS232 profile, which can be used to connect a PC; 6. It's going to be powered from main through an adaptor. - Build a boilder switch (another client). This switch has an A7105 transceiver and a simple AVR. It is going to be powered by batteries only. Each client will have to register with the server. The server Assign a key and a device ID to the client. The A7105 can help to filter the device ID. However, the communication packet will be encrypted with the key. Periodically the client will connect to the server to post its own status and check out command. The detail of the protocol has not been decided yet. If a client, after certain retries, can not connect to the server, it will switch to the alternative channel. Time for bed now. I'll post more later. David
Posted on:
@davidfat: 2.4GHz is not good idea for this. Many building have steel/concrete parts and this building have BIG problem with wifi from room to room communication. It is same wavelength. Except this, in city center I can found over 50 wifi networks and it make communication near to impossible, noise is too big. Data speed is not critical, battery life is bigger broblem. Antena length is not problem on 868MHz (RFM12 modules, antena fits inside valve I will post photos), and wavelength is better for comunication throw walls. For "server" I has another goal. For me is not critical direct connection to computer, but connection to internet. It can be maintained remotely. Therefore I was use minimal AVR based protocol translator and mips/linux based small router. But stand alone server is significat for many others people, I hope that your ideas have many potential users (probably include you) @Others: I have some small changes in code on todo list, It come from real usage. - battery warning or error will be one way. When battery is on end of life and not on drain it measure too opimistic values. - less communication. Enable slave receivers twice every minute for few miliseconds is too expensive (battery life). Current plan: communicate on changes or every 2(4) minutes or twice every minute if user activity is detected. - improvements on WWW interface.
Posted on:
@jdobry 868MHz has better path loss. However, given similar size, its antenna may be not as efficient as a 2.4GHz one. I'm interested to see your antenna inside the HR20. Higher throughput for a network is still good, at least, a) it takes less time to transmit, hence saving power; b) the channel is less used, so better latency. I also feel the bandwidth can be used in 868MHz is actually just 1MHz (868MHz~869MHz). When there is interference, there is less space to maneuver. Although 2.4G band is quite busy, the protocols there can normally use FHSS or DSSS to make robust link. One more thing worries me about the RFM12 is that, according to its datasheet, its lowest working voltage is 2.2V. If the HR20 is powered by NiMh batteries, the voltage may be blow that when there is still half capacity left. Have you got chance to test an RFM12 at something like 2.0V? The server sounds better to be made with a PoE interface, and it'll need an ARM. Re the transceiver power consuming. Suppose a short heart-beat packet is sent from a client to the server every 10 second. The heart-beat packet consists of 4 byte preamble, 4 byte server ID, 4 byte client ID and 2 byte CRC. The packet is FEC encoded, hence take 7/4 of the raw length. So it has (4 + 4 + 4 + 2) 8 7/4 = 196bits. Given 250kbps, it takes 0.784ms. The client will also try to receive a wake-up packet from the server, which is of same size. So roughly the whole procedure will take about 2ms. A7105 has RX current 16mA and TX 19mA. One heart-beat costs about 35mAmS. In one day there are 24*3600/10 = 8640 such communication, and it costs 0.084mAh. A good battery gives ideally 2000mAh, which means 65 years. Let me know if this is possible or I did my calculation wrong. I don't see RFM12 consumes more power. Why you can't do it twice every minute? When there is need to post server any status from the client, the client will wake up by itself. Or if the server wants to talk to the client, it sends a wake-up right after the client heart-beat. The client transceiver goes to sleep after certain time no RF activity.
Posted on:
@davidfat: You calculation about battery life is bad. Problem is not energy for send data (it is small). Problem is here: - internal PLL loop for frequency syntetizer need some time to stabilization, it is more time than for TX data. - current for RX is near to same as for TX, and because timing can't be perfect, you need enable it few ms before packet. - "heart-beat" packet must be also encrypted. Reason is potential synchronization poisoning from attacker. PS: Where is datasheet for A7105? Jiri
Posted on:
@jiri At 2.4G the PLL seems to lock faster. According to the datasheet I think the extra overhead would be about 200us. However, without testing, I can't confirm. I would say bad programming if you can only get real-time response in a few ms. It is quite possible to get sub-100us timing accuracy, or even better with a simple device like AVR, for example, the heart-beat proceding can totally be done in the ISP. You don't need to identify someone before he/she can knock at your door. You just need to do the checking/encryption before letting him/her in. The datasheet is here http://bbs.ednchina.com/Upload/Blog/2009/3/7/6e103...
Posted on:
@david: - Oscilator start-up overhead is 2mS (page 7 of datasheet) - timing precision cant be better than 3.9mS Reason is 32768Hz x-tal and prescaler /128 . If you will use smaller prescaler you will increase volume of CPU wake-ups and it is not good for bateries. Use internal RC oscilator for this situations is also possible, but battery hungry.
Posted on:
@jdobry - Even if it's 2ms, it only lowers the battery life for transceiver from 65years to 32.5 years. Also, the standby state consumes much less power than TX/RX state. The 2ms is the time from sleep to standby. Interestly, although in the table it gives 2ms, in the diagram on page 38, it is 0.9ms (from sleep to PLL). - Absolute timing does not matter. When sending the heart-beat, MCU a) wakes up at certain time, b) disables all other request (for better determinstic timing), c) changes to 1MHz or so, d) wakes up the tranceiver, e) goes to idle/sleep(if possible) for 2ms, f) sets up the PLL, and idle for 80us, g) triggers the heart-beat sending, (the heart-beat packet can be stored inside the transceiver, so everytime you only need to trigger it), h) sleep/idle 0.7ms, i) keeps checking until TX finish, j) sets transceiver to RX, k) sleep/idle 1ms, l) checks if any wake up packet received, m) transceiver goes to sleep. I think that's pretty much the whole heart-beat procedure.
Posted on:
Hi Build environment? Just found this project and is very eager to try to build the software and hack my HR20 thermostats. I have more than 10 in my house. Unfortunately I'm not very good at German so I have some troubles understanding the "Heizungssteuerung mit Honeywell HR20" page. Is it correct that I need WinAVR or "AVR Studio 4" to compile and they are both Windows only tools? I am not wery experienced with Windows and have no license so I really would prefer a Linux based development platform. From the discussion above I see that some of you prefer *nix as well. Is it possible to build and download the project on a linux platform?
Posted on:
@Mr_Manor: AVR Studio is needed only for debugging, not for compilation. For compilation WinAVR-20071221 compiler is recomended. Reason is that newest GCC produce significantly longer code and it can be too big into flash. But it depend to configuration. Linux distributions usualy contain AVR GCC and avr-libc. You must try it. Or you can use precompiled HEX from repository. For programming use avrdude tool. Jiri PS: from where are you?
Posted on:
@jdobry ok, thanks for your answer. I have installed VirtualBox and XP within so I hope that will enable me to compile. I'm very interested in the Wireless branch - several years ago I was into hardware so I think I am able the build the radio into the device. Is the project state as described on on the wiki page up to date? I will most likely return with more questions when/if I get a build environment working ;-) I'm from Ugerløse,Denmark.
Posted on:
@Mr_Manor: Information in wiki is not 100% up to date. But information in SVN is up2date. SVN contain schematics and photos for wireless modification. And if you want know communication protocols you must read source files, it contain human readable documentation. Low level wireles layer have documentation file in SVN (PDF and OpenOffice file). Many greetings from Czech rep. Jiri PS: I also use Linux at home, 100% in desktop and 80% in laptop. Remaining 20% of laptop time is WinVista because linux have not comfort tools for AVR debug :-(
Posted on:
Hi, Is it possible to switch between full-stroke/default-stroke mode on a "not-hacked" HR20? (I don't have the necessary hardware). BR, Thomas Fogh
Posted on:
@Thomas Fogh: It is for ORIGINAL SW: FULL stroke mode: unmount valve, press and hold "C" button, mount valve and you will see "FULL" on LCD DEFault stroke mode: unmount valve, press and hold "PROG" button, mount valve and you will see "DEF" on LCD
Posted on:
@jdobry: Thanks! But what's the "C" button? I have the "auto/man", "prog" and the day/night temperatur buttons. BR, Thomas Fogh
Posted on:
I mean day/night middle button. Because moon looks like "C" :-)
Posted on:
Any news on the development? I'm going to move during the turn of the year and then would like to use some RFM-enhanced HR20. At the moment, I've only got two with the stock firmware, because I couldn't get my USBprog JTAG to work yet :( But I would buy a "real" JTAG adapter if I need to :)
Posted on:
@Marco G." RFM12 sotware simply works on my home. I have plan to some improvemnts, but nothing critical.
Posted on:
Hi jdobry, I guess you mean the firmware compiled from the repo/rfmsrc/OpenHR20 directory? And you are using the "internal_RFM12" hardware modification? Is it difficult to use the external one? And what's your master? A HR20 with a special firmware or an extra piece of hardware? Please excuse my pile of questions, if there is any documentation please point me to it :) I hope I'll be able to improve the documentation soon :)
Posted on:
My answer from yesterday evening didn't make it into the forum :( By reading through the thread I found out that the master is an ATmega+RFM12, connected to an OpenWRT router.
Posted on:
@Marco G. Diferrences between internal and externel RFM12 - with external RFM 12 you can't use ICE debugger - external module can be easily damaged or accidenataly disconnected. It is significant if you have childens. - internal version need expert skill for soldering, chiset pins is extremely small. And you are right. "Master" is RFM12 + Atmega connected to OpenWRT based router (I was test it with Asus GL500-deluxe and Buffallo WHR-G54S) It provide web interface for valves ( Yes, it can be used by iPhone :-) or any bother browser )
Posted on:
Hmm, you're right about the risks of an external module, but I thought it could be easier to connect a cable to the 10-pin connector but put the module inside. Can both - internal and external - be used? There are preprocessor defines, but also a warning message in \rfmsrc\doc\external_RFM12\README.txt.
Posted on:
Warning in \rfmsrc\doc\external_RFM12\README.txt is little bit obsolete. You can not use it with birary files in SVN, it need recompilation where you change hardware type.
Posted on:
jdobry, do you already have a PCB for master hardware? Or does anyone else have a layout? If not, I would design one and order some PCBs...
Posted on:
No I don't have PCB. Just prototype on universal PCB and wires. If you will have it, please send me one.
Posted on:
Ok, that will be my task for the weekend :) Maybe we should start a new thread for designing the PCB: http://embdev.net/topic/158895 But I'm unsure about the connection to a router. Does yours have a serial interface?
Posted on:
@Marco G.: My router have serial interface inside. (3V3 logic levels)
Posted on:
Hello All, I am new to this forum so thought to be first introduce myself, i from Gray Mountain and interested in Internet Surfing, Forum Posting and Listening Music specially the old clasics Even i thought forum posting is one of the best way to enhance knowledge as well grab new things, that is the reason me joined this forum, i found this forum very informative and valuable, it is really great to be a part of this forum. Thanks & Keep Sharing!
Posted on:
Hello, I use my HR20 (currently one) with an external 433MHz RFM12 module from Pollin. I modified the initialization of the RFM. I set the Band to 433MHz and the capacitor to 12.5pF. The frequency is 434MHz and the range limit is set to +3-4 for 433MHz band ,respective to the programming guide. My master is an ATMEGA32 on an prototype PCB powered via USB. Now my problem: I start the master and the daemon and the first 5minutes all work well .Then I receive only errors for hours, sometimes it work for a few packet and then the same problem. If I restart the master , the first minutes it work well. What´s wrong ? Have somebody an helpful hint ? Maybe is there an wrong initialization value for 433MHz. Thanks in advance! Ronny
Posted on:
@Ronny Kunze: Can you send me any log? One of possible problems is time synchronization. Master broadcast real time and slaves enable receiver for synchronization packet. Real time is one of parameter to encrypt packet and if master have another time than slaves, encryption not work and it can't decrypt packages. Master clock is not from XTAL but from RFM12 clock output (10MHz). Maybe that you change it on init sequence. What happen when sync is lost? - Master normaly send SYNC packet on 00 and 30 second in every minute - Slave show "E4" error 1) Slave try enable receiver for 4 minutes till receive SYNC 2) When SYNC is not found, receiver will be disabled for 40minutes (save batteries) and after go to step 1) Jiri
Posted on:
Hello Jiri,
did you mean the Debug log in the database or the log from the daemon ?
The Masterclock is from RFM and it is 10MHz , i have veryfied it whit an
oscilloscope. THe Slave doesn't show E4 and if i change the time on my
HR it will set back automaticly to the time of the master.
Here a short dump :
2009-12-08 12:38:07 @07.48 ERR04df 24 06 3f e4 44 43 b5 0f 87 1d...
2009-12-08 12:37:07 @07.49 ERR04de 24 06 18 e5 38 f7 08 55 b7 b0...
2009-12-08 12:37:01 ?
2009-12-08 12:36:07 @07.50 ERR04dd 24 06 63 38 37 91 0e 06 60 c5...
2009-12-08 12:35:07 @07.49 ERR04dc 1a 06 9f 7b 8a e8 dc 5e b7 c3...
2009-12-08 12:34:07 @07.49 ERR04db 1a 06 51 80 12 51 cf e8 0a c6...
2009-12-08 12:33:07 @07.49 ERR04da 1a 06 7c d0 06 01 67 d6 97 c3...
2009-12-08 12:32:07 @07.48 ERR04d9 1a 06 ee 43 5d 7e cf f9 22 47...
2009-12-08 12:31:07 @07.49 ERR04d8 10 06 f1 b3 10 9a 73 b1 5a ca...
2009-12-08 12:30:07 @07.47 ERR04d7 10 06 38 65 40 95 3d 99 6e 17...
2009-12-08 12:30:01 ?
2009-12-08 12:29:07 @07.48 ERR04d6 10 06 80 aa d5 32 4d b3 48 ec...
2009-12-08 12:28:30 @30.11 ERR04d5 8c 70 ec 16 26 33 de ad 7c 2e...
2009-12-08 12:28:07 @07.48 ERR04d4 10 06 9e 84 0f 48 e1 6f 7b 6b...
2009-12-08 12:27:07 @07.45 ERR04d3 06 06 e7 f5 fd 16
2009-12-08 12:27:01 1)?
2009-12-08 12:26:01 @58.57 ERR04d2 3f b7 3d 45 91 08 04 55 ac 3c...
2009-12-08 12:25:07 <06> -D m32 s03 - V46 I1884 S1900 B2941 E00
2009-12-08 12:25:07 <06> -D m27 s49 - V45 I1885 S1900 B2940 E00
2009-12-08 12:25:07 <06> -D m23 s39 - V45 I1890 S1900 B2947 E00
2009-12-08 12:25:07 <06> -D m19 s28 - V45 I1890 S1900 B2956 E00
2009-12-08 12:25:07 <06> -D m15 s16 - V45 I1890 S1900 B2953 E00
2009-12-08 12:25:07 <06> -D m11 s06 - V45 I1890 S1900 B2946 E00
2009-12-08 12:25:07 <06> -D m06 s55 - V44 I1897 S1900 B2956 E00
2009-12-08 12:25:07 <06> (06){
2009-12-08 12:25:07 }
2009-12-08 12:25:07 @06.13 PKT04d1
2009-12-08 12:24:07 @07.54 ERR04d0 4c 06 86 c7 c2 14 5c b1 10 b0...
2009-12-08 12:23:07 @07.54 ERR04cf 4c 06 5e bf 45 ae c3 c4 b3 11...
2009-12-08 12:23:01 )?
2009-12-08 12:22:07 @07.53 ERR04ce 4c 06 50 de 31 23 24 86 62 0a...
2009-12-08 12:21:07 @07.54 ERR04cd 4c 06 b9 c1 c0 35 56 74 1b c9...
2009-12-08 12:20:07 @07.54 ERR04cc 4c 06 25 9d bf 22 22 ec fd 52...
2009-12-08 12:19:07 @07.54 ERR04cb 4c 06 9d 3e 1f 97 a3 ec c6 d8...
2009-12-08 12:18:10 @09.95 ERR04ca 4c 06 e0 24 03 12 bb 1f 4a bb...
2009-12-08 12:17:07 @07.54 ERR04c9 4c 06 f7 2d 46 33 e2 67 88 d2...
2009-12-08 12:16:07 @07.53 ERR04c8 4c 06 23 54 02 7b ac 24 e9 80...
2009-12-08 12:15:07 @07.55 ERR04c7 4c 06 9b 1e 10 aa ad 18 d2 aa...
2009-12-08 12:14:07 @07.53 ERR04c6 4c 06 38 b1 45 f5 7d a7 87 b9...
2009-12-08 12:13:07 @07.54 ERR04c5 4c 06 2d a6 5d 22 18 c0 7d 07...
2009-12-08 12:12:07 @07.54 ERR04c4 4c 06 d1 e3 50 72 91 a3 f1 97...
2009-12-08 12:11:07 @07.54 ERR04c3 4c 06 11 38 b5 a1 64 fd 0c 98...
2009-12-08 12:10:07 @07.54 ERR04c2 4c 06 96 e8 a5 af 38 3e f1 a6...
Ronny
Posted on:
How often is the Time of the Master synced whit the PC ? The timedrift on my ALIX2 is very strong , so i update the Time from a NTP server every 10 minutes. Could this problem influence the decryption ? Ronny
Posted on:
It looks like lost SYNC. "Master" ask daemon on computer for time every minute and daemon tell time in 1/100 precision. Do you use Windows or Linux? I am not sure if Win&PHP combination can use this precision. Part of encryption key is created from time. Therefore key in 0.99 second is not same as 0.01 second. If daemon is not abble te tell time in this presisoon, time in master must float over +- 1 sec adn it is not abble to comunicate. It is just idea. PS: I use NTP for real time in router where runs daemon. But absolute value is not significant.
Posted on:
@Ronny Kunze: I read the log ant it is definitively lost of SYNC. See too log and follow my sentences: - Log is in reverse order - You have slave with address 6. This means that timeslot for communication is from 6.00 to 6.99 second 2009-12-08 12:25:07 @06.13 PKT04d1 - Is correct packet received in 6.13 2009-12-08 12:24:07 @07.54 ERR04d0 4c 06 86 c7 c2 14 5c b1 10 b0... - Correct packet from 06 (see to second byte) but received too late on 7.54 - Packet like this can't be accepted, because encryption key is expired and normaly this is possible only on "replay attack" - This means that master receive from daemon wrong time. Maybe without correct 1/100 second and "jumping" around correct time. If you want to have better verbose log (include time sending daemon->master) you can start daemon without redirect to /dev/null because it generate verbose log compare to log stored in database (database engine is too slow for it on embeded routers) I apologise to code qality on current "daemon". This peace of code was hang together as proof of concept when I need to debug code in master and slave. I was plan to rewrite it completely, but it not happen (have not time and urgent motivation). But it works.
Posted on:
Hello Jiri, I think i found the problem. I tried following on my server :
voyage:~# ntpdate ptbtime3.ptb.de;sleep 60;ntpdate ptbtime3.ptb.de 9 Dec 09:29:38 ntpdate[30871]: step time server 192.53.103.103 offset -0.749543 sec 9 Dec 09:30:37 ntpdate[31034]: step time server 192.53.103.103 offset -1.480186 sec |
Lo and behold! The drift whitin 1 minute is around 1,5 seconds. Then i tried to update the clock every minute , it looks better. At least i tried to update via ntp every 10 seconds and every packet is OK ... It seems i should fix the problem on my Server ... Regards, Ronny
Posted on:
Can you use ntpd (daemon) and not ntpclient? It is abble to compensate drift.
Posted on:
Hello, is there a how-to-file or wiki for beginners/dummies? Peter
Posted on:
Hi Peter, I've started one, but haven't got further than flashing yet :(
Posted on:
Hello Jiri,
Yes I use ntpd , but it was not precise enough. Now i found a other
solution. I have modified the handling of the time update at the
master.The request is send every minute , but it ignore the the answer
if onsync greather than 0xe1. This should be a time of 1 hour.
I found a other problem in the daemon. The serial connection will only
work if the system set the right baudrate. I add a
exec('stty -F /dev/ttyUSB0 38400 '); to the daemon. Now it is anytime
the right baudrate.
Ronny
Posted on:
Hello, i have just converted my 2. Hr20 to the Open Hr20 with an RFM12 module. when i measure the current, the Hr20 takes around 1 mA. This current consumption seems a little bit high. Ludger
Posted on:
Ludger: I know that we have some problem with wireless and power. Normal cheap alcaline batteries is empty after 2-3 months. I will try fix it on xmas vacation. Till now I has feeling, that nobody except me use use wireles in HR20, but it slowly changes in last two months. :-)
Posted on:
Hi Jiri, now that we are back in heating period again :-(, I have changed two of my HR20 running older versions of the OpenHR20 firmware (still without wireless) to the newest (?) version 234. Experience so far: both failed miserably, showing 'Open' for hours and both rooms cold this morning and again this afternoon (my wife is not amused). Best thing for me at the moment would be to disable the window open detection completely (any hint how to do that easily by changing parameters ?). Regarding your last post about wireless. I think one of the reasons why this is not used by so many people is: - the lack of an easily available master unit - the way you are using it (with a router as master control, maybe too complicated for most of us ???) What I would love to do is have the individual units run on their own with their own sets of parameters and monitor these units via wireless with a master unit most of the time. Only in some special situations I want to control the units remotely, e.g.: - if the circulation pump is not running (at night) - if i leave the house for a weekend holiday - ..... BR, Jörg.
Posted on:
Hi Jörg, i have had the same Problem with my HR20. Here are my settings to disable the window open detection.
Posted on:
Hello Jiri, I think the problem with the current consumption, ist the crystal oscilator of the RFM module, it's always on. I can measure the output frequency of 10Mhz. You can switch off the the oscilator output to save some energy. Ludger
Posted on:
Hi Ludger, thanks a lot for this info regarding window open detection. I will try that immediately. BR, Jörg.
Posted on:
Why don´t you switch off the RFM completely with a little transistor, if it has nothing to do? I would implement short time slots in the protocol, where the module is active and waiting for incoming data or transmitting.
Posted on:
Opps, RFM oscillator must be enabled only in master (it is used as clock for ATMEGA) but not in valves. I will fix it early (I hope today). We don't need switch off RFM by transistor, it can be switched off by command, I don't know where is problem for now, but I will find it. Window: In current SW is this third version for window detection, and I have similar problem. Do you have anybody idea to improve window detection algorithm? For next version I will prepare window open timeout ( from 1-255 minutes ) When HR20 clear window open flag automatically. Current detection is too sensitive, and today during change from 21 -> 17 degree detect window open in 3 rooms. Temperature decreasing too fast (outside temperature was -16) Master: It can be connected directly to PC, not to router. It is less complicated, but you can not set valves remotely. Remote control is fundamental feature for me, sorry. This SW can be installed on PC but is is not optimal. If you have not permanently enabled PC, you will not have logging. GPL: it is GPL SW, this mean that everybody can modify it by own felling what is better :-)
Posted on:
Attached files:Today outside temperature in my location.
Posted on:
>We don't need switch off RFM by transistor, it can be switched off by >command, Sure, but how big is the quiescent current consumption in power down mode? Is it noticeable, compared to the Mega169, or not?
Posted on:
@ TravelRec Hi, i have running to RFM12 + SHT75 + Tiny45 for almost a year now. And the batteries ( 2 Alkaline AA ) are the first. The current consumption quit low Ludger
Posted on:
Ahh, okay. In my tests the Mega169P needs around 25µA during sleep with LCD active and cyclic main calls 4 times a second. If the RFM takes more than 10µA all the time, then the battery life will decrease dramatically.
Posted on:
Jiri, I think the idea with a programmable timeout after window open detection is the best , because I can not imagine how it COULD work automatically regarding the huge variety of circumstances (we have the same -15°C here at the moment as you and the room temperature falls extremely fast and never recovers. Temperature regulation is also not nearly perfect. Because of the low temperatures outside and high heating water temperature I see extreme overshoot in very small rooms with comparatively big radiators whereas in other rooms temperature increases very slowly with valves full open). One other (maybe optional) possibility if the HR20 is located near to the window/door would be to use one of the cheap reed contacts for burglar alarm and cable this directly to the HR20 interface connector. And, yes, I know that everyone is allowed to change the sources :-), but there is simply not enough time for me to do that. BR, Jörg.
Posted on:
@ Jiri, i know about the GPL, but i have some problems to compile the source file correctly for a running HEX file. The compiler has the right version and use the makefile for compiling. Do you use AVR studio for building the HEX ? I got always a lot of compiler warnings. regards Ludger
Posted on:
Jiri, Ludger, for me the .aps file in the wireless directory works perfectly, whereas the one in the trunk directory does not. Calling make from command line works (although I am not the command line guy, started with that 35 years ago and am happy that we have fully integrated graphical development environments now!). If the .aps is not maintained any more, than it should perhaps be deleted. BR, Jörg. PS: Ludger, changing the parameters for wod worked for me, warm bathroom this morning, happy wife :-),.... thanks again.
Posted on:
Jiri, has anything been changed on the serial routines? These worked ok in V2.03 which I used in my HR20 before changing to V2.34. Now I get a number of rubbish symbols when the HR20 answers to a command before the correct answer (like yyyyyD: d4...) and nearly only rubbish (yyyyyyyyyyyyyyyyyyyyyy......) when the units send their message every 4 minutes. I have no clue at the moment what's going wrong. BR, Jörg.
Posted on:
@Jörg Becker: It is debug messages when I was try find reason of motor position offset on some situations. You can disable it by set DEBUG_PRINT_MOTOR to 0 But main trun at this moment have not maintainer, therefore I am recomend use rfmsrc trunk na compile it like "make RFM=-DRFM=0" or disable RFM extension on config.h ALL: new rev 253 in SVN have this changes: - window detection have timeout, default value is 90 minutes. After this time window open flag will be cleared in eny situation. - This version is possible compile without RFM extension - I was add one more "watch" to count all motor pulses (diagnostic) - this version is NOT fully tested, I am just commit wirking version because I need to continue find problem with current on sleep state (only for RFM)
Posted on:
Jiri, thank you for the info. I got it to compile and work. BR, Jörg.
Posted on:
Current from batteries on RFM12 is fixed in revision 254. Actual current is arround 40uA on standby. Oscilator was enabled because I forget disable RFM12 CLK output. Oposite to official documentation it enable oscilator.
Posted on:
WARNING: Be sure that "OCDEN" programming flag is disabled after programming. It is usualy enabled by debbuger, and it take over 1mA from batteries.
Posted on:
Do you have anybody this alternative to HR20? http://media.conrad.de/m/6000_6999/6100/6160/6161/... I would like to know what HW is used inside. (Microcontroller, radio module). If it is AVR based, it can be used on this project.
Posted on:
@ Jiri, tell me more about the motor offset problem, maybe i can help..... Ludger
Posted on:
Merry christmas together, I'm still busy on writing my own firmware for the HR20E - it's still done in Assembler. Nearly all functions, also the wireless communication are intergrated and working fine. Now I want to integrate the ,window-open' functionality too. But how can I realize the algorithm to do that. How many (centi-)degrees diffrence by what time detects the ,window-open'- state ? Sorry for my freshman english... Marcus
Posted on:
Marcus, the original algorithm is written in the HR20 Datasheet: "Bei Temperatur-Änderung von 1,5°C/3Min. schließt das Ventil u. öffnet wieder bei Temperaturanstieg o. spätestens nach. 45 Min." -> slope must be at least 1,5°C in 3 minutes to detect a window change, and a 45 minutes timeout is used. The datasheet can be found at Reichelt.de: http://www.reichelt.de/?;ACTION=6;LA=3;ARTICLE=787...
Posted on:
@ Marco, thank you for your support, I've read the consumer documentation. I think the threshold of 1,5°C is in many situations too much - it takes too long till the software detects the open (only tilted?) window. There should be an integrated dynamic component, consisting of the in-,decreasing PID-Value's tendency and the sign of the D-Part (last measured temperature higher/lower than the current value)? Last night I advanced my PID by this extension and to time it's looking good. Marcus
Posted on:
Well, I've used the original HR20 firmware last year, and it did recognize my open balcony door almost immediately. Of course I opened it completely and did not tilt it. Marco
Posted on:
An open balcony door causes a big and fast heat loss - the temperature decreases rapidly, so it's easy to detect this. But a slow loss - about a few centigrades/PID-cyle cannot be recognized by this way. I think the valve constantly opens until the limit (or setpoint) is reached, or am I wrong? Marcus
Posted on:
Yes you're right, that's a big heat loss. But isn't opening a window completely the "better" way to exchange the air in a room? I don't know anything about the original nor the OpenHR20 algorithm :(
Posted on:
Yes, indeed. But not every window can be completely opened - like mine in the attic. I also consider this function as a kind of protection for forgetful people who forget to close their doors/windows - it's not really required for a few minutes air exchange. Marcus PS:Do you use OpenHR20 on your valve(s)?
Posted on:
Jiri reported about some very cold days when his /window open/-detection falsely recognized an open window. Maybe a reed contact connected to a GPIO would be more suitable? I'm not using OpenHR20 yet, I'll be moving at the end of February and then start with OpenHR20.
Posted on:
I'm seeking for a solution, without any external switches cabled to the valve. The evaluation of wireless informations, for example a window open detection or distant temperature values is already is already supported by my software but not used. Perhaps in the (distant) future... Marcus
Posted on:
Here's my master board. Any suggestions? Anyone who is interested in a PCB when I order some? http://embdev.net/topic/158895#1533392
Posted on:
RFM12 modification users: !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! Please update to version E0.07 (SVN revision 261) !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! It contain bug in time setting and program temperature change can be lost. Old version without RFM12 modification and compilation with RFM12 disabled is not touched.
Posted on:
Opps Rev 261 was not fixed, please use Rev 262
Posted on:
Issue still not completly fixed, it have one more layer on AVR rtc timmer synchronization. It will be fixed tomorow, it's too late.
Posted on:
Attached files:Hello, now my patch for the second LED for the master . It is adapted to the Version from Marco G.
Posted on:
RFM12 modification users: !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! Please update to version E0.07 (SVN revision 263) !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! It contain bug in time setting and program temperature change can be lost. Problem was in timmer2 async opertaions. Main trunk is also touched, but it can't lost point in program. In this case update is not critical.
Posted on:
Hello, I recently changed my old HR20 (which work with a nec micro controller) by new ones (HR20 not HR20E). I tried to connect one of those to the computer but get constantly the error : --------------------------- AVR Dragon --------------------------- Unable to find supply voltage on target. Please verify that the AVR Dragon is correctly attached to the target, and that target power has been switched on. Click OK to retry. --------------------------- OK Cancel --------------------------- The Board seems to detect 2.7V, but as soon as I try to read something I get this error and the voltage drops to 0.2V which seems to be the default voltage when nothing is connected. I don't know if I'm doing something wrong. Could someone help me please?
Posted on:
Hello Manu, This sounds like a wrong connection of your HR20E to the AVR-Drangon. May be the voltage measured by the Dragon is one of an IO Port. I use also a Dragon and it work fine. Ronny My adapter : HR20 DRAGON 1 RESET 6 nreset 2 PE2 - 3 TMS 5 TMS 4 TCK 1 TCK 5 TDO 3 TDO 6 TXD - 7 RXD - 8 TDI 9 TDI 9 BAT 4 VREF 10 GND 2 GND
Posted on:
Yes it works! Thanks a lot for the info. I guess I tried to go too fast without first reading all the docs.
Posted on:
@jdobry (2009-12-21 10:51): I have one of those devices (article number 616100 - 62 @ Conrad's). The board looks a little like the one mentioned here: Beitrag "Untersuchung Heizungsthermostat Lifetec MD12460" (German) except the second chip IS mounted (under an "Epoxy Glob Top", like the first) an it is a lot better processed ;-). Sorry, a few low-quality pictures from my mobile phone is the most I could offer you (I'm an absolute doofus in terms of "analyzing" such boards. could help with Java/PHP or a small virtual host, though :-) )
Posted on:
@MajorTom: Thanks, but it NOT look like compatible with OpenHR20. But I hope that I miss and inside Blob is ATMEGA.
