I have a RS232 to RS485 converter. It has a 25 pin female connection intended to connect to a RS232 serial port. It also has a terminal block that is used to feed it DC power, and also to connect to the 485 bus. The problem is that when using any RS-485 aware program (such as, but not limited to the open source Realterm), a zero byte is immediately returned. Nothing even has to be connected to the bus pins for this to happen. I however have a termination resistor connected. So for example if I transmit a 0x55, a 0x00 is immediately received. No matter what I transmit, no matter what the length, baud rate, 7 or 8 data bits, one 0x00 is immediately received once the transmission is complete. If I do have a MODBUS device connected to the bus line, the device correctly receives what the adapter transmits, only that the received response is preceded by a zero byte. I have tried the adapter on a different computer, with an older version of Windows, and it's the same thing. Is this a common thing? I called the maker of the adapter and he said he's never heard of this before. I have the A line biased to +5, and B biased to GND.
RS-485 is a 2-wire bus. All stations use this bus for sending and receiving. E.g. you have to switch between sending and receiving, otherwise you have collisions. Your software must control this. gk
>>RS-485 is a 2-wire bus. All stations use this bus for sending and >>receiving. E.g. you have to switch between sending and receiving, >>otherwise you have collisions. Your software must control this. >>gk I know. I'm using off the shelf software that is doing this.
A MODBUS slave uses the "driver output enable" pin of its RS485 transceiver to switch between sending and receiving. A MODBUS slave is in receiving mode nearly all the time, which is accomplihed by disabling its output enable. Only if the slave is allowed to send the corresponding output enable is activated and the tranceiver is sending. Do you control this pin of transceiver?? Without careful control of this pin you will suffer from bus collisions!
>A MODBUS slave uses the "driver output enable" pin of its RS485 >transceiver to switch between sending and receiving. >A MODBUS slave is in receiving mode nearly all the time, which is >accomplihed by disabling its output enable. Only if the slave is allowed >to send the corresponding output enable is activated and the tranceiver >is sending. >Do you control this pin of transceiver?? Without careful control of this >pin you will suffer from bus collisions! As I explained in the original post, this is occurring with a RS232 to RS485 converter connected to to a computer, the converter's power supply, and nothing else. There is nothing but a terminating resistor on the bus pins. I did have a slave connected previously, but to prove the slave wasn't causing it, I disconnected it.
>As I explained in the original post, this is occurring with a RS232 to >RS485 converter connected to to a computer, the converter's power >supply, and nothing else. This is no standard Modbus setup, so the results of your "experiment" make no sense. A standard Modbus slave must be able to receive and to send. How do you want achieve this with your simple RS232 to RS485 converter??
You likely need bias resistors on your RS485 line to pull the line to "inactive" state. Otherwise there might be a spike when your RS485 converter turns off its line driver, which might be interpreted as a start bit causing the extra zero to be recieved. See http://en.wikipedia.org/wiki/RS-485 for a simple circuit diagram. Basically add a 680 Ohm resistor from +5V to the RS485 positive line (mostly called A, but there is a standard calling the positive line B), and a 680 Ohm resistor from GND to the RS485 negative line (mostly called B). Regards Tassilo
>>As I explained in the original post, this is occurring with a RS232 to >>RS485 converter connected to to a computer, the converter's power >>supply, and nothing else. >This is no standard Modbus setup, so the results of your "experiment" >make no sense. A standard Modbus slave must be able to receive and to >send. How do you want achieve this with your simple RS232 to RS485 >converter?? Achieve what? As stated in my original post, the problem is that when I transmit something, even with no slave attached, the RS485-capable communications program (doesn't matter which one I use) immediately receives a single zero byte at the end of transmission. I can't blame a slave for this, because there isn't one. Had I left the slave connected, the question of course would immediately be "is the slave causing it?" The answer of course is no, because there isn't a slave, yet I still receive this phantom zero. Tassilo, At least you are understanding the issue. I have tried biasing the line as you describe, however it was with slave power. I may try to do that with master power.
>As stated in my original post, the problem is that when I transmit >something, even with no slave attached, the RS485-capable communications >program (doesn't matter which one I use) immediately receives a single >zero byte at the end of transmission. But you wrote this line as well: >If I do have a MODBUS device connected to the bus line, the device >correctly receives what the adapter transmits, only that the received >response is preceded by a zero byte. And I ask you again: How do you communicate with the slave, if you do not control the output enable pin in your RS485 transceivers??
>>As stated in my original post, the problem is that when I transmit >>something, even with no slave attached, the RS485-capable communications >>program (doesn't matter which one I use) immediately receives a single >>zero byte at the end of transmission. >But you wrote this line as well: >>If I do have a MODBUS device connected to the bus line, the device >>correctly receives what the adapter transmits, only that the received >>response is preceded by a zero byte. >And I ask you again: How do you communicate with the slave, if you do not control the output enable pin in your RS485 transceivers?? On the slave, I control the transmit and receive enables separately as required. When transmitting I enable the transmit driver, and when not transmitting, I disable the transmitter and enable the receiver. But the slave is not the issue. As for the RS232->RS485 converter, the RTS/CTS lines are controlled by whatever Windows program I'm using. I've tried: Realterm, which has a setting for RS485 modpoll.exe, a free program by FOCUS Software Engineering Pty Ltd Simply MODBUS 7.0 All three see this phantom zero immediately returned after transmitting something.
This is weird. I have seen a setup like yours working (RS232-RS485 converters on PC side with Eurotherm Modubus temp controllers). The only pitfall with MODBUS in such a setup is that it is necessary to send all data bytes of a MODBUS packet to the windows driver at the same time to ensure the maximum char-to-char time for a MODBUS frame is maintained. Things to try: Are you sure the polarity of the biasing resistors is correct? Keep in mind that sometimes the two RS485 lines are labeled A+/B- (common practice that A equals positive), whereas there is some ISO or IEC standard specifying A-/B+. Be aware that simple converters rely on the RTS line to switch at the end of a PC-side transmission. Your terminal programs should have taken care of that, though. To avoid the issues with the RTS-controlled line driver enable, I can recommend USB-RS485 converters with FTDI chipset, e.g. at http://www.ftdichip.com/Products/Cables/USBRS485.htm They have worked well for me. Regards Tassilo
Hi, I see this is an old topic, I do have the same problem I wonder how this was solved In my case communication works great when using RS232, but with Rs485 I get the leading zero as well. I have 2 little boards for my Arduino mega, one for RS232 and one for RS485 I attached a document where you can see that data over RS232 and over RS485 For RS485 I use the enable pin. At this time I only have one slave connected to my PC On my PC I have an KK systems USB to RS485 convertor (I have used these before in other applications) Any input will be helpful. best regards Wubbo
:
Edited by User
Wubbo, Check the rs485 biasing. http://www.avrfreaks.net/forum/modbus-checksum-errors http://www.ti.com/lit/an/slyt514/slyt514.pdf http://www.ni.com/support/serial/resinfo.htm Cheers, Tony
Hi Wubbo. I know this is an old post, but i am experiencing the exact same behaviour. I wonder if you has solved the problem? Thank you in advance.