Posted on:
Hello Forum, i am new to the Forum, but have some experience with embedded devices, and have "steckbrett-fun" with the Atmel uC for some time. We have several Thermotronic "Sparmatic Basic" Thermostats in use and i wanted to hack around with them. I found the OpenHR20 project and must say you have done fantastic work. Also the simulation of the Display is very cool. I tried OpenHR20 with one of them. (downloaded the code from svn, built it with the define THERMOTRONIC, chiperased, flashed flash eeprom and fuses (fuse values as shown here http://www.mikrocontroller.net/articles/Heizungsst... ) It boots, runs the motor forward and back, but shows an "E3" All menus operate properly, i can set the time and so on. From the code i understood that E3 means the motor doesnt run properly. The Reflexcoupler works (measured a signal at PE1) I both tried with batteries and external power supply, because i read something about that in the Forum - makes no difference. Before digging deeper into the code i'd like to ask you. Do you have any clues ? Perhaps Confiuration values to adapt to make the software more tolerant ? Is there anyone running OpenHR20 on a real thermotronic device ? (Not the Sparmatic zero !, i have the "Sparmatic Basic" with this board http://img407.imageshack.us/img407/8021/thermotron...) greetings Alex
Posted on:
Hello, I have the problem, that my Bathroom-HR20 loses steps until now (see my posts last year). It´s definitely the problem of a "strong spring" in the valve or (in my case) high pressure in the heating system. If I reduce the pressure (via open of every heater in the [rented] flat) then everything is ok. So this strong power must changed the position AFTER the motor stops @jdobry: You wrote last year, that you had an Idea to leave the photo eye active some seconds after the motor stoped. How this can be realized? Ronny
Posted on:
Alexander: there exists a separate project for sparmatic zero thermostates, it can easily adapted to the sparmatic basic, but is not opensource yet: Beitrag "Preisgünstiger Heizungsregler bei Praktiker" Ronny: >You wrote last year, that you had an Idea to leave the photo eye active >some seconds after the motor stoped. How this can be realized? To leave the reflex coupler on for a few seconds after the motor stops is the only solution to count all pulses surely. I´ve had this problem on thermotronic/sparmatic thermostates too.
Posted on:
Hi Travelrec, i know this thread but i have the sparmatic basic hardware. And i want to run the openhr20 firmware. travelrec wrote: > Alexander: there exists a separate project for sparmatic zero > thermostates, it can easily adapted to the sparmatic basic, but is not > opensource yet: Beitrag "Preisgünstiger Heizungsregler bei Praktiker"
Posted on:
AFAIK the sparmatic basic hardware is incompatible with HR20E. Unless the OpenHR20 gives you the possibility to adapt it for the sparmatic basic.
Posted on:
Alexander Haarer: Error E3 means that motor counter is out of range. Current SW need for thermotronic minimum 50pulses maximum 500pulses from end to end. Ronny H.: problem on last year was that first generation of SW haven't suficient timers. Second generation (with RFM extension, but it can be compiled without RFM) allow this feature, but it is not done. I will make this modification, but on weekend.
Posted on:
travelrec wrote: > AFAIK the sparmatic basic hardware is incompatible with HR20E. Unless > the OpenHR20 gives you the possibility to adapt it for the sparmatic > basic. The code of openhr20 contains various ifdefs "thermotronic". its activated in the makefile. I believe that is for "sparmatic basic"
Posted on:
Attached files:Jiri Dobry wrote: > Alexander Haarer: > > Error E3 means that motor counter is out of range. Current SW need for > thermotronic minimum 50pulses maximum 500pulses from end to end. > I believe that i found the problem. The software counts just the high time of the photoeye pulse to determine the current motor speed. The Sparmatic Basic generates a signal with ~60mS High and ~15ms Low. The HR20 does just the other way round (shown at the logicanalyser pic in svn) attached is a screenshot I changed the following - it seems to work for me, can please someone review it ? Index: F:/privat/sourcecode/atmel/openhr20/trunk/source/motor.c =================================================================== --- F:/privat/sourcecode/atmel/openhr20/trunk/source/motor.c (revision 260) +++ F:/privat/sourcecode/atmel/openhr20/trunk/source/motor.c (working copy) @@ -406,7 +406,7 @@ } #endif // motor eye - // count only on HIGH impulses + // count HIGH impulses for HR20 and LOW Pulses for THERMOTRONIC #ifdef THERMOTRONIC if ((PCMSK0 & (1<<PCINT1)) && (((pine ^ pine_last) & (1<<PE1)) != 0)) { #else @@ -415,7 +415,7 @@ uint16_t dur = motor_diag_cnt - last_eye_change; last_eye_change = motor_diag_cnt; #ifdef THERMOTRONIC - if ((pine & _BV(PE1))==0) { + if ((pine & _BV(PE1))!=0) { // #else if ((pine & _BV(PE4))==0) { #endif
Posted on:
Ronny H.: I thing that I found solution for delayed motor eye after motor stop. It is not on SVN now, because it need testing. (If you want to have patch send me email) This solution make code shorter and it is possible port to first generation of SW. Possible delay after motor stop is from 0.1 sec till 4.2 second
Posted on:
!!!!!!!!!!!!!!!! WARNING !!!!!!!!!!!!!!!!! rfmsrc branch revision 265 is experimental support for count pulses after motor stop. It is not fully tested, if you want almost stable version please use Rev 264. Ronny H.: You are found real problem, with counting pulses after motor stop it have better precision, because it normaly lost few pulses. Please try Rev 265.
Posted on:
I ha$s bad few weeks when I try found why OpenHR20 valves lost some one second tick every day. Current code (Rev 269) is almost fixed, but I thing that I found bug in MCU. Try code on http://openhr20.svn.sourceforge.net/viewvc/openhr2... It must show one '*' char every second (9600 baud). But if I use synchronization sequence from Atmel datasheet, it miss massive volume of 1 sec ticks. A am not sure bug is on my reading of datasheet or in MCU. Can you help me? Jiri
Posted on:
I was try to contact Atmel support for any solution and we will see. Current code works on most of cases, but I know case when 1 second pulse will be lost. After this RTC will be delayed. But it not happen on my five valves on past 12 hours.
Posted on:
It is definitively MCU bug, see to http://www.avrfreaks.net/index.php?name=PNphpBB2&f... It is common to many AVR procesors (AT90CAN128, ATmega48/88/168, ATMega32) I will try found workaround for last remaining 1 second lost possibility. ALL: I am not abble to support first generation of SW. Can we mark first generation as deprecated and use code based on rfmsrc tree? This code can be compiled without RFM extension also. But I need port Thermotronic patch into this SW. Any volunteer? I have not HW.
Posted on:
Hello Jiri and all Thermotronic users I tried the last SVN Version with my old Thermotronic an get the E3-Error mentioned by some others before. I tried, from which version this issue exists: 122 seems to be ok - in versions from 124 to head I get the error. Due to my job I don´t have enough time to check the essential difference between the versions. Maybe someone can do this. When the SVN Head rev. works fine with the Thermotronic I think it will be not a big problem to put the changes into the rfm-branch. Greetings, Thomas
Posted on:
@ Thomas V.: E3 error on Thermotronic is caused by better motor eye noise protection and inverse polarity of signal. It was fixed by: Author: Alexander H. (aha) Posted on: 2010-01-15 14:47 I add this patch into SVN now, therefore you can use newest version.
Posted on:
Hello, I struggled with the E3 error (on HR20!) too: I saw "Adap 1", then I mounted the head to the valve for a short time the "Adap 2" was seen (with little motor movement), then E3 occured. In my case the reason must some noise in the adc temperatur conversion (I extend the temperatur sensor with a 2,5m shielded cable): If I disable the noise protection in uint8_t task_ADC(void)->"case 5" completely, then all is ok. Strange situation: If I put a "COM_print_debug(valve);" at the end of "CTL_update" in controller.c (so that every second an output is generated), the error was also away. Any explanation for this? Ronny @Jiri: because of these problems I started the test of your new motor eye routines today evening...
Posted on:
@Ronny: If you are abble to see E3 on current SW, plese send me log and tracepoints (command "T00" to "T0d") It is strange that ADC measure have some effect. But if you want to disable ADC noise filter, you must not remove step 5, but you must remove step 4 rename 5->4 and delete countent under condition "if ((ad>dummy_adc+ADC_TOLERANCE)||(ad<dummy_adc-ADC_TOLERANCE))"
Posted on:
Attached files:Hello Jiri,
here are logs from the current version.
Same procedure on both logs:
- flash the version without mounted valve
- mount valve
- wait for calibration end or E3-error
- read Tracepoints T00-T0d
I used the current version in the rfmsrc branch (but without RFM
compiled).
The log without the error is produced by uncommenting the following
lines in adc.c (:
//
// if
((ad>dummy_adc+ADC_TOLERANCE)||(ad<dummy_adc-ADC_TOLERANCE)) {
// adc noise protection, repeat measure
// dummy_adc=ad;
// state_ADC=4;
// break;
// }
I think, that produces the same result as you advised in your last post
(I used the easy way, I´m lazy :-)
The log with the E3-error is the original source in the rfmsrc branch.
But I saw also a strange effect (you can see it in the error log):
I couldn´t get the tracepoint T00-T02 and T0a-T0d !??? Nothing happened,
if I type these Txx commands.
regards
Ronny
PS: What changed I additionally to the original source:
in Makefile I commented out the RFM switch
#CFLAGS += $(RFM)
in main.c (because I got errors about undefined values)
//FUSES =
//{
// .low = (CKSEL0 & CKSEL2 & CKSEL3 & SUT0 & CKDIV8), //0x62
// .high = (BOOTSZ0 & BOOTSZ1 & EESAVE & SPIEN & JTAGEN),
// .extended = (BODLEVEL0),
//};
in config.h I changed the #defines, because I got errors about already
defined values (RFM_WIRE_MARIOJTAG)
#define DEFAULT_TEMPERATURE 2000
#ifndef RFM
#define RFM 0 //!< define RFM to 1 if you want to have support for
the RFM Radio Moodule in the Code
#endif
#if (RFM == 1)
#define RFM_WIRE_MARIOJTAG 0 //!< define that if you want to wire your
RFM to external JTAG pins
#define RFM_WIRE_JD_INTERNAL 1 //!< define that if you want to wire your
RFM to free internal pins
#define RFM12 1 // just a synonym
#define RFM_DEVICE_ADDRESS 0x00
#if (RFM_WIRE_MARIOJTAG == 1)
#define DISABLE_JTAG 1 //!< define DISABLE_JTAG if your RFM's
connection uses any JTAG pins
#endif
#define SECURITY_KEY_0 0x01
#define SECURITY_KEY_1 0x23
nothing else, double checked with diff
Posted on:
@Ronny H.: Which compiler version you use? I must ask because this version is not able compile code with FUSES.
Posted on:
@Ronny H.: It looks, that you valve need much bigger force to move. Could you try it again with: #define DEBUG_PRINT_MOTOR 1 You can also try set motor PWM limitation to bigger force (only for test because touch on the end of motor range will be hard): S0dff S0eff And expand tolerance for motor stop conditions (only for test because touch on the end of motor range will be hard) It is normaly 130% for calibration and 150% after. This values are how much slow down is detected as motor end, this values is 180%. S12b4 S13b4
Posted on:
Hi Jiri, one question about init() function in main.c! At line #04 and line #10 - Why are some PORTB pins set and then immediately re-set again? I think that doesn't make any sense. 01 //! Disable Analog Comparator (power save) 02 ACSR = (1<<ACD); 03 04 PORTB = (0<<PB0)|(1<<PB1)|(1<<PB2)|(1<<PB3)|(0<<PB6); 05 DDRB = (1<<PB4)|(1<<PB5)|(1<<PB7); 06 07 DDRD = _BV(PD1) | _BV(PD6); 08 PORTD = 0xff; 09 PORTA = 0xff; 10 PORTB = 0xff;
Posted on:
@Marko B: Ooops, it is copy&paste bug.
Posted on:
Attached files:Hello Jiri, S0dff S0eff did the job! (you can see the log - same software version like yesterday with E3-error: today without E3 error!) But it is very, very strange, that the modifications in my post from "2010-01-26 20:30 " also hide the E3 error! Some critical timing? So I have to play with S0dxx to make a compromise between E3-error and hard-touching the end, right? All logs (also yesterday) were generated with "#define DEBUG_PRINT_MOTOR 1" I use "avr-gcc (WinAVR 20090313) 4.3.2" Some question (for my education): How did you see, that S0d="min motor_pwm PWM setting" was the reason for this misbehavior? What means the output + 0610 fe + 0365 fe + 0332 fe + 0325 fe + 0316 fe ... ? Thanks for your patience and very fast help! Ronny
Posted on:
"+ 0332 fe" "+" means walve open "-" means close 0332 if time between two eye pulses. Software try it control around wanted value (G14 * 8). For this it change pwm "fe" is actual pwm value (G0d and G0e are allowed min and max)
Posted on:
First experiences with OpenHR20E: Day of installation: No problems. The day after: Cold because of the window-function. The problem: In the morning, our central heating goes up to 90°C. As soon as a certain room reaches 20°C, the water temperature is reduced. This results in a slight temperature drop which is interpreted as open window (especially as the sensor is close to the radiator). The vent closed and never opend again, because with a closed vent, there is no rising temperature. Besides: This is a problem in poor isolated bulidings, too. When a window is closed, temperatures do not rise because there is nothing around which is warm enough. What about some kind auf "timer" to end the open-window-state after e.g. 30 minutes? There was another problem which is related to too high motor current which causes resets. This happens when I completely open the vent by rotating the blue cogwheel before "plugging" the HR20 in. When adaption starts, the motor is blocked immediately and it resets. This then repeats endless. Newer batteries help, but the "old" ones were fresh enough to get a good contrast on the lcd and caused no problems with the original HR20e. Maybe some kind of soft start could help here? Especially when opening the vent, there is not much force needed (at least for me). I plan to buy and flash some more units soon, especially the rfm12 thing is very interesting.
Posted on:
@Chris:
First generation of SW not support anything like window open timeout.
Please use rfmsrc branch and compile it without RFM support ("make
RFM=-DRFM=0")
Window open function you can modify by this setting:
/* 23 */ uint8_t window_open_detection_diff; //!< threshold for window
open detection unit is 0.1C
/* 24 */ uint8_t window_close_detection_diff; //!< threshold for window
close detection unit is 0.1C
/* 25 */ uint8_t window_open_detection_time;
/* 26 */ uint8_t window_close_detection_time;
/* 27 */ uint8_t window_open_timeout; //!< maximum time for
window open state [minutes]
For other setting see too eeprom.h
This settings can be changed from service menu (press&hold all buttons)
or you can use "S271e" (example: set timeout to 30 minutes) serial
command.
I have not any problem with batteries and reset when motor starts. You
could modify start up current when you decrease "max pwm" setting \, but
you will risk that force will not sufficient to motor start.
Posted on:
Hello, I had the same problem as Chris with the window open function. I just disabled it in the code as it's not a big deal to reduce manually the valves when you shortly open the window. You can comment out the call to the function CTL_window_detection in controller.c (it's in the CTL_update function). Since then I don't have any problem with the thermostats. Manu
Posted on:
Hello, I have ported the Thermotronic changes to rfmsrc (rev 272). I didn´t have much time to test, but it seems to work. RFM-features for Thermotronic are not implemented, but I think it could work with a different pinning in main.c. @Jiri: I will send you the changed files by email Thomas
Posted on:
Thanks to ThomasV we have THERMOTRONIC patch for rfmsrc based code. Therefore I can move old main trunk into archive and support only second generation of SW (rfmsrc based) Any objection to this step? If no, I will do it tomorrow. Jiri
Posted on:
Hi!
I have a problem with the initial sync from rfm-master to HR20e. My
HR20e using jiris internal rfm12 wiring but my HR20e doesn't sync with
rfm-master.
So i check the sync packets coming from rfm-master with another homemade
test-receiver (µC m168 + rfm12b module). My test receiver using the same
RFM_init (Conf., FIFO, Freq., AFC...). The receiver gets the sync
packets correctly. (don't worry about the date, it's only for testing)
rfm-master sends sync packet
06.03.10 15:28:00 8B 0A 30 CF 38 00 00 D3 ...
06.03.10 15:28:30 8B 0A 30 CF 39 00 00 3D ...
06.03.10 15:29:00 8B 0A 30 CF 3A 00 00 28 ...
test-receiver gets sync packet
06.03.10 15:28:00 8B 0A 30 CF 38 00 00 D3 ...
06.03.10 15:28:30 8B 0A 30 CF 39 00 00 3D ...
06.03.10 15:29:00 8B 0A 30 CF 3A 00 00 28 ...
But my HR20e gets sync packet
06.03.10 15:28:00 8B 4A 30 CF 78 40 40 D3 ...
06.03.10 15:28:30 8B 0A 70 0F 39 40 00 3D ...
06.03.10 15:29:00 8B 4A 30 CF 7A 40 40 68 ...
What i see - some correct packet bytes, but others have a 0x40 offset.
The first packet byte 0x8b (rfm_framebuf[0] -> sync pattern + packet
site) always seems to be ok.
I changed the rfm12 frequency (original 868.35 Mhz) but the problem
still exists. I didn't change the orginal RFM_init parameters (AFC, Data
Filter, RX control,...) in openhr20 source!
What's the problem? Wrong rfm12 tuning in my HR20e? Any suggestions?
Note:
First 8 bytes of rfm packet were printed with additional debug command
and output of rfm_framebuf[i] in COM_commad_parse() OpenHR20\com.c
e.g.
case 'G':
for(i=0; i<8; i++) {
print_hexXX(rfm_framebuf[i]);
}
break;
Posted on:
@Marko B.: Do you have this problem only on one valve of more? At this moment I don't have any idea. Here are you connect ground and VCC for RFM module in valve? Do you crop properly original PE6 connection? Jiri
Posted on:
Attached files:Hi Jiri! Currently i only have one valve with rfm12. Yes, i cropped the PE6 connection. I will check Vcc, GND and PE6 again. One question about soldering DATA/nFFS: Is DATA/nFFS soldered with SMD104 (100kΩ) or with 58C left side (inside the blue circle) and SMD104 to 58C right side? I can't see the solder connection exactly. The circuit diagram says DATA/nFFS to 100kΩ.
Posted on:
DATA/nFSS if connected only too 100k rezistor and oposite end of this resistor is connected to VCC I known that it is not clear from picture, but it is clear in schematics
Posted on:
Hello, I'm new to this forum and i want to congratulate your for this marvelous work. I own 3 HR20 bougth in germany as it is really expensive in France (more than 55€ each!!!) and one of them has something that look like the trouble described above: the heater stay cool even if the temperature in the room is below the programmed value. I need to flash it with your firmware but i must confess that i'm a bit lost. I have an avr dragon and avr studio as i work already with avr but usually with bascom and i don't really know anything about the other compiler. I've read the entire thread (the english part) and i've never found any wiki or comprehensive instruction on how to do it. I've also try to understand the german part but even with google traduction it's difficult to read. So i've a few question and i apologize if the information is easylly available and i didn't find it: -the hr20.hex and hr20.eep found in the repository visibly take into account the rfm12 wath happen if i use this software without this part of hw? -is there somewhere a complied version up to date without the rfm12 part? -is there a guide of the configuration of the hr20 (i mean temperature, time with the buttons and wheel) after the flashing? -is there a precompiled up to date version of the openhr20suite to facilitate configuration? thanks in advance stephane
Posted on:
Attached files:@ssaul the attached files are compiled from the current version (275) without rfm-support. @all: I think, I´ve found some cosmetic errors, if I compile without rfm: in config.h: the 2 defines #define RFM_WIRE_MARIOJTAG 0 //!< define that if you want to wire your RFM to external JTAG pins #define RFM_WIRE_JD_INTERNAL 1 //!< define that if you want to wire your RFM to free internal pins should be after "#if (RFM == 1)" without that I got several warnings about redefinition - and in my opinion it makes sense to move rfm-definitions in the RFM part in ../common/rtc.h in line 575 and 681 the variable should be inititlized: next=0, else I get warning about uninitialzed variables
Posted on:
Last SVN revision have changes to remove possible warnings. Problem is, that some warnings can't be removed. Example is uninitialized variables. In this situation I need it uninitialized, because "random" contend will be overwriteln, but compiler cant see it. Add initialization is possible, but it need flash. We must save each possible flash word.
Posted on:
MASTER code for RFM extension is updated to "Macro G" hardware. LED light time is extended to 0.3sec It make it visible easy. Real sync or RX is too short.
Posted on:
OOOPS. New master hardware is here http://embdev.net/topic/158895#1533392 And author is Marko B. (sorry Marko)
Posted on:
Yesterday night I was salami instead of brain. Author of master PCB and new version of HW is Marco G. I am verry sory Marco.
Posted on:
Is there anything special to do to get the rfm12 working? I used the current rfmsrc, defined external connection (jtag-pins) and set device ID from 00 to 01 to enable wireless. How can I see if connection to the rfm12 module works? Is ist supposed to transmit or does it wait for packets from the master board (I did not build it yet...). Using a radio scanner, I did not hear any transmissions (except of many other 433Mhz devices and my other rfm12 plattforms...). BTW: The window-function seems to work ok now for me, at least there are no false positives. Chris
Posted on:
@Chris: current rfm12 varian can't work without "master" board.
Posted on:
I solved my problem with the initial sync from RFM-master to HR20e. I can't say why this problem occures. Maybe a fragile/unwanted solder connection or something like that. I made a little modification of the internal wiring. Connection of my rfm12 is a mix of internal and external wiring scheme. All connections and rfm12 are still inside. It is easier to solder than m169 pins. Vcc - internal Vcc GND - internal GND DATA/nFFS - internal 100k-Vcc SDO - int. wire to ext. connector pin2(PE2) nSEL - int. wire to ext. connector pin3(TMS) SCK - int. wire to ext. connector pin4(TCK) SDI - int. wire to ext. connector pin5(TDO) My rfm-master (crumb168) and wireless hr20 are working quite well.
Posted on:
I just updated my HR20 to the opern source firmware, because i had problems with the full-movement mode of the original software. My original software did not allow me to enable this full-mode. But now, i think the usage is a little different, than in the original software. Is an open-source-user-manual available ? Where can i read the usage?
Posted on:
@AntonMayer What do you mean with "full-movement mode"? At this time no manual exists... the usage can be determined from the source
Posted on:
AntonMayer: you probable mean full stroke mode. OpenHR20 don't have it, but have something better. You can set valve position manualy. How? Unmount HR20, close valve manualy, press&hold "C" button, mount H20 back and release button after it. This setting can be also changed manually on service menu
Posted on:
Yes, i mean the full stroke mode. My problem is that i have no idea how to use the new software.
Posted on:
Can someone help me with openhr20 + rmf12(433) + master, please? I flashed my hr20e and connected rfm12 (433Mhz, not the new b-version) to the external jack. I changed the id from 0 to 2 and configured it to external rfm12. I build the master board as shown in layout version 5, flashed and set fuses. I connected the master board to a com-port and opened a terminal application. On power on I can read the version-string, after that it outputs sequences of numbers and =?. The leds on the master-board do not light (except very short at power on) and hr20 displays E4 after some minutes. Sometimes I can read something like "ERR000". Where is my mistake? Thanks :)
Posted on:
Hello Chris, you must have run the deamon. He send the OpenHR20Master the time for synchronisation until it's done ,you will nerver see any data from the HR20. Ronny
Posted on:
Hello, I want to change the temperature sensor to a ds1820 1-wire device (because I need more than one temperature per device). Therefore I rely on a good calibration of the rc-oscillator. I saw in the main.c init-routine a "todo" for that. So I made a new one. I coded the "measurement heart" in assembler, so that the compiler can´t change it. The codesize is about 60 bytes. Maybe someone need it too and want to put it in the svn: Ronny
void calibrate_OSCCAL(void) { uint8_t temp; volatile uint16_t Z;// very important volatile define CLKPR = (1<<CLKPCE); CLKPR = (1<<CLKPS1); // set the CPU Frequency to 2MHz ASSR = (1<<AS2); // set 32,768kHz osc as source for timer2 TIMSK2 = 0;// disable any interrupt sources TCCR2A = 1;// start timer while(ASSR & (1<<TCR2UB)); // wait for TCR2UB to be cleared _delay_ms(500); //important delay for stabilize the crystal !! real: 1s, because FOSC=4MHz but we set 2MHz TCNT2 = 0; // reset TCNT2 temp = 127; for(;;) { temp--; OSCCAL = temp; Z=0; TIFR2 = 0xFF; // reset counter // wait for the compare-match on timer2: while ( !(TIFR2 & (1<<TOV2)) ) {Z++;} asm volatile ( "jmp1:" "\n\t" "adiw %A0,1" "\n\t" /*2 cycles*/ "sbis %[tifr2],0" "\n\t" /*1 cycle*/ "rjmp jmp1" /*2 cycles*/ : "+e" (Z) /*input and output*/ : [tifr2] "I" (_SFR_IO_ADDR(TIFR2)) : "memory" ); if (Z<(3125+5)) break; } return; } |
Posted on:
I got it running with the master now. This is a quite cool thing :) However, it sometimes looses sync or misses transmissions. Distance is not too far and the rfm12 modules I use in my other projects seem to reach further.... Maybe reducing the data rate would help (I'm using rfm12 without "B" at 433Mhz). I think any window-detection feature is useless: When I open the window, it needs some seconds to detect it and to close the vent. After the vent is closed, the heating stays warm/hot because it needs much more time to cool down. When I come back to close the window (let's say after 5 minutes) it's still warm/hot. So it does not save energy here :) After I close the window the heating gets cold and openhr20 opens the vent after 90 minutes because temperature does not rise without heating. So no matter how you configure it: It does not work for me. If you open the window for a long time (maybe 30 minutes or longer) it is usefull. But then the walls cool down which is not very efficient. My aim was to provide a feedback to the central heating about the vent positions and actual/wanted temperatures in our house so that it can rise water temperature in the morning until rooms are warm and so that it can lower temperature if temperatures should be reduced because no one is at home.
Posted on:
I guess the trick is that without the window open detection, the temperature sensor would recognise the fall in temperature (well it does always) and the algorithm would open the valve completely. So it's better to close the valve and jst loose the energy already stored in the heating. Isn't there a button one can press while closing the window to force the OpenHR20 to end the window detection? I haven't managed to flash the OpenHR20 firmware on my valves yet, moving costs far too much time :(
Posted on:
>I want to change the temperature sensor to a ds1820 1-wire device >(because I need more than one temperature per device). Therefore I rely >on a good calibration of the rc-oscillator. Why that ? Timing for 1-wire is extremely wide, the difference between fastest and slowest has a factor of two. If 1-wire does not work it is definitely not due to a bad RC-calibration. Axel
Posted on:
Hello, i flashed my Hr20 and built a Master. But i seem to be not able to get the master-software running on my PC. Maybe someone can explain step by step for windows xp or opensuse: Which software do i need? Which config files do i have to change? Thank you very much!
Posted on:
@ Marco G.:
I think if you manually change temperature by moving the wheel it leaves
open window mode.
@ OpenHr20-Fan:
You need a webserver (like apache2) with php-support (version 5),
php-cli for running the daemon.php from command line, sqlite for the
database and php-sqlite for database access from php.
Copy the files and folders from www to the directory your webserver uses
for the websites (/var/www on Debian Linux).
Copy the files from tools to another location.
Take a look at the files config.php, daemon.php and create_db.php and
edit the location of the sqlite database (dont place it in the /var/www
directory of apache...).
Create the database by running create_db.php.
Configure com-port (Debian: stty -F /dev/ttyUSB0 38400). You can also
include this command in daemon.php:
exec('stty -F /dev/ttyUSB0 38400');
Start daemon.php on command line.
Go to the webinterface (localhost/index.php).
Posted on:
Hello together, I'm new to this list. I found this project, because I get a complete new heating system in my house. I've tried a first test with openhr20 software, and I think it is a very well done and well documented project. Thanks to all :-)) For my purpose, I want to realize a network of all my HR20 via RS845. I've seen , somebody has thought about this, but nobody has realized it now. Is somebody intrested in this new part of the project ? I've some ideas what can be usefull, but somebody may have additional ideas. First ideas: - connection of the HR20 with a 4-wire cable for RS485-bus and 5V power - a little hardware for the HR20 with 3V Voltage regulator and RS485 driver - advanced communcation with adress parts - connection to a PC via an RS485 - USB adapter best regards Wolfgang
Posted on:
Hello Wolfgang, I would be interested in a solution with an RS485-bus (using the I²C interface) connected to multiple HR20E. For power supply and data transport, I have wires at each HR20E in the wall. The problem is, that I have not much time, todo much work on this project. ELV has developed a new series with remote interface, remote window and dore switches and USB stick for remote access via PC (see http://www.elv.de/Funk-Heizungsregler/x.aspx/cid_7...). I am not sure, whether it is worth the time to develop an own solution although it has some advantages (specially the WEB Server solution). Regards, Karim
Posted on:
Hello Karim, I want to adapt the HR20 via the 10 pin connector, using TxD and RxD and the PE2 port to switch the direction of the RS485-driver. I've develope a small board, but I'm still waiting for some parts to start the test (If I have finnished the hardware-test, I will post it here). I will do the project, with or without help from other users, but Ideas and help is welcome :-) The ELV-products are based on communication via RF, and I don't like to much RF-activity (there is enough electro-smog in the air)! The other advantage of wired connection is no need for batteries ! best regards Wolfgang
Posted on:
Hello, Is the HR20-style the same electronic like the HR20 ? best regards Ronny
Posted on:
Hi, Has there been any further developments with new firmware revisions ? Wolfgang, did you make any progress with RS485 ? Thanks Stuart
Posted on:
Hi! I'm using the openhr20 firmware with two of my rondostates because with the original firmware, vents do not open to 100% after a few days. Openhr20 works perfectly :) I only had to disable the window open detection because it kept on triggering when no window was open. I'm also using the serial port to get temperatures and valve position. I noticed the following: On rondostat 1, the baud rate is 9600 which is correct. On rondostat 2, the baud rate is 10416.
Posted on:
@Chris: On rondostat 2 you have wrong internal oscilator calibration value. Jiri
Posted on:
Hi, can someone send me the latest, non RFM12, HEX and EEP files ? I will only flash my HR20s. I'm not interrested in programming and compiling. I will try to flash my HR20s with an free ISP-Programmer. Thomas
Posted on:
Attached files:Hi, just successful flashed my first HR20 to OpenHR. Works well. It was that easy ;-) But, is there a litte description of the functions, a manual or somethine else available ? Ich understand most of the dsiplay output, but still some questions. I've added an externel connector for the ISP. It took some thime to do this. Thanks to Jiri, who send me the HEX-Files :-) Thomas
Posted on:
Control is almost compatible with original SW with some features. man difference: middle button can show actual time, actual temperature and valve position (0-100%) press&hold middle button can set 4 preset tempeteratures press&hold AUTO/MANU = time setings press&hold PROG = assign preset temperatures to time ( it have one program for 1-7 or individual for each day in week) Press & hold all button show service menu. It have 2 modes switched by middle button. First mode is internal settings (see too http://openhr20.svn.sourceforge.net/viewvc/openhr2...) Second is is some diagnostic values PS: why do you not use JTAG? It don't need modification and it is cheap, example here http://cgi.ebay.com/ws/eBayISAPI.dll?ViewItem&item... 15.90USD
Posted on:
Hi Jiri, some examples : Ad 1 to 3 - calibration ? E 2 - HR20 not connetcted to valve ? E 3 - ??? OPEn - Window open ? - C - ??? * - Freeze-protection ? ( (moon) - Nighttime/-temperatur o (sun) - Daytime/-temperatur ( and o (both symbols) - ??? After first flashing, I get "EEpr" in the display. Don't know why, after second frashing, the problem was solved. Sorry, I don't understand the service menue and your program. I'm not firm with C :-( JTAG: Hmmm, I'm normally using BASCOM as programming. This is also the reason why I ask you for the HEX-files. My programmer is the "Sample Elektronics Programmer", only 5 wires from parallel-port-interface. I have a mySmartUSB light too, this device operates with BASCOM and can program HEX-files for standalone too. I never found an cheap programmer which is compatible with BASCOM. Edit: How can I activate RFM for later usage ? Must the programm recompiled ? Must the RFM12 be connected, when I'm not using RFM ? Thomas
Posted on:
Hi Thomas, you're right, Ad 1 to 3 - Adaptation to mechanic valve E 2 - HR20 not connected to valve (like original firmware) E 4 - wireless HR20 out of sync OPEn - Window open * - Freeze-protection temperature ( (moon) - Nighttime/-temperatur o (sun) - Daytime/-temperatur ( and o (both symbols) - "comfort" temperature You can set 4 different temperatures, that's why there are 4 symbols :)
Posted on:
Hi, what does "comfort"-temperature mean ? Thomas
Posted on:
No special meaning, it is Jiri's expression for a third temperature level :) You may want to set it 2°C higher in the evening than during the day, that's what it's for...
Posted on:
Hi. Problem : I can set 4 temperatures. Fine ! But I only can set times for 2 temperatures : ( and (o Ok, the * is for the frost-protection, but when is o active ? Thomas
Posted on:
Hi Thomas, I just tested it: - press&hold PROG to switch to scheduke programming - press prog again to set same schedule for each day - adjust the time using the wheel - adjust the temperature level using the temperature button. For me, all 4 levels can be choosen here.
Posted on:
Hi Marco, That was the tick ! ;-) Adjusting temperature levels IN the time-programming menue ! Thanks a lot :-) RS232: Protocol ist 9600,8,n,1, correct ? If I connect a second AVR (3V Vcc) on the RxD & TxD, must I convert the signals ? Or is it possible to connect it directly ? Thomas
Posted on:
you're welcome :) 9600 8N1 is correct, as far as I can see from the code. I think you can connect it directly, you just have to swap Rx and Tx. The voltage levels on HR20 side are also about 3 V, i.e. two batteries. Maybe you want to add 1k series resistors as current protection. In the service menu (press&hold all 3 buttons) you can edit the EEPROM. The contents are shown in Jiri's link above (http://openhr20.svn.sourceforge.net/viewvc/openhr2...) in line 51-91. The 2 digits in front of the colon are the EEP address, the last two digits are the value. PROG switches between address and value. Changes are saved when switching back to address (I'm not 100% sure about that). greetings Marco
Posted on:
Thanks Marko G for more information. I must add only one E3 - is invalid mechanical calibration (too short range or too long range) Same as original SW Mechanical range of valve can be calibrated manualy. see to my post from 2009-04-01 10:07 "EEPr" - EEPROM not contain valid settings
Posted on:
Hi Thomas, do you have a schematic for your ICSP port ? delboy
Posted on:
Attached files:Hi, it's standard ISP to processor. I use the 6-pin ISP. All pins of the processor going to a via of the pcb. I soldered the wires on ths vias. Thomas
Posted on:
Hi all, great so see this project still active. I'm using 4 OpenHR20 Rondostates now, but I still have problems with the open window detection. How can I turn it of? I set 0x22 to 0xFF and 0x24 to 0xFF, but it still shows "open". @Knickohr: You can connect an external avr to the rondostat, it works without problems. Hint: OpenHR20 sends out a status every 4 minutes. I use it to wake an external avr from power down mode (connected TX of the rondostat to RX and external interrupt pin of my atmega8). It wakes up fast enough to get the serial.
Posted on:
@Chris: version of your SW? Best could be SVN version number.
Posted on:
Hi Chris, hi Jiri, I have the same problem with the Open Window. Don't know, which SW-version. You send me the HEX-File ;-) Thomas
Posted on:
Window close detection - disable: set 0x23 to 0xFF (for SVN revision != 281 can be different index see too http://openhr20.svn.sourceforge.net/viewvc/openhr2... ) If you have problem with noise from motor, you can disable allow_ADC_during_motor (setting 0x28 = 0x00)
Posted on:
for normal trunk setting map see too http://openhr20.svn.sourceforge.net/viewvc/openhr2...
Posted on:
Attached files:So I used this simple LPT ICSP circuit with avrdude on windows and it worked (btw 220R resistors). I connected MISO, SCLK & MOSI to some vias near the screw and the GND and RESET to the ISP port. These are the dos commands :- install_giveio.bat avrdude -p m169 -c stk200 -P lpt1 -U flash:w:"D:\Rondostat\openhr20\trunk\source\hr20.hex":a -F avrdude -p m169 -c stk200 -P lpt1 -U eeprom:w:"D:\Rondostat\openhr20\trunk\source\hr20.eep":a -F I couldn't read any of the fuses, so I decided not to try and program them, but I fired it up and it WORKS !!! Next stage is to get some cheap Oventrop adapters and rfm12 modules.
Posted on:
Hello. Where can I get the c-code (or some more informations) for the software. Every link will bring me to a blank page. Thanks a lot, Turtleman
Posted on:
Sourceforge SVN is down Yesterday our vigilant operations guys detected a targeted attack against some of our developer infrastructure. The attack resulted in an exploit of several SourceForge.net servers, and we have proactively shut down a handful of developer centric services to safeguard data and protect the majority of our services. see too http://sourceforge.net/blog/sourceforge-net-attack/ Please wait.
Posted on:
With AVR-GCC 4.5.2 and avr-libc 1.7.0 on Archlinux i've got several
errors regrading fuses like this:
'CKSEL0' undeclared here (not in a function)
the header-file only declares FUSE_CKSEL0. After i changed that the
software compiled.
---snip---
Index: main.c
===================================================================
--- main.c (Revision 281)
+++ main.c (-)
@@ -334,9 +334,9 @@
FUSES =
{
- .low = (uint8_t)(CKSEL0 & CKSEL2 & CKSEL3 & SUT0 & CKDIV8), //0x62
- .high = (uint8_t)(BOOTSZ0 & BOOTSZ1 & EESAVE & SPIEN & JTAGEN),
- .extended = (uint8_t)(BODLEVEL0),
+ .low = (uint8_t)(FUSE_CKSEL0 & FUSE_CKSEL2 & FUSE_CKSEL3 &
FUSE_SUT0 & FUSE_CKDIV8), //0x62
+ .high = (uint8_t)(FUSE_BOOTSZ0 & FUSE_BOOTSZ1 & FUSE_EESAVE &
FUSE_SPIEN & FUSE_JTAGEN),
+ .extended = (uint8_t)(FUSE_BODLEVEL0),
};
/*!
---snip---
I used the 10-Pad-Connector on my Sparmatic (Thermotronic) Basic and it
seems mostly working. Sadly they used PE1/TXD for the motor-eye on this
model so without PCB-hacking no EIA232 for me but there is SPI on the
10-Pad-Connector (pins shared with buttons!) and TWI/I2C/Whatever on
JP6.
Posted on:
Hi Jiri, I did not manage to turn of the window detection... I dont know the svn revision, but in eeprom.h it says:
/* 22 */ uint8_t window_open_detection_diff; //!< threshold for window open detection unit is 0.1C /* 23 */ uint8_t window_close_detection_diff; //!< threshold for window close detection unit is 0.1C /* 24 */ uint8_t window_open_detection_time; /* 25 */ uint8_t window_close_detection_time; |
I set all to 0xff or as high as possible, but it still displays open. Chris
Posted on:
Hi Jiri, I just saw that the rfm12-code (\openhr20\rfmsrc\OpenHR20) differs from (openhr20\trunk\source). Which one should I use when I do not need rfm12? Chris
Posted on:
I recomend rfmsrc branch with disabled RFM extensions "make RFM=-DRFM=0" This branch contain last updates.
Posted on:
I looked through the HR20 threads last weekend and I have to admit you did a great job. I have some questions which I don't understand at the moment: Is there a cyclic (e.g. once every quater) full open and close of the valve implemented to keep it movable? Window open and close seems to be detected by a reduction of the measured temperature. Is the RF protocol able to created a mashed net where a window sensor talks to one or more valves? Is there free flash space left to extend the S/W? Is a low battery indication / battery voltage transmitted to the master? Cheers, Knut
Posted on:
Hi Knut, Knut Schwichtenberg wrote: > Is there a cyclic (e.g. once every quater) full open and close of the > valve implemented to keep it movable? there is, AFAIK every Sunday at 12.00 > Is a low battery indication / battery voltage transmitted to the master? yes, the battery voltage is transmitted to the master The other questions have to be addressed by Jiri, I'm not sure about them. Greetings, Marco
Posted on:
Cyclic movement is planned to Sunday 10:00am. Another reason to do it is mechanical recalibration.
Posted on:
H Marco and Jiri, thanks for your replys. @Jiri the following questions from my first email remain unanswered by Marco: Window open and close seems to be detected by a reduction of the measured temperature. Is the RF protocol able to created a mashed net where a window sensor talks to one or more valves dirctly? Is there free flash space left to extend the S/W? Cheeers, Knut
Posted on:
@Knut Schwichtenberg: Current wireless network is not "mesh" but star topology with one master. Free space in flash is problem (0.5kB free), but we can remove some low priority code (watched variables in service menu, 0-24 bars in LCD, in extreme situation we can remove local serial line communication in wireless case) This is my TODO list for this project: - optional window contact wired to PE2 signal on valve (time: 1 week, I must mount magnetic contact where it is possible) - add command to "block" valves remotely = remote childlock (time: 1-2 months) - change wireless protocol. I remove fixed communication windows and I will use random access with collision detection. It will improve communication speed and allow add wireless items without RTC and signal repeaters (time: 2 weeks - 3 months) - add more sensors into wireless network. Examples: remote window open contact, humidity sensor, int/out temperature, door sensor for automatic heating switch on. (time depend to PCB availability, probably end of Feb) Jiri
Posted on:
Some more information about wireless "extension" board: - ATMEGA16 / ATMEGA32 CPU depend to destination - RFM12b - optional SHT21 humidity/temperature sensor - optional DS18S20/DS18B20 temperature sensor - optional FTDI FT232RL USB, this PCB can act as master board - optional LE33 stabilizer (3v3 power from USB, optional if 50mA from FTDI is not sufficient or for VUSB) - optional VUSB interface (http://www.obdev.at/products/vusb/index.html) - optional I2C EEPROM (24c02 - 24c1024) - optional LCD from Nokia 3310 with optional backlight (LCD is low power, visible without back light. Destination for show temperature or status) - optional power from 2xAA or 1xLipol - it have I2C and SPI on connector - 7 A/D free lines in connector or 7 digital I/O - PCB size 50x50mm Today evening at home I will store schematic and PCB layout into SVN. PCB layout is done, but I must wait for china spring festival end (Reason is price, PCB from http://www.seeedstudio.com is 5x cheaper than from local sources.) NOTE: this board have RFM22/23 option, but it can't be RFM12 compatible on wireless, it is for another project.
Posted on:
Note for window detection: Temperature slope is not, and can't be perfect solution for window open detection. Reasons: - in some situation, depend to air flow in room, temperature fall is too slow. (in my bedroom detection take 2-3 minutes and can't be improved, unacceptable, reason is balcony door on side to heating) - sometimes heating is far from window, temperature fall is extremely slow and hidden by radiator heat (example: my bathroom) - cold air stream from window with bad thermal isolation can create false window open positives (my kitchen) In reality, I have only 2 rooms, where window detection works fine. In other cases, I don't have any idea how to improve it only with temperature. I have long series of temperature measurement and it is sometimes difficult to detect window open for human, impossible for computer. This is reason, why I will use magnetic window contact.
Posted on:
Jiri Dobry > - optional VUSB interface (http://www.obdev.at/products/vusb/index.html) Have you see the following USB implementation? http://www.xs4all.nl/~dicks/avr/usbtiny/ it is also public but with a more open license... Knut
Posted on:
@Knut Schwichtenberg: I am using something similar to this project (Igor Cesko IR receiver). But VUSB is little bit more "adu1t" and maintained project. And we have not any problem with license. OpenHR20 is also GPL project, documentation is also available.
Posted on:
Wireless Expansion board layout is in repository. You can check it. NOTE: SVN web interface on SourceForge.net still offline. You must us SVN directly:
svn co https://openhr20.svn.sourceforge.net/svnroot/openhr20 openhr20 |
Posted on:
Some more notes about Thermotronic: The "TWI/I2C/Whatever"-Port i mentioned earlier (JP6 at <http://www.mikrocontroller.net/attachment/29357/sc... ) is actually grounded near the soldering-points - i had to cut this connection to make the pins useable. Another thing i noticed: Makefile says F_CPU = 1000000 but my fuses are set to 8MHz (no CLKDIV) and i'm pretty sure i didn't change this…
Posted on:
I got the code. I want to test the hr20 first without a wireless module. So what means "make RFM=-DRFM=0" How can I compile the software without rfm? Is it ok to define RFM = 0 in config.h? (line 102, rev. 278) By the way. Where do I find the rev. number of the actual software version. It's true that I'll find the newest version in \openhr20\rfmsrc\OpenHR20 In config.h revision seemed to be set to 278 but I heard something about rev 281. Thanks, Thomas
Posted on:
Thomas Pehmöller wrote: > So what means > > "make RFM=-DRFM=0" > > How can I compile the software without rfm? > Is it ok to define RFM = 0 in config.h? (line 102, rev. 278) Thomas, make is a kind of scripting. The command line sets the variable RFM to the value "-DRFM=0". I expect from the normal makefile behaviour this is forwarded to the C-compiler's command line. "#define" in a file are overwritten by identically named "-D" command line parameter. So the make command line and your finding are identical. Cheers, Knut
Posted on:
What are your experiences ? Let's assume the system (radiator and HR20) are in a stable state... What accuracy (room temp. e.g. 22°C) is typical for the original firmware and the OpenHR20 firmware ??
Posted on:
Thermotronic: Ctrl+Z for 8MHz - There was a bug in the fuse-gui i'm using - original at 1MHz was correct. Got basic i2c in but some (timing?-)problems. Getting my measurement-tools back next week and hopefully also some time to look after that. @Richard G. I guess since the temperature inside your room varies even if your radiator would keep a constant temp thats mostly negligible
Posted on:
Hi to all the Pros here ... lot of work done here ... really impressive !!! The HR20 will be my first AVR project ... I'm comeing from the automation business, but have not done any C-programming for the last 10 years ... So far I bought myself an AVR Dragon board, installed AVR Studio and then WinAVR. I have read through the original german and this thread. I also do not need wireless, but want do use this branch, as it is the only one maintained. I want to do 2 things: 1. Flash the latest File from yours to check if I can handle the hardware (dragon, cabeling, hr20..) ... please tell me which file I should use 2. If that works I want compile the source myself and make little changes... Do I need SVN - I never used it before - what do you suggest the rookie ... ;-)
Posted on:
Hello, After long, long, long time I made release of version 1.0. See here https://sourceforge.net/projects/openhr20/files/ This zip contain binaries for all supported configuration options. last change except bug fixes is option for hardware window detection. Jiri
Posted on:
Richard G: For programming/debug you need ICE (you can use AVR ICE, AVR ICE mkII, AVR Dragon, AVR ONE) I recommend AVRICE first generation clones, it is cheap, approx 15USD from ebay include shipping. For programming only you need any ISP, but ONLY WITH HW MODIFICATION (example AVRISP mk II, or USBASP) You don't need SVN, but I recomend it. Without SVN you will must merge bug fixes from official code manually (see to TortoiseSVN) . Another choice is download snapshot from here http://openhr20.svn.sourceforge.net/viewvc/openhr2... Sources contain notes about compiler WinAVR-20071221, but WinAVR-20100110 is tested too without problems. Current official release is compiled with linux avr-gcc (GCC) 4.3.5
Posted on:
@Jiri - thanks for all your support !!!!! OpenHR20 SW variants: original_* - honeywell HW without modification rfm_int_* - honeywell with internal RFM12 module rfm_ext_* - honeywell with external RFM12 module thermotronic_* - thermotronic HW Me and others would like to use your software without rfm ... OpenHR20rfm_no_rfm* - rfm branch without RFM modules It would be great, if you could integrate this into the .zip as well !!!
Posted on:
OpenHR20rfm_no_rfm* - rfm branch without RFM modules is this not the same as original_* - honeywell HW without modification ??? Or is original* the original Honeywell-sw ? Thomas
Posted on:
Richard G. wrote: > OpenHR20 SW variants: > original_* - honeywell HW without modification > > Me and others would like to use your software without rfm ... > OpenHR20rfm_no_rfm* - rfm branch without RFM modules Hi, original_* is the version without RFM, just as you wanted :) The original software from Honeywell cannot be read from the Flash, because of the lockbit settings.
Posted on:
Hi Jiri, hi Marco. Is there a changelog available ? Thomas
Posted on:
original_* is code from rfmsrc branch compiled without RFM12 support. It is for valve "out of the box". I am not have any changelog file, but you can see to SVN logs and major changes is in this thread.
Posted on:
which SVN Soft do you recommend for a Win XP / Win7 novice User
Posted on:
Jiri - thanks for Your advice regarding svn. 1. Can You guys please verify the following: I thought, when the wheel is not turned, the 2 encoder signals should be either 0 = or 1. Because the state between the two should only differ during a small periode, when turning the wheel. On my HR20 one signal changes as expected between 0 (position A) and 1 (position B). But the second signal is always = 1 no matter if the wheel is in position A ob B. (it changes state between the 2 Positions). Is my encoder defect ? 2. I only found something about the encoder in keyboard.c. But where is the evaluation of the 2 encoder signals direction phase ...?
Posted on:
@Richard G.: Encoder have 4 states ....00-01-11-10-00.... (or back) ROT1 signal have permanent pull-up. (value in schematic is wrong) ROT2 use pull-up in AVR, but this pull-up is enabled only for reading (save energy) If you have only "1" on wire, encoder must be failed. Direction code is in keyboard.c lines 69-81
Posted on:
1. encoder YES I know about the 4 states and that rot2 is only enabled during reading....BUT let's assume the following: We have wheel position A, B, C and position A-B, B-C which is between A and B (or B and C) when turning the wheel one step (always the same dircetion). rot2e ... is what I would expect from rot2! turning the wheel 1 step from A to B: signal______A____________A-B____________B rot1________0____________1______________1 rot2________1_0_____________1___________1 rot2e_______0_______________1___________1 turning the wheel 1 further step from B to C: signal______B____________B-C____________C rot1________1____________0______________0 rot2________1_______________0_________1_1 rot2e_______1_______________0___________0 So rot2 is late at position A and early in position C. The hr20 is still dedecting the the turning of the wheel correct...BUT I am going to simulate the encoder rot1/2 with the PLC I have set up in my house and here it causes me troubles .... Anyway I think the encoder is defect .... ? 2. Toolchain A typical novice question - I know ;-) but I have installed AVR studio SP3 and WinAVR20100110(GCC 4.3.3,avr-libc 1.6.7cvs). I did not install avr-toolchain-installer-3.0.0.240(AVR-GCC: 4.4.3, AVR-LIBC: 1.7.0) so far. I would like to produce excatly the same binary and hex as you do. But I still want to use AVR Studio 4 for loading and debugging together with my AVR DRAGON.... a) What do I have to download/install ??? b) In studio I tried to use your makefile from ..rfmsrc\OpenHR20. But at least I can't tell studio to pass the make parameters "RFM=-DRFM=0". What do you suggest ?
Posted on:
add Info regarding 2. toolchain: These are the restriction for ext. makefiles in studio4: -The name of the elf file to debug must be projectname.elf - To enable clean or rebuild, the clean target must be defined in the makefile. - The makefile must reside in the same directory as the output elf file. - Compiling of single files will only work if this file is defined as a target in the makefile.
Posted on:
@Richard G: Why do you need simulate wheel? If you want control walves remotely, you can use serial connection (done in code), wireless connection (done in code), or RJ485 (need HW mod and small SW mod) Simulate wheel can make problem, it is not used only for temperature setting. If you want debug code in AVR studio, you need change you configuration in config.h. Compile code in AVR studio (you have project file in repository), start debug with dragon and enjoy. Where is problem? ------------------------ PS: do anybody any news about "Homeexpert HR20 Style" hardware from Conrad?
Posted on:
Hi Jiri, description from Conrad says: > the wheel looks nicer now and the display can be read from a larger angle. The rest seems to be the same. But the SW version would be interesting... http://www.conrad.de/ce/de/product/615950/HEIZKOeR...
Posted on:
Jiri: I have a homeexpert from amazon at home - so far PCB seems to be the same. I will get my Dragon end of this week.... Encodersimulation: Thanks for your hints but I have parallel cabeling (50 wires 24VDC/220VAC ;-) running through my house and PLC has no RS485. It works already fine without SW-change on this one: http://www.amazon.de/Heizk%C3%B6rperregler-Energie... But on hr20 I have to change the wheel task ... ________STUDIO&DEBUGGING_____WILL THIS WORK ? I hoped that I could debug if I use your hr20.aps and tell studio to use your makefile from ..\rfmsrc\OpenHR20\ with the following changes : Line 137: # Place -D or -U options here for C sources HW_WINDOW_DETECTION=-DHW_WINDOW_DETECTION=0 RFM=-DRFM=0 #REV=-DREVISION=\\\"$(REV)\\\" Line 269 #---------------- Programming Options (avrdude) ---------------- AVRDUDE_PROGRAMMER = dragon_jtag ________TOOLCHAIN___ - What is your toolchain ? - Is it available for Windows Users ?
Posted on:
Richard G. wrote: > Jiri: I have a homeexpert from amazon at home - so far PCB seems to be > the same. I will get my Dragon end of this week.... > @Richard: what does the display show during boot (after inserting the batteries) before you have to enter the date?
Posted on:
Problem is that I want to know about this "HR20 style": http://www.conrad.de/ce/de/product/615952/ @Richard G: Makefile in AVRstudio is used only for compile, not for communication with AVR dude.
Posted on:
Hi all, I wanted to ask who of you is running the daemon on which device? AFAIK Jiri has an OpenWRT router and connected the master HW via serial lines. I have a AVM FritzBox 7270v3 and I'm using the FTDI FT232R USB-serial converter. The problem is that my FritzBox crashes after 1-8 hours of running the daemon.php with php-cli, and I'm not sure why. There might be several root causes: 1. Kernel is too old and FTDI driver also. Kernel version is 2.6.19.2 and cannot be updated, because AVM has closed-source drivers for DECT, WLAN, phone etc. 1a USB driver part 1b FTDI driver part 2. php-cli with daemon.php is unstable. Although I've done some debugging and tried some changes in daemon.php, it didn't get any better. php-cli does not report any error when the FritzBox crashes and reboots. So I'm thinking about: - trying the serial console of the FritzBox (no USB) - trying a Prolific PL2303 serial converter - rewriting daemon.php in plain C as a real daemon Jiri, is there any documentation of the protocol between the master HW and the daemon? Greetings, Marco
Posted on:
@Richard G: Makefile in AVRstudio is used only for compile, not for communication with AVR dude. I have 3 toolchains: - AVRStudio + WINAVR + AVRJTAG mkI(clone) - linux AVR GCC + AVRDUDE + same AVRJTAG - ECLIPSE + dgb + avarice + same AVRJTAG You can try any of this, its your choice :-)
Posted on:
@Marco G: I am sorry I don't have any documentation about protocol between master board and php script. Except source code. And frankly spoken: daemon.php is worst part of OpenHR20 project. I wrote it without concept only for debuging master-slave wireles communication. And because it works, it still in project. Problem with your fritzBox is probably RAM. I have hacked HW to 64MB of RAM and it is "rock stable" independent to dirty code in daemon.php Do you have swap? (you can use flash, it is almost not used). Old and persistent problem of PHP are memory leaks.
Posted on:
jiri: I had both at home. Your Link HR20 has the same electronics like the homeexpert http://www.amazon.de/Homexpert-Honeywell-HR20-Styl... Sorry but now you confused the novice ... does it mean one can't use an external makefile if one wants to debug with studio ??? Could you/someone please explain "Makefile in AVRstudio is used only for compile, not for communication with AVR dude."
Posted on:
Hi Jiri, RAM shouldn't be the problem. I can see some MB still free in rrdstats, and I have a 128 MB swapfile on USB storage, which is only up to 3% in use. The FritzBox already has 64 MiB RAM. My php is 5.3.5. I'll try to find out the protocol from source code in the next few days and then you can check if I got it right :)
Posted on:
@Richard G: where is problem with development environment? You have HR20.aps project file. Open it in AVRstudio, press F7 for compilation. and you have ELF binary + hex DEBUG: Find Debug->Select platform - dragon and you can start debug session PROGRAM: Tools->Program AVR -> Connect - dragon ....
Posted on:
I thought, that the ..\rfmsrc\OpenHR20in\makefile sets a lot of defines and ifdefs necessary
Posted on:
@Richard G: minimaly this http://www.amazon.de/Heizk%C3%B6rperregler-Energie... can't be same HW as HR20. From first point of view, it have different LCD (weekday symbols) I have idea where is problem with wheel external control. Problem is in pull-ups. My SW enable ROT2 pull up close to reading signal. Pull-up is normaly disabled, because it increase consumption (60uA-150uA on "bad" encoder position). But if you connect external wires, you increase parasite capacitance and internal pull-up is not able to pull signal up in time. Solution is simple, use additional external permanent pull-up. Makefile contain many choices, but you need only disable RFM extension. Others are for test or special situations.
Posted on:
Attached files:Jiri: This Valve attached is not HR20 Style, but works for me without SW-Mod.... I still have not understood, why I should not be able to use the ..\rfmsrc\OpenHR20in\makefile from within studio4 including this Modifications: Line 137: # Place -D or -U options here for C sources HW_WINDOW_DETECTION=-DHW_WINDOW_DETECTION=0 RFM=-DRFM=0 #REV=-DREVISION=\\\"$(REV)\\\" Line 269 #---------------- Programming Options (avrdude) ---------------- AVRDUDE_PROGRAMMER = dragon_jtag Maybe I will understand it when I get my Dragon ...
Posted on:
you need only this: RFM=-DRFM=0 all others can be default you don't need makefile for programming PS: your picture looks completly incomatible with OpenHR20
Posted on:
Richard G: Your picture look like this Beitrag "Untersuchung Heizungsthermostat Lifetec MD12460"
Posted on:
The novice was lion-hearted, Valve is running ... but.... I programmed the original_sww V1.0 hr20.elf File and the Verify of the EEprom brings up this: "warning EEprom Adr.14 is A0, should be A4" Hints would be very welcome
Posted on:
Attached files:maybe the jpg from the settings help - checkboxes for programming fuses and lockbits where not checked
Posted on:
Hi Richard, the EESAVE fuse is set, so you cannot program the EEPROM correctly. Clear it and program the EEPROM again, then it will be fine. Then set the fuse again to preserve the EEPROM content during future updates.
Posted on:
Thanks for the very fast reply !!!!!!!! The jpg from the last post was before programming ... after programming the .elf the lockbit Tab loos different ... My translation of your hint: 1 uncheck the EEsave fuse in the fuses tab 2 check the fuses checkbox in the programming tab 3 programm EEprom (or .elf file ???) Right ?
Posted on:
Attached files:here is the jpg missing in my last post
Posted on:
nearly right ;) step 1: uncheck EESAVE step 1.1: program fuses on fuses tab step 2: not necessary, that's only for reading from the device and saving to an elf file step 3: choose ELF and program it
Posted on:
1a - You saved the evening for me (and my family ;-) I don't know why - but I also had to check the lockbits flag
Posted on:
Hi! I just flashed version 1.0 with the hardware window detection. I think this is the only way to really determine if a window is open or not, so I much appreciate this new function. Thank you very much! The hardware window detection uses the PE2 pin. If I leave it open (not connected), rondostate shows "open". If I connect it to VCC, it shows open. If I connect it to Gnd, it detects a closed window. I think it should be just the other way around, because if someone does not want to use the hardware window detection or if you disconnect the sensor, ist goes to open and won't heat any more. Idea: - Enable pullup - Check if pin is high or low - When high: Not connected or closed window - When low: Open Window - Disable pullup for power safe Chris
Posted on:
Dear all !
a) What is the right way to change the Temp.Offset (room 23,0 / Valve
says 22,3). Do I have to change it here in eeprom.h or is there a
simpler way ?:
/* 19 */ {295-TEMP_CAL_OFFSET,295-TEMP_CAL_OFFSET, 0, 255},
//!< value for 35C => 295 temperature calibration table
/* 1a */ {340-295,340-295, 16, 255}, //!< value for 30C
=> 340 temperature calibration table
/* 1b */ {397-340,397-340, 16, 255}, //!< value for 25C
=> 397 temperature calibration table
/* 1c */ {472-397,472-397, 16, 255}, //!< value for 20C
=> 472 temperature calibration table
/* 1d */ {549-472,549-472, 16, 255}, //!< value for 15C
=> 549 temperature calibration table
/* 1e */ {614-549,614-549, 16, 255}, //!< value for 10C
=> 614 temperature calibration table
/* 1f */ {675-614,675-614, 16, 255}, //!< value for 05C
=> 675 temperature calibration table
b) Please explain function of Temp.tollerance (set to 50) in
controller.c
c) I would like to implement a BOOST function I saw on the other valve:
If the user presses e.g. middle and right button the valve should open
to 100% for e.g. 5 Minutes (eeprom).
- Where is the best location to implement that ?
- Some hints hoe to implement that would be very very welcome ;-)
Posted on:
@Chris: You have almost same idea as is implemented in code. Only one difference: "low" means closed window. Reason is magnetic window contact. It is imposible buy inverse functionality. @Richard: a) you have correct space to do this, but table is inverted, you must recalculate it. b) config.temp_tolerance: Integrator is not updated everytime. It test change direction and it is "lazy" around zero error +- config.temp_tolerance c) right place is menu.c & controller.c/CTL_update. - menu.c you need update for event from long key press - controller.c for change functionality
Posted on:
Thanks Jiri: RE: Temp.Offset ... The temp. gap comes from the cold wall. As this offset differs depending on outside temp I am thinking about one simple variable I use as Offset for the user. Do You have a better idea ?
Posted on:
Hi Jiri, I always used magnetic contacts for alarm alarm systems. They have 3 pins (com, no, nc) and switch a common pin between the other 2 pins. But it seems they are not so widely used any more, neither reichelt nor conrad has them... However, it doesn't really matter because you can easily disable the windows function. @Richard: I think you can't fully compensate the influence of cold walls or hot heaters, because they both change too much. The only way would be to mount the sensor at a different place.
Posted on:
@Chris: Reichelt has such sensors with 3 contacts, made of glass. I'll look up the name when I'm back home... greetz, Marco
Posted on:
I don't know about sensors with 3 contacts. It is not problem change it for inverse sensors:
// PE2 on GND = window closed
w = ((PINE & _BV(PE2))!=0) && config.window_open_detection_enable;
if (!w) PORTE &= ~_BV(PE2); // disable pullup for save energy
|
// PE2 on GND = window open
w = ((PINE & _BV(PE2))==0) && config.window_open_detection_enable;
if (w) PORTE &= ~_BV(PE2); // disable pullup for save energy
|
Posted on:
@jiri: Where is the best place for an central Temp.Offset Variable e.g. ADC_Convert_To_Degree(int16_t adc) ?
Posted on:
@Richard: yes, ADC_Convert_To_Degree(int16_t adc) but please use config.temp_offset (it must be 8 bit only, but +- 1.28 eventualy +-12.8=multiplied by 10 degree can be enough)
Posted on:
8 Bit * 10 would be fine. But the old guy is not very firm in C. What you mean with config. ... I thought about a Variable in EEPROM ... how do I have to implement that ?
Posted on:
Offest_temp might differ betwenn some heaters. So SRAM would be fine too. The oly disadvantages are, that it has to be set again after a batttery change and during software development ... In any case, the value must be adjustable by the user ... 1. What do you prefer ... and how do I have to implement that ? 2. Which menu should I use to let the user set the value ?
Posted on:
@Richard G: I prefer store it in EEPROM. Why? - you need only add this into eeprom.h (config structure and value,default,min,max table) - mechanizm to change this value it already implemented in service menu etc. -except change in eeprom.h you need only use this value Do you realy want it? It is only 0.7degree (precision of used NTC is worst) nad it depend to air flow (external temperature)
Posted on:
Small regression in Rev 286: Makefile (openhr20/rfmsrc/OpenHR20/Makefile) is Windows-only again. For Linux: 423c423,430 < ELFSIZE = $(SIZE) --mcu=$(MCU) --format=avr $(TARGET).elf --- > # different command line parameters for "avr-size" on Linux and Windows. > ifdef ComSpec > # WIN32 > ELFSIZE = $(SIZE) --mcu=$(MCU) --format=avr $(TARGET).elf > else > # Linux > ELFSIZE = $(SIZE) $(TARGET).elf > endif
Posted on:
Jiri: YES. Actual to measured temp. differs between 1,5 and 1,9 °C (even more, if outside temp falls) in my rooms ! Change by Service-Menue is not comfortable enough. What about menu_preset_temp4 ?? @adlerweb: I use this openhr20/rfmsrc/OpenHR20/Makefile with studio4 ... must I check out your change ???
Posted on:
stan wrote: > @Chris: > Reichelt has such sensors with 3 contacts, made of glass. http://www.reichelt.de/?ACTION=3;ARTICLE=27696;PROVID=2402
Posted on:
@adlerweb: it is not regresion. It depend to version of avr-size. I have version "GNU size (GNU Binutils) 2.20.1.20100303" and it works on linux fine. I must know it, because linux is my primary system and official binaries for version 1.0 is compiled on linux.
Posted on:
Small warning: If you aren't experimentalist, please don't use SVN code Revision > 294 ( > Feb 26 18:20:11 2011 UTC ). I am trying to modify PI controller to allow use lower gain on loop. Reason is improve stability in some situations ( versions <= 294 can have oscillation around wanted value. note: normal mechanical "wax" regulator have same problem in this situation ) But current code have "PI windup" problem. It can cause long delay after temperature change. Current(= SVN rev 297) anti-windup protection (based on detect valve saturation) isn't sufficient.
Posted on:
Jiri Dobry wrote: > b) config.temp_tolerance: Integrator is not updated everytime. It test > change direction and it is "lazy" around zero error +- > config.temp_tolerance Valve setpoint=23,0 ValveTemp=23,4 It seems this difference(0,4°C) stays all the time / is not corected by the controller ... is config.temp_tolerance causing this ??
Posted on:
Should I change #define EE_LAYOUT (0x10) to ???? if I add my Offest temp
to config_t ?
/* 29 */ int8_t room_temp_offset;
/* 29 */ {18, 18, -127, +127}, //!< offset to
roomtemp 1=0,1°C
BTW: I always get this warnings:
../common/rtc.c: In function 'RTC_timer_set':
../common/rtc.c:575: warning: 'next' may be used uninitialized in this
function
../common/rtc.c: In function '__vector_4':
../common/rtc.c:678: warning: 'next' may be used uninitialized in this
function
Posted on:
@Richard G:
Your code looks OK, bud nin&max must be one-complement number (this
table is unsigned) {18,18,0,255}
In config_t you can use signed int8_t without problem.
Warning on rtc.c is correct, compiler is not able to see, that we don't
need init it. I can be fixed by "dummy" init, but it take space in flash
and situation on free space is almost critical.
Posted on:
@Jiri: Thanks, but is /* 29 */ int8_t room_temp_offset; correct or do I have to use uint8_t here as well ? 1. Should I change #define EE_LAYOUT (0x10) to ???? 2. Controller Problem? Valve setpoint=23,0 ValveTemp=23,4 It seems this difference(0,4°C) stays all the time / is not corrected by the controller ... what could be the cause ??
Posted on:
Jiri: I tried to calculate/understand the controller with I=0 and my error=400=0,4°C WHERE IS THE MISTAKE IN MY CALCULATION ? error16 400 PP_Factor * abs(error16) 17600 .P_Factor <<8 3840 sum 21440 pi_term *= error16 8576000 pi_term >>= 8 33500 valve_center)*scalling_factor 14080 sum 47580 pi_term16 >>=8 186
Posted on:
Attached files:@Richard G: In config_t you can use signed int8_t without problem. add 1. You can, but it is condition only on public code. add 2. except temperature we need optimize motor movements. It is normal if temperature is +-0.6 degree around wanted. See to my data from last night. Most significant for compensate systematic offset is integration part of controller. But it take many hours to find this value (gain of this loop is small and must be small to prevent oscilations)
Posted on:
Jiri: a) where in the controller is the part for reducing motor movements ? (power consumption is not important to me, because HR20 is supplied by PLC controlling its setpoint (by encoder simualtion;-) b) still have not got the problem in my calculation: pi_term = ((int32_t)config.PP_Factor * (int32_t)abs(error16)); 17600=44*400 pi_term += (int32_t)((uint16_t)config.P_Factor <<8); 21440=17600+15*256=17600+3840 pi_term *= (int32_t)error16; 8576000=21440*400 pi_term >>= 8; 33500=8576000/256 pi_term += (int16_t)(config.valve_center)*scalling_factor; 47580=33500+ 55*356=33500+14080 pi_term16 >>=8; //= scalling_factor; 186=47580/256
Posted on:
@Richard G: Now you don't have any problem on calculation. 4 degree error is outside regulation range. Few lines later, result is limited to valve_max (80%) and it fully open valve.
Posted on:
a) where in the controller is the part for reducing motor movements ? b) I see - thanks ... so error16=0,4°C= 40 then ??? c) Is valve_min (30) the point where the heater sould stay cool ? d) What do you suggest - where to start to reduce the error from 0,4 to +-0,15°C. In your chart, one can see that temp over- AND undershoots the setpoint. But in my case it stays above all the time (whole night). Maybe P/PP is to small, to correct possible offsets for valve_min/center points ?!
Posted on:
ad d) // Calculate Iterm and limit integral runaway
if ((lastProcessValue!=0) && ( ((d==0) && (abs(error16)>config.temp_tolerance)) |
or should I try lowering temp_tolerance from 50 to 30 ?
Posted on:
@Richard: a) - one part for reduce movements is PI gain setting - second part is on 1.0 version line 323 here http://openhr20.svn.sourceforge.net/viewvc/openhr2... - second part (better) on actual SVN lines 317-324 http://openhr20.svn.sourceforge.net/viewvc/openhr2... b) error16 = 0.4degree = 40
// 1760=44*40 pi_term += (int32_t)((uint16_t)config.P_Factor <<8); // 5600=1760+15*256 pi_term *= (int32_t)error16; // 224000=5600*40 pi_term >>= 8; // 875=224000/256 pi_term += (int16_t)(config.valve_center)*scalling_factor; // 14955=875+ 55*256 pi_term >>= 8; // 58=14955/256 |
result is 58% but it ignore integration part like I_factor=0 c) valve_min/max are points where any change have not any effect on water flow. In reality its for example min=42/max=60, but it depend from valve to valve d) +- 0.15 is outside reality. You can't increase PP/P, it will oscillate because whole system have big "propagation delay". And it is impossible without I part (old name for this is "zero compensation") valve_center (VC) you need on point where value < CP cause cooling value > CP heating on usual situations. This setting is not critical, it is compensated by I part of controler. (note: latest code in SVN have litle improved code but it have unwanted "windup"-see to http://en.wikipedia.org/wiki/Integral_windup)
Posted on:
Richard G: you can change temp_tolerance from 50 to 30 or lower but you risk oscillations
Posted on:
Jiri: Thanks very much for the deep look inside the secrets ;-) Is there a way to set/force/fix the valve manual to a certain position. I would like to find out where the heater starts heating ??
Posted on:
Jiri: should I test with 303 or 304 ?
Posted on:
and can you pls explain function and why the value=64: valve_hysteresis; valve movement hysteresis (unit is 1/128%)
bool gt = (uint8_t)(pi_term16>>8 /*/scalling_factor*/) >= old_result; // asymetric round, ignore changes < 3/4% pi_term16 += scalling_factor/2; // prepare for round if (gt) { pi_term16 -= config.valve_hysteresis; // prepare for round } else { pi_term16 += config.valve_hysteresis; // prepare for round } pi_term16 >>= 8; // /= scalling_factor; |
Posted on:
@Richard G: You can try it on 304 or higher without problem. About valve_hysteresis: Example:
input: old_result=50% pi_term = 50.6 ; 50.8 ; 49.4; 49.2 (four examples) --------- pi_term += 0.5 (converted to decimal via scalling_factor) -> pi_term = 51.1 ; 51.3 ; 49.9 ; 49.7 pi_term -= 0.25 (for example 1;2 valve_hysteresis converted to decimal) pi_term += 0.25 (for example 3;4 valve_hysteresis converted to decimal) -> pi_term = 50.85 ; 51.05 ; 50.15 ; 49.95 pi_term16 >>= 8 is equivalent to truncate in decimal fix point format -> pi_term = 50 ; 51 ; 50 ; 49 Now it is clear that it create hysteresis +-valve_hysteresis/scalling_factor. Because it is +-, whole range must be multiplied by 2 => unit is 1/128% First 50.6 is rounded to 50, and 49.4 too |
Posted on:
Jiri: Thanks for the explanation ! 1. So the aim is: Just move valve if difference from controller is more than 0,75% RIGHT? 2. Could you please add the feature request RoomOffset as mentioned in my Email... 3. Yesterday I changed the controller back to 1.0. With 304 roomtemp. continously increased (difference was already >1°C), but 304 controller reacted just with small reductions (about 2-4% in 1,5 hours or so) 4. Do you change controller or valve factors from eeprom, when you do your tests ... if so, what are the values ?? My valve settings are: Min:50% (it opens above 57 so I set to 50 to make sure it is closing), Center 65%, Max:90%
Posted on:
1. Exactly, right 2. No, sorry. It have 2 reasons. I can't improve regulation of temperature, measured value is not and can't be equal to real temperature. For real temperature, you need more than 6 sensors and calculate average. Try it move one thermometer around a room, you will see. Second reason is flash size, we want to save almost every byte, flash is almost full. 3. try 306, its side efect of windup protection, 306 use another than 304. Not tested now. 4. I usually using default values.
Posted on:
add 2: I will add it into SVN, but with conditional compilation.
#define TEMP_COMPENSATE_OPTION 0 #if TEMP_COMPENSATE_OPTION 0 .......... #endif |
Posted on:
Thanks a lot: 306: After calibration valve stays at 0%, no matter what temp. diff is ... know bug ??
Posted on:
Richard G: it is fixed bug, please update your files from SVN
Posted on:
Jiri: Rookie question ;-) During development it would be nice to which SVN Revision e.g. 309 is running on the valve. - Why don't we have something like 1.1_309 displayed on the LCD during startup ??? - is their a revision-variable that is automatically updatet somewhere ?
Posted on:
new_valve = pid_Controller(calc_temp(temp),temp_average,valve,updateNow);
}
{
bool plus = ((new_valve == valve)?lastMovementPlus:(new_valve>valve));
if (!updateNow && (plus != lastMovementPlus)) {
CTL_allow_integration = config.I_allow_time;
}
lastMovementPlus = plus; |
explanation would be nice !!! (why only new_valve>valve)
Posted on:
and Jiri: I still have not understood your PID-controller... could you post just the formular using your variable names like pi_therm = error16*P3 + error16*P + sumError*I .... new_valve = valve_center + pi_therm*....
Posted on:
used fixed point aritmetic 3bytes-dot-1byte
pi_term = (
( error^3 ) * P3 // cubic
+ ( error * P ) // linear
+ ( sumError * I ) / 256 // integral
+ valve_center * 256 // basic zero compensation
)
result is new (valve position * 256) in %
after trim, it is fixed point 1byte-dot-1byte in %
follow rounding with hysteresis and we have new valve position
Almost standard PI controler, but with non-linear response.
-------------
"why only new_valve>valve" is wrong question, it is polarity detection
of valve change. For "plus" it must be "new_valve>valve"
I want to find protection to windup problem. This code was test and not
work what we want.
Posted on:
Jiri: perfect expplantion ;-) THX Missing in makefile: CFLAGS += $(TEMP_COMPENSATE_OPTION) Rookie question ;-) During development it would be nice to see which SVN Revision e.g. 309 is running on the valve. - Why don't we have something like 1.1_309 displayed on the LCD during startup ??? - is their a revision-variable that is automatically updatet somewhere ?
Posted on:
Revision number you can see in config.h And it is send by terminal on start. Problem is how convert SVN revision string into number for C compiler. In Linux it is not problem, on Win I don't have solution.
Posted on:
Jiri: Am I right ? 1 Every time wanted temp changes (in my case 3 times a day) the I part (sumerror) is reset - but where in the code ? 2 P + P3 error correction just have an impact of 3-5% when temp. diff is about 1°C. 3. I do not understand the code where sumerror is limited with 50*I. What is the result of Limit in % ? 4. So just I part brings us to the right valve setting, but this takes several hours .... 5. Result: Maybe I watched it wrong, but it looks like if wanted temp is changed, valve starts close to center position and the heater starts heating, even if roomtemp is already 1°C to high !!!!!!!!!!!!
Posted on:
1. It is true on version 1.0, not in current code 2. you can increase P_factor, but major problem is that you not have final "sumError" and wrong valve_center. If you increase P factor, it will increase response of valve to error, but it will probably oscilate If you really need to know what happen, please use converter from 3v3 to RS232 or usb and create log. Without log you know nothing and usualy have obly bad feeling. 3. it is 50% 4. It is normal after restart or battery change. Where is problem on normal continous functionality. 5. You made deductions, but you don't know facts. Make logs and you will see.
Posted on:
Jiri: RS232 has been/ is on plan for this weekend ;-) 1 Rev.309 I-Part: Allow integration = integration time set to 4 minmutes, if error==0 OR sign of error changes OR direction of valve movement changes... a) ==> so this means, that if there is a constant error, the error is added max 4 times (once a minute) to sumerror ? b) The max impact on PI then is 4*error*I 2 Under which conditions would you change P3 and und when P factor
Posted on:
Richard G: last SVN version 311 have completely another model of windup protection. Try it. You can enlarge P_factor to 6-12 ( default is 8 now )
Posted on:
Jiri: I'm just trying 317. I have a problem with hyperterminal. It does not catch the CR (just LineFeed)...looks like this
V:OpenHR20 17.1 Mar 5 2011 20:02:26 $Rev$
D: d5 01.01.10 12:34:23 - V: 58 I: 236
4 S: 2300 B: 2644 Is: fe00 X
D: d5 01.01.10 12:37:11 - V: 58 I: 2364 S: 2300 B: 2
644 Is: fe00
|
any idea ?
Posted on:
Richard G: Correct, code using UNIX end of lines to save flash and communication size. Please use terminal which is able accept it. I recommend putty and set it. PS: MS hyperterminal is piece of ..... except other problems it was many years unfixed bug, when you use bar to shift window contend, it change contend !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! NOTE: SVN rev 318 contain biggest change after more than year, it is not fully tested now. If you want to have rock stable code, please use release 1.0 (SVN rev 285) !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
Posted on:
Attached files:Jiri; Here is the protokoll from last night. Params of my valve:
/* 0a */ {52, 30, 0, 100}, //!< valve_min
/* 0b */ {60, 45, 0, 100}, //!< valve_center
/* 0c */ {90, 80, 0, 100}, //!< valve_max
- It took from 22:42 until 1:50 until I part starts.
- I part does not increase until 2:29, no impact on V so far
- next I increase 3:37, no impact on V
- next I increase 4:09, no impact on V
- next I increase 4:13, no impact on V
- next I increase 4:17, no impact on V
- 5:01 my encoder simulation is runnning and needs about 15s to reach
the previous S=23,0"C again.
1.??? I thought that it takes 10s after wheel stops before PID is
updated ???
- next I increase 5:05, no impact on V
...
- next I increase 6:49, 1% impact on V
Resumee:
2. It starts increasing V, neverthelsess room is 1,75°C higer then S
3. Impact of I param is week. It seems that sumerror is increasing to
slow and I param is to low.
4. V on LCD is 1% less than on COM
Posted on:
Richard G: What is your P, P3, I factors ? Why you change setting in code, you can use service menu or terminal (commands G,S) 1) it take 10sec, because wait to final setting. It is mornal if human use wheel, that it not have machine precision. You ca see it in CTL_temp_change_inc 2) again, what is P, P3, I ? 3) normaly it my valve it take 12-24 hours to find sumerror (I impact). It must be slow, you can try in rfmsrc/doc/PI_tuning what happen on big gain. I hope that 318 is faster without impact to windup (do yyou know what is it?) 4) com show wanted valve, LCD show truncated real position. In real world, I want 29, com show 29, but real position after valve stop is 28.99 -> LCD show 28. Reason is allow see motor movements on LCD in real time.
Posted on:
Jiri: PI params are standard, yes I understand windup, but 24 hours to find error is to long, because setpoint is changed more often - ad 1) This would help to prevent update during wheel action: controller.c 150: if (((PID_update_timeout == 0)
&& (PID_force_update==-1) |
) ||(PID_force_update==0)) {
- How can we prevent 2 ?
Posted on:
no 24 hours is not too long, it persist after change setpoint for remove delay, please change in CTL_temp_change_inc PID_force_update = 10; to => PID_force_update = 1;
Posted on:
Thanks Marco ! Thanks for the hints Jiri: PID_force_update = 1; forces update But we want prevent update during wheel move: if (((PID_update_timeout == 0)
&& (PID_force_update==-1) |
) ||(PID_force_update==0)) {
This prevents "normal" update (every 4 minutes) until 10s after wheel
stops !
Posted on:
Hi! How do I find the "correct" values for minimum and maximum vent position (0x0A, 0X0C)? Maybe a feature to "live-control" the valve would be nice. Chris
Posted on:
- set Max=Center= Min+1, wait until heater is cool - increase all params +1 until hater starts getting warm - set Min e.g. 5 lower and center 10-20 higer. leave max at 80
Posted on:
You don't precision values for valve_min a valve_max. It is used only as protection to not move valve to hard limits.
Posted on:
Does the adaptation which is done after mounting have any influence on the min and max values?
Posted on:
Jiri just did some redesign on that, but I think NO. Calculation in controller.c works with center position. Only I part (sumerror) can't increase when MIN/MAX are reached ... This is why I set the center closer to MIN ...
Posted on:
Jiri - do you simulate your PI ? Do you have an .xls maybe ??
Posted on:
Richard G: simulation you can find here rfmsrc/doc/PI_tuning.ods
Posted on:
Thanks Jiri, I saw that before, but there is no formula for the simulation in the Excel sheet ?? BTW: Where do I find Karims latest Version of his openHR20Suite. I only found Version 0.2.4.23954 posted on page 2 ??
Posted on:
@Richard, the last released Version V 0.2.4.23954 of openHR20Suite can be found here http://embdev.net/topic/118781#1157863, but I think, it will not be completely data compatibel. It seemed to me, that no body was interested in this program and I had to do a lot of other stuff, so I had not the time and motivation to keep it uptodate. But since I am still interested in this project, I need to look, wether I am able to compile and flash the latest Version of OpenHR20 firmware an check, what has to be modified in the Suite SW. May be I can take a look at it on next weekend.
Posted on:
Hi Karim, I have this Version runnning since last weekend. Execpt the difference in the EEProm names it seams to work. But once I had a jam on COM - no more data transfer, which just could be released by using putty to send some manual commands... The only thing, that bothers me a bit is, that I had to install .NET35. Usally nearly every PC has some .net version installed. Very often it is 2.x ... Would it be possible to parse the appropriate eeprom.h. This way one could only copy this file e.g. into the program dir and would be up to date. The second thing is that one has to configure which #defines were set ..
Posted on:
Since the program uses WPF technology, it requires .NET V>=3.0. If you want to see a flash movie, you have to install the appropriate flash player, same for Silverlight or here .NET. That is how it works and the installation is only once required. The installed .NET framework versions can be found here C:\WINDOWS\Microsoft.NET\Framework and generally you have anyway several versions on your PC. It would be possible to read the eeprom.h file but it has a very processing unfriendly format, which is errorness. It would be better, to have an xml file, which contains the required definitions and on modifications in eeprom.h, everybody could edit the changes to this xml, which will be loaded by the Suite. Different versions of the eeprom data/HR20 firmware could be handled by this method as well. But I can't promise to program that one of these days.
Posted on:
Attached files:@Karim: Would be nice ! Put your tool into trunk !!! @Jiri: My experience with 319 controller in a 15m² room during some nights with no persons in it and predifined Params (except MIN=52,CENTER=60): 1 I Part takes about 2 hours until reaction is seen on temp. Maybe I can be increased ?? 2 I think it is important to set the MIN value close to the real CLOSE of the valve, beacuse this limits I part 3 I is still increasing/decreasing even if the temp gradient has already changed (from falling to increasing or vice versa) ... 4 suggestion: Why don't we stop increasing/decreasing sumerror, as soon as the gradient of the real temp changes to the wanted direction ? 5 D part missing: In my case, the Valve runs on accu with permanent charge of 5mA via data connection. I need something, that reacts when e.g. a person enters the room or a heating source like a PC is started ... waht do xou suggest ? 6 I have no idea of what is the impact/aim of P3 - can you please explain ? 7 Regarding simulation: I saw the .ods before, but there is no formula for the simulation in the Excel sheet ?? Do you have something like that ... how are you doing it ? 8 Am I right ? On COM we don't see every move of valve, because of integer value ? Why not put valve*10 to display and COM ?
Posted on:
1. I thing not, you can just create oscilations 2. problem is that MIN value float after every calibration. And you need value below to insure close and prohibit unlimited heating 3. do you have better idea to protect to windup and allow integration if valve still in position and you have permanent offset ? 4. If you want it, please use version 1.0. Problem is, that it increase oscilations on some situations (in my case only in one room) 5. D is removed because usually we have only batteries, and it have problem with transport delay (it take more than 20 minutes till you are able to see effect when valve close) 6 regulation characteristic of valve is non linear with unknown "center". If you use big P you will get oscilations. If you use low P, you are not sufficient reaction if calculated "center" (I part) is too far for real. Therefore you need compromise, small reaction for small errors and big for big. 7. .ods contain simulation formulas, you can convert it into excel 8. COM show final position on every valve move start
Posted on:
add to 4) I was wrong. It is realy used on release 1.0. I remove it, because it not solve windup completely. Normaly you have more heat sources (ex: sun) and it can create any temperature profile independent to valve. It is replaced by another idea, but it is compatible. I plan to use longer temperature history than only previous.
Posted on:
ad4) but you agree, that a further increase after temp gradient changed leads to a unnecessary high I part ? ad6) what is the max P3 before oscillation starts, can it be increased ??? ad7) I used excel2010 to open it, but did not see any formula. You say convert ?? How ? ad8) I thought smallest move is 0,75%
Posted on:
4) right, but with side effect, it slow down integration if you have small offset to wanted temperature (ex 0.5-1 degree). 7) what is in rows P-V ? If just number please send compliment to Redmond and download OpenOffice 8) it move valve in 1% steps. You need hysteresis to inhibit move for ex from 40 to 41% if result of controller calculation is 40.49 and 40.51
Posted on:
4) but you inject one idea to my bain, thanks
Posted on:
Welcome ;-) looking forward to it ad6) what would be the max for P3 before oscillation will start ? 6a) why one doesnt use P^4 /5 then ?
Posted on:
Jiri: R320 controller.c 151 ... still missing ... see: 2011-03-06 10:54
if (((PID_update_timeout == 0)&& (PID_force_update==-1)) |
||(PID_force_update==0)) {
Please quick explain the change 319>320 ??? THX
Posted on:
Richard, I made another (shorter in flash) solution for (PID_force_update==-1) now. It is in SVN about 319>320 Basic idea is:
after wanted temperature change or after real temperature crossing wanted temperate (error from + to - and vice versa) => interator get some credit for not successful error curve direction - if abs(error[t]) >= abs(error[t-2]) then credit=credit-1 - if credit == 0 then not allow update integrator - temperature change must have same orientation like valve change in near history. Otherwise integrator is not updated. - integrator is limited on valve_min and valve_max |
real code is litle bit more complicated, it must contain more boundary conditions and it is optimised for small flash, but idea is eqal
Posted on:
THX - I will try it ad6) what would be the max for P3 before oscillation will start ? 6a) why one doesnt use P^4 /5 then ?
Posted on:
R325: e.g. Temp is to high: Some time after temp is sinking it stops integrating = OK, but then sun shines into the room and temp is increasing agein. In this case it should continue integrating - it seems that credit was already=0 at this time ?!
Posted on:
controller line 315
lastAbsError = absErr;
last2AbsError = lastAbsError;
should'nt this be the other way round ?:
last2AbsError = lastAbsError;
lastAbsError = absErr;
Posted on:
Example: D: d5 01.01.10 12:00:17 A V: 52 I: 2380 S: 1700 B: 2459 Is: 0000 D: d5 01.01.10 12:04:17 A V: 52 I: 2390 S: 1700 B: 2459 Is: 0000 D: d5 01.01.10 12:06:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: 0000 D: d5 01.01.10 12:10:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: fd60 D: d5 01.01.10 12:14:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: fac0 D: d5 01.01.10 12:18:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: f820 D: d5 01.01.10 12:22:37 M V: 56 I: 2382 S: 2300 B: 2459 Is: f820 D: d5 01.01.10 12:26:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: f580 D: d5 01.01.10 12:30:37 M V: 56 I: 2384 S: 2300 B: 2459 Is: f2e0 D: d5 01.01.10 12:34:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: f040 D: d5 01.01.10 12:38:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eda0 D: d5 01.01.10 12:42:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00 D: d5 01.01.10 12:46:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00 D: d5 01.01.10 12:50:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00 D: d5 01.01.10 12:54:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00 D: d5 01.01.10 12:58:37 M V: 55 I: 2384 S: 2300 B: 2459 Is: eb00
D: d5 01.01.10 13:02:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00 |
I think latest here credit should be set to max_credit D: d5 01.01.10 13:06:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00 D: d5 01.01.10 13:10:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00 D: d5 01.01.10 13:14:37 M V: 55 I: 2390 S: 2300 B: 2459 Is: eb00 e.g. something like: if (((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) || (error16==0)
|| (absErr>last2AbsError)) |
{ //sign of last error16 != sign of current OR error16 == 0
Posted on:
Richard G: Thanks for last2AbsError=>lastAbsError order problem. Fixed. But I can't set credit to max_credit on (absErr>last2AbsError) condition. This is exactly condition which must be "pay" from credit. Otherwise we will see windup again.
Posted on:
Prob is, that the error persists right now. Is stops about e000. The influece of I&P is to low this way. Heater keeps on heating ... room is getting hotter ... with last2error > error it would only wind up if the error is getting bigger and in this case we must do something about it !? Is 327 just the copy prob or did you have a new idea ;-)
Posted on:
maybe we can do something like
if ...|| (last2error>(error+hysteresis(optional))) { if
credit<max.credit) credit+=1
Posted on:
on one valve since 2 day (since 321) I very often get E3 after flahing. In this situations the valve head (sitting on the heater) is fully open before installation. If I set head valve manualy somewhere between open&close before installation, the error is gone ... any idea ??? old questions: ad6) what would be the max for P3 before oscillation will start ? 6a) why one doesnt use P^4 ^5 instead of p^3 ?
Posted on:
Richard G: Example1 for (absErr>last2AbsError) condition:
Wanted temperature is 18 real is 18.5 valve for this is 40% (just example) Whats happen when sun shine directly into room? Temperature will grow. This mean, that error grows. In this case (absErr>last2AbsError) is true independently to valve. You will integrate this error typicaly 2-3 hours and result is too low unreal value of integrator. Name for this is windup. |
Example2 for (last2error>(error+hysteresis(optional)) condition:
You have wanted 21, real 21 and you will change wanted to 18. Valve will closed to valve_min and temperature descends 0.3 degree/hour. When temperature drop to 19 (just example) valve will compensate temperature drop. Temperature will descent slowly because come warm air from other rooms (ex 0.1 degree/hour) But it unblock integrator limitation. Condition from example2 is true therefore integrator drops down, it will move valve back to limitation. And temperature descents more, therefore valve will compensate .... and cycle repeats. Result is unreal value of integrator, again. |
Both example situations are from real life.
Posted on:
Hi! I'm using v1.0. I too have the E3 problem in one room. I swapped the hr20 (but not the part which contains the blue wheel) without success. Now I swapped that part too. Tomorrow we will see if that helped. Next problem is in the morning when the system heats up with water temperatures up to 80 celcius. Wanted temperature is for example 16 celcius, but room temperature goes up to 19 celcius because the vent does not close fast enough. In other rooms, wanted temperature is set to 21 celcius, the room goes up do 23-25 celcius. If I change wanted temperature (even from 16 to 16,5 celcius) the vent starts to close. Idea: Whatever is being reset when doing this, it perhaps should be done as soon real temperature crosses wanted temperature? Other idea would be to add some kind of temperature prediction, so that openhr20 monitors if temperature rises and how fast it rises, and then calculate 30 minutes into the future to compensate inertia of the radiator. Chris
Posted on:
Chris: If you have E3 problem on one valve, it probably have problem with "smooth" move. Solution is simple, set faster motor movement. It is more nosily, but safe. In version 1.0 its setting "14", change it in service menu. Where you have valve and where you measure temperature? I was use controller same as in 1.0 over year, without problem. Temperature prediction would be nice. Problem is that we don't know "transfer function" for all many different valves and it is imposible implement Laplace transform (flash is too small and space is almost gone). If anybody have any idea, please feel free to do it. It is GPL code :-)
Posted on:
some update to motor speed setting info: for faster, you need LOWER number
Posted on:
Jiri I will think about it ... but my feeling is: It is better to accept windup in situations where Error grows and just block integration when error gets smaller ... Do you have explanation for this E3 phenomenon ?
On one valve since 2 day (since 321) I always get E3 after flashing when reinstalling it. In this situations the valve head (sitting on the heater) is fully open before installation. If I set head valve manualy somewhere between open&close before installation, the error is gone ... any idea ??? |
Posted on:
Richard windup is not acceptable, integrator value outside reality make slow reaction of controler (hours to start heating). Too slow and resulting error is bigger compare to "permanet error". Please accept that less than 1 degree of error is nothing compare to measure precision (+-2degree, try compare 2 identical valves) Except this you must compare it after may hour of operation when it stabilize. Another way to solve it is reset integrator after any change like in 1.0 release. But it need bigger I_factor (rel 1.0 use another scale than current SVN). Problem of this is oscilaton in some condition (real example from my one room: t<-15 degree outside make oscilation +-1degree inside with 2 hours period. valve oscilate +- 5%)
Posted on:
Attached files:OK: R327 see this log from last night - error stays ... Please comment on my E3 situation. Sometimes ADJ 1 stays longer then usual ... on this valve
Posted on:
Richard you have 0.37 degree difference ;-) And it will be better after few changes of temperature, because you will have integrator more close to reality. Calibration: "Ad 1" is delay before real real calibration start "Ad 2" open till motor slow down hard end. "Slow down" on this end in reality is almost impact. "Ad 3" close till motor is not possible keep it on wanted speed and slow down over threshold (force to continue is too big) Result is motor range in pulses. You can see it in service menu or Txx command (see to watch.c) If measured volume of impulses is <100 or >1000 it create E3 error Usual volume of pulses is around 500
Posted on:
THX: 1 but how come that ADJ 1 then sometimes stays longer in the display ?? 2 that error disapppears, if head (part mounted on heater) is adjusted between open and close before installing valve
Posted on:
Jiri: In my case E3 typical comes under the following 3 conditions: 1. If I set the haed (blue wheel) to fully open and mount the valve. E3 comes directly after ADJ_1. This sometimes also happens on other heaters/valves and seems to be a software prob. It can be cured by setting the head somewhere between fully open & close... 2. It comes directly after calibration (after ADJ_3), when the valve should move to its 1st position. 3. It comes during operation ...
I wanted to find out the cause for my E3: |
So I exchanged the motorunit (not the PCB) and the mounting head (blue wheel). E3 is still there.
Facts: |
A. It looks like theese E3 only occure, when the valve wants to start. B. It has nothing to to with "smooth move" of the motor unit, but maybe with the PCB. C. The force needed to move the valve on this heater seems to be higher. D. I am running on accu. So VCC is only 2,4-2,6V
Questions/Conclusions: |
1. Is there a timeout after motor_start that can leed to E3? 2. Is there something like a torque_limit that can leed to E3 on startup? 3. Can we give the motor more torque (boost) during start up ? 4. which eeprom parameters (e.g. light eye) also can leed to this problem, please explain ? 5. I found a lot of E3(CTL_ERR_MOTOR) in the source code. It would be easier to determine what caused E3, when we sepearate E3 into different errors like E3a, E3b,....
Posted on:
Richard G: answers to Q: 1) yes, (motor.c line 241) 2) no, it not detect torque_limit. It detect stop or slow down. 3) yes, but it have compensation to battery voltage (motor.c line 253) 4) - motor_pwm_min - minimum PWM for motor - motor_pwm_max - maximum PWM for motor - motor_end_detect_cal - define maximum time between two impulses to detect end in % of motor_speed - calibration (motor.c line 237) - motor_end_detect_run - same as previous, but for normal run - motor_speed - time between 2 impulses - simple controller keep motor in this speed - motor_speed_ctl_gain - speed controller gain - motor_pwm_max_step - speed controler max step on PWM
Posted on:
- what do you think could cause the prob ? - what steps should I try next ? - what about 5. ?
Posted on:
You can try motor_pwm_max=0xff you can try change line 241 you can try higher motor_end_detect_cal (default is 130 - you can try 200, but "touch" on the end of range will be little bit strong) you can speed up motor_speed (default is 168, you can try for ex 100) You can in debug.h "#define DEBUG_PRINT_MOTOR 1" and see serial console (recommended, but it is just numbers because speed on this line is limited) It is many choices. But I can't found where is problem because it works more than year for me without problem.
Posted on:
Jiri THX for your hints !!!!!!!!!!!!!!!!! I built in E31-E35: Usally it is this error:
if ((MOTOR_calibration_step == 0) && (MOTOR_PosMax<MOTOR_MIN_IMPULSES)) { MOTOR_calibration_step = -1; // calibration error CTL_error |= CTL_ERR_MOTOR; |
The causes are: week accu about 2,45V, new head which leeds to more torque needed
I suggest following solution: |
1. Change back motor speed
/* 15 */ {184, 184, 10, 255}, //!< motor_speed
2. Change battery compensation to 2,7V
MOTOR_pwm_set((int16_t)(((uint16_t)config.motor_pwm_max
* 256) / ((bat_average)/(2700/256))));
3. The cause for the longer adj_1 in the display could have something to
do with bat calculation ...
Anyway, do we have enough time to calculate the bat average after boot
to secure bat compensation before calibration starts ?? Sometimes I saw
wrong values over COM like 4V... It also seems to be part of the problem
...
Can we secure and validate bat calculation AND compensation
Posted on:
Only one question: are you sure to slowdown motor? 184 is bigger time for one pulse = slower
Posted on:
yes, because it is OK as long as battery is fine. I think the prob has to be cured somewhere else ;-) Just an example of wrong battery calc (accu has 2,4V): #Connection opened @ COM1, 9600, 8N1, DTR:On, RTS:Off >V V:OpenHR20 (10*16+3).( 2*16+7) Mar 14 2011 20:21:46 101 >D D: d5 01.01.10 12:13:56 A V: 52 I: 2524 S: 1700 B: 3969 Is: 0000 E:08 X >D D: d5 01.01.10 12:13:56 A V: 52 I: 2524 S: 1700 B: 3969 Is: 0000 E:08 X _____________________________________________ V:OpenHR20 (10*16+3).( 2*16+7) Mar 14 2011 20:21:46 101 D: d5 01.01.10 12:00:17 A V: 80 I: 0000 S: 1700 B: 0000 Is: 0000 D: d5 01.01.10 12:04:17 A V: 52 I: 2530 S: 1700 B: 4207 Is: 0000 E:04
Posted on:
We have enough time to calculate the bat average after boot. bat_average cant be > 0 till we have AVERAGE_LEN measures (adc.c line 92) and calibration can't start (main.c line 295)
Posted on:
how come, that we have wrong voltage calculation then ? - accu=2,4V!! V:OpenHR20 (10*16+3).( 2*16+7) Mar 14 2011 20:21:46 101 D: d5 01.01.10 12:00:17 A V: 80 I: 0000 S: 1700 B: 0000 Is: 0000 D: d5 01.01.10 12:04:17 A V: 52 I: 2530 S: 1700 B: 4207 Is: 0000 E:04 D: d5 01.01.10 12:08:17 A V: 52 I: 2530 S: 1700 B: 4203 Is: 0000 E:04 D: d5 01.01.10 12:12:17 A V: 52 I: 2530 S: 1700 B: 4198 Is: 0000 E:04 D: d5 01.01.10 12:13:05 M V: 52 I: 2530 S: 2300 B: 4240 Is: 0000 E:04 D: d5 01.01.10 12:17:05 M V: 52 I: 2529 S: 2300 B: 4292 Is: 0000 E:04
Posted on:
It must be something different. Are you sure that you don't have some parasite source of power? Usually it is 5V powered JTAG or serial converter. It you have 5V powered serial, 5V come from RXD signal to CPU. Solution is simple, add one diode (example 1N4148 or any) anode to RXD on CPU, katode to serial convertor.
Posted on:
JTAG is connected, but board has no power ... Serial comes from a MAX2232 ... I will check that ! But anyway can we validate the calculate voltage to sensible limits like 1-3,5V
Posted on:
Jiri: As most times - you were right. Seial and JTAG influence voltage calculation... BUT the situation stays confusing: - I made 3 versions ... bat. compensation with 2,6/2,7/2,8V - I flashed 2,6V = Revision 327, - disconnected everything - accu (2,45V) out, wait 10s, accu in - mount on head (heater) - AD1, E3, motor was quite slow when it tried to start - I flashed 2,7V - same procedure, E3, no acustical difference when it tried to start - I flashed 2,8V - same procedure, WORKS OK, motor faster - I flashed back 2,6V - same procedure, WORKS OK, motor as fast as at 2,8 ??????????? - I took accu out for abot 10min. - AD1, E3, motor was quite slow when it tried to start ??????? - I flashed back 2,8V - same procedure, E3, no acustical difference when it tried to start ??????? - I took accu out for about 10min. - same procedure, WORKS OK, motor faster ??????? during this test, most times I just flashed the Programm and not the EEPROM (EEsave fuse is set). - Are there any parameters stored in EEprom until calibration is done ? - Are there any variables not initialised, that may stay in RAM ? I am confused and frustrated now .. I need some fresh ideas .. pls help
Posted on:
voltage compensation is ONLY for motor start. After start it keep speed on config.motor_speed value (define time for 1 pulse)
Posted on:
Jiri: I dont understand the connection to the prob from my last post ???
Posted on:
- Maybe 1 pulse is to short that motor reaches sensible speed ... ? - but waht are your suggestions regarding the confusing E3 situation described in my post ?
Posted on:
Jiri: The Prob comes to 99% from a wrong ADC bat value. Waht did I do: Reboot over COM and imediately disconnect COM (Diode implemented) from valve:
D: d2 02.01.07 00:38:59 M V: 52 I: 2421 S: 2300 B: 3385 Is: e3f8 X D: d2 02.01.07 00:39:05 M V: 52 I: 2423 S: 2300 B: 3386 Is: e3f8 X D: d2 02.01.07 00:44:23 M V: 52 I: 2426 S: 2300 B: 3387 Is: e3f8 X BD: d2 02.01.07 00:44:56 M V: 52 I: 2430 S: 2300 B: 3391 Is: e3f8 B1324 V:OpenHR20 (10*16+3).( 2*16+7) Mar 15 2011 07:05:51 101 D: d5 01.01.10 12:00:41 A V: 80 I: 2430 S: 1700 B: 4755 Is: 0000 E:08 X D: d5 01.01.10 12:00:55 A V: 80 I: 2430 S: 1700 B: 4759 Is: 0000 E:08 X V:OpenHR20 (10*16+3).( 2*16+7) Mar 15 2011 07:05:51 101 D: d5 01.01.10 12:00:17 A V: 80 I: 0000 S: 1700 B: 0000 Is: 0000 D: d5 01.01.10 12:00:41 A V: 80 I: 2435 S: 1700 B: 4596 Is: 0000 E:08 X D: d5 01.01.10 12:01:07 A V: 80 I: 2437 S: 1700 B: 4596 Is: 0000 E:08 X D: d5 01.01.10 12:01:08 A V: 80 I: 2437 S: 1700 B: 4596 Is: 0000 E:08 X V:OpenHR20 (10*16+3).( 2*16+7) Mar 15 2011 07:05:51 101 D: d5 01.01.10 12:00:17 A V: 80 I: 0000 S: 1700 B: 0000 Is: 0000 D: d5 01.01.10 12:00:27 A V: 80 I: 2437 S: 1700 B: 3050 Is: 0000 X D: d5 01.01.10 12:00:33 A V: 80 I: 2437 S: 1700 B: 3034 Is: 0000 X D: d5 01.01.10 12:00:35 A V: 80 I: 2437 S: 1700 B: 3029 Is: 0000 X V:OpenHR20 (10*16+3).( 2*16+7) Mar 15 2011 07:05:51 101 D: d5 01.01.10 12:00:53 A V: 80 I: 2437 S: 1700 B: 4705 Is: 0000 E:08 X V:OpenHR20 (10*16+3).( 2*16+7) Mar 15 2011 07:05:51 101 IsB1324 D: d5 01.01.10 12:01:16 A V: 80 I: 2437 S: 1700 B: 4708 Is: 0000 E:08 X |
As valve thinks it has more than 4V it reduces PWM at motor start and motor does not start ... what should I try next ??
Posted on:
Hi! Replacing the electronic part or the mechanical part of the hr20 was no solution for the e3 problem. I also changed batterys. I'm now trying with lower and higher values for 14. It only happens at one radiator, so I think it's moving to heavy. Besides: It is the only rondostat which shows a voltage of 3,55V (or above, the output is limited by 8 bit + offset of 1V because I'm using my own systen to readout the serial data from the rondostats).
Posted on:
Hi Jiri, I can confirm this: I have no external voltage at my rondostat, only the two internal batteries and I'm also reading too high voltages. I do not provide any external power to the rondostates. Richard, how old are your rondostates? I bought four new ones and used only one of them, which then showed the E3 error. Then I started replacing the rondostat, but always used the new ones... never tried one of the older ones. Maybe they changed something with the hardware?
Posted on:
1. Chris do you have the wrong voltage reading all the time ? 2. When does the error occure (after AD1 = ADJ2 ?) In my case it sometimes is OK, but I did not find out the case for i so far. It might really be a Prob of the PCB. Because as I wrote I tried to exchange the motorunit, but the error stayed ! Got mine (I have 6) http://www.amazon.de/gp/product/B003URRKP8/ref=ox_... from amazon last month ... did you find a fabrication date somewhere ? 3. I attached You a Version ehich has implemented 4 different errors for E3 = E31-E34 which correspond with the different locations in the code, where E3 comes from !
Posted on:
Attached files:3. I attached You a Version which has implemented 4 different errors for E3 = E31-E34 that correspond with the different locations in the code, where E3 comes from ! All my changes in code are marked //jr Most times I get E34.
Posted on:
It looks that we have problem with motor start you can try: - change "#define MOTOR_IGNORE_IMPULSES 2" to bigger. It define number of motor pulses ignored on start to control speed. - change motor.c line "motor_timer = motor_max_time_for_impulse<<2;" to multiply by more than 4. Ex "motor_timer = motor_max_time_for_impulse<<3;" multiplies by 8 - enable "DEBUG_PRINT_MOTOR" Richard G: battery voltage measurement is one of oldest part of code. (more than 2 years) and I have not any problem with this. Please found where is problem, it can be useful for others.
Posted on:
Ex "motor_timer = motor_max_time_for_impulse<<3;" I tried that some time ago. It did not help. Prob is wrong voltage and this PWM calc: MOTOR_pwm_set (config.motor_pwm_max * 256) / ((bat_average)/(2800/256)) If valve thinks it has 4V: PWM=175, 2,4V: PWM=291(will lead to 255) Is voltage calculated with the same adc like temp ? It must have something to with the adc or something is wrong with pcb.
Posted on:
PWM value will not lead 255, see too MOTOR_pwm_set function
Posted on:
will lead to pwm_max of cause ... ;-) How many pulses are needed for 0,5% move (can be max ignored), so that we dont drive to far ?
Posted on:
1. so we should not ignore more than 5 (MOTOR_IGNORE_IMPULSES ) pulses ~ 0,5%... right ? 2. Can you pls quick explain the 6 states of task_ADC. Is noise cancelation only done for temp ( case 3: update_ring(BAT_RING_TYPE,ADC_Get_Bat_Voltage(ADCW)))
Posted on:
you can use bigger value for MOTOR_IGNORE_IMPULSES. It is only for motor speed controller, motor will be stopped on wanted position independent to this. Tip for test: use config.motor_pwm_max=config.motor_pwm_min=0xff and see whats happen AD steps: 1) (start_task_ADC) not used, just start ADC 2) battery, not used 3) battery, prepare for temperature 4) first temperature for compare 5) temperature, used only when result is same as previous, or repeat 5)
Posted on:
THX, so no noise canceling for bat. Jiri do you have any further idea (except external power) where theese wrong bat measurements can come from ...
Posted on:
Is there any chance to read the voltage directly an the valve ? (like watch...)
Posted on:
I built it into watch.c.voltage is defenitly measured wrong on this valve = same values as when connected to COM D: d5 01.01.10 22:55:16 - V: 56 I: 2534 S: 2450 B: 3255 Is: 0000 E:04 Motor when error occures: + 0aeb ae + 0767 ae + 075f ae + 0764 ae - 0a7f ae 07db ae AND of course no error when setting pwm_min=max + 029f fa + 05bb fa + 04c4 fa + 04aa fa + 04a0 fa + 049c fa + 04a0 fa + 049d fa + 0498 fa ... + 04b4 fa + 04b2 fa + 04b7 fa + 06d0 fa - 054d fa - 04ae fa - 049c fa - 04d3 fa - 04f1 fa - 0504 fa - 0502 fa - 0509 fa - 0501 fa - 050a fa ...
Posted on:
another error situation: V:OpenHR20 (10*16+3).( 2*16+7) Mar 16 2011 17:55:45 101 D: d5 01.01.10 12:00:17 A V: 80 I: 0000 S: 1700 B: 0000 Is: 0000 + 08b7 96 - 0fcd 96 and after connecting and disconnecting JTAG voltage is measured OK ????: V:OpenHR20 (10*16+3).( 2*16+7) Mar 16 2011 17:55:45 101 D: d5 01.01.10 12:00:17 A V: 80 I: 0000 S: 1700 B: 0000 Is: 0000 + 076e fa + 0501 fa + 05db fa - 0515 fa - 04b6 fa .... D: d5 01.01.10 12:00:56 A V: 80 I: 2457 S: 1700 B: 2529 Is: 0000 E:04 X After taking accus out/in voltage on valve (nothing connected) is wrong again - valve starts but stops short after: D: d5 01.01.10 12:01:17 A V: 80 I: 2457 S: 1700 B: 3428 Is: 0000 E:08 X + 05aa b9 + 0760 b9 + 06f2 b9 + 0722 b9 + 0727 c3 + 06c5 cd + 063f d5 + 05e2 d7 + 05ab d6 + 0598 d4 + 05a1 d2 + 05b7 d2 + 05c5 d2 + 05ca d2 + 05d0 d3 + 05ce d4 + 05ba d4 + 05b6 d4 + 05c2 d4 + 05c7 d4 + 05ba d4 + 05b9 d4 + 05cb d4 - 099e ba - 074f ba 080d ba
Posted on:
nice, it is definitely compensation to wrong battery voltage. I remember correct that you have Dragon? If yes, try it manualy. Without start SW: Set AD reference to VCC, input channel to BadGap reference and start measure. Result will be number representing known voltage (1.1 badgap) on unknown scale (VCC). Calculate is easy. You can compare this value to VREF pin on MCU (ADMUX must be switched to "AVCC with external capacitor at AREF pin") But this make one idea. VREF is "AVCC with external capacitor at AREF pin" If you have different (bigger capacity) on VCC, it can create problem with charge this capacitance after AD switch on (normally it is in power down state). You can try add one or more "dummy" measures before real or use code like for thermometer.
Posted on:
I repeated accu out/in noe several times and sometimes V is OK. Interesting is, that the wrong measurements also differ .... Offest is 0,5-1,5V. I did not find this phenomenon on another valve .. but I just tried reboot 5 -10 times.... 1. Jiri can you please integrate a voltage display into menu (middle button) 2. Do You have any idea to diagnose this wrong measurement and display an error ??? 3. Of Courese we could always start with MAX_PWM and it would work ... but this way the users wont find out that they might have a defect valve ...
Posted on:
you can disable battery compensation completly and use simple: MOTOR_pwm_set(config.motor_pwm_max);
Posted on:
Attached files:same thinking, but error stays hidden this way... @Jiri please enter voltage display at least with a #ifdef for me and the novice software guys ;-) with middle button @Chris: here is my "hack version" with voltage display on first watch variable and , E31-34, 5 Ignore Pulses, motor_timeout*8
Posted on:
Jiri why did you or the others implement this bat compensation ? What about 1 & 2 from last post ???
Posted on:
Battery voltage on LCD can be enabled on rev 330. change #define MENU_SHOW_BATTERY 0 to #define MENU_SHOW_BATTERY 1 I am not able detect wrong battery measurement. How? We are not known reason.
Posted on:
Good guy - THX !!!!!!!!!!!!! Jiri why did you or the others implement this bat compensation ?
Posted on:
Reason for battery voltage compensation was external power. For debug and somebody for normal functionality use 5V power. With this power it works, but motor is too strong on start. With "normal" batteries one reason is bigger noise on motor start. We can remove it or create option for this.
Posted on:
let us keep it for the moment and wait what Chrisis results are ... see you tommorow ;-) @chris: please read/answer from post 9:44 on ...
Posted on:
Attached files:@Chris: this is rev.330 with bat display (last Param on middle button) including differentiation of E3 into E31-34
Posted on:
@Jiri: It would be quite usefull, if one could choose, that the parameter menue (middle button) and the watch menues do not return automatically to main menue. This way one could watch a specific parameter without warming up the valve (by pressing the buttons all the time) ... and it would be a lot easier during testing or valve setup ... I hope to confice you ;-)
Posted on:
means .. something more professional than my quick hack: if (( kb_events & KB_EVENT_NONE_LONG ) && (menu_state<menu_home2 || menu_state>menu_home5)) BTW: A little prob i have not figured out in menue is: if I set a manual temp and enter menu_home2..5 and press AUTO/MANU button to leave this menue ... sometimes my manual set temp is back to auto again and sometimes it stays on manu - I think this has nothing to do with my change !!???
Posted on:
Jiri: 1. Regarding my prob with changing to AUTO TEMP from last post (As I am simulating the wheel with PLC, I am always on manual) Why do we change_mode in menue_homeX keyboard.c ~260 ? Is this the cause why temp is set to AUTO when pressing AUTO in this menue (sometimes) ?
if ( kb_events & KB_EVENT_AUTO ) { CTL_change_mode(CTL_CHANGE_MODE); // change mode menu_state=menu_home_no_alter; ret=true; } else if ( kb_events & KB_EVENT_AUTO_REWOKE ) { CTL_change_mode(CTL_CHANGE_MODE_REWOKE); // change mode menu_state=menu_home_no_alter; ret=true; |
why not just: menu_state = menu_home; 2. integratorBlock=6; means blocking for 6x4 minutes ?
Posted on:
1. Why not? It is just alternate content of main screen 2. agree
Posted on:
mistunderstandig?!: If I want to exit alternate menue by pressing AUTO, the wanted temp should not change, also the Mode should not change ... in my case from "23,0 MANU" to "17,0 AUTO"... in some other menues AUTO is also for EXIT without SAVE ! This is also bad for testing, because integrator start all over again ;-) BTW: The more I look into it, the more I am fascinated from the work sticking in this source code !!!
Posted on:
Hi Jiri and Richard, I'm sorry but I do not have my jtag programmer at the moment so I can't flash the rondostates right now. I just connected a logic analyzer to tx of the rondostat to see the serial output and I get this: "B: 4446". Real voltage is 2,88V... At the other rondostates, they report 2,62V to 3,34V. The one which shows 3,34V is aprox. at 2,8V too in reality. Interesting: When I used a multimeter to meassure the voltage, I caused a short circuit between vcc and ground, so the rondostat did a reset. Back in my room, where my laptop shows all rondostates, it says 255 which is <=3,55V. And: The rondostat sowed e3 after the reset.
Posted on:
ups, the last line should be: which is >=3,55V. And: The rondostat showed e3 after the reset. Btw: This is one of the newer rondostats, it still has the foil on it which protects the display against scratches...
Posted on:
Out of 4 rondostates, only one showed a voltage of 2,8V as expected. The others showed something between 3,5 to 4,4 volts.... The one with 4,4V shows E3.
Posted on:
Chris: Are you sure that you don't have other power source than batteries? (Ex: serial cable powered by 5V, JTAG, anything) You can try code from SVN. It contain EXPERIMENTAL improvement on battery measure. PS: it is strange that you measure invalid battery value. This functionality need only MCU and capacitor on VREF pin.
Posted on:
Chris an I measure the same symptoms... I have just one valve that behaves like this. Chris, when wiil you programm new code ?? Jiri: 1 mistunderstandig?!: If I want to exit alternate menue by pressing AUTO, the wanted temp should not change, also the Mode should not change ... in my case from "23,0 MANU" to "17,0 AUTO" (I am always on MANU because of my wheel simulation;-) ... in some other menues AUTO is also for EXIT without SAVE ! This is also bad for testing, because integrator start all over again ;-) BTW: The more I look into it, the more I am fascinated from the work sticking in this source code !!! 2. What about putting integrator_credit on "D" line for COM ... at least during our testings ??
Posted on:
ad2) OK?
#if DEBUG_PRINT_I_SUM
print_s_p(PSTR(" Is: "));
print_hexXXXX(sumError);
print_s_p(PSTR(" Ic: ")); //jr
print_decXXXX(CTL_interatorCredit);
#endif
3. How can I set Is after reboot manually to a certain value (necessary
during testing). Do we have a COM command or any other way ... ? Can we
use the EEprom edit mechanisem some how ??
Posted on:
Richard, I almost accept your notices. Only one difference is hex output for CTL_interatorCredit, reason is missing support for decimal numbers<0. Jiri
Posted on:
Jiri did you accept 1 & 2 ???!!! (I thought credit is only poistive ...) How can I achieve 3 ?? 4. How come - see sumerror D: d6 19.03.11 09:41:08 M V: 56 I: 2317 S: 2300 B: 2707 Is: e1f0 D: d6 19.03.11 09:45:08 M V: 56 I: 2317 S: 2300 B: 2706 Is: e168 D: d6 19.03.11 09:49:08 M V: 56 I: 2317 S: 2300 B: 2705 Is: e0e0
D: d6 19.03.11 09:53:08 M V: 55 I: 2324 S: 2300 B: 2702 Is: e020 D: d6 19.03.11 09:57:08 M V: 55 I: 2324 S: 2300 B: 2701 Is: df60 D: d6 19.03.11 10:01:08 M V: 59 I: 2324 S: 2300 B: 2694 Is: ff40 |
D: d6 19.03.11 10:05:08 M V: 59 I: 2330 S: 2300 B: 2701 Is: fe50 D: d6 19.03.11 10:09:08 M V: 59 I: 2330 S: 2300 B: 2701 Is: fd60 around 10:05 valve started calibration ??? why ? today is saturday
Posted on:
THX: just verified the changes ;-)
bat voltage display has a prob = shows only 2. instead of 2.123
LCD_PrintChar |
(bat_average/1000, 2, LCD_MODE_ON);
LCD_PrintDec(bat_average/100, 2, LCD_MODE_ON);
LCD_PrintDec(bat_average%100, 0, LCD_MODE_ON);
Jiri please stay with /100, because this way I see wether accu is
charging or discharging earlier (I charge them from PLC) THX
pls comment on 3 & 4
Posted on:
Regarding alternate and service watch from one of the last posts should no be left automatically (because we want to watch a certain parameter for a longer time ;-) menu.c 125:
} else if (( kb_events & KB_EVENT_NONE_LONG ) && ! (menu_state>=menu_home2 || menu_state<=menu_home5 || menu_state==menu_service_watch)) { |
Posted on:
@Richard: I have to wait until I get my jtag programmer back.... don't know how long it will take.... BTW: The rondostat at which I caused the short circuit keeps running into E3 error. Question: When is battery voltage meassured? For me it looks as if it is read only at startup, because that coult perhaps explain the wrong voltage (?)
Posted on:
@Jiri: There is no other power source: - At the other rondostats which are mounted at the radiators, there is an external circuit connected which captures the serial data and sends values using rfm12. It gets its power from the rondostat. So it will perhaps add capacity, but it definitly is no power source ;) - The logic analyzer is connected to gnd and tx pin, but it has high impedance inputs, no pullups and so on.
Posted on:
battery is measured quite often (<10s)...wait until you have your programmer back. there is a bat display in alternate menue already ;-)
Posted on:
batt voltage show only 2. ? For me it is correct, show 2.55. You don't need 3) it is almost equal to config.valve_center. Difference is only in units. Problem is that we don't have free flash for any useful idea. Every Sat on 10:00 is automatic recalibration. It is useful also for keep valve heath.
Posted on:
I change battery voltage in LCD back to mV without decimal point. battery voltage is measured every second. Presented value is average from last AVERAGE_LEN (= default 15) values
Posted on:
men you are fast THX "mV"
Regarding alternate and service watch from one of the last posts should
no be left automatically (because we want to watch a certain parameter
for a longer time ;-) menu.c 125: } else if (( kb_events &
KB_EVENT_NONE_LONG ) &&
! (menu_state>=menu_home2 || menu_state<=menu_home5 ||
menu_state==menu_service_watch)) {
ad3) in my case different heaters have quite different valves, so for
testing purposes it would be great to start with manual set Is by COM or
LCD. I thought during debuggin it would be quite helpfull to be able to
manipulate static variables or variables from service_watch
Posted on:
Richard, add to your sumErr log (4): I down know why, it looks strange.
Posted on:
Attached files:here it is. around 7pm, 9pm, and today 5am and 7:40 there is a temp update with same temp=23.0
Posted on:
Attached files:Jiri Bat display does not work for me with CHAR. I press middle button right after version string and DATE skip define is set ! Display shows 10:00 (no clear screen) and when first bat calc is done the left 0 looks like this - -
Posted on:
if (((CTL_error & (CTL_ERR_BATT_LOW | CTL_ERR_BATT_WARNING)) == 0) && (RTC_GetDayOfWeek()==6) && (RTC_GetHour()==10) && (RTC_GetMinute()==0)) { // every sunday 10:00AM // TODO: improve this code! // valve protection / CyCL |
6 .. then is saturday and not sunday as stated in comment ???
Posted on:
I connected a rondostat to a variable power source. When it callibrates and I change power, the motor of the rondostat gets slower or faster, but it returns to its normal speed after a very short time (a second or so). So the voltage messurment seems to work. Strange1: I set it to 3.0V, but it displays "batt". Why? Is this condition cleard automatically when voltage rises, or only at reset or button-event? Strange2: Serial Output reports a voltage of 3,06V now. Multimeter says 3,06V too (hm, very precise, it was rather cheap....) Power-Supply is set to 3,0V. => All correct. But when it was on batteries, the same rondostat showed 3,2V (serial) while real voltage was 2,8V. I set power supply to 2,8V now. Serial reports 2,87V now. I set power supplay to 3,5V, serial reports 3,5V. Connected batterys while power supply is still connected to prevent reset, then disconnected power supply. Serial shows 2,8V, real voltage is 2,8V. Still shows batt. Removed and reinserted batteries to do a reset. Real voltage is still 2,8V . Batt-Message is gone, serial output reports 3,55 or more volts. Motor speed seems to be lower and when it starts the boost is barely there. Switched on power supply (3V), batteries still in the rondostate. Serial still shows 3,55V or greater.
Posted on:
bat displays are not reversible (except reboot or #define). Once voltage droped below 2,4 bat warning comes on. Low bat is 2.0. On my defect valve I also could not reproduce the situation ... I gues if you try it several times (powerless in between each time!!) with powersupply you will get wrong readings there as well
Posted on:
- battery warning and error is not reversible by good reason. Battery on end of life usually refresh voltage without stress. In this situation is show low voltage information only when motor runs. I want to keep this information. - I fix "char" problem on voltage on LCD. Richard: You are right about mistake in comment about Saturday automatic recalibrate. Chris: I don't have any idea why batteries is measured wrong and external power supply is OK. I am not able repeat this problem. Maybe some difference on PCB? Just idea, can you compare your PCB with photos and other documentation?
Posted on:
Jiri: 339 bat display OK, but we have a : in display (before we had a .) a) Do we realy need the Highword of summerror .. it is FFFF or 0 and if it is ffff the lowword will start with f..a anyway ?? But it is cleaner code of course ;-) b) It would be quite usefull, if one could choose, that alternate menue (middle button) and watch menue do not return automatically to main menue. This way one could watch a specific parameter without warming up the valve (by pressing the buttons all the time) ... and it would be a lot easier during testing our valve setup ... I hope to convice you ;-) menu.c 125:
} else if (( kb_events & KB_EVENT_NONE_LONG ) && ! (menu_state>=menu_home2 || menu_state<=menu_home5 || menu_state==menu_service_watch)) { |
c) did you find anything in my log ?
Posted on:
":" in voltage fixed a) it could be 0x00012345 or 0xffff2345. Low word is same, but meaning is different b) I want to have automatic return to main_menu. You can create change on your sources and it will kept after "svn update" command. c) what is wrong on this log? PS: create chart in OpenOffice or Excel is sometimes useful.
Posted on:
a) What was your maxsumerror so far ? mine typ. stops at ffff a/9 b) I tried snv commands some time ago, but it doesnt work in some of my network surroundings (proxy,firewall,...), so I have to patch al my changes all the time hope to convince you at least to:
} else if (( kb_events & KB_EVENT_NONE_LONG ) #if NO_AUTORETURN_FROM_ALT_MENUES && ! (menu_state>=menu_home2 || menu_state<=menu_home5 || menu_state==menu_service_watch)) #endif { |
c) I dont understand, thought you mentioned something strange ...
Posted on:
strange is this part: D: d6 19.03.11 09:57:08 M V: 55 I: 2324 S: 2300 B: 2701 Is: df60 D: d6 19.03.11 10:01:08 M V: 59 I: 2324 S: 2300 B: 2694 Is: ff40 what happen at this time?
Posted on:
I thought sat 10:00 auto_calibration, main.c 241
if (((CTL_error & (CTL_ERR_BATT_LOW |
CTL_ERR_BATT_WARNING)) == 0)
&& (RTC_GetDayOfWeek()==6)
&& (RTC_GetHour()==10)
&& (RTC_GetMinute()==0)) {
// every saturday 10:00AM
// TODO: improve this code!
// valve protection / CyCL
sumError=0; |
sumerror=0 should not happen here ! right ? should only happen if valve is taken from head (E2)
Posted on:
1a ... I hope I may be looking forward to my bonus ;-) "#if NO_AUTORETURN_FROM_ALT_MENUES"
Posted on:
R341: Jiri, why should autocalib need new sumerror. 99 times out of 100 ;-) calib stays about the same ! This way every saturday it gets to hot or to cold at 10:00. I think giving credit is good enough !! Only if valve is taken from head (E2) we should reset sumerror ...
Posted on:
max sumError if defined on controller.c line +-319 (max inpact to valve is 50%) option NO_AUTORETURN_FROM_ALT_MENUES is added
Posted on:
Richard, Calibration is same only on same conditions. But normally last calibration is 1 week old. And it depend to battery, heater tempterature atc. But you are right, last value can be better than 0. I will create option for it.
Posted on:
THX and a beer for R342: Yes regarding impact of max 50%, but you agree that most times autocalib will bring about the same results ... so we do not need sumerror=0 here !! giving credit to adapt little changes will be good enough. (in my case 5% change mean 1-2°C more/less in the room. min/max/center are quite different on my heaters; they also have different valvetypes) Only if valve is taken from heater (E2) we should start all over again with sumerror=0
Posted on:
R343: Why not ?
#if CyCL_RESETS_sumError
sumError=0; // new calibration need found new sumError
CTL_interatorCredit=config.I_max_credit;
integratorBlock= DEFINE_INTEGRATOR_BLOCK (or eeprom)
#else
CTL_interatorCredit=config.I_max_credit;
integratorBlock= DEFINE_INTEGRATOR_BLOCK (or eeprom)
#endif
When do we need the block ? Also here ?:
if (mont_contact & KBI_MONT) {
CTL_error |= CTL_ERR_MONTAGE;
sumError=0;
Posted on:
suggestion:
#if CyCL_RESETS_sumError
sumError=0; // new calibration need found new sumError
#endif
CTL_interatorCredit=config.I_max_credit;
______controller.c
if (CTL_interatorCredit==config.I_max_credit) {
integratorBlock=DEFINE_INTEGRATOR_BLOCK (or eeprom)
if (updateNow) {
Posted on:
you mean 344 ;-) ... tommorow ... my girls are waiting ... see you
Posted on:
Jiri, I verified all the changes compared to 339:
!!! VERY VERY WELL DONE !!!
Suggestion regarding controller:
1.Your new idea from last weeks regarding I part works well. But
sometimes an offset 0,1-0,2 stays. I know that is not much ;-). My
suggestion is to give credit, if error is around 0 (instead=0). Existing
code
if (absErr >= last2AbsError) { // error can grow only limited time
will prevent growth of sumerror anyway.
An Option could be to give the "tollerance credit" just once. But this
would produce more code ;-). This is why we should try this first:if ((error16 >= 0) ? (v0 < config.valve_max) : (v0 > config.valve_min)) { if (((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) || ((absErr==last2AbsError) && (absErr<=I_0_TOLLERANCE))) { //sign of last error16 != sign of current OR abserror around 0 CTL_interatorCredit=config.I_max_credit; // give credit |
#define I_ERR_TOLLERANCE_AROUND_0 15 // unit 0,01°C. Set it quite
restrictive !
2. I suggest a define in controll.c 303:
CTL_interatorCredit-=(absErr/I_ERR_WEIGHT)+1; // max is
1200/25+1 = 49 impact of error on I part
#define I_ERR_WEIGHT 25 //impact of error on I part
Posted on:
Attached files:Hi Jiri, I logged temperature and vent position in one room to see the overheating in the morning. Here it is. Any idea what causes the wrong battery messurements? Why is is it after reset and not before with the same rondostat? Strange. Chris
Posted on:
btw: The "own sensor ic2" does not messure room temperature. You can ignore it.
Posted on:
Hi, I got my jtag programmer back and flashed rev 344 (without rfm12). I hear the initial boost of the motor (I see you disabled compensation in config.h, so wrong battery messurements should not be a problem any more?) Bat on lcd shows 3281, multimeter shows 2,89V. Csn I use rev 344 as "productive" version, or won't it work? Chris
Posted on:
I also use it with the mods from above - no prob so far
Posted on:
I took the batteries in and out several times. There was nothing else connected to the rondostat and I did not mount it. Here is the batt output: 2,8V (ok) 3,5V 4,4V 5,4V 2,8 2,9 2,9 3,1 2,9 2,9 2,9 2,9 2,9
Posted on:
Could it be a bug somewhere in the firmware (ad-init?) or a bug of the atmega itself? I don't think it is a "defect" in hardware because it occurs only sometimes and changes only on reset (not sure about this... I never watched a rondostat whith wrong messurements correct itself without reset... did you?) I habe 6 rondostats with openhr20 that work like a charm (except for the overheating problem in the morning which is in all rooms). And I have 4 rondostates which are not mounted because auf E3 problem / wrong voltage problem or wrong callibration byte so serial data is not working. (how can I correct this?)
Posted on:
I agree but have no idea how to get closer to the reason
Posted on:
Chris, comments to your values: You have externaly disabled heating and SW wan't to fix this error. Mechanism to do it is integrator (old name was "zero error compensation") Problem is that current version of windup protection not help in this situation (I will improve it later). Soloution for you is set I_Factor to 0 and set valve_center very precise manualy.
Posted on:
Chris, I have idea how to solve your problem. Please wait till tomorrow.
Posted on:
I thing that problem with regulator windup on "central heating off" can be solved on Rev345. It need tests. I have NO idea where is problem with bad battery measure. But I create some debug, please enable DEBUG_BATT_ADC in debug.h and report me result. (need SVN rev 346)
Posted on:
Jiri, men you are fast - when I was ready with patching 349, you were at 350 already. I take this for the night ;-)
Posted on:
Jiri add this to com.c ?!
#if DEBUG_PRINT_I_SUM
print_s_p(PSTR(" Is: "));
print_hexXXXX(sumError>>16);
print_hexXXXX(sumError);
print_s_p(PSTR(" Ib: ")); //jr
print_hexXX(CTL_integratorBlock);
print_s_p(PSTR(" Ic: ")); //jr
print_hexXX(CTL_interatorCredit);
print_s_p(PSTR(" Ie: ")); //jr
print_hexXX(CTL_creditExpiration);
#endif
Posted on:
Jiri could you please explain the changes regarding controller since 344
Posted on:
It s simple: - when integrator credit is empty or temperature change I compare current error with error on last change. If it isn't smaller than 1/2 change on integrator is reverted. - integrator credit have limited lifetime
Posted on:
1. OK. Isnt the aim of CTL_interatorCredit and CTL_creditExpiration the same. Both expire. The 3rd function is revert (I think its a good idea). All 3 mechanisems have the same goal = prevent windup = right ? This is why I dont understand why we need CTL_creditExpiration - pls explain? 2. When do I have to change I_ERR_WEIGHT and when I_Factor ?
Posted on:
Attached files:ad2) log from last night: Impact on I at errors <0,5°C is to low / to slow ...
Posted on:
too slow? Try create chart in excel. I can't be better. :-) We need 2 different CTL_interatorCredit - allow maximum change volume, depend to integrator change size CTL_creditExpiration - allow maximum time
Posted on:
Jiri, I nearly expected your answer ;-) ... I am perfectionist ... as you know ... But right now I have the prob, that Summeroor, Ic and Ib in bathroom is = 0 (I dont know Ie). Instead of 24 I have 26° = just P part active .. I have no log and no idea so far ... maybe the gap is too big, as that it is closed during credit/expiretime 2. When do I have to reduce I_ERR_WEIGHT and when increase I_Factor ?
Posted on:
Jiri: a. if (absErr>=(lastTempChangeErrorAbs/2)) reverts too often ... If just by chance the error is quite small we freeze wrong I part value "forever". E.g. in some of my rooms (e.g.bathroom) I have a floor heating as well. So it is not valve on its own who tries its best, doors to other rooms sometimes stay open the whole day,...). In R351 valve reverted quite often and ended up beeing controlled by P part close to center. Bathrooom has 26 instead of 24 this way. So this "one time small error" might be quite wrong, because it was produced by external influences !! Generell revert aim is to prevent wrong summerror produced by external influences (shorten the time to correct I part). So aim is, to just revert if really necessary ... Suggetsion: revert if: (absErr>=lastTempChangeErrorAbs) && (absErr>=I_REVERT_TEMP_THRESHOLD) && (lastTempChangeSumError>=I_REVERT_ERR_TRESHOLD) #define I_REVERT_TEMP_THRESHOLD 50 //unit 0,01°C, revert only if error is larger than e.g. 0,5°C. Dont go for small errors that by chance might have been produced by external influece and will be stored "forever" ! #define I_REVERT_ERR_THRESHOLD 0x1000 //revert only if sumerror has impact on valve move = do not revert on small values that have no impact on valve position. This way even wrong sumerrors will be corrected during the first periode, where external influence is gone. b. expiration credit: do we relly need this ? I understand, that aim is to stop valve during non heating periodes: If no temp change occures, I part should be frozen to stop valve from moving. This is why I would like to set it to 24hours (no tempchange a whole day) =24x60/4=360 but max is 255 ;-) c) please answer 2. from last post...
Posted on:
a) must be: .. && .. && (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD)
Posted on:
Attached files:Idea for "revert" is solve 2 situations: Ex1: you want to heat more, but central heating is switched off. Integrator will move valve. And we need detect this situation: we are not able to heat up, valve position have no effect Ex2: you need lower temperature, but temperature declines too slowly (open door, external heat source) Situation is same, any change on valve can't help. See too attachment I both situation: any integrated change of valve is invalid, because it can't have any effect ------------------------ expiration - Lets this situation: 22degrre in room, wanted temperature is 18. It take many hours to pass 20degrre and it leave valve_min position. Now valve slowly grow and follow temperature decline. Without expiration, integrator will decline valve without reason again to valve_min. expiration in other words: If valve change have not effect in defined time (default 2 hours!!!) we can't believe that measured error depend to valve position. We must have impact from another source. Maximum expiration is (255*4/60) = 17 hours Do you believe that measured effect after 17 hours is caused by valve change? ------------------------ But you are right, condition (absErr>=(lastTempChangeErrorAbs/2)) can be too strong. I will change it. (absErr>=I_REVERT_TEMP_THRESHOLD) <= bad idea, compare it mainly with Ex2, it will not work in this situation (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) <= tell me why? What is a goal? ------------------------ "When do I have to reduce I_ERR_WEIGHT and when increase I_Factor?" A: Anytime, and see whats happen. Frankly spoken, I don't know ideal setting for this. It is too new, I have only limited data (only my valves, only short time). ------------------------ Ideal solution for enable/disable integrator update is put all magic like "credit" to trash and use "regression analysis" to determine rate of valve change to temperature. It is perfect clear solution. But we have limited resources in MCU. If you enable all options on code, free space in flash is less than 0.5kB (less than 250 assembler instructions!!) This is reason why I disable program/time settings by valve wheel on wireless case. Now I have 1432bytes free flash. It make it possible. I will try create better mathematical model of valve (not just calc/excel sheet) and try press some "regression analysis" into code. But I am sure that end of heating season will be faster.
Posted on:
also today bathroom was reverted the whole day .... idea a) and b) work togehter ! ad (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) <= tell me why? This way we just do a revert if the sumerror which we take for revert has an impact on valve (the effect should be >= 1% ...) e.g. we have stored a lastTempChangeSumError=0x050 at a lastTempChangeErrorAbs=0,1°C. But those values were influenced by externel source. R351 will revert all the time 0x050 because abserr will be > lastTempChangeErrorAbs=0,1°C most time. And when the ext. source is gone abserror will get larger all the time ... As I is small 0x050 it has no impact ... and I part is OFF "forever". (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) secures that we just revert sumerrors that have a real influence (e.g. >=1%) on valve. And if this lastTempChangeSumError was wrong (because of ext. influence) it will lead to a larger error, which will not be reverted again because of my condition a) !!!!!!! I think A&B together will work for both examples, because we revert on large errors.
Posted on:
my explanation was not quite OK. b) on its own secures: Only revert values (e.g >0x1000) that have real impact. So if stored values were wrong, the error will get worse and I part will start working a) if stored values were wrong, one of the next periodes for sure will be able to reduce the error below 0,5°C(I_REVERT_TEMP_THRESHOLD) ... and reverting will stop I gave a&b a try for tommorow in bathroom
Posted on:
ad b) when I say "I part eill start working" I mean this part !
if (absErr >= last2AbsError) {
CTL_interatorCredit-=(absErr/I_ERR_WEIGHT)+1; // max is 1200/20+1 = 61
Posted on:
Richard but you compare integrated value, not change from last temperature change. It can't work. Or I understood wrong. Any chart ?
Posted on:
no chart ... log will come tommorow .... goal of a) Do not revert on small errors, this way valve can get out of REVERTING by itself (it gets out of the trap if controller controls the error to < 0,5°) If we dont limit the error REVERTING will last "forever" (e.g. if lastTempChangeErrorAbs=0), because controller cant do any better. But if the sumerror stored is wrong controller is in the trap!!) b) only revert if I part has influence on controller. small summerrors have no effect on valve position. Only P part works. Large values have real influece on position. So if wrong (large) summerror will be reverted, position will be worse then before (when the ext. source was active). This way I part "if (absErr >= last2AbsError)" will start working on this error and next time abserror will be <0,5 and reverting will stop....
Posted on:
Attached files:(absErr>=lastTempChangeErrorAbs) && (absErr>=I_REVERT_TEMP_THRESHOLD) && (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) 1. V starts with 43 (center= 58, Min=42) through P part 23.03.11 23:41:42 Ic is used up but V is 44 now: So I_Factor should be increased to at least compensate the loss on P. We should have V<42 there. Jiri we should increase I to 35 2. 24.03.11 04:03:03 Tempchange to 2300: summerror stays as Vmin is reached. room is heated up by floor heating, ... no revert was necessary > no revert done > OK
Posted on:
Attached files:another room: Vmin=52 Center=58 I set Vmin at 18:02:03 and Ifactor to 35 around 17:38
Posted on:
Attached files:bathroom during last night: Vmin=40, Center=58, I=35 heater stops heating about V=41 At the beginning valve was warmed up from my hands... I think I is still to low ?!
Posted on:
Richard, why do you set Vmin too close? This result is not surprise, controller disable integration if valve is out of range and in your case it usual situation. Except this, valve calibration depends to battery status, and with this setting is easy to see valve on Vmin and heating warming.
Posted on:
Jiri, I thought battery should not interfear, beacause we count pulses ... ? Actually I set Vmin = VheaterOFF - 4. This way I part cant "wind down". -4 was good enough so far to compensate the calibration tollerances which usally are not more than 2. If you read the bathroom logs, be aware that bathromm has floor heating, hand towel hater (with normal valve, shuts down about 26°C) and the heater controlled by hr20. And if door is opened temp slowly goes down to 24. This room is perfect for testing the reverting prob I had with R351 ;-).
Posted on:
Valve calibration depend to battery because maximum force depend too. It is simple, motor controller try to keep same speed till slow down on "close end" (Ad3 state). Problem is that maximum force depend to battery state (maximum PWM is constant). I my valves valve range is ~600pulses end to end with fresh batteries and ~480pulses with end of live batteries. (if you need exact position of valve, try to find "manual calibration" in this thread)
Posted on:
Jiri, - #define WATCH_N (10) should be (11) (values 0..0a) - why dont we start autocalibration with searching CLOSE first. This way one could manually set head to CLOSE, mount valve, valve checks that it cant go any further and store this manually set CLOSE, then valve goes to OPEN. This way we could reproduce the CLOSE position in automatic as well .. ?
Posted on:
- why dont we store the positions found during automatic calib in eeprom ?
Posted on:
- e.g. by setting MOTOR_ManuCalibration |= 0x8000 0 ... no calib, >0 ... auto, <0 ... manu
Posted on:
WATCH_N you are right, fixed Calibration starts to "OPEN" direction by few reasons: - when valve is on "CLOSE" side, force to start closing depend to valve position. I will create calibration depend to position on start salibration. - when valve is "CLOSE" side, it can be on position, where motor have not force to reach. In another word, manually you can brace stronger than motor. Where is benefit if you store automatic calibration in EEPROM? If you remove had from valve you must calibrate it anyway.
Posted on:
THX for explanation regarding calib start direction Benefit - what I am looking for: a) one would like to see, wether position ater valve install is about the same like last time. So we can be sure everything is fine. b) right now I always look at MOTOR_PosMax to see wether the number of pulses are about the same (the gap so far always was < 10 pulses, this is about 2% from 0x200 to 0x2d0 pulses on my valves. c) one thing could be to set calibration data manually
Posted on:
Attached files:Jiri, 1 I think we should give integrator credit when valve starts moving because of p part e.g.: D: d7 27.03.11 00:13:57 M V: 41 I: 2520 S: 2450 B: 2491 Is: ffffc900 Ib: 00 Ic: fd Ie: e2 D: d7 27.03.11 00:17:57 M V: 41 I: 2520 S: 2450 B: 2489 Is: ffffc900 Ib: 00 Ic: fd Ie: e1 D: d7 27.03.11 00:21:57 M V: 41 I: 2520 S: 2450 B: 2488 Is: ffffc900 Ib: 00 Ic: fd Ie: e0 D: d7 27.03.11 00:25:57 M V: 42 I: 2516 S: 2450 B: 2490 Is: ffffc900 Ib: 00 Ic: fd Ie: df D: d7 27.03.11 00:29:57 M V: 42 I: 2514 S: 2450 B: 2490 Is: ffffc900 Ib: 00 Ic: fd Ie: de D: d7 27.03.11 00:33:57 M V: 42 I: 2514 S: 2450 B: 2492 Is: ffffc900 Ib: 00 Ic: fd Ie: dd D: d7 27.03.11 00:37:57 M V: 42 I: 2514 S: 2450 B: 2488 Is: ffffc900 Ib: 00 Ic: fd Ie: dc controller.c 399:
if ((lastCTL_interatorCredit<=0) && (pi_term16!=(uint8_t)processValue)) { //give credit if p part moves valve CTL_interatorCredit=config.I_max_credit; CTL_creditExpiration=config.I_credit_expiration; } return (uint8_t)pi_term16; |
last2AbsError = lastAbsError;
lastAbsError = absErr;
lastErrorSign = (uint8_t)(error16>>8)&0x80;lastCTL_interatorCredit = CTL_interatorCredit; |
2. REVERT http://embdev.net/topic/118781?goto=2120075#2116213 (absErr>=lastTempChangeErrorAbs) && (absErr>=I_REVERT_TEMP_THRESHOLD) && (abs(lastTempChangeSumError)>=I_REVERT_ERR_TRESHOLD) works OK. see log D: d6 26.03.11 21:34:12
Posted on:
ad1) integrator_block was missing:
if ((lastCTL_interatorCredit<=0) && (pi_term16!=(uint8_t)processValue)) { //give credit if p part moves valve CTL_interatorCredit=config.I_max_credit; CTL_creditExpiration=config.I_credit_expiration; CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; //block to wait for p part impact } return (uint8_t)pi_term16; |
Posted on:
ad1)
if ((lastCTL_interatorCredit<=0) && ((uint8_t)pi_term16!=(uint8_t)processValue)) { //give credit if p part moves valve CTL_interatorCredit=config.I_max_credit; CTL_creditExpiration=config.I_credit_expiration; CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; //block to wait for p part impact } lastCTL_interatorCredit = CTL_interatorCredit; return (uint8_t)pi_term16; |
Posted on:
I think its even better to block integrator after any change of valve position caused by p part
if ((lastCTL_interatorCredit==CTL_interatorCredit) && (uint8_t)pi_term16!=(uint8_t)processValue) { CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; //block Integrator if only p moves valve if (lastCTL_interatorCredit<=0) { // if credit is expired CTL_interatorCredit = config.I_max_credit; //give new credit if p part moves valve CTL_creditExpiration = config.I_credit_expiration; } } lastCTL_interatorCredit = CTL_interatorCredit; return (uint8_t)pi_term16; |
a better position to implement blocking after P change could be line 175, but then we need something like lastSumError ...
Posted on:
I took wrong variable: instead of process_value we have to use old_result of course ...
if ((lastCTL_interatorCredit==CTL_interatorCredit) && (uint8_t)pi_term16!=old_result) { CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; //block Integrator if only p moves valve if (lastCTL_interatorCredit<=0) { // if credit is expired CTL_interatorCredit = config.I_max_credit; //give new credit if p part moves valve CTL_creditExpiration = config.I_credit_expiration; } } lastCTL_interatorCredit = CTL_interatorCredit; return (uint8_t)pi_term16; |
Posted on:
Attached files:controller.c 312 uint8_t v0 = valveHistory[0]; why dont we use old_result here ? my changes did well over the night ...also revert ... see LAST PART of log: Vmin=36 PS: I set blocking to 3 to get faster results during testing phase. credit_expiration=FF PPS: Maybe we could give credit on each P Move instead of just if credit is expired ...
Posted on:
Attached files:log from normal room (16m²) Vmin=52/54
Posted on:
Jiri, did you or others ever think about or try replacing the thick wires of the temp sensor by very thin ones to get faster temp respons ??? BTW: I am blocking integrator now after any move of valve
Posted on:
did someone ever try to move in smaller steps - is it possible to count and stop 0,5% ?
Posted on:
Attached files:hu hu ... any anwsers to my last posts would be very welcome ... the attached jpg shows R354, reverting deactivated and integrator blocked after any move of valve... as one could see in small rooms (16m²) with outside temps >10°C our actual 1% valve step is too big for me... Heating was deactivatetd in the afternoon, because of sun .. blocking I: controller.c 396
} if ((uint8_t)pi_term16!=old_result) { CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; //block Integrator on any valve move } return (uint8_t)pi_term16; |
Posted on:
1. did you or others ever think about or try replacing the thick wires of the temp sensor by very thin ones to get faster temp response ??? 2. did someone ever try to move valve in smaller steps - is it possible to count and stop 0,5% ? 2a what do I have to change to try it ? 3. in the morning I want to boost temp 1-2° as fast as possible. The actual controller is way to slow to get the childs room warm in the morning. We need something like: if the new wanted temp differs by more than e.g. 1°C from the actual setpoint we have to open/or close the valve with another algorithm and hand over to the actual controller one some time or if temp is within 0,3°C to the new temp wanted ...
Posted on:
1. Why? You don't need faster response. Frankly spoken, compare to heating response it is fast enough. 2. motor.c function MOTOR_Goto replace 100->200. But you need check all valve calculation, because after this same values can be overloaded. You must also update LCD and COM functions for correct reports. 3. It if exactly reason for P3_Factor. It is "boost" for big temperature difference.
Posted on:
Richard G, about "blocking I: controller.c 396": It is interesting idea, I will test it too.
Posted on:
Attached files:1. As heater heats up valve. the temp sensor is heated up via its wires. With thin wires, see chart 06:30 hr20_1354_110401a_thin_wire_blocking_I.jpg the impact on sensor is less. Sensor is still heated up, but just by air. This way we are closer to real room temp. Newer valves from other manufacturers have smd sensors with 0,2mm lines... 3. I implemented a boost function...quite preliminary still... just using max and min positions of valve. This is the fastest way to heat up or cool down... in the next step I will calculate boost_time depending on error.. see chart 6:10 hr20_2354_110402a_thin_wire_boost.jpg Description: if setpoint is changed and gap is larger than setpoint_diff (50=0,5°) and actual error is large enough (boost_error 30=0,3°) we start boost funtion. boost sets valve to max or min position depending on error. boost lasts for boost_time in minutes (15). boost ends earlier if actual error is less than boost_error - boost_hystereses (30-10=0,2°). During boost PID controller only calculates errors (no PID values) and integrator is blocked. eeprom.h
/* */ {50, 0, 0, 255}, //!< temp_boost_setpoint_diff, unit 0,01°C /* */ {10, 0, 0, 255}, //!< temp_boost_hystereses, unit 0,01°C /* */ {30, 0, 0, 255}, //!< temp_boost_error, unit 0,01°C /* */ {15, 0, 0, 255}, //!< temp_boost_time, minutes |
controller.c 150
if ( minute_ch && (PID_boost_timeout>0)) { //timeout in minutes (15) PID_boost_timeout--; if (PID_boost_timeout==0) { PID_force_update = 0; } } |
if (updateNow) {//jr needed in PID update, so set it later CTL_temp_wanted_last=temp; goto UPDATE_NOW; // optimize |
valveHistory[0]=new_valve;
} CTL_temp_wanted_last=temp; //jr was after line "if (updateNow) {" before |
}
COM_print_debug(0);
controller.c ~310:
if (updateNow) {
CTL_interatorCredit=config.I_max_credit;
CTL_creditExpiration=config.I_credit_expiration;
CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; // do not allow
update integrator immediately after temp change
testIntegratorRevert(lastAbsError);
lastTempChangeErrorAbs = absErr;
lastTempChangeSumError = sumError;if ((PID_boost_timeout==0) && (abs(setPoint-CTL_temp_wanted_last)>=config.temp_boost_setpoint_diff) // change of wanted temp large enough to start boost (0,5°C) && (absErr>=(int16_t)config.temp_boost_error)) { // error large enough to start boost (0,3°C) PID_boost_timeout = config.temp_boost_time; // temp_boost_time in minutes |
}
} else {
controller.c ~360:
}
lastProcessValue = processValue;
if ((PID_boost_timeout > 0) && //choose position of code, because parameters like error are calculated above (abs(error16)<=(int16_t)(config.temp_boost_error-config.temp_boost_hystereses))) { // error <= temp_boost_error-temp_boost_hystereses PID_boost_timeout=0; // end boost earlier, if error got to small (0,2°) } if (PID_boost_timeout > 0) { // boost active CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; //block Integrator if (error16>0) { return config.valve_max; //boost to max, no PID calculation } else { return config.valve_min; //boost to min, no PID calculation } |
}
if (config.I_Factor > 0) {
Posted on:
Attached files:@Chris any new ideas about bat ADCprob ?? I am having it again ...
Posted on:
looks like adc meaeures x01bb all the time. But after reset (just by programming fuses) the same value is interpreted differently:
batAD x01bb batAD x01bb D: d5 01.01.10 12:00:22 A V: 30 I: 2274 S: 1700 B: 2542 Is: 00000000 Ib: 06 Ic: 28 bo: ff E batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb D V:OpenHR20 (3*16+3).( 5*16+4) Apr 3 2011 12:33:06 101 V:OpenHR20 (3*16+3).( 5*16+4) Apr 3 2011 12:33:06 101 V:OpenHR20 (3*16+3).( 5*16+4) Apr 3 2011 12:33:06 101 batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD x01bb batAD xbat batAD x01bb D batAD x01bb batAD x01bb batAD x01bb D: d5 01.01.10 12:00:21 A V: 80 I: 0000 S: 1700 B: 0000 Is: 00000000 Ib: 06 Ic: 28 bo: ff X batAD x01bb batAD x01bb batAD x01bb D batAD x01bb D: d5 01.01.10 12:00:25 A V: 80 I: 2267 S: 1700 B: 3728 Is: 00000000 Ib: 06 Ic: 28 bo: ff E:04 X batAD x01bb |
Posted on:
@Jiri: still dont look through the ring buffer secrets ... but is it
possible that this
static void shift_ring(void) {
#if ! HW_WINDOW_DETECTION
ring_pos = (ring_pos+1) % AVERAGE_LEN;
should look like that ????
static void shift_ring(void) {
ring_pos = (ring_pos+1) % AVERAGE_LEN;
#if ! HW_WINDOW_DETECTION
Posted on:
average is definitely miscalculated: istead of 9b6 we get ee4 AV is calculated average, followed by the 15 values aof ring buffer AV0ee4 009b6 109b6 209b6 309bc 409b6 509b6 609b6 709b6 809b6 909b6 A09b6 B09b6 C09b6 D09b6 E09b6
Posted on:
Should this:
static void update_ring(uint8_t type, int16_t value) {
ring_sum[type]+=value;
better look like that:
static void update_ring(uint8_t type, int16_t value) {
ring_sum[type]+=(int32_t)value;
It looks like sum is calculated wrong.. SUm is e910 this is 18 * 09b6
SUe910
AV0f89
009b6
109b6
209b6
309b6
409b6
509b6
609b6
709b6
809b6
909b6
A09b6
B09b6
C09b6
D09b6
E09b6
Posted on:
OK so the bugs are = corrected bugs look like:
a) static uint8_t ring_used=0;
b)
static void shift_ring(void) {
ring_pos = (ring_pos+1) % AVERAGE_LEN;
#if ! HW_WINDOW_DETECTION
c)
ring_sum[type]+=(int32_t)value;
ring_sum[type]-=(int32_t)ring_buf[type][ring_pos];
if (ring_used>=AVERAGE_LEN) {
The main reason is that update_ring is called more often than shif_ring
during the phase were ring_used is less than average_len
d) Another question:
switch (++state_ADC) means präfix ++
is this OK then for noise protection:
state_ADC=3;
state_ADC=5;
Posted on:
Attached files:in attachement find next step preliminary boost function with time calculation. description http://embdev.net/topic/118781?goto=2130451#2129904
Posted on:
I found, where was battery measurement problem. Normally it call update_ring twice (one for battery, one for temperature). And shift_ring only once after measure finish. But noise cancellation loop can cause, that measurement repeats many time and next second pulse come earlier. It restart measures. It repeat update_ring without shift_ring and this situation with (ring_used<AVERAGE_LEN) create this problem. Fixed in rev 355, change is here: http://openhr20.svn.sourceforge.net/viewvc/openhr2...
Posted on:
Option BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE added http://openhr20.svn.sourceforge.net/viewvc/openhr2...
Posted on:
Option BOOST_CONTROLER_AFTER_CHANGE added. Richard, please check it (contain one small difference to your code) http://openhr20.svn.sourceforge.net/viewvc/openhr2...
Posted on:
Jiri, THX d) Another question: switch (++state_ADC) ..... ++ here means increment before operation !! is this OK then for noise protection: state_ADC=3; state_ADC=5; I will check the new code tommorow ... BTW: After 10-15 hours I had this error today .. what is the typical reason for ir ?
if (motor_timer>0) { // normal stop on wanted position if (MOTOR_calibration_step != 0) { MOTOR_calibration_step = -1; // calibration error CTL_error |= CTL_ERR_MOTOR; CTL_error_jr = 1; //jr CTL_ERR_MOTOR; |
Posted on:
(++state_ADC) is correct, next call not execute step 3(5) but 4(6) Reason for your error is overload maximum volume of pulses during calibration. (see to MOTOR_MAX_IMPULSES)
Posted on:
Battery voltage error fix was not complete. Updated.
Posted on:
"Reason for your error is overload maximum volume of pulses during calibration. (see to MOTOR_MAX_IMPULSES)" Can it be another reason, because there was no clalib sceduled after valve was installed ???? - Maybe it started calib for another reason (not saturday 10:00) - why would it do that ??? - It might have something to do with the boostfunction. It moves valve to MAX and later back to MIN ????
Posted on:
R359 THX Jiri:
1.adc I dont understand the -1, because we want to fill all 15
positions(0-14) before we calc average. ring_used runs as ring_pos from
0 to 15 !!!
With -1 we start calculating after 14 (pos=0-13) entries. So pos[14] is
still=0. This way the first calculated average will be wrong ???
if (ring_used>=AVERAGE_LEN-1) { // note for "-1", last measurement can
update ring_average
2.controller line 171 has to be moved after line 200, because
boostdedection needs temp_wanted last see line ~334
valveHistory[0]=new_valve;
line 200 } CTL_temp_wanted_last=temp; //jr was after line "if (updateNow) {" before |
}
COM_print_debug(0);
3. See last post. I still dont understand where my E3 can come from. As
I marked the different E3 errors with E31-E34, it must be the one I
posted... Why should it calibrate ? why should this gi wrong then ? Low
Voltage on a long valve move ???
Posted on:
1. It is simple. In this case, we have 15 complete measurement. In table (0-14), ring_pos=ring_used=14. But ring_used will be incremented later. It is reason to compare with 14, not 15. 2. Changed in Rev 360 3. calibration is not start after set position to min or max. I start after valve mount reboot every Sat 10:00 Never else. And see to condition for this error (MOTOR_calibration_step != 0) it means calibration on progress or calibration error before this.
Posted on:
New idea for reverting:
Build a moving average of sumerror from max. n(should last for a week or
so...e.g. 255) values. Only use an sumerror for average, if error is
small (<0,3) and stable.
Average is built only after update (typ. 1-4x per day). I need your help
on a simple idea to handle it like the temp_ring_average !!
if (updateNow) {
CTL_interatorCredit=config.I_max_credit;
CTL_creditExpiration=config.I_credit_expiration;
CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; // do not allow
update integrator immediately after temp change
testIntegratorRevert(lastAbsError);if ((absErr==lastAbsError) && (absErr<(I_ERR_TOLLERANCE_AROUND_0<<1)) //stable error & error < 0,3°C) && (average_sumerr_count<=255) ) { average_sumerr_count++; lastTempChangeSumError += (sumError-lastTempChangeSumError)/average_sumerr_count; //average of sumerrors } |
lastTempChangeErrorAbs = absErr;
Revert only is done, if the error could not be reduced by 25% and the
error is larger than 3.g. 0,3°Cstatic void testIntegratorRevert(uint16_t absErr) { if (absErr>=(lastTempChangeErrorAbs>>2*3) && absErr > (I_ERR_TOLLERANCE_AROUND_0<<1)) { // if error could not be reduced to 3/4 and Error is larger than 0,3°C // if (absErr>=(lastTempChangeErrorAbs/2)) { // revert Integrator to previous state if current error is not smaller than 1/2 of original sumError=lastTempChangeSumError; } lastTempChangeErrorAbs = 0xffff; // function can be called more time but only first is valid } |
Posted on:
Richard: first - we don't have space for average buffer (used 685 bytes (66.9% Full) but without unknown stack size on top) second - something like "stable" error not exist. See here to real data http://embdev.net/attachment/102842/1.png third - exist only one correct way. This mean make model function and use regression analysis to find unknown parameters on real time.
Posted on:
testIntegratorRevert is updated note: price of this change is 80bytes in flash (0.5% of size)
Posted on:
OK, 1. of course I am looking forward to your math model !! I know that there is no real stable error.... Actually the posted version works without ringbuffer anyway (less code). But I have to think about a better moving of the average... right now moving stops after 255 values... 2. in line 308 it was (I_ERR_TOLLERANCE_AROUND_0<<1). This way it only revert on errors >= 0,3°C ... 3. Jiri why did you solve that with so many #if #else ?? is it less code ? Because this simple change based on 359 was easier to undestand (for me;-) ...
if (updateNow) { //jr needed in PID update, so set it later CTL_temp_wanted_last=temp; goto UPDATE_NOW; // optimize } if ((PID_update_timeout == 0)) { UPDATE_NOW: PID_update_timeout = (config.PID_interval * 5); // new PID pooling uint8_t new_valve; new_valve = config.valve_max; } else { new_valve = pid_Controller(calc_temp(temp),temp_average,valveHistory[0],updateNow); } { int8_t i; #if BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE if (valveHistory[0]!=new_valve) { CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; //block Integrator if valve moves } #endif for(i=VALVE_HISTORY_LEN-1; i>0; i--) { if (updateNow || (new_valve <= config.valve_max) || (new_valve >= config.valve_min)) { // condition inside loop is stupid, but produce shorter code valveHistory[i]=new_valve; } else { valveHistory[i]=valveHistory[i-1]; } } valveHistory[0]=new_valve; } CTL_temp_wanted_last=temp; //jr was after line "if (updateNow) {" before |
Posted on:
2. ???? Where is problem ? 3. I know that it is little bit complicated. But try it and you will see difference in code size. This code is significantly smaller for BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE = 0
Posted on:
ad2) I_ERR_TOLLERANCE_AROUND_0
<<1 |
missing
Posted on:
a) I am curious why you used *2: Does <<1 not work with constants ? another C thing: b) When do we declare variables "static" in HR20 c) is an "extern" declared variable automatically "static" ? example is "lastTempChangeSumError" is static, but as I wanted it beeing sent over COM I had to declare it extern ...
Posted on:
a) *2 is better for reading. Because is is constant, it is not need optimize it for execution. b) "static" is for local only variables and function. "static" function have one more benefit, it can be linked into call point and it is nice for compiler optimization. c) if you need use variable or function outside "C" file it can't be static.
Posted on:
THX:
#if ! BOOST_CONTROLER_AFTER_CHANGE
if (updateNow) {
172 CTL_temp_wanted_last=temp; |
...
#else
if (updateNow||(PID_update_timeout == 0)) {
#endif
PID_update_timeout = (config.PID_interval * 5);
uint8_t new_valve;
if (temp>TEMP_MAX) {
new_valve = config.valve_max;
} else {
new_valve =
pid_Controller(calc_temp(temp),temp_average,valveHistory[0],updateNow);
}
187 #if BOOST_CONTROLER_AFTER_CHANGE |
188 if (updateNow) { |
189 CTL_temp_wanted_last=temp; |
}
#endif
Jiri,
a) I think line 172 (CTL_temp_wanted_last=temp;) can be at the end
=line189 in both cases... (I checked that already)
b) so we can also forget the #if from 187
c) and the if in 188 is not needed. It does not matter if
CTL_temp_wanted_last is set under any condition more often...
Posted on:
OK I clean up this code. note: price of moving "CTL_temp_wanted_last=temp;" line is 8 bytes. We has code bigger than flash already. Current code uses MANY hack to optimization.
Posted on:
Jiri you can also keep it, your decision, I can live with it, Then just delete the if from line 188...
Posted on:
THX Jiri R362: Program: 13398 bytes (81.8% Full) Data: 485 bytes (47.4% Full) EEPROM: 392 bytes (76.6% Full) R363: Program: 13392 bytes (81.7% Full)
Posted on:
Jiri, I had this E31 error again - please comment on this When I mounted the valve it was nearly fully open (12 pulses) .. when the error came up it was fully closed (i nearly could not move it any further by hand) Values when E31 came up: MOTOR_PosMax=12 MOTOR_PosAct=fde9 MOTOR_PosOvershoot=1 MOTOR_counter=23b The next time calib was OK: MOTOR_PosMax=2c6
Posted on:
R363 with RFM and normal "wheel" settings
Program: 16022 bytes (97.8% Full) Data: 690 bytes (67.4% Full) EEPROM: 400 bytes (78.1% Full) |
but with CTL_temp_wanted_last=temp; like previous versions
Program: 16014 bytes (97.7% Full) |
16022 means 362bytes free and it is less than 181 AVR machine instructions. Not nice.
Posted on:
I think we could save some bytes, because with I_ERR_TOLLERANCE_AROUND_0
we have covered this good enough ...
if ((error16 >= 0) ? (old_result < config.valve_max) : (old_result >
config.valve_min)) {if ( // ((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) || //sign of last error16 != sign of current |
((absErr==lastAbsError) && (absErr<=I_ERR_TOLLERANCE_AROUND_0)))
{ //abserror around 0
and please set the error variables to an invalid value and they have to
be different
please comment on my E31 from above
Posted on:
the post timed out... and please set the error variables to an invalid value and they have to be different: static uint16_t lastAbsError = 0xFF; //set invalid static uint16_t last2AbsError= 0xFE; //set invalid and different to lastAbsError
Posted on:
E31 means here ?
if (motor_timer>0) { // normal stop on wanted position
if (MOTOR_calibration_step != 0) {
MOTOR_calibration_step = -1; // calibration error
CTL_error |= CTL_ERR_MOTOR;
}
|
Strange. MOTOR_PosMax-MOTOR_PosAct = 552[dec] But mininum posion for this error is (MOTOR_PosMax-MOTOR_MAX_IMPULSES) = -982 = 0xFC2A And this position was not reach. Motor stops in 2 conditions: - reach to final positon (not happen) - motor slow down or stop mechanicaly, but in this condition is motor_timer==0 This mean, that it can't be this error, or we have some bug in code. what was in motor_diag (trace variable 0x05)
Posted on:
if (motor_timer>0) { // normal stop on wanted position
if (MOTOR_calibration_step != 0) {
MOTOR_calibration_step = -1; // calibration error
CTL_error |= CTL_ERR_MOTOR;
CTL_error_jr = 1; //jr CTL_ERR_MOTOR;
menu.c ...E35 is spare} else if (CTL_error & CTL_ERR_MOTOR) { if (CTL_error_jr==1) { LCD_PrintStringID(LCD_STRING_E31,LCD_MODE_ON); } else if (CTL_error_jr==2) { LCD_PrintStringID(LCD_STRING_E32,LCD_MODE_ON); } else if (CTL_error_jr==3) { LCD_PrintStringID(LCD_STRING_E33,LCD_MODE_ON); } else if (CTL_error_jr==4) { LCD_PrintStringID(LCD_STRING_E34,LCD_MODE_ON); } else if (CTL_error_jr==5) { LCD_PrintStringID(LCD_STRING_E35,LCD_MODE_ON); } } else if (CTL_error & CTL_ERR_BATT_WARNING) { |
LCD.c... in any language
{32,14, 3, 1}, //!< " E31" LCD_STRING_E31
{32,14, 3, 2}, //!< " E32" LCD_STRING_E32
{32,14, 3, 3}, //!< " E33" LCD_STRING_E33
{32,14, 3, 4}, //!< " E34" LCD_STRING_E34
{32,14, 3, 5}, //!< " E35" LCD_STRING_E35
{32,14, 4,32}, //!< " E4 " LCD_STRING_E4
it is this code position for sure 99,99% ... I used the motor diag watch
for something else ;-)
it seems like it happens only after I flashed a new programm and had the
batteries out ... can this be a trace ??
Posted on:
I just tried to dismount, batteries out/in, remount 5 times ... no error
Posted on:
when calib goes OK. motor_diag on this valve runs typ at 5c0 and at the close position it is 784
Posted on:
I have 4 different error messsages for the 4 different code lines of E3
(E31-E34 see last posts)
E31:
if (motor_timer>0) { // normal stop on wanted position
if (MOTOR_calibration_step != 0) {
MOTOR_calibration_step = -1; // calibration error
CTL_error |= CTL_ERR_MOTOR;CTL_error_jr = 1; //jr CTL_ERR_MOTOR E3(1) |
...menu.c
} else if (CTL_error & CTL_ERR_MOTOR) {if (CTL_error_jr==1) { LCD_PrintStringID(LCD_STRING_E31,LCD_MODE_ON); |
Any idea how I can reproduce the prob. ??
Posted on:
see to my post from 2011-04-08 16:51
Posted on:
1. I think we could save some bytes, because with
I_ERR_TOLLERANCE_AROUND_0
we have covered the sign change as well ... delete highlighted line
if ((error16 >= 0) ? (old_result < config.valve_max) : (old_result >
config.valve_min)) {
if (// ((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) || //sign of last error16 != sign of current |
((absErr==lastAbsError) && (absErr<=I_ERR_TOLLERANCE_AROUND_0))) {
//abserror around 0
2. please initialize the error variables with an invalid
value and they have to be different:static uint16_t lastAbsError = 0xFF; //set invalid static uint16_t last2AbsError= 0xFE; //set invalid and different to lastAbsError |
3. I use a moving average for reverting ... this way the problem of
short periodes (some days, depending on I_SUMERR_CHANGE_WEIGHT ) with no
heating looks quite well ...
if (updateNow) {
CTL_interatorCredit=config.I_max_credit;
CTL_creditExpiration=config.I_credit_expiration;
CTL_integratorBlock=DEFINE_INTEGRATOR_BLOCK; // do not allow
update integrator immediately after temp change
testIntegratorRevert(lastAbsError);
if ((lastAbsError==last2AbsError) &&
(lastAbsError<(I_ERR_TOLLERANCE_AROUND_0*2))) {//stable error & error <
0,3°C) lastTempChangeSumError += (sumError-lastTempChangeSumError)/I_SUMERR_CHANGE_WEIGHT;
//imapct of SumErr changes on lastSummError, averaging for integrator revert |
}
lastTempChangeErrorAbs = absErr;
// lastTempChangeSumError = sumError;
#define I_SUMERR_CHANGE_WEIGHT 10 // impact on lastSumError which is
used for reverting
Posted on:
1) I thing that it is not covered, this is reason : (absErr==last2AbsError). See here http://embdev.net/attachment/102842/1.png Except this I thing that zero cross is better than something with(absErr==last2AbsError) 2) You are right, it is best practice. But because situation in flash space is critical, I will use it only if it really needed. I thing, that 0 not make any problem. 3) Why? You don't need make any average from stable value. If this value is not almost stable, something is wrong. We need solve causation, not mask result.
Posted on:
ad1) (absErr==last2AbsError) this prevents, that we give credit, if
temperature rushes up/down = ext. influence. In your example I guess it
was P part and not integrator moving the valve. So a fast change of sign
should not be handled by I-part and a slow change is covered by
"dedection around 0"... I live quite well for a while without the sign
dedection, but loosened the restriction (absErr==last2AbsError) to
(absErr==lastAbsError)...
ad2) well, directly after boot, temp is updated and comparisons like
this go wrong then.. but I can live with that ... your decison...
if ((lastAbsError==last2AbsError) &&
(lastAbsError<(I_ERR_TOLLERANCE_AROUND_0*2))) {//stable error & error <
0,3°C)
// && (average_sumerr_count<255) ) {
ad3) Because right now - in times where heating is deactivated temporary
by high outside temps during day or night ... the actual code
lastTempChangeSumError = sumError;
produces more wrong reactions (I-parts) than a continous averaging:
lastTempChangeSumError +=
(sumError-lastTempChangeSumError)/I_SUMERR_CHANGE_WEIGHT; // weight
e.g.=10
I thik this is a compromise (with liitle code) until we find a better
(math) solution for revert
Posted on:
Attached files:here is a quick status from my side which includes: NO_AUTORETURN_FROM_ALT_MENUES=-DNO_AUTORETURN_FROM_ALT_MENUES=1 BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE=-DBLOCK_INTEGRATOR_AFTER_VALVE_CHANGE=1 BOOST_CONTROLER_AFTER_CHANGE=-DBOOST_CONTROLER_AFTER_CHANGE=1 and a modified code for reverting (posted above, value Isl in the chart) Valve MAX=80, MIN=CENTER=52, Credit_expiration=255
Posted on:
Attached files:I changed MAX to 96 around 13:00, 80% did not open the valve wide enough. This way boost function works more effective.. room gets warmer about 0,7° within 1 hour ... during this valve reverted SumError=Is (vlack line) to lastSumError=Isl (moving average with 10% impact of SumError ... see black dotted line) Heating was OFF from 22:00-4:30..
Posted on:
Attached files:@Jiri: I found some bugs in my code (BOOST) and deleted unnecessary EEprom variables ... Could you please integrate the changes from OpenHR20_R363_mod110417.zip in a new revision ... THX
Posted on:
Attached files:Jiri: I mailed the changes to you... as your mailbox seems to be full I add the .zip here ...
Posted on:
Also my last MAil returned .. so I post the changes here: The files are zipped in my last post ;-)
com.c 309 print_s_p(PSTR(" bo: ")); //jr print_hexXX(PID_boost_timeout); print_s_p(PSTR(" Iac ")); //jr print_hexXX(average_sumerr_count); print_s_p(PSTR(" Isl ")); print_hexXXXX(lastTempChangeSumError>>16); //jr print_hexXXXX(lastTempChangeSumError); //jr controller.c: 60: #if BOOST_CONTROLER_AFTER_CHANGE uint8_t PID_boost_timeout; //boost timout in minutes uint8_t PID_boost; //boost value, either valve max or min #endif 183: cosmetic: CTL_integratorBlock=CTL_INTEGRATOR_BLOCK; //block Integrator if valve moves 248: PID_boost_timeout = 0; //to disable boost change mode, then change setpoint and change back mode 271: static uint16_t lastAbsError = 0xFF; //set invalid static uint16_t last2AbsError= 0xFE; //set invalid and different to lastAbsError 290: static uint16_t lastTempChangeErrorAbs=0xffff; int32_t lastTempChangeSumError=0; uint8_t average_sumerr_count=0; // counting # of averages, just for diagnosis purposes 296: just comment: // if error could not be reduced to 3/4 and Error is larger than I_ERR_TOLLERANCE_AROUND_0*2 °C 320: CTL_integratorBlock=CTL_INTEGRATOR_BLOCK; // do not allow update integrator immediately after temp change testIntegratorRevert(lastAbsError); if ((lastAbsError==last2AbsError) && (lastAbsError<(I_ERR_TOLLERANCE_AROUND_0*2))) {//stable error & error < 0,3°C) average_sumerr_count++; //just for diagnosis, how often do we average lastTempChangeSumError += (sumError-lastTempChangeSumError)/I_SUMERR_CHANGE_WEIGHT; //imapct of SumErr changes on lastSummError, averaging for integrator revert } lastTempChangeErrorAbs = absErr; // lastTempChangeSumError = sumError; #if BOOST_CONTROLER_AFTER_CHANGE PID_boost_timeout = 0; if (absErr>=(int16_t)config.temp_boost_error) { // error large enough to start boost (0,3°C) if (error16 >= 0) { PID_boost = config.valve_max; PID_boost_timeout = config.temp_boost_time_heat; } else { PID_boost = config.valve_min; PID_boost_timeout = config.temp_boost_time_cool; } PID_boost_timeout = (uint8_t)(MIN(255,abs(error16)/10*(int16_t)PID_boost_timeout/CTL_BOOST_TEMPCHANGE)); //boosttime=error/10(0,1°C)*time/CTL_BOOST_TEMPCHANGE(0,5°C) } 340: this prevents, that we give credit, if temperature rushes up/down = ext. influence. In your posted example I guess it was P part and not integrator moving the valve. So a fast change of sign should not be handled by I-part and a slow change is covered by "dedection around 0"... I live quite well for a while without the sign dedection if ( // ((lastErrorSign != ((uint8_t)(error16>>8)&0x80))) || //sign of last error16 != sign of current ((absErr==last2AbsError) && (absErr<=I_ERR_TOLLERANCE_AROUND_0))) { //abserror around 0 with slow change CTL_interatorCredit=config.I_max_credit; 370: #if BOOST_CONTROLER_AFTER_CHANGE if (PID_boost_timeout > 0) { CTL_integratorBlock=CTL_INTEGRATOR_BLOCK; //block Integrator CTL_creditExpiration=config.I_credit_expiration; return PID_boost; //return valve_MAX or MIN } #endif eeprom.h: ~100: #if BOOST_CONTROLER_AFTER_CHANGE /* */ uint8_t temp_boost_error; /* */ uint8_t temp_boost_time_cool; /* */ uint8_t temp_boost_time_heat; #endif ~250: #if BOOST_CONTROLER_AFTER_CHANGE /* */ {30, 30, 10, 255}, //!< temp_boost_error,start boost if error to new setpoint is larger than this,unit0,01°C /* */ {64, 64, 0, 255}, //!< temp_boost_time_cool, minutes boost should last during heat up, if error = CTL_BOOST_TEMP_CHANGE(0,5°C) /* */ {48, 48, 0, 255}, //!< temp_boost_time_heat, minutes boost should last during cool down, if error = CTL_BOOST_TEMP_CHANGE(0,5°C) #endif controller.h ~63: #define CTL_INTEGRATOR_BLOCK 6 //jr was=6 #define I_ERR_TOLLERANCE_AROUND_0 15 // unit 0,01°C. Set it quite restrictive ! #define I_ERR_WEIGHT 25 //impact of error on I part #define I_SUMERR_CHANGE_WEIGHT 10 //imapct of SumErr changes on lastSummError, averaging for integrator revert #define CTL_BOOST_TEMPCHANGE 5 //unit 0,1°C, estimated change of temp during boosttime, for calculating boost time 80: extern uint8_t PID_boost_timeout; extern uint8_t CTL_creditExpiration; extern int32_t lastTempChangeSumError; extern uint8_t average_sumerr_count; motor.c: 111 CTL_integratorBlock=CTL_INTEGRATOR_BLOCK; watch.c: /* 00 */ ((uint16_t) &sumError) + B16, /* 01 */ ((uint16_t) &CTL_integratorBlock) + B8, /* 02 */ ((uint16_t) &CTL_interatorCredit)+ B8, /* 03 */ ((uint16_t) &PID_boost_timeout)+ B8, /* 04 */ ((uint16_t) &average_sumerr_count) + B8, /* 05 */ ((uint16_t) &lastTempChangeSumError) + B16, /* 06 */ ((uint16_t) &MOTOR_PosMax) + B16, //12 az:2c6 bad:22c /* 07 */ ((uint16_t) &MOTOR_PosAct) + B16, //fde9 az:18d bad:c4 /* 08 */ ((uint16_t) &MOTOR_PosOvershoot) + B8, //1 #if DEBUG_MOTOR_COUNTER /* 09 */ ((uint16_t) &MOTOR_counter) + B16, //23b /* 04 */ ((uint16_t) &motor_diag) + B16, // /* 0a */ ((uint16_t) &MOTOR_counter)+ 2 + B16, //0 #endif |
Posted on:
Hi Jiri - are you still there ? - I would like to finish up, before the summer comes and I forget everything .... ;-) RE: "Can you generate "diff" file? (for ex in TortoiseSVN)" Sorry, no know how in those things ... a) either you instruct me or b) I could also edit the changes into R363 files and send you those ..
Posted on:
I am still here. But I am too busy on another tasks till end of may.
Posted on:
Ok .. then we'll clean up end of May/June ... BR .. Richard
Posted on:
Need some help. I receive following error msg during compiling: **** Build of configuration Debug for project HR20 **** make all Building file: ../src/lcd.c Invoking: AVR Compiler avr-gcc -Wall -g2 -gstabs -O0 -fpack-struct -fshort-enums -std=gnu99 -funsigned-char -funsigned-bitfields -mmcu=atmega169p -DF_CPU=1000000UL -MMD -MP -MF"src/lcd.d" -MT"src/lcd.d" -c -o "src/lcd.o" "../src/lcd.c" ../src/lcd.c: In function 'LCD_HourBarBitmap': ../src/lcd.c:627: error: r28 cannot be used in asm here ../src/lcd.c:627: error: r29 cannot be used in asm here make: *** [src/lcd.o] Error 1 **** Build Finished **** lcd.c revison: 192 how can i fix this error(s)?
Posted on:
transis: Which compiler? Please try WinAVR-20100110.
Posted on:
it is already the compiler: WinAVR-20100110 !
Posted on:
I've also tried to compile it with AVR-Studio 5 => same compiler error(s): Error 1 r28 cannot be used in asm here ...\lcd.c 627 1 OpenHR20 Error 2 r29 cannot be used in asm here ...\lcd.c 627 1 OpenHR20
Posted on:
Error:
../src/lcd.c:627: error: r28 cannot be used in asm here
../src/lcd.c:627: error: r29 cannot be used in asm here
Fix-Proposal:
modify line in lcd.c
from:
: "r14", "r15", "r16", "r28","r29", "r30", "r31"
to:
: "r14", "r15", "r16", "r30", "r31"
after this modification the compilaton will pass.
What are the side-effects of this fix?
(I'm not so experienced with assembler coding ...)
Posted on:
Problem is that this line not create any code. It just inform compiler optimizer about used registers. If you remove it, ASM code rewrite this registers and compiler will not know it. It will fail. Are you sure that in compilation you use WinAVR-20100110 ? It is tested with this without problem.
Posted on:
yes, i am sure. It is the compiler "WinAVR-20100110"! But this errors was also reported by AVR-Studio5. I think it is not a compiler specific problem.
Posted on:
Hello again, I've tried to compile it with "release" setup, and it is compiling.(Before, it was in the "debug" setup => with this setup i got the above mentioned errors.) are the compiling options wrong? release-setup: avr-gcc -Wall -Os ... debug-setup: avr-gcc -Wall -g2 -gstabs -O0 ...
Posted on:
After some further testing.... The parameter/option "-O0" raise this errors. When i am select one of the other optimization levels "-O1..3" the errors are not occured. Can someone explain me this crazy behavior?
Posted on:
Hi, -O0 means no optimization, so it seems that without optimization these two registers are necessary for the C code and then the compiler complains.
Posted on:
sounds plausible. ;-) What will be the workaround/fix (is it a bug?) Why this error was only reported/seen by me (i think the compilers with same options should report same errors...)?
Posted on:
I any way, compile it for debug with -O0 have not solution. Simply before code will be too big for only 16kB flash.
Posted on:
jdobry wrote: > I am still here. But I am too busy on another tasks till end of may. Hi Jiri, hope you have/had a good summer ... can we continue to integrate the changes from post http://embdev.net/topic/118781#2153401 BR Richard
Posted on:
@ Richard G.: I review this changes, and it is not possible use as is. It contain many other changes that only core. It is not encapsulated into ifdef. And I has not time to rewrite it. Please send me it as "patch", or I must say sorry for this moment. I have some urgent concern to solve. Jiri
Posted on:
Jiri, what you mean with patch ? example please
Posted on:
Richard G: Howto create patch 1) tortoise SVN http://tortoisesvn.net/docs/release/TortoiseSVN_en... 2) commandline: http://ariejan.net/2007/07/03/how-to-create-and-ap...
Posted on:
Hi! I flashed 7 rondostates with the firmware of 29.8.2011. It seems to me that the vent does not open, even if the room is too cold. Example: Temperature is 18,7, wantet temperature is 20, Vent is about 55-60%. (max vent position 96, min position 30). Maybe I have to set min position to a higher value, because the vent closes at about 45%? Chris
Posted on:
Hi, I plan to buy RFM12(x) modules to use with HR20E. What are the correct types to use? Currently I prefer: RFM12 for MASTER (because it is specified for 5V) RFM12B for all (Rondostat-) slaves (because it is specified for 3,3V). What frequency should be used: 433MHz vs. 868MHz? What types are supported by current existing SW? (I didn't find any switch in source code to choose B-Type or 433/868MHz) Thank you for some useful suggestions. -Holger
Posted on:
Attached files:I want use some HR20 as central control. Temperatures are measured externally. To to this i have extended the firmware: 1. Improved input operation in com.c 2. Serial Bus mode Ixx enables the communication with ID=xx all other devices are silent. 3. Override measured themperature via Oxxxx 4. Debug prints free RAM With 2. i have an problem. Variable 0x27 holds the bus id but i cannot change this. 0x27 is allays set to 0xff By the way: 5. i can communicate only with 1200 baud when i set COM_BAUD_RATE to 1140 on higher speed i receive no correct characters. 6. the hr20 prints 22.6°C while an DS1820 messures 24.87°C 7. i have changed the boot loader to fastboot. With lboot i can flash with 115200 baud
Posted on:
@Holger T.: I use 868MHz modules. RFM12B is improved version of RFM12. I recomend new. @Frank: Thanks for patch I will try it later. add 5) see to http://atmel.com/dyn/resources/prod_documents/doc2555.pdf add 6) HR20 use only cheap thermistor. But you can calibrate it in EEPROM add 7) I don't use bootloader. Reason is some temporary problems with flash space and in this case, every byte is needed.
Posted on:
Attached files:Hi Jiri, as wanted here is the Tortoise SVN patch... Only those chenges are relevant: http://embdev.net/topic/118781?page=4#2153401 Explanations start here http://embdev.net/topic/118781?page=4#2140184
Posted on:
Attached files:I have written an r/c clock calibration code. I uses no timers other than rtc and no interrupts. I thin this code is good enough to call it periodically to avoid communication problems while voltage or temperature is changing.
Posted on:
Jiri, you remember I also had calibration errors last year.... again this year on different valve.. It is the error from the else part (my ident CTL_error_jr = 2)
if (MOTOR_ManuCalibration==0) {
if (a >= MOTOR_MIN_IMPULSES) {
MOTOR_ManuCalibration = a;
eeprom_config_save((uint16_t)(&config.MOTOR_ManuCalibration_L)-(uint16_t)(&config));
eeprom_config_save((uint16_t)(&config.MOTOR_ManuCalibration_H)-(uint16_t)(&config));
MOTOR_calibration_step = 0;
} else {
MOTOR_calibration_step = -1; // calibration error
CTL_error |= CTL_ERR_MOTOR;
CTL_error_jr = 2; //jr CTL_ERR_MOTOR;
|
MOTOR_PosMax 47, MOTOR_PosAct 47, MOTOR_PosOvershoot 2, MOTOR_counter 5E6, motor_diag 779 How it happens: 1 I pressed a button and got E2 (valve not mounted, maybe I pressed to hard ;-) 2 I took valve off 3 I set the heater valve head manually near full open 4 put valve back on 5 valve starts adapting and stops with the error on full open position I took it off again and repeated from 3. Same error again ... Then I took battery out and repeated from 3. No more error !
Posted on:
Hi Jiri, I too experienced a E3 error and could not find any reason for it, but it could be because I used empty batteries. With current version, I have 2 main problems: 1: The window open function still triggers randomly, for example if the central heating goes out for a few minutes and there is a slight drop in temperature. I tried different eeprom settings to disable the window open detection, but it still triggers. 2: With default settings, valve is always around 50%. Our water temperature is only high enough to reach wanted temperatures, but only if vents are at about 90%. So I increased the value for valve-center. Problem is that valve is opend or closed with a too flat curve. For example, when wanted temperature is 20 and real temperature is 21, valve only closes a little bit, which is not enough. I think I have to change impact of P-Part of the controller? Chris
Posted on:
Hi all, I've been reading this, and the other German thread (through google translate), along with the documents referenced in those, but still have some questions. I currently have one HR20 and one HomExpert HR20Style. As soon as I get everything working I will purchase 7 more HR20Style (since they're cheaper than the original HR20.) My goal is to power and control the thermostats over wiring already present for this purpose. What I need to do is to set the desired temperature, and read the actual temperature. Reading the valve state would be a plus. I now have the HR20 hooked up (it's SW 204), and can read the information it sends me (fe.: "K: 0b1 [0x0D][0x0A]>") I cannot successfully send it any commands, I always get the message "Error in command[0x0D][0x0A]>" After a while any commands I send it are ignored. (I assume the device has gone to sleep.) I have not found a way to wake it up. Apparently all this is because the information I'm using concerns the protocol of an earlier hardware version (with a NEC chip instead of the Atmel AVR mine has?) I have not found a protocol specification for the SW 204 specifically. Is it possible to control the SW 204 in the same way as the earlier edition? If so, could someone point me to the correct protocol specification? If not, then I assume I will need to flash the HR20 with OpenHR20? I have a ICSP programmer, but as I understand it I cannot use this unless I actually open up the HR20 and solder some extra wires to it? So I've ordered a cheap AVR JTAG ICE from ebay (I figure I'll be able to use it later for other purposes anyway, even if I don't need it after all.) If I'm correct so far, these would be the steps required to flash the HR20? * I will not be able to connect the JTAG connector directly to the HR20 and will need to make some wires to connect the right pins to the JTAG connector. * I will then use avrdude (I do not have any Windows) to upload the file hr20.bin to the HR20 using the AVR JTAG ICE. * Afterwards, I can use the OpenHR20 protocol to accomplish my goal. I've checked out the svn repo, and have also downloaded the v1.0 zipfile. I see no .bin files inside the svn repo. Is the zipfile's original_sww/hr20.bin the file I need, or would you recommend (considering my goal) to compile one from the latest svn source instead? If I need to compile a bin file, could you tell me how to do this? My C knowledge is very limited, so the correct avr-gcc (if that is the correct application?) command line would be very helpful. All the thanks, Bernard Kerckenaere
Posted on:
Bernard K: - serial protocol for original SW 204 is unknown. - I don't known if HR20 style contain same HW as HR20. Please check it ane tell us results. - You are right ICSP can't be used without open valve and soldering. - connector on HR20 have't same layout like AVR JTAG, you will need special cable. - I am not using Windows too. You need "avr-gcc" package. On actual source directory simple start "make". I recommend do it in "rfmsrc" directory and result hex files will be on "bin" - Here is TESTED avrdude commands. You will probably need both in same order. Without first is impossible rewrite EEPROM.
avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -U hfuse:w:0x19:m avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -e -U flash:w:hr20.hex -U eeprom:w:hr20.eep -U hfuse:w:0x11:m |
Posted on:
update: for compile under linux you need "gcc-avr" and "avr-libc"
Posted on:
Attached files:@Jiri, @Bernard I have flashd without soldering. All ISP pins are on the connector and under the tree keys. The display can be easy removed from battery side. With fastboot http://www.mikrocontroller.net/articles/AVR_Bootlo... the new firmware can be flashd via serial cable. This is my modified Makefile:
--- Makefile.orig 2011-09-29 10:50:21.000000000 +0200 +++ Makefile 2011-09-29 11:02:07.015224003 +0200 @@ -37,7 +37,7 @@ # MCU = attiny85 # MCU = atmega2560 # MCU = atmega1281 -MCU = atmega8 +MCU = atmega169p # Name of the Atmel defs file for the actual MCU. # @@ -50,16 +50,16 @@ # files" and unzip it in the same directory as this Makefile. # # Examples (select one of them or add your own): -# ATMEL_INC = m168def.inc +ATMEL_INC = m169def.inc # ATMEL_INC=m64def.inc # ATMEL_INC=tn85def.inc # ATMEL_INC = m2560def.inc # ATMEL_INC = m1281def.inc -ATMEL_INC = m8def.inc +#ATMEL_INC = m8def.inc # Processor frequency. The value is not critical: #F_CPU = 14745600 -F_CPU = 8000000 +F_CPU = 4000000 # AVR Studio 4.10 requires dwarf-2. # gdb runs better with stabs @@ -68,11 +68,11 @@ # Define the Tx and Rx lines here. Set both groups to the same for # one wire mode: -STX_PORT = PORTD -STX = PD1 +STX_PORT = PORTE +STX = PE1 -SRX_PORT = PORTD -SRX = PD0 +SRX_PORT = PORTE +SRX = PE0 ####### End user presets ###################### |
This is my avrdude call. You need the EEPROM image from OpenHR20
sudo avrdude -c usbtiny -p m169 -u \
-U flash:w:bootload.hex \
-U eeprom:w:../OpenHR20/openhr20/trunk/source/hr20.eep \
-U efuse:w:0xfd:m \
-U hfuse:w:0x94:m \
-U lfuse:w:0xe2:m |
Posted on:
I am sorry, in avrdude commands I write invalid hfuse. Here is correct:
avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -U hfuse:w:0x99:m avrdude -p m169 -c jtag1 -P /dev/ttyUSB0 -e -U flash:w:hr20.hex -U eeprom:w:hr20.eep -U hfuse:w:0x91:m |
Posted on:
Thank you very much for all the information, I really appreciate it! I'll wait for my JTAG programmer to arrive (it's on its way, and looks to be a bit easier to use than ISP), and will then try and verify whether I can flash and get the sought after results on both the HR20 and the HR20Style. Again thank you!
Posted on:
Richard G: your patch file "richard363_111008.patch" is not possible apply to fresh 363 revision. You probably made same mistake.
Posted on:
Jiri: I thought it might be a good idea to just include the files with major changes. Otherwise you will also get beautifiing stuff ... do you want them all ?
Posted on:
Hi! Did anybody consider adding 1-wire connectivity yet? (Axel_5 mentioned something in other threads but no details.) This could use the one free pin in the connector (PE2 I think). No need for Hardware adaptions. The device could mimic multiple "standard" 1-wire devices: - a temperature sensor (RTC value) - ADC (valve target position) - EEPROM (non-volatile config) - RAM (current state) perhaps even: - switch/PIO (for buttons) but this would possibly be missed when polling is intentionally slow. User interface would need the possibility to configure the address. I'm thinking of semi-autonomous operation - current target mode and timetable are uploaded regularly, temperature values are centrally logged. Full "slave mode", just using the temperature sensor, the valve actor and the wheel and buttons for user requests and doing the rest centrally would also be possible. I plan to implement this, but would like to hear your thoughts.
Posted on:
I got the first HR20-E flashed with JTAG last night. I'm very impressed. So thanks. Now, my question, assuming this is the right forum for this... I also got an HR-25 (http://www.homexpertbyhoneywell.com/en-DE/Products...) which has a very, very similar PCB to the HR-20. It has a MEGA329P on board and a fancier LCD and only a couple of extra tracks/vias that I can spot. I'm tempted to get more of these instead for the nicer LCD and bigger code space. Before I go reinventing wheels, has the OpenHR20 code been ported to this, the LCD mapped out etc.? i.e. has anyone done work already on supporting the HR25?
Posted on:
>Did anybody consider adding 1-wire connectivity yet?
I can upload my code tonight.
However I have forked this a long time ago, so maybe it is quite
difficult to merge this in the current branch.
Basically the temperature can be read as a simple 1-wire temperature
sensor, target temperature can be set. The value of the valve can also
be read.
However power consumption is quite high as I have removed all sleep
modes as the device is always powered through the cable. Also the
timetable is removed as this is now done by the central controller.
Best regards
Axel
Posted on:
@Axel Laufenberg: If you want store your code into repository please contact me on jdobry-at-centrum-dot-cz and send me your account name from sourceforge. Is it based on trunk(I will not make improvements) or rfmsrc (recomended)? If it is encapsulated to "ifdef" preprocessor you can add this into current code. Otherwise please create new branch in repository.
Posted on:
Attached files:Sorry, I do not have time right now to add to the repository, I just spent some time to translate most of the stuff into English. And I recognized that I used a version from 2008, so I guess this does not have too much in common with the current version. Actually only the attached files are affected. The main.c only gets the additional function to assign the values received and transmitted from/to the onewire interface and gets the sleep mode disabled. motor.c is changed because the external interrupt is used. This now has to handle also the 1-wire edge handling. The file onewire.c handles the timing for the onewire. I just recognised that the ISR is in the code twice, once within the motor.c and once in the onewire.c. Actually it is only used in motor.c as otherwise the interrupt routine may be too slow. Actually you should be aware that the AVR needs to be clocked at 8 Mhz, otherwise it is too slow to handle the onewire timing. I tried to document as good as possible, so it should be no problem to add this to the code. If I find the time I can try to make this all a bit nicer and merge it with the repository, but .... So I hope this is in any case helpful to somebody, if you have questions please feel free to ask. Axel
Posted on:
@Axel: Wow, thanks a lot - mostly what I hoped for. It's a pity that it will need to run on 8MHz. The code looks good and well documented too (and I have no problem with the german parts ;-) ). @Axel&Jiri: When I have this running (which still might take me a few weeks), I'll try to integrate it with the current version and into the repository. Maybe I can even invest some of the effort saved into thinking a bit more about the 1-wire-bootloader :-). Rupert
Posted on:
Attached files:I have got the LCD working on the HR25. It seems to work fine. I'll have to wait until the RFM12s arrive before testing further. See https://sites.google.com/site/slangey/misc/honeywell-hr25 for some more details including pictures of the board. I've done the changes against rfmsrc and it touches the Makefile, lcd.c/.h and rs232_485.c/.h. I would appreciate if someone could please review and give comments before (hopefully) getting this in to svn? Bruce.
Posted on:
Bruce_a: I made fast review and looks OK. Committed into revision 364. PS: I made only small fix (compilation need remove one space in rfmsrc/OpenHR20/Makefile) and modify rfmsrc/Makefile to create new target platform files. It looks that it can support hardware window detection and RFM without any additional changes. But I am not create target files for this because I can't test it.
Posted on:
Is there any technical difference between HR20 and HR25 than CPU and display? There is at least little space left in the 169 flash so it might make sense to replace the CPU and take the HR25 SW-version. Cheers, Knut
Posted on:
Hi Knut, It would appear just to be a CPU/LCD difference. Amtel's migration docs suggest not much interesting has changed. The code would need just one more target to specify the new cpu correctly. Be aware that the cheap JTAG programmer I got off ebay doesn't program the 329 :( (see the link in previous post). So I'm thinking RFM12b & serial bootloader... and/or replacing the JTAG pins on the side with ISP ones.
Posted on:
Hi All, I've been watching this thread for a while now, and have taken the plunge and purchased an HR20. Could someone advise what is the best lowcost JTAG programmer to get started with for the HR20. Cheers Stuart
Posted on:
I ordered this one: New AVR USB Emulator debugger programmer JTAG ICE+Protecter for US $10,90 Ebay-Artikel Nr. 200667489423
Posted on:
Thanks for the info. Is anyone using linux to do development work & programming ? This would be my preferred environment.
Posted on:
I do. See Jiri Dobry's posts of 2011-11-01 for some information on how to go about creating and flashing the necessary file.
Posted on:
Bernard, thanks. Out of interest what sort of USB device does your programmer appear as, is it FTDI based ?
Posted on:
I haven't received mine yet, but according to the documentation it's CP2102-based, not FT232. That said, CP2102 support is part of the usb-serial driver nowadays, so I don't foresee any problems there.
Posted on:
Jiri Dobry:
I keep getting these messages:
avrdude: Device signature = 0xffffff
avrdude: Yikes! Invalid device signature.
Double check connections and try again, or use -F to override
this check.
And when I try it with -F, I get this after setting the fuse:
avrdude: jtagmkI_initialize(): warning: OCDEN fuse not programmed,
single-byte EEPROM updates not possible
avrdude: AVR device initialized and ready to accept instructions
Reading | ################################################## | 100%
0.04s
avrdude: Device signature = 0xffffff
avrdude: Yikes! Invalid device signature.
avrdude: Expected signature for ATMEGA169 is 1E 94 05
avrdude: reading input file "0x99"
avrdude: writing hfuse (1 bytes):
Writing | ################################################## | 100%
0.01s
avrdude: 1 bytes of hfuse written
avrdude: verifying hfuse memory against 0x99:
avrdude: load data hfuse data from input file 0x99:
avrdude: input file 0x99 contains 1 bytes
avrdude: reading on-chip hfuse data:
Reading | | 0%
0.00savrdude: jtagmkI_read_byte(): timeout/error communicating with
programmer (resp )
and this after flashing:
avrdude: jtagmkI_initialize(): warning: OCDEN fuse not programmed,
single-byte EEPROM updates not possible
avrdude: AVR device initialized and ready to accept instructions
Reading | ################################################## | 100%
0.04s
avrdude: Device signature = 0xffffff
avrdude: Yikes! Invalid device signature.
avrdude: Expected signature for ATMEGA169 is 1E 94 05
avrdude: erasing chip
avrdude: jtagmkI_initialize(): warning: OCDEN fuse not programmed,
single-byte EEPROM updates not possible
avrdude: reading input file "hr20.hex"
avrdude: input file hr20.hex auto detected as Intel Hex
avrdude: writing flash (12842 bytes):
Writing | ################################################## | 100%
2.93s
avrdude: 12842 bytes of flash written
avrdude: verifying flash memory against hr20.hex:
avrdude: load data flash data from input file hr20.hex:
avrdude: input file hr20.hex auto detected as Intel Hex
avrdude: input file hr20.hex contains 12842 bytes
avrdude: reading on-chip flash data:
Reading | ################################################## | 100%
3.13s
avrdude: verifying ...
avrdude: verification error, first mismatch at byte 0x0000
0x14 != 0xff
avrdude: verification error; content mismatch
avrdude: safemode: Fuses OK
avrdude done. Thank you.
I've connected the device as follows:
With the debug port on the HR20, seeing it with the controls on top and
the valve connector on the left:
bat [rx] tdo tms rst
gnd tdi [tx] tck [pe2]
I've connected to the jtag device (as seen from the end of the cable
with the thick part on bottom):
gnd - rst bat gnd
tdi - tms tdo tck
I've made sure that the correct wires from the hr20 are going to the
jtag device (using the above for the hr20, and the silkscreen on the
jtag device), and I've checked the cable I made from one end to the
other for both shorts and breaks, and everything seems fine to me.
Have I got some of the connections wrong?
StuartP, this is how my ubuntu 11.10 sees the device:
[161812.004460] usb 5-2: new full speed USB device number 2 using
uhci_hcd
[161812.643212] usbcore: registered new interface driver usbserial
[161812.643229] USB Serial support registered for generic
[161812.643276] usbcore: registered new interface driver
usbserial_generic
[161812.643279] usbserial: USB Serial Driver core
[161812.663934] USB Serial support registered for cp210x
[161812.663975] cp210x 5-2:1.0: cp210x converter detected
[161812.772084] usb 5-2: reset full speed USB device number 2 using
uhci_hcd
[161812.977264] usb 5-2: cp210x converter now attached to ttyUSB0
[161812.977284] usbcore: registered new interface driver cp210x
[161812.977286] cp210x: v0.09:Silicon Labs CP210x RS232 serial adaptor
driver
Posted on:
>> avrdude: Device signature = 0xffffff This means that you have not connection or JTAG programmer is broken, AVR chip broken, JTAG is disabled in AVR fuses (it can be done by SPI programmer) MOST probably version is that you have some problem on wires. Your pinuot in text looks fine. You can compare it openhr20.svn.sourceforge.net/viewvc/openhr20/trunk/doc/steckerbelegung/steckerbelegung.jpg JTAG pinout is here http://mdfly.com/images/Wireless/JTAGlayout.jpg Are you sure that you not rotate/mirror some connector. I mean swap pin 1-5 5 or 1-2 or rotate some pinout 180deg ?
Posted on:
Bernard, did you also check with TDI and TDO crossed?
Posted on:
I just tried crossing TDI and TDO, but I'm getting the same result. How should they be connected in fact? TDI of HR20 to TDI of JTAG (according to the pinout in the jpgs Jiri posted), or crossed? I'm sure everything is correct as it should be, I've measured the cable through from one end, where it connects to the pins on the programmer, to the other, where it goes onto the pins of the HR20. The pinouts I've followed are the same as in the jpegs as well, and match the silkscreen on my programmer. And as soon as I connect the cable to the HR20, the second light on the programmer goes on, where the voltage protector gets its power from the Batt pin on the HR20, so if that pin is correct, the orientation should be correct too. There isn't anything I need to do on the HR20 itself before I can start using the jtag right? I've put in batteries, and now it's blinking 2005, and I haven't done anything else to it since. I'll play with it some more tomorrow morning. If you would have any other tips on what I could try, I'm all ears. I'm quite new to this, so I don't have a lot of experience in debugging errors like these. Thank you for all the help so far!
Posted on:
Ah, one more thing: I've also taken off the valve part, so I could put batteries inside, and I haven't put that part back on. I don't know if that makes any difference, but I figure I'd better mention this as well.
Posted on:
Basically, the programmer and the target shall be a daisy chain regarding TDO and TDI, but it depends on the description of the programmer: whether it is its output for or the target's output. I am using an AVR Dragon with AVR Studio on Win7. The batteries have to be inserted. When reading and programming, the Dragon resets the HR20, so it does not matter in which state the HR20 is...
Posted on:
is there anywhere a discription, how to make the hex-file to programm the hr20? i find in the repository nothing how to do it. i want to programm the hr20 by SPI, i habe no jtag-programmer, i know that i have to sold some cables to the pcb, but its ok for me. but i need the hex-file thx a lot Jan
Posted on:
ok, i found something in the rfmsrc/openhr20 folder. do i need any of these files to make the hex-file? i also found the description in branches/before_refactoring/doc, this can i use to make the hex-file or?
Posted on:
Marco: considering these pinouts: http://openhr20.svn.sourceforge.net/viewvc/openhr2... http://mdfly.com/images/Wireless/JTAGlayout.jpg Should I connect TDI to TDI or TDO?
Posted on:
Compilation: it simple, just start "make" command (command line) JTAG: right connection is TDI-TDI and TDO-TDO
Posted on:
jiri, where do i find the "make" file? is it from avr studio or gcc? i only programmed with bascom till today.
Posted on:
"make" is "GNU make" And it is added to winavr (not only) It using "Makefile" to compile project.
Posted on:
Hi all, I'm new here and want to control my home using the HR20-style and a simple and modified Moduline 15, to turn on and off the central heating unit. I've (almost) read the entire thread, but still have some questions: 1. Have anybody used the HR20-Style instead of the 'old' HR20? 2. Does anybody know if the RFM12B works and if it's the same soldering? (http://jeelabs.com/products/rfm12b) 3. Is there some step by step manual how to do the complete modification? It's pretty hard to find all the steps in this thread... If not, I will try to make one and ask for your verification. Thanks in advance! BTW There are a lot of posts about the master board. I use a lot of these: http://jeelabs.com/products/jeenode (Quite cheap and easy to use) Justin
Posted on:
Justin M: add 1) It is not confirmed. But it looks like same HW as HR20. add 2) You can use RFM12B. Compare to RFM12 you can omit pullup on the FSK/DATA/nFFS pin. I have RFM12B also. add 3) maybe later. I know about http://jeelabs.com/products/jeenode It can be used as "master" in this application. But I use my own HW because jeenode does not support JTAG ICE to debug. Current SW is not Arduino compatible, this mean that you will need small modification in source code (pinouts and change mega 32 to mega328) and write it into this HW raw without Arduino.
Posted on:
jbodry: Thanks for the quick reply! 1) I will order one and try and post my findings 2) Just SW wise I suppose? 3) I will work on this and post it back By "Current SW is not Arduino compatible" you mean the Master side? Because I have my own protocol for wireless transfer (For any type of device like lamps, switches, dimmers, temp sensors and so on), just have to change the slave source... I ordered an AVR Programmer (http://www.ebay.nl/itm/ws/eBayISAPI.dll?ViewItem&i...), but that doesn't work?
Posted on:
Correction after checking the 'schaltplan': 2) Just SW wise I suppose? should be 2) One less to solder ;-)
Posted on:
2) SW (rfmsrc) is same. You will have less soldering. This programmer will work. But it allow only programing, no debug. And you will need use wires, because external connector not contain SPI but only JTAG. For JTAG programming (HR20 connector) you need JTAG AVR tool. Cheapest is this Ebay-Artikel Nr. 160685211172 But it is clone of obsolete HW. This means, that support only "old school" AVRs. Ex: support mega169p used on HR20 but not almost same mega329 on HR25.
Posted on:
Justin: I use HR20 style home expert with jiris soft for about a year now. Electronics are 100% kompatible (I did not want to write "the same" because I never had the old hr20)
Posted on:
I also did a search for "AVR JTAG" on ebay, but I'm not sure if that's the right way to find the right programmer. Where to look for? Is this one also possible for example: Ebay-Artikel Nr. 190531487895
Posted on:
Richard G. wrote: > Justin: I use HR20 style home expert with jiris soft for about a year > now. Electronics are 100% kompatible (I did not want to write "the same" > because I never had the old hr20) Thanks for your reply! I will also put this in the 'manual' ;-)
Posted on:
jdobry wrote: > For JTAG programming (HR20 connector) you need JTAG AVR tool. Cheapest > is this > Ebay-Artikel Nr. 160685211172 > But it is clone of obsolete HW. This means, that support only "old > school" AVRs. Ex: support mega169p used on HR20 but not almost same > mega329 on HR25. I've modified a similar cheap JTAG programmer to allow it to program the 329 used by the HR25. Obviously I didn't buy a Dragon due to my community spirit and not my cheapness. ;) I've taken AVRminiProg and hacked it to use the serial port. The changes are truly awful but get the job done. It allows JTAG programming the HR25s in the same way as HR20s. The original ebay programmer I've got had unprotected code, allowing that to be read and flashed back to restore its former abilities. More details at https://sites.google.com/site/slangey/misc/honeywe... . It may be a different one from the on Jiri posted, but likely similar at HW layer at least. Bruce PS I was surprised the stick code was unprotected. I gave up trying to disassemble and change the code for the 329... perhaps others have more strength and/or better disassemblers.
Posted on:
Hi everybody, I accidentally destroyed the temperature sensor on my HR20, can anybody on this list help me get the data for the sensor, so I can get a replacement? Thanks in advance.
Posted on:
Hi Flemming, there is a document about the analysis of the HR20 hardware [1] which contains information about the AD converter input from the thermal resistor (table 9). The thermal resistor is in series with R3, so it should be possible to calculate the data of the thermal resistor. [1] http://openhr20.svn.sourceforge.net/viewvc/openhr2...
Posted on:
HI Stan, Thanks. Based on the document I found the following: The Analysis.pdf documents the sensor to be an NTC thermistor, and lists a lot of measurements at various temperatures. From this I got the following: 25 degr.C = 397 counts, probably measured with a 10 bit ADC. Supply to AVR: 3.3V Thus, 397 counts equals 1.279 volt. From the schematic and tracing the images of the board, I found: The R3 SMD Resistor is marked 43C, suggests it's 27k4, 0.5% Calculation: (See this as a simple schematic, top to button) 3.3V 27k4 = 2.021V = 73.74uA 1.279V NTC = NTC Nom. calculated to 17k34 0V Closest match to the calculated NTC value seems to be Vashay/dale 01M1752SPC3 or 01C1752SPC3, both have 17k5 as nominel value. However, both are not easily available, and costs as much as a new HR20 or HR25. :-(
Posted on:
Jiri: If I want to increase p part, In which situation should I use p or p3
Posted on:
Hi Stan, Yes, almost that price (20 EUR without shipping). But looking around I did find some cheaper alternatives, such as at Mauser, where the price goes down to only about US$ 5 (without shipping)... but the ETA lead time is at least 7 weeks. I'm considering if it won't be quicker to use a more readily available (and cheaper) NTC and simply rewrite the conversion table. Well... time will tell...
Posted on:
I've been trying to solve my problem with the support people of the ebay seller I got the programmer off (hongkong_electronics, they've all been extremely helpful and really friendly by the way, I'd strongly recommend them.) There's one more question he'd like me to answer before he ships me a new programmer, to which I don't know the answer myself: "if your target board has set the JTAGEN fuse" Is this something I would've needed to do myself, or would the HR20 have come with this fuse set? Thanks for all the help!
Posted on:
Ah, just to clarify, in order to make sure the problem isn't with avrdude, I've been trying to get my programmer to work using avrstudio 4 on a windows xp virtual machine. I know with avrdude I'm first supposed to set a fuse, but as far as I can tell, I can't set one with avrstudio until I've actually connected to the device first? (Which is the point where I'm getting the invalid device id error.) Or is there something I could do in avrstudio before trying to connect?
Posted on:
Hi Bernard, reading the device signature does definitely work without setting a fuse first. Surely JTAG is enabled in stock HR20.
Posted on:
Attached files:Does anybody has any experience using AVR Studio 5? Version 4 can't be installed in Windows 7.... I would love to use a linux version (avr dude), but to make sure the fuses are right, I would like to set this in Windows first. (using the screen captures) I found most settings in AVR Studio 5 to set the fuses and lock bits, but not the Advanced and Board settings. Maybe these are only available when the board is connected? One other question: Should the cable be connected like picture 904 or like 847? Thanks!
Posted on:
Justin M.: AVR JTAG cable can't be connected to HR20 directly. It have different pinout, therefore you need cable with special wiring. See to my previous posts. About AVR Studio 5: By my mean it is worst decision from Atmel. It can't work with JTAGICE1. It is based on MSVisualStudio = vendor lock. Atmel buy key winavr developer to this project = factical end of winavr project.
Posted on:
Justin M. wrote: > Does anybody has any experience using AVR Studio 5? Version 4 can't be > installed in Windows 7.... Hmm, I have AVR Studio 4.18 installed on Win7 32 bit, and I use an AVR Dragon for JTAG.
Posted on:
Has anyone already ported or have hints for porting the master code to a Nanode RF? (arduino (328p) + ethernet + RFM12b)
Posted on:
Marco G. wrote: > Justin M. wrote: >> Does anybody has any experience using AVR Studio 5? Version 4 can't be >> installed in Windows 7.... > > Hmm, I have AVR Studio 4.18 installed on Win7 32 bit, and I use an AVR > Dragon for JTAG. I've got it installed also. (Win7 64 bit) You'll have to wait for ages, but it will finish in the end...
Posted on:
Attached files:Hi, three days ago I flashed the last 3 HR20 with HW window detection, now all 6 valves use a reed contact. That works great :) But 2 valves (Kinderzimmer + Schlafzimmer) now have problems to reach the wanted temp, see the attached pictures. Is that the same effect Richard has seen? Wohnzimmer for example is working, even I flashed it the same day with same software and EEPROM. Both failing valves have fresh batteries, and I tried to remount them several times. To which position do I have to turn the blue part before mounting? Near 0% or near 100%? This is my setup:
#define MENU_SHOW_BATTERY 0 #define MOTOR_COMPENSATE_BATTERY 0 #define NO_AUTORETURN_FROM_ALT_MENUES 0 #define MENUES_AUTOBROWSE 1 #define CALIBRATION_RESETS_sumError 0 #endif #define BLOCK_INTEGRATOR_AFTER_VALVE_CHANGE 0 #define BOOST_CONTROLER_AFTER_CHANGE 0 #define CONFIG_ENABLE_D 0 |
Posted on:
Hi! I have the same problem like it can be seen in "Kinderzimmer.png". So I increased P_Factor (06) and P3_Factor (05) to both 0x50 and now I come close to wanted temperature. But of course there is much more vent movement and oscillating now, because a small change in temperature can case the vent to to a change of 30%... What about the following idea: If temperature is far away from wanted temperatur (1 or 2 °C too high or too low) open or close valve completely to speed up heat up or cool down. Chris
Posted on:
"If temperature is far away from wanted temperatur" It is exactly why we have "P3" regulator. In other words if we have difference 1 degree = 100 in 0.01 units. impact = P*100 + P3*100*100*100 = P*100 + P3*1000000 P3 impact can be stopped by valve limitation very easily.
Posted on:
After rising the I_Part to 0x50 (might not need to be so high) it is fine :)
Posted on:
Attached files:Can anyone confirm this wiring? (Well, drawing in the first place :-) ) (NC == NOT CONNECTED I guess) Thanks!
Posted on:
Just a short update. I got the HR20 flashed. My problem was that the power supplied by the HR20's batteries was insufficient for the programmer. After hooking up the V+ of the programmer to an external lab power supply, all started working fine. It still complains about the OCDEN fuse, and the verification still fails, but the HR20 is now running OpenHR20, so all is fine as far as I'm concerned :) Thanks for all the help!
Posted on:
Jiri Dobry wrote: > "If temperature is far away from wanted temperatur" > It is exactly why we have "P3" regulator. In other words if we have > difference 1 degree = 100 in 0.01 units. > > impact = P*100 + P3*100*100*100 = P*100 + P3*1000000 > > P3 impact can be stopped by valve limitation very easily. Sorry still do not catch it - If I want to increase p part, In which situation should I use p or p3
Posted on:
P and P3 are used always. Difference is in dependency to error value (difference between wanted and real temp). P is linear, P3 is cubic.
Posted on:
hi at all, i'm developing my own firmware for the HR20 and i have some questions about to save power. my HR20 is currently running in POWERSAVE mode and it needs 330uA current. In POWERDOWN mode it will need 110uA but with LCD not working, it will work in POWERSAVE mode. in which mode are you running the HR20? and do you have some ideas for me for to save more power? thank you very much Jan
Posted on:
Problem on power save / power down modes on HR20 is internal pull-ups. For encoder. It have 2 lines, and only one have external big pull-up. This line can be used as interrupt source. Second need pullup in MCU. But in must be enabled only during read. Otherwise depending to encoder position this pull-up it can have more current that complete MCU. For sleep modes in source you can see to http://openhr20.svn.sourceforge.net/viewvc/openhr2... lines 136-145 It yse both modes idle/sleep dependig to situation. Sleep is prefferred, but for serial communication, high precision timer or AD conversion I need clock = Idle mode. PS: why you will write complete new code? Current code is under GPL = you can use it and add what you need.
Posted on:
but with idle or sleep, the lcd dosn't work, damn. but thank you for the tip to disable the pullups, and i made every unused input to an output, now i have a consumption of 283uA. did you have measured yours HR20 current consumption? and how do you initialize the lcd controller, like in the analysis of the HR20 document? what interrupt do you use, to wake up the mega169. timer2? PS: i write my own fw, because i have an existing system here in my house that consists of temp.sensors and an main-heater-ecu, which are using the rfm12 to communicate, and now i want to integrate the HR20 into this system.
Posted on:
I have 30-40uA with LCD. For wakeup I use T2 owerflow, T2 compare (for timers), pinchange from encoder and pinchange from buttons. PS: You can use this code and rewrite only communication protocol. This project use rfm12b also.
Posted on:
but the problem is, i programm in bascom and i have no knowledge in programming in C. and i've tested all powermodes, my min. consumption is 280uA. i use the timer2 overflow too for waking up the processor. but in powerdown mode, the timer is disabled, and for that, the processor didn't wake up from sleepmode. you have 30...40uA in powersave/idle mode??? Jan
Posted on:
good morning jdobry, i have tested some different lcd-init.parameters, and i can decrease the consumption to 217uA, but it's still too much. please, can you tell me which hardwaremodules you switch off? especialy the 3 V3-Pin (pine.6 from mega169). when i set this to logiclevel 0, the current is more than 18mA, only when i set it to logiclevel 1, there is minimum current. i think, that the hardware arround the atmega causes the current problem. i have an other board, with attiny84 und rfm12, and this board current consumption is 5,6uA in sleep. thank you, Jan
Posted on:
So, i solved the problem. now i have a current consumtption of 36uA with lcd. Jan
Posted on:
And i observed, that the new version of the hr20 (2.04) uses much less current than the older version. the same software runs on the new one with 15,6uA (instead the old one with 36uA) Jan
Posted on:
Hello, @Marco G. (stan) You posted on 2011-12-11 10:56 a part of a definition file. There is an #define MENUES_AUTOBROWSE 1 which I could not not find anywhere. Is this your own extension ? Does it automatically scanning the menue ? If it is so , would you like to publish your changes ? Ronny
Posted on:
Hi Ronny, yes it is my own extension, and yes, I wanted to browse through the temperatures and valve position automatically. But no, it does not work :( This is what I changed in menu.c, maybe you can check and correct it:
#if NO_AUTORETURN_FROM_ALT_MENUES && ! (((menu_state>=menu_home2) && (menu_state<=menu_home5)) || menu_state==menu_service_watch) #elif MENUES_AUTOBROWSE && 1) // (config.menues_autobrowse)) { if ((menu_state>=menu_home_no_alter) && (menu_state<=menu_home3)) menu_state++; if (menu_state==menu_home4) menu_state=menu_home; // return to main home screen ret=true; #else ) { menu_state=menu_home; // return to main home screen ret=true; #endif